Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1895 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 29
    • 30
    • 31
    • …
    • 95
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

In Webstation Alarm history view is different than in workstation

  Issue EBO 5.0 and all other revisions, In workstation When selecting `View history` of an alarm, we get columns more focused on alarms such as Alarm state, Alarm text,.. etc  But  in WebStation, we have “ View Events “ that shows columns that are more focused on object event history (including Value before, Value After, etc) rather than alarm history.       Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Webstation Building Operation Automation Server Premium Cause Navigating to View Alarm history in webstation is different than in workstation Resolution Alarm is a subset of Event, so it is reasonable to see it is under 'Event viewer'. There is no such a thing called 'Alarm history record' in webstation.This is Function as Designed (FAD) If we click on any of the events, after opening it we can see full alarm details.
View full article
Lt. Commander Ramaaly Lt. Commander
‎2024-03-27 01:12 PM

on ‎2024-03-27 01:12 PM

Labels:
  • EcoStruxure Building Operation
3722 Views

Connecting Multiple RPC-12-A Inputs to the Same Dry Contact

Issue In a life safety-related application, such as a fume hood, it is a requirement that the status of the end switch is not shared via peer-to-peer bindings. Instead, the end switch status must be hard-wired to all four controllers. What precautions should be taken to ensure that this will not cause issues. Product Line EcoStruxure Building Operation Environment Building Operation Room Controller (RPC) 24 V Cause Connecting multiple RP-C to the same dry contact.    Resolution Make sure to use individual transformers to each controller (i.e. one transformer to one controller power supply) to minimize the risk of short circuit.
View full article
Guinan MikaelKrantz Guinan
‎2024-03-24 05:32 PM

on ‎2024-03-24 05:32 PM

Labels:
  • EcoStruxure Building Operation
4729 Views

TAC Xenta alarms comes in with a different priority in StruxureWare Building Operation

Issue TAC Xenta alarms are configured with a priority of 1 in Menta, but these same alarms appear with a priority of 100 in EcoStruxure Building Operation. Product Line EcoStruxure Building Operation Environment Building Operation Workstation TAC Xenta 301, TAC Xenta 302, TAC Xenta 401, TAC Xenta 281, TAC Xenta 282 Cause This is per design, Building Operation supports priorities from 0-1000, aligning alarm priorities from TAC Xenta within the range of 100-900 is a deliberate choice. By default, all alarm priorities from TAC Xenta are multiplied by 100 to fit this scheme. Resolution To revert the priority back to the original, open the properties for the alarm and manually adjust the priority.
View full article
Picard Product_Support
‎2018-09-10 01:31 PM

Last Updated: Administrator CraigEl Administrator ‎2024-03-24 05:21 PM

Labels:
  • EcoStruxure Building Operation
1941 Views

MPx Triac Minimum current requirements

Issue There is no minimum current listed on the datasheet for Triac outputs on MPx controller. