Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1895 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 28
    • 29
    • 30
    • …
    • 95
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

AS-P Cloud Connectivity Issues

Issue The site has cloud connectivity issues, and R&D requires the trace log to see the communication. The trace logging for the cloud plugin (/System/Modules/Trace/Loggers/nsp/nsp.pin/nsp.pin.Cloud) has been enabled and set to Trace, and there are no records of nsp.pin.Cloud referenced within the trace log. Product Line EcoStruxure Building Advisor, EcoStruxure Building Operation Environment EcoStruxure Building Advisor EcoStruxure Building Operation v3.0.3 or earlier  Cloud Connectivity Cause In versions before 3.0.4, by default, the cloud plugin does not report on the trace log. Enabling trace log reporting for nsp.pin.Cloud is a high-level procedure that requires support intervention.     Resolution This version (3.0.4) and lower are now out of support, so it is recommended that to upgrade to a supported version. Cloud messages are now recorded in the trace when enabling the logging level to TRACE on the /System/Modules/Trace/Loggers/nsp/nsp.pin/nsp.pin.Cloud object. 
View full article
Commander JonGreen Commander
‎2021-11-19 01:21 PM

Last Updated: Picard RobertAndriolo Picard ‎2024-05-30 06:20 PM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
1639 Views

In a network with multiple Automation Servers, changing IP addresses don't always propagate properly throughout the network.

Issue The properties of any server, Enterprise Server or Automation Server, in SmartStruxure has a Communication tab that will list the IP addresses of all associated servers on the network. Changing the IP address of an AS requires every other AS to know about the change in order to preserve any server-to-server communication. In the example below, the system has been engineered in-house on a 10.10.x.x network domain. It was then moved to site where the domain of the ES and all AS were changed to 10.159.x.x. Viewing the Communication tab on the ES shows all IP addresses have been properly updated: However, if the DNS/IP Address column is viewed from the Communications tab of one of the Automation Servers, the results vary as to which IPs have been properly updated: Automation Server A Automation Server B Automation Server C If there is any communication between two Automation Servers, and the IP addresses have not properly updated, then communication between them will break. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause Any change to an Automation Server's IP address must be represented in the Enterprise Server (if there is one). It must also be updated in all associated Automation Servers. It is best practice following the change of any IP address on the system to perform a refresh of the addresses from the Enterprise Server. Note: This is also applicable in a network with Enterprise Central hosting Enterprise Servers. Resolution Right Click on the ES. Select Advanced>Repair Server Communication. Refer to: Repairing EcoStruxure BMS Server Communication
View full article
Picard Product_Support
‎2018-09-11 01:25 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-05-22 01:28 AM

Labels:
  • EcoStruxure Building Operation
1837 Views

How to identify what ports are being used on a PC

Issue How to identify what ports are being used on a PC. Product Line All product Lines. Environment Any Windows OS Cause Running multiple applications on the same PC without managing TCP/UDP port assignments can lead to conflicts. Resolution TCPView will help you identify all ports and services to each application. Download from Microsoft's website http://technet.microsoft.com/en-us/sysinternals/bb897437.aspx Detailed instructions are available at the site.
View full article
Picard Product_Support
‎2018-09-10 01:28 PM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-05-22 01:21 AM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
2252 Views

Can an Automation Server operate as a device on a third party BACnet MSTP network?

Issue Can an Automation Server operate as an MSTP device on a third party BACnet MSTP network? Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Want to connect an Automation Server to a 3rd party system as an MSTP device, is this supported? Resolution An Automation Server operating as a device on a third party BACnet MSTP network is NOT a supported solution. An MSTP network needs to be managed and usually accessed from a network master, the AS is designed to be that device. The Automation Server is supported as the management and routing device for an MSTP network. From the PIC statement, an Automation Server will operate as a MSTP Master.
View full article
Picard Product_Support
‎2018-09-06 09:32 AM

