Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,852
  • TAC IA Series 1,825
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 10
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1849 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 28
    • 29
    • 30
    • …
    • 93
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Audible alarms not sounding when there are active alarms

Issue Audible alarms not sounding when there are active alarms. Workspace has multiple tabs for graphics navigation and a tab for Alarm View. If a user is not on the alarm tab when an alarm is activated, the audible alarm is not heard, and the user does not know that an alarm has been activated. The audible alarm works when the user navigates to the alarm tab.  Product Line EcoStruxure Building Operation Environment Building Operation WorkStation Building Operation WebStation Cause The Workspace content does not have an Alarm Pane added.  Resolution Edit the Workspace to add an Alarm Pane to the Workspace content. If the user does not wish to display the Alarm View due to screen space etc., configure the Alarm Pane Default visibility to Hidden.  Note: Audible alarms are available in WebStation from 3.2 onward.
View full article
Picard Product_Support
‎2018-09-06 07:36 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-21 06:43 PM

Labels:
  • EcoStruxure Building Operation
1762 Views

Collect logs from the Enterprise Server and Enterprise Central

Issue When troubleshooting server issues, it can be helpful to look at the logs that are recorded within the Enterprise Server or Enterprise Central Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Cause Within the Enterprise Server and Enterprise Central logs are many records that are logged as a part of normal operations and unexpected events. Resolution Collect ES and EC Logs via EBO Workstation: Refer to the Workstation section of KB article: Collect logs from an Automation Server Collect ES and EC Logs via Windows Explorer, especially if ES or EC will not run as a service or keep crashing: The ES or EC database path is listed in Software Administrator.   For Windows 7, Server 2008, or higher, the default paths for the logs folder are: Enterprise Server: C:\ProgramData\Schneider Electric [EcoStruxure|StruxureWare]\Building Operation [n.n]\Enterprise Server\db\logs Enterprise Central: C:\ProgramData\Schneider Electric EcoStruxure\Building Operation [n.n]\Enterprise Central\db\logs In EBO V3.2 or higher, shortcut buttons can be found in Software Administrator to go to the folder for logs and database directly.    By default, the "Program Data" folder is hidden, so Windows needs to be configured to view hidden files and folders. For Windows 10 or 11, open Windows Explorer and select View > Show > Hidden items. For other Windows versions, please refer to this Microsoft help article: Show hidden files (microsoft.com). Using Windows Explorer, Navigate to the ES or EC logs folder to find System and Trace logs. Copy the Logs folder contents and send them to Product Support as a compressed file if required. To open a log file, Right-click on one of the logs and select Open with... Expand the window and select WordPad. For Windows XP:   Other ways to review site-specific issues: Is the issue site-specific regarding workstation being used or applications/programs running on these machines? Always try to keep the programs on a workstation to a minimum. Review the Windows Event Logs. What specifically happens when an error occurs? Follow this KB article to view and save the Windows Events: Viewing, Saving, Sharing Windows Event Logs for Troubleshooting Purposes - Communities Make sure that PCs and Windows OS used for WorkStation, ES or EC meet the requirements mentioned in Information Technology System Planning Guide (se.com) Make sure that the firewall and antivirus are correctly configured, and required ports are open for EBO, as explained in Information Technology System Planning Guide (se.com) Make sure that the current installed EBO version is supported, as per the Software Support Policy for EcoStruxure Building Operation - PA-00300. Check if Microsoft currently supports the installed Windows OS: Lifecycle FAQ - Windows | Microsoft Docs
View full article
Picard Product_Support
‎2018-09-06 03:56 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2022-08-21 06:41 PM

Labels:
  • EcoStruxure Building Operation
4964 Views

Xenta Servers support in StruxureWare Building Operations

Issue Are Xenta Servers supported in StruxureWare Building Operations? Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Xenta 701, 711, 721, 731, 511, 527, 555 Cause Want to use Xenta Server as a controller in StruxureWare Building Operations. Resolution No there are no special support for Xenta servers. But you can add them as normal LonWorks devices. You can only read/write SNVTs from the Xenta server. Normal Lon rules applies here, you can have a maximum of 64 nodes to a segment (we recommend to keep it under that). TAC Xenta Server I/O modules will not be seen in StruxureWare Building Operation, but they will count towards the 64 nodes on the segment. See Maximum number using StruxureWare Building Operation (Scalability and Capacity) for more information on Lonworks units in StruxureWare Building Operation.  
View full article
Picard Product_Support
‎2018-09-10 12:06 PM

