Conversion of b4920 to b3920 in the field

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Conversion of b4920 to b3920 in the field
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AbeMeran
    AbeMeran
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2755 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Conversion of b4920 to b3920 in the field

Captain AbeMeran Captain
‎2024-04-19 10:56 AM

Last Updated: Administrator CraigEl Administrator ‎2024-04-28 10:03 PM

Warning

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

One way conversion: Conversion of b4920 to b3920 is not reversible, once the b4920 controller has been converted to b3920 device, it cannot be converted back to b4920.

Issue

A b3920 device has failed in the field and the only available replacement at hand is a b4920

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • Continuum b4920

Cause

The b4920 is a Continuum BACnet router its hardware is almost identical to that of the b3920 device, the only difference is the Ethernet port in the b4920, which is not populated in the b3920.

When a b3920 must be replaced, and the only available replacement is a b4920, use the steps outlined in this article to convert the b4920 to a b3920.

Resolution

Before starting the procedure, you need the following items:

  • The b4920 device to be converted.
  • The serial number of the b4920 device to be converted.
  • Continuum Cyberstation with b4920 to be converted, configured, and online. (***)
  • A RoamIO2 and BACnet Service Tool
  • A special firmware b4920 application upgrade file provided by Product Support
  • A b3920 bootloader file provided by Product Support

Steps to convert b4920 into b3920

  1. Contact Product Support and request the b4920 to b3920 conversion files. You will be provided with an application file (e.g. b4920toB3920B4.500077.upd) and a boot loader file (e.g. B3920BootB4.500077.upd).
  2. From Continuum Workstation, take note of the baud rate of the MSTP operating under the b4920 (In Comm1 settings)
  3. From Continuum Cyberstation, edit the b4920 controller object and take note of the BACnet Device ID and the controller Serial Number, typically they will be the same but this is not always the case.
  4. In the "General" tab, click 'Update OS' and send the Application file provided by PSS. Please note that once the application file has been sent and the controller re-starts, its MSTP will shut down and RoamIO2 is required to re-start the MSTP for operation as a b3920, the reason for this is Continuum uses mac id 0 (zero) for router controllers such as the b4920 and the bCX4040, in Continuum, b3 devices are not allowed to use mac id 0.
  5. Disconnect the Ethernet cable from the b4920, the Ethernet port is now unusable.
  6. Connect the RoamIO2 directly to the b4920's Service Port then cycle power to the b4920.
  7. Start the BACnet Service Tool
  8. In the BACnet Service Tool, de-select View by networks, then click the connect icon, the conversion from b4940 to a b3920 causes the now b3920 device to come up with an unknown baud rate and an invalid (for b3s) mac id 0, so now need to find out the baud rate the converted b3920 is using
  9. From the "View" menu, select "RoamIO2 Properties and take note of the MAC ID the RoamIO2 is using
    RoamIOMAC.PNG

     

  10. From the 'Tools' menu, select 'Set b3 baud rate' and set it to Baud9600, and click apply
    AbeMeran_5-1713201310902.png

     

  11.  From the 'Tools' menu, select 'Set offline b3 MAC id' and enter the serial number of the device and a valid MAC ID ( DO NOT ENTER ZERO NOR THE MAC ID IN USE BY ROAMIO2), then click on 'Apply'
    AbeMeran_0-1713540281832.png

     

  12. If you get the message below, repeat the steps above for the next baud rate...
    CantTell.PNG

    when you have found the correct baud, you will see the message below after setting the MAC ID

    Success.PNG

     

  13. Once the baud and MAC id have been set successfully, the device will automatically pop up in the tree, but it will only be partially online, to bring the device fully online, click the red disconnect icon on the BACnet Service Tool to disconnect from the device, wait about 30 seconds then  click the now green connect icon to reconnect the BACnet Service Tool to the device
  14. Right-click on the device, then select 'Update OS' and send it the appropriate boot loader file provided by Product Support
    AbeMeran_1-1713540701435.png
  15. Once the uprev of the boot loader has completed, click 'Done' button to dismiss, select the device, right-click and select 'Cold start device', and click 'Yes' on the confirmation window
    AbeMeran_2-1713540905507.png

     

  16. You should now be able to commission the converted device as a b3920, either as a new device or as a replacement device, following the steps for replacing a b3 device. (those steps are not in the scope of this procedure)

***

b4920 controllers are not easily defaulted to factory settings. If one gets an old b4920 from the shelf, use the steps below to find out the controller's current IP address and ACCNetId which are needed to put the controller online in Continuum.

IP ADDRESS

Upon start-up the b4920 sends a gratuitous ARP, use Wireshark to connect directly to b4920 controller using a crossover Ethernet cable, restart the controller, and inspect the gratuitous ARP to determine the IP address configured in the b4920

ACCNetID

Once you have the IP address, use the attached utility tool to discover the ACCNetID of the b4920.

Unzip the attached file and use the Windows Command Line to execute FindEnodeID.exe as seen below

 

image (2).png

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Attachments
FindEnodeId.zip
Tags (1)
  • Find more articles tagged with:
  • AbeMeran24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of