Last Updated: Administrator CraigEl Administrator ‎2024-05-22 08:22 PM

Labels:
  • EcoStruxure Building Operation
2050 Views

Difference in Expansion IO Port power consumption between i2 and b3 field devices

Issue Continuum i2 and b3 devices share the same hardware platform, however, power consumption on the devices IO Expansion Port differs depending on the communication protocol firmware (Infinet or BACnet) running in the device. Product Line Andover Continuum, EcoStruxure Building Operation Environment All i2 devices All b3 devices Cause Even though the hardware of an i2 device is identical to that of its counterpart b3 device, the difference in firmware causes variation in power consumption on the device's Expansion IO port, specifically, it has been observed that the b3 devices adhere more strictly to the 180 mA limit than the i2 devices, resulting in loss of operation on IO channels located on the Expansion Port if the power limit is exceeded.  Now that conversion of devices from one protocol to another is occurring in the field, it has become evident that there are cases where the 180 mA limit is exceeded in an i2 device without any negative results, but once the i2 device is converted to a b3 device, all IO on the expansion port stop working. Resolution Before converting an i2 device to a b3 device in the field, it is crucial to review the Expansion IO Datasheet (attached) to ensure that the configuration does not exceed the specified power consumption limit. If the configuration exceeds the 180 mA limit, take the following steps: Remove any additional xP module causing the limit to be exceeded. Reconfigure the xP modules to ensure that the configuration does not consume more than 180 mA.
View full article
Captain AbeMeran Captain
‎2024-05-02 07:14 PM

on ‎2024-05-02 07:14 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
20926 Views

Vista SmartStruxure Interface service not found

Issue Opening the Vista SmartStruxure Interface setup, found in the status box, message "service not found" is displayed. Product Line EcoStruxure Building Operation Environment TAC Vista server Vista SmartStruxure interface Cause Some dll may be missing causing the service could not start. Resolution Manually run the VistaInterface execution file. By default TACVistaSmartStuxureInterface.exe file is stored in C:\Program Files\Schneider Electric\TAC Vista SmartStruxure Interface 1.0.5. Double click on the TACVistaSmartStuxureInterface.exe file, if the service could not be started, it will pop out an error message window. If it is a dll file missing, can find the corresponding dll on the internet, and solve this issue. If the error message shows some other error, please make a copy of the error message and contact the local support team for further assistance.
View full article
Picard Product_Support
‎2018-09-11 06:53 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2024-04-30 12:05 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1760 Views

Replacing the screw terminals on an Automation Server

Issue Replacement screw terminals for an Automation Server (AS/AS-P) Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Cause The screw terminals are missing on an Automation Server Resolution The AS-P Screw Terminals are 5.08mm pitch and are available from RS Components:- 3 way plug part no. 189-6026 4 way plug part no. 189-6032 5 way plug part no. 189-6048 Or alternatively from  Farnell:- 3 way plug part no. MOLEX 39530-0003 4 way plug part no. MOLEX 39530-0004 5 way plug part no. MOLEX 39530-0005
View full article
Picard Product_Support
‎2018-09-11 04:33 AM

Last Updated: Sisko GavinHe Sisko ‎2024-04-29 02:10 AM

Labels:
  • EcoStruxure Building Operation
1640 Views

How to reset the backup to flash circuit breaker on i2/b3 devices

Issue After 2000 backups an attempt to perform a backup to flash results in the error 'Flash backup for this controller has been disabled.' Product Line EcoStruxure Building Operation, Andover Continuum Environment b3 controller i2 controller Cause Flash memory has a limited write count; Controllers implement a flash circuit breaker that trips after 2000 backup operations in order to protect the flash device from damage. Resolution (Applies to all b3 and i2 controllers) EcoStruxure Building Operation In EBO, a command has been added that will re-enable backup to flash after the circuit breaker has been tripped (2000 backups) From Workstation, in the object tree, right-click the i2/b3 device. From the context menu select, DEVICE->ENABLE BACKUP TO FLASH     Andover Continuum From CyberStation command line set the ACCStatusBackup system variable of the device to ACCBackupEnable. NOTE: The flash circuit breaker CANNOT be reset from Script/Plain English.  This is by design as it was deemed too risky to allow resetting it programmatically.  A poorly written program could very quickly cause damage to the flash device.
View full article
Picard Product_Support
‎2020-09-22 09:25 AM