Last Updated: Janeway Jonas_Brissman Janeway ‎2022-08-12 01:47 AM

Labels:
  • EcoStruxure Building Operation
2054 Views

TAC Xenta Server conversion to EcoStruxure Building Operation (EBO)

Issue In the Xenta Servers, it is possible to set the communication port to RS232 or RS485. In EBO this is not possible on the Automation Server (AS) Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Building Operation Automation Server  Xenta 500 Xenta 700 Xenta 900 Cause The AS serial ports are RS-485, not RS-232. Resolution There are two solutions to consider when Xenta is using an RS-232 connection: If the connected device also has a RS-485 connection switch to that. (Optionally replace the device with one that has RS-485.) Use a RS-232/RS-485 converter. The converter must have automatic data direction detection and control on the RS-485 side, since our Automation Server devices have no RTS signal (to enable the transmitter) available externally.
View full article
Picard Product_Support
‎2018-09-06 07:40 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2022-08-12 02:00 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
2198 Views

Unable to commission Xenta 913 in EcoStruxure Building Operation

Issue If a Xenta 913 with SNVT(s) is added as a Lon device to an Automation Server Lonworks network the commission process fails in the last step with error 0 Product Line EcoStruxure Building Operation Environment Building Operation Automation Server TAC Xenta 913 TAC Xenta 700 Cause This is a bug in the Xenta Server firmware. Resolution This issue will be fixed in Xenta 913 firmware version 5.1.9, however  hotfixes have been made for 5.1.8 and can be requested from PSS (TACXenta913-5.1.8.15 and TACXenta700-5.1.8.47). Note: All data will be lost in the Xenta Server when applying the hotfix.
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2022-08-12 02:21 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
2055 Views

Enable incoming HTTP communication option is grayed out

Issue "Enable incoming http communication" option is grayed out and cannot be unselected. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause When Building Operation Workstation is connected to the SmartX Server using a HTTP connection, the option to disable incoming HTTP connection is unavailable.     Resolution Use HTTPS in Building Operation Workstation to connect to the SmartX Server to allow this option to be unselected. Refer to the Online Help Topic: Disabling Incoming HTTP Communication
View full article
Admiral RyanSuar Admiral
‎2019-02-20 02:23 PM

Last Updated: Lt. Commander Reza Lt. Commander ‎2022-08-19 01:00 PM

Labels:
  • EcoStruxure Building Operation
1478 Views

Changing the Automation Server HTTP / HTTPS ports

Issue Changing the Automation Server HTTP / HTTPS ports, 1.3 or higher. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause There is a need to change the Automation Server's HTTP and/or HTTPS ports from the default ports of 80 (HTTP) and 443 (HTTPS). Resolution The HTTP / HTTPS ports of the Automation Server can be changed from Struxureware/EcoStruxure Building Operation WebStation, requires SBO/EBO V1.3 or higher.  From a web browser*, connect and log on to the Automation Server. After you have logged on, click on the 'Account menu' near the top right corner: EBO 4.0.3 or higher,  From the "Options" select 'Setting'. From the network tab, you can change the HTTP / HTTPS ports.    EBO V4.0.2 or lower, From the "Options" select 'Device Configuration'.   The TCP/IP configuration page should appear. From here, you can change the HTTP / HTTPS ports.       3. Perform a Warm Start on the Automation Server to apply the HTTP / HTTPS port changes to the server.     * Check supported web browsers for Struxureware/EcoStruxure Building Operation at the WebStation specification sheet, make sure to select the correct SBO/EBO version: WebStation (se.com)     Firefox 4 or later (32-bit)
View full article
Picard Product_Support
‎2018-09-10 11:30 PM

Last Updated: Lt. Commander Reza Lt. Commander ‎2022-08-19 10:41 AM

Labels:
  • EcoStruxure Building Operation
4977 Views

Only receive one Email notification per alarm

Issue An alarm goes on and off several times in a short amount of time. Each time the alarm condition clears and reasserts itself, by default, another email will be sent. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation SMTP alarms Cause Every time an alarm goes off, the email notification checks its parameter and, if true, sends an email. Resolution Filter the email notification by "count." Set it to "from 0 to 1" and you will only get a email on the first alarm (count).
View full article
Picard Product_Support
‎2018-09-06 09:30 AM

