Difference in Expansion IO Port power consumption between i2 and b3 field devices

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Difference in Expansion IO Port power consumption between i2 and b3 field devices
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
13395 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Difference in Expansion IO Port power consumption between i2 and b3 field devices

Captain AbeMeran Captain
‎2024-05-02 07:14 PM

on ‎2024-05-02 07:14 PM

Issue

Continuum i2 and b3 devices share the same hardware platform, however, power consumption on the devices IO Expansion Port differs depending on the communication protocol firmware (Infinet or BACnet) running in the device.

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • All i2 devices
  • All b3 devices

Cause

Even though the hardware of an i2 device is identical to that of its counterpart b3 device, the difference in firmware causes variation in power consumption on the device's Expansion IO port, specifically, it has been observed that the b3 devices adhere more strictly to the 180 mA limit than the i2 devices, resulting in loss of operation on IO channels located on the Expansion Port if the power limit is exceeded. 

Now that conversion of devices from one protocol to another is occurring in the field, it has become evident that there are cases where the 180 mA limit is exceeded in an i2 device without any negative results, but once the i2 device is converted to a b3 device, all IO on the expansion port stop working.

Resolution

Before converting an i2 device to a b3 device in the field, it is crucial to review the Expansion IO Datasheet (attached) to ensure that the configuration does not exceed the specified power consumption limit. If the configuration exceeds the 180 mA limit, take the following steps:

  • Remove any additional xP module causing the limit to be exceeded.
  • Reconfigure the xP modules to ensure that the configuration does not consume more than 180 mA.
Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Attachments
Tags (9)
  • Find more articles tagged with:
  • 180
  • AbeMeran24
  • b3
  • expansion
  • i2
  • io
  • ma
  • power
  • xp
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of