Last Updated: Sisko GavinHe Sisko ‎2024-04-25 02:42 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
7244 Views

Conversion of b4920 to b3920 in the field

Warning Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices. Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. One way conversion: Conversion of b4920 to b3920 is not reversible, once the b4920 controller has been converted to b3920 device, it cannot be converted back to b4920. Issue A b3920 device has failed in the field and the only available replacement at hand is a b4920 Product Line Andover Continuum, EcoStruxure Building Operation Environment Continuum b4920 Cause The b4920 is a Continuum BACnet router its hardware is almost identical to that of the b3920 device, the only difference is the Ethernet port in the b4920, which is not populated in the b3920. When a b3920 must be replaced, and the only available replacement is a b4920, use the steps outlined in this article to convert the b4920 to a b3920. Resolution Before starting the procedure, you need the following items: The b4920 device to be converted. The serial number of the b4920 device to be converted. Continuum Cyberstation with b4920 to be converted, configured, and online. (***) A RoamIO2 and BACnet Service Tool A special firmware b4920 application upgrade file provided by Product Support A b3920 bootloader file provided by Product Support Steps to convert b4920 into b3920 Contact Product Support and request the b4920 to b3920 conversion files. You will be provided with an application file (e.g. b4920toB3920B4.500077.upd) and a boot loader file (e.g. B3920BootB4.500077.upd). From Continuum Workstation, take note of the baud rate of the MSTP operating under the b4920 (In Comm1 settings) From Continuum Cyberstation, edit the b4920 controller object and take note of the BACnet Device ID and the controller Serial Number, typically they will be the same but this is not always the case. In the "General" tab, click 'Update OS' and send the Application file provided by PSS. Please note that once the application file has been sent and the controller re-starts, its MSTP will shut down and RoamIO2 is required to re-start the MSTP for operation as a b3920, the reason for this is Continuum uses mac id 0 (zero) for router controllers such as the b4920 and the bCX4040, in Continuum, b3 devices are not allowed to use mac id 0. Disconnect the Ethernet cable from the b4920, the Ethernet port is now unusable. Connect the RoamIO2 directly to the b4920's Service Port then cycle power to the b4920. Start the BACnet Service Tool In the BACnet Service Tool, de-select View by networks, then click the connect icon, the conversion from b4940 to a b3920 causes the now b3920 device to come up with an unknown baud rate and an invalid (for b3s) mac id 0, so now need to find out the baud rate the converted b3920 is using From the "View" menu, select "RoamIO2 Properties and take note of the MAC ID the RoamIO2 is using   From the 'Tools' menu, select 'Set b3 baud rate' and set it to Baud9600, and click apply    From the 'Tools' menu, select 'Set offline b3 MAC id' and enter the serial number of the device and a valid MAC ID ( DO NOT ENTER ZERO NOR THE MAC ID IN USE BY ROAMIO2), then click on 'Apply'   If you get the message below, repeat the steps above for the next baud rate... when you have found the correct baud, you will see the message below after setting the MAC ID   Once the baud and MAC id have been set successfully, the device will automatically pop up in the tree, but it will only be partially online, to bring the device fully online, click the red disconnect icon on the BACnet Service Tool to disconnect from the device, wait about 30 seconds then  click the now green connect icon to reconnect the BACnet Service Tool to the device Right-click on the device, then select 'Update OS' and send it the appropriate boot loader file provided by Product Support Once the uprev of the boot loader has completed, click 'Done' button to dismiss, select the device, right-click and select 'Cold start device', and click 'Yes' on the confirmation window   You should now be able to commission the converted device as a b3920, either as a new device or as a replacement device, following the steps for replacing a b3 device. (those steps are not in the scope of this procedure) *** b4920 controllers are not easily defaulted to factory settings. If one gets an old b4920 from the shelf, use the steps below to find out the controller's current IP address and ACCNetId which are needed to put the controller online in Continuum. IP ADDRESS Upon start-up the b4920 sends a gratuitous ARP, use Wireshark to connect directly to b4920 controller using a crossover Ethernet cable, restart the controller, and inspect the gratuitous ARP to determine the IP address configured in the b4920 ACCNetID Once you have the IP address, use the attached utility tool to discover the ACCNetID of the b4920. Unzip the attached file and use the Windows Command Line to execute FindEnodeID.exe as seen below  
View full article
Captain AbeMeran Captain
‎2024-04-19 10:56 AM