Last Updated: Captain SharlinaRe Captain ‎2022-08-19 07:54 AM

Labels:
  • EcoStruxure Building Operation
1677 Views

Items not displayed in the workstation system or binding tree

Issue Various items are not being displayed in the system tree or the binding tree of EcoStruxure Building Operation Workstation. When navigating through the tree, items such as folders or parameters may be missing. Product Line EcoStruxure Building Operation Environment Workstation System tree Cause If items are missing in the system tree or the binding browse tree then the filter settings are not set up correctly. Resolution If the expand icon next to a folder is missing or items are missing from the system tree, follow the steps below.     If the expand icon next to a folder is missing or items are missing from the system tree, make sure that the funnel icon is not clicked or activated (Show/Hide non-presentation objects)     If points are missing in the bindings browse window, make sure the funnel in the top left corner of that window is not clicked or activated (Hide parameters)
View full article
Picard Product_Support
‎2018-09-11 12:54 AM

Last Updated: Captain SharlinaRe Captain ‎2022-08-19 07:54 AM

Labels:
  • EcoStruxure Building Operation
1922 Views

EBO Server backup process fails

Issue Unable to back up the Automation Server Unable to retrieve a working backup from an Automation Server Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Automation Server Premium Building Operation Enterprise Server Building Operation Enterprise Central Cause Corrupt configuration.db Network environment issues Power failure Resolution Database Corruption When the server backup process is initiated, the server tests the integrity of the configuration.db.  If the database does not pass the integrity test, the backup process is terminated, and no resulting backup is produced. In this case, an older backup will need to be used.  The backup should be bench tested for integrity before restoring to the production server.   Network Environment In some cases, the AS may produce a valid backup file, but when the backup is saved off of the server the file size is unusually small.  This can happen when network issues interfere with the backup save to disk process.   In such cases, Automation Server backups taken from the Enterprise server will usually be damaged as well.    You can work around this problem by connecting a Workstation laptop PC directly to the AS with an ethernet cable, thus eliminating the network from the process. Backups can also be retrieved in this way using most versions of Device Administrator.    Power Failure The power fails while the EcoStruxure BMS server is backing up and the system displays a “Failed backup” message in the Event view. The solution is to initiate a new backup when the power resumes and the EcoStruxure BMS server goes back online. Power Failure Occurs During Backup     
View full article
JohnBoehmer Schneider Alumni (Retired)
‎2022-02-09 08:58 AM

Last Updated: Lt. Commander Reza Lt. Commander ‎2022-08-19 06:20 AM

Labels:
  • EcoStruxure Building Operation
2227 Views

License Violation alarm in EBO

Issue A license violation alarm is shown in the alarm viewer even though the system has all licenses necessary. The alarm returns to normal without any action from the operator. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause The Enterprise Server / Central contacts the License Server installed on the computer to determine what licenses are available. The License Server will then contact the "Trusted Storage" on the computer which is created when activating the licenses and ask how many licenses are available. The issue comes when the "Trusted Storage" creates some metadata once a day.  The metadata is a file created showing which licenses are used at that moment.  This is not currently used but could be by a third-party client who is interested in the license information for the system.  When the "Trusted Storage" creates the metadata it will be busy and not answer the License Server.  This is when the license violation alarm will be activated.  The alarm will return to normal after the "Trusted Storage" has finished creating the metadata. Resolution An investigation is ongoing. This issue has been fixed in EBO 2022. Please refer to License Violation Alarm 
View full article
Janeway Jonas_Brissman Janeway
‎2019-11-19 11:59 AM

Last Updated: Lt. Commander Reza Lt. Commander ‎2022-08-15 08:43 AM

Labels:
  • EcoStruxure Building Operation
4164 Views

b3 or i2 PE Script program not working

Issue PE Script program created in b3 or i2 has no error but its not executing. Product Line EcoStruxure Building Operation Environment Infinet i1, I2 BACnet b3 Automation Server, AS, ASP, ASB Cause Program compilation was not valid. Resolution Examine the code and determine what is causing the compilation issue. Known causes... 1. Variable declared in the code but not used (unbound)
View full article
Picard Product_Support
‎2018-09-11 07:57 AM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2022-08-16 03:55 AM