Last Updated: Administrator CraigEl Administrator ‎2024-04-28 10:03 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
5243 Views

"Unable to display events" error message in Schedule in Workstation

Issue Error message "Unable to display events. To view or change, go to Text view on the Advanced tab." in a Schedule in Workstation. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause The error message appears when attempting to view events with a duration of five minutes or less in the graphic view of Schedules in Workstation. Additionally, the message can also occur when the time between two events is five minutes or less.  The screenshot below shows an event with a duration of four minutes that causes the error message to be displayed. Resolution Two potential solutions are available to address this issue: Utilize Webstation: Webstation does not have the same limitations as Workstation. Users can leverage Webstation to view and edit events with a duration of five minutes or less, or where an event starts five minutes or less after another event ends. Switch to Text View: As indicated in the error message, users can switch to the Text view on the Advanced tab to list short-duration events. To do this, navigate to the Advanced tab (1), then click on the Text view button (2) to switch to text view.
View full article
Janeway PeterEdvik Janeway
‎2024-04-28 09:56 PM

on ‎2024-04-28 09:56 PM

Labels:
  • EcoStruxure Building Operation
3791 Views

When an Enterprise Central (EC) is connected to two External Log Storage systems, how does it determine which one to contact for accessing trend logs?

Issue An Enterprise Central has two Enterprise Servers, both connected to External Log storage as pictured below. How can the EC access trend logs in both External Log storage locations when it is only connected to one of them? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Central Building Operation Enterprise Server Building Operation Automation Server Premium (AS-P) Cause It is only possible to specify a connection to one External Log storage location in the EC Resolution When a user needs to access trend data from a specific log located in, for example, an AS-P while the Workstation is connected to the EC, the following process occurs: The EC contacts the specified External Log storage for the log data using the trend log ID. If the trend log ID is not found in the specified External Log storage, the EC then contacts the Enterprise Server (ES) associated with the AS-P to request the log data. The ES connects to the External Log storage specified within it and retrieves the log data using the trend log ID. The ES delivers the log data to the EC, which in turn delivers it to the Workstation for access. This process ensures that the EC effectively manages connectivity to External Log storage systems and retrieves the required trend data for users.
View full article
Janeway Jonas_Brissman Janeway
‎2024-04-28 09:40 PM

on ‎2024-04-28 09:40 PM

Labels:
  • EcoStruxure Building Operation
3101 Views

Capture BACnet MSTP Traffic with Tshark

Issue When using mstpcap.exe to capture, it automatically stops after 65535 packets. Similarly, when using Wireshark, it will stop capturing if the dissector encounters an issue. This article provides a solution to continuously capture BACnet MS/TP traffic in a ring buffer and store it as files. Product Line Andover Continuum, EcoStruxure Building Operation, TAC IA Series Environment Wireshark Any BACnet MSTP RS-485 network Cause Analyze BACnet traffic via capture files. Resolution Install Wireshark. Ensure TShark is checked when installing options.  Ensure Wireshark is installed with Npcap (default) or WinPCap has been installed by IA Series Workplace Tech. Install mstpcap.exe referencing BACnet MSTP Capture Application. Ensure that mstpcap.exe has been configured for the correct port and baud rate. Here is an example for Command Prompt and PowerShell: # Command Prompt cd "C:\Program Files\Wireshark\extcap" mstpcap.exe com3 38400 # PowerShell cd 'C:\Program Files\Wireshark\extcap' ./mstpcap.exe com3 38400 Run Tshark to determine the interface being used by mstpcap so that one can reference it by number. For this example, we are going to choose 9. COM3 (BACnet MS/TP on COM3). Please change the number below to the number of your interface.  Start Tshark capture by entering the following command, updating as needed. The commands below save Test01.pcap to the Username's desktop. Please store to a location that the user has access to write.  # Command Prompt cd "C:\Program Files\Wireshark" tshark.exe -i 9 -b duration:3600 -b files:72 -w "C:\Users\Username\Desktop\Desktop\Test01.pcap​"​ # PowerShell cd 'C:\Program Files\Wireshark' ./tshark.exe -i 9 -b duration:3600 -b files:72 -w 'C:\Users\Username\Desktop\Desktop\Test01.pcap​' Note: Change  -i 9  to the number of the interface on the capturing machine. Change  -b duration  to time in seconds (3600 is one hour). Change  -b files  to the number of files to cycle through (72 is 3 days of 1-hour captures, 3x24). Change  -w  to write to the location and filename you choose. Change  \Username\  to your Windows User, if you want to save to that user's Desktop Reference: tshark(1) Manual Page (wireshark.org)
View full article
Picard David_Purser Picard
‎2024-04-24 05:43 AM

on ‎2024-04-24 05:43 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC IA Series
5989 Views

Galvanic isolation for SHD2/SCD2

Issue Does SHD2/SCD2 have galvanic isolation? Product Line EcoStruxure Building Operation Environment Building Operation SmartX Living Space Sensor Cause Galvanic isolation is a principle of isolating functional sections of electrical systems to prevent current flow; no direct conduction path is permitted. Resolution The SHD2XP2A/SCD2XPXAVX does not have galvanic isolation.
View full article
Guinan MikaelKrantz Guinan
‎2024-04-24 04:18 AM

Last Updated: Janeway PeterEdvik Janeway ‎2024-04-24 04:19 AM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
3358 Views

Long delay in Graphic that displays values read from remote server over EWS

Issue ES is connected to a remote server via EWS; when loading a graphic in a web browser or workstation, the values take a long time to read. (a few minutes.) It makes no difference what the settings for polling are configured for. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Cause Every time the graphic is brought up, the ES needs to subscribe to all values from the external EWS server, this is the cause of the delay. Resolution Workaround Solution: Maintaining Active Subscriptions The recommended workaround solution involves maintaining active subscriptions. This can be achieved through the following methods: Persistent Graphic Display: Always keep the graphic displayed on a client. This is crucial as the subscriptions are terminated when the graphic object is closed. By keeping the graphic open, the subscriptions remain active. Watch View Creation: Create a watch view that includes the values displayed in the graphic. This ensures that the values are constantly monitored and updated. As long as a client subscribes to these values, the update process will be expedited when the graphic is launched. This is because the subscriptions remain active, and the values do not need to be re-initialized. However, if there are no active subscriptions to the values, all values must be set up each time the graphic is opened. This can potentially slow down the process. Therefore, maintaining active subscriptions is highly recommended for efficient operation.
View full article
Captain AbeMeran Captain
‎2024-04-19 11:02 AM

Last Updated: Picard David_Purser Picard ‎2024-04-19 11:05 AM

Labels:
  • EcoStruxure Building Operation
3509 Views

Unable to create new dates and new values in Webstation Calendar

  Issue The WebStation menu used to create new calendar dates and values is not visible. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Webstation Building Operation Enterprise Server Cause The panel used to display the calendar schedule is incorrectly configured Resolution In Workstation, right-click on Panel and go to Properties, go to Show Toolbars, and choose Yes.    Now when you log in to Webstation, you will see the toolbar including the menu on the top of the calendar in the panel.     
View full article
Lt. Commander Ramaaly Lt. Commander
‎2024-04-16 09:48 AM