Labels:
  • EcoStruxure Building Operation
1399 Views

Compilation error when binding to priority array in b3 Script program

Issue Unable to compile a b3 Script program if there is a bind to the priority array of a commandable property. How to command an object at a particular priority in b3 Script program. Product Line EcoStruxure Building Operation Environment b3 WorkStation Automation Server Cause Because of historical reasons (that are outside the scope of this article) in the evolution of the b3 firmware, binding to the priority array of an object within a Script program in the b3 is NOT supported. Resolution To command an object from a Script program in the b3 at a specific priority the WriteProperty command MUST be used. NOTE If the b3 firmware is 4.500064 then priority 10 will always be set rather than the one specified in the WriteProperty command. This was fixed in v4.500076, it is best to use the the latest firmware
View full article
Picard Product_Support
‎2018-09-11 11:18 AM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2022-08-16 04:00 AM

Labels:
  • EcoStruxure Building Operation
1796 Views

Unable to access ES or AS after setting a new Domain as the default domain

Issue Unable to access ES or AS after setting a new Domain as the default domain Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium (AS-P) Cause If you set a domain as a default domain before logging in through that domain, it is possible that you do not have users set up and therefore will be locked out of the system. Resolution Open Building Operation Workstation Enter a Username and password for the Local domain or another previously functional domain Set the Domain as "Local", please note that this is case sensitive. Select the correct Server Log in Change the default domain back to Local until you have successfully logged in using the new domain.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 08:09 PM

Labels:
  • EcoStruxure Building Operation
1741 Views

10k Thermistor compatibility with Xenta controllers

Issue Certain Xenta controllers and I/O modules can accept 10k thermistor temperature inputs. Product Line EcoStruxure Building Operation,TAC Vista Environment Xenta 102-AX Xenta 420A, Xenta 450A Cause The Xenta 102-AX has always used 10k thermistors. Now some of the I/O modules and programmable controllers also have an option for 10k thermistor inputs. A common question is -- what type of 10k thermistors? Type 2? Type 3? Resolution The reason there is no reference to 10k Type 2 or 10k Type 3 is because these are Continuum-specific terms. The 10k thermistor that is compatible with Xenta 42XA and 45XA I/O modules are the same that I/NET uses. They are Vishay Dale Curve #1. View this PDF for the Resistance vs. Temperature Conversion Tables for this thermistor.
View full article
Picard Product_Support
‎2018-09-07 03:41 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 08:03 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
2804 Views

Failed to import backup set file.

Issue Backup set file cannot be imported.   Product Line EcoStruxure Building Operation Environment Building Operation Workstation Automation Server Enterprise Server Backup set file Cause Backup set file is very large so import of backup set file fails.   Resolution A current workaround is to manually copy the backup file set to the default backup location. Browse to C:\ProgramData\Schneider Electric StruxureWare\Building Operation 1.x\Enterprise Server\db_backup or C:\ProgramData\Schneider Electric EcoStruxure\Building Operation x.x\Enterprise Server\db_backup By default the ProgramData folder is hidden. To view the ProgramData folder follow the below steps: Select Organize>>Folder and Search options. In Folder options under view tab select "Show hidden files,folders and drives". Manually copy the Enterprise Server Backup set file and paste to the below location: C:\ProgramData\Schneider Electric StruxureWare\Building Operation 1.x\Enterprise Server\db_backup\LocalBackup   Manually copy the Automation Server Backup set file and paste to the below location: C:\ProgramData\Schneider Electric StruxureWare\Building Operation 1.x\Enterprise Server\db_backup\ASArchives
View full article
Picard Product_Support
‎2018-09-07 08:45 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 08:01 PM

Labels:
  • EcoStruxure Building Operation
2713 Views

.NET Framework errors in general

Issue When launching a program or when working with a program, you get an error from "Microsoft .NET Framework".   Product Line EcoStruxure Building Operation, Satchwell MicroNet, TAC INET, TAC Vista Environment Windows .NET Framework Cause Microsoft .NET Framework is used in almost all larger applications, and there can be various reasons why you see an error. One reason can be application specific, meaning that there is an actual issue with the software and the way the software is using .NET Framework, but another reason can be that the .NET Framework installation itself is corrupted. If it's an application specific issue, you need to contact product support, but in many cases simply repairing the .NET Framework installation has proven to solve the issue. Resolution 1: Close all applications 2: Make sure you have the correct version of .NET Framework installed for the software you use referencing the product's data sheet. You can use this tool to check what versions you have. Here is a direct download link. 3: Install versions that might be missing. You can download the various versions from the tool linked above. 4: Download Microsoft's .NET Framework repair tool and run it applying all fixes the tool suggests. Here is a direct download link.
View full article
Picard Product_Support
‎2018-09-11 09:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 07:58 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
3050 Views

Automation Server - Warm and Cold Start differences

Issue Automation Server - Warm and Cold Start differences Product Line EcoStruxure Building Operation Environment Building Operation Automation server Cause The explanation on the differences between a warm start and a cold start in the documentation and web help may not be clear to some.  Resolution Warm Start: Restarts the controller's application Cold Start: Restarts the controller's operating system An Automation Server can be warm/cold started from Workstation or by using the reset button on the Automation Server. Refer to Reset Functions on Web Help for an explanation of the differences between warm and cold starting the AS.  Basically, you can set the Retain Levels for variables in Building Operation to 'No', 'warm start' or 'cold start'. To change the retain level of a variable and go to its properties.  - Click on the gear icon. - Set the retain level of the variable. 1. Retain level set to 'No' - The variable is reset to the value set when the object was created. When you create an Analog Value object, the value of the newly created object is '0'. A user can set this to another value. When retain level is set for this Analog Value object, after a warm or cold start, the value of this object will default back to '0'. 2. Retain level set to 'Warm start' - The value is set back to the last value set by the user. If a user change the value of an Analog Value object to another value and save, after a warm start, the object will return to the last value set by the user.  3. Retain level set to 'Cold start' - The value is set back to the last value set by either the user or the system (for instance by a program). The operation is similar to the warm start but in this case, the last value set by the system will also be retained. 
View full article
Picard Product_Support
‎2018-09-11 07:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 07:25 PM

Labels:
  • EcoStruxure Building Operation
7700 Views

.xif files for SE7200 / SE7300 / SE7600

Issue Where can we find the LON xif files for SE72xx, SE73xx, SE76xx controllers? Product Line EcoStruxure Building Expert,EcoStruxure Building Operation,Field Devices Environment SE7200 / SE7300 / SE76000 Room Controllers Cause xif files are needed for LON applications. Resolution All LON related files for these controllers are available for download on The Exchange Download Center:   XIF files and plug-ins Resource files (DRF kit)
View full article
Picard Product_Support
‎2018-09-11 06:42 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 01:57 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
2964 Views

Resolving I/O module device address changed and Blacklisted device detection errors.

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue Some IO modules status showing as 'Blacklisted device detected" or "Address shift detected" or a system alarm is received indicating the condition. AS trace logs may show one of the following entries... 2015-08-18 17:41:02.675 [1256862784] nsp.pin.cio.IODevice Module at address 14 is reporting Internal Error Code 32 2015-08-18 17:41:02.757 [1256862784] nsp.pin.cio.IODevice Module at address 28 is reporting Internal Error Code 32 2015-08-18 17:41:02.825 [1256862784] nsp.pin.cio.IODevice Module at address 12 is reporting Internal Error Code 32 2015-08-18 17:41:02.869 [1256862784] nsp.pin.cio.IODevice Module at address 13 is reporting Internal Error Code 32 2015-08-18 17:41:02.951 [1256862784] nsp.pin.cio.IODevice Module at address 15 is reporting Internal Error Code 32   2015-06-18 10:05:13.912 [1255584832] nsp.pin.cio.CIOException Error: Bad_Address (0xb0000), module Automation_Server_Io_Bus(31), moduleCode 0, dispString "AS address is invalid", techString "nsp_servers/plugins/CentralIOPlugIn/CIO/source/IOManager.cpp line 460" 2015-06-18 10:05:20.789 [1255584832] nsp.pin.cio.IOBus IOBusServer::run: Caught CIO exception from slot 3   Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Cause One or more terminal base may have to be replaced. Intermittent IO connection (typically in S-cable). Resolution Follow this document or Blacklisted Device Detected for steps to resolve the problem.
View full article
Picard Product_Support
‎2018-09-11 12:02 PM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2022-08-18 05:42 AM

Labels:
  • EcoStruxure Building Operation
7907 Views
  • « Previous
    • 1
    • …
    • 28
    • 29
    • 30
    • …
    • 93
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of