Last Updated: Administrator CraigEl Administrator ‎2024-04-16 04:45 PM

Labels:
  • EcoStruxure Building Operation
3892 Views

Container Servers create same Instance ID for BACnet interface

Issue When the BACnet Interface is created in Container Servers, the automatically generated Device Object ID aka Instance ID can be the same as another Container Server on the same container host. Product Line EcoStruxure Building Operation Environment Building Operation Edge Server Building Operation Enterprise Server for Linux Cause The algorithm used to pick BACnet Interface Device IDs in individual Automation Servers does not work for Container Servers since they share the same ethernet connection,. Resolution Perform tasks to ensure Instance IDs are unique. One can prevent the issue by ensuring uniqueness when adding the BACnet Interface  When adding Interface -> BACnet Interface, do NOT click Create or Create and Edit, but click Edit in Wizard.  Enter the following data BACnet Name Instance ID (ensuring unique ID to the entire BACnet system) Leave Network Type = IP network Network ID (this should be the same network ID as the IP network is attaching)  One can repair the issue and ensure uniqueness after creating the BACnet Interface. Changing the BACnet Device ID in an Automation Server to configure unique ID Repair Hosting a BACnet controller and IO Module  Fixing References in BACnet/IP Controllers 
View full article
Picard David_Purser Picard
‎2024-04-08 10:08 AM

on ‎2024-04-08 10:08 AM

Labels:
  • EcoStruxure Building Operation
5281 Views

Energy Expert Compatibility Matrix

Issue There is a need for a single Compatibility Matrix that shows EBO, PME, Energy Expert and relevant software versions all in the same location.   Product Line EcoStruxure Building Operation, Other   Environment EcoStruxure Energy Expert (formerly Power Manager) ETL tool Cause Energy Expert version compatibility information is currently available but is stored in many different places such as release notes and online documentation, rather than one single matrix.   Resolution The full ETL for EBO compatibility matrix is shown in the following table. Energy Expert  PME EBO ETL Integration Utility .NET Framework Power Manager 1.0 7.2.3 1.6.1 3 1.0.14304.2 4.5 Power Manager 1.1 8 1.6.1  1.7.1 4.1 1.0.15306.1 4.5 Power Manager 1.2 8.1 1.6.1  1.7.1  1.8.1 4.3 2.1.16081.1 4.6 Power Manager 1.3 8.2 1.8.1 1.9.x  4.6 2.2.17056.2 4.6 Energy expert 2.0 9 2 5 3.0.18215.3 4.6 Energy expert 3.0 2020 3.0 3.1 6 3.1.19319.1 4.6 Not commercialized  - (n/a) 2021 3.2.3 6 Integrated - (n/a) 4.8 Not commercialised - (n/a) 2022 4.0.2/2022 6 Integrated - (n/a) 4.8 Not commercialised - (n/a) 2023 5.0/2023 6 Integrated - (n/a) 4.8   Great care must be taken when choosing the correct version of ETL to use when integrating Energy Expert and EBO, as there are actually two families of ETL in production.  One ETL designed and tested for PME use only and ETL for EBO designed and tested with an EBO Extract Task specifically for integrating the two systems.  (For example, a version of ETL 4.7 exists, but this is not ETL for EBO and therefore does NOT contain an EBO Extract Task, even though it is a valid version of ETL for the Power Community) New PME 2023 now offers EWS Client 1.2 which can be used to transfer data from EBO to PME instead of ETL.  The merits for and against using this new EWS Client rather than ETL are discussed at length in the PME 2023 System Guide
View full article
Lieutenant JG Robert_Davis Lieutenant JG
‎2020-12-29 10:10 AM

Last Updated: Admiral David_Kendrick Admiral ‎2024-04-04 04:17 AM

Labels:
  • EcoStruxure Building Operation
5394 Views

ES upgrade from 3.2.3.59 to 5.0.3.117 is failing

  Issue Performing an Enterprise Server upgrade preview from 3.2.3.59 to 5.0.3.117, the upgrade fails with the error "INET legacy interface no longer supported." message      Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Cause An existing folder in the Enterprise Server contained graphics underneath the INET interface. This folder was moved within the system, and the INET interface was deleted. However, the moved folder still had links to the INET interface, causing the upgrade to fail since this interface is not supported in Building Operation 2022 (v.4) and above.  Resolution Delete any references in the database linked to the INET Interface. Bindings Diagnostics provides a quick method for locating these unresolved references.   After deleting these objects and/or references, the upgrade will completed successfully.
View full article
Lt. Commander Ramaaly Lt. Commander
‎2024-03-27 01:17 PM

Last Updated: Picard RobertAndriolo Picard ‎2024-03-27 04:14 PM

Labels:
  • EcoStruxure Building Operation
4397 Views

How to Mass Create Trend Logs and Extended Trend Logs

Issue How to Mass Create Trend Logs and Extended Trend Logs Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause If you did not create Trend Logs at the same time as you created the points or values, it is possible to create several trend logs or extended trend logs at the same time. Resolution For this example, we assume all of the values are in the same folder. You can hold down SHIFT to select multiple adjacent objects, or CTRL+click to select non-adjacent values Mass Creation of Interval Trend Logs Select all of the Values you wish to add the same type of Log to Right Click and select New connected object>Trend Select the Log type and the settings you wish to use.  Note that the log name will be the values name with either a prefix or suffix defined by the user Be sure to Select a useful folder location, either same folder as each selected object, a different folder, relative to the selected object or a single folder for all created objects. Click Edit in wizard. Set the Interval Settings, if iterval log type is selected. Click Next, configure initial meter settings if required, click next tehn click create Mass Creation of Extended Trend Logs if required Select the group of Logs you wish to create Extended Trend Logs for Right Click and select New connected object>Extended Trend Log Enter the desired settings. Just as above, the Extended log will use the Log' name plus either a prefix or suffix Be sure to Enter an appropriate Location. Use a folder on the ES if you wish these logs to show up on the Reports Server (Report server is not supported in EBO 2022 and higher). Click Edit in Wizard, Configure the Extended Log as desired, then click create. Fore more information, refer to: Mass Creating Trend Logs and Mass Creating Extended Trend Logs
View full article
Picard Product_Support
‎2018-09-07 05:13 AM

Last Updated: Spock PeterLarsen Spock ‎2024-03-25 10:38 PM

Labels:
  • EcoStruxure Building Operation
3539 Views

EBO 5.0 Alarm attachment will display a PDF file instead of TGML graphic when alarm is enabled

  Issue The customer has created an alarm, this alarm has an Attachment that displays a Graphic (Display on Alarm enabled). All the remote Workstations at this site show the graphic popup on alarm, except a single Workstation. That Workstation will display PDF Files 'On alarm', but not TGML graphics. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Building Operation Workstation Cause Either, they at the same time had two monitors and placed the graphic attachment on the other monitor, and then the position was saved. Or by mistake managed to move the attachment out of the current monitor scope Resolution Remove WorkStation cache from both (User + Program data) :  User: C:\Users\*user-name*\AppData\Roaming\Schneider Electric EcoStruxure\Building Operation\WorkStation  Program data: C:\ProgramData\Schneider Electric EcoStruxure\Building Operation\WorkStation The alarm will now display the TGML graphic attachment
View full article
Lt. Commander Ramaaly Lt. Commander
‎2024-03-27 01:14 PM

on ‎2024-03-27 01:14 PM

Labels:
  • EcoStruxure Building Operation
6676 Views
  • « Previous
    • 1
    • …
    • 28
    • 29
    • 30
    • …
    • 95
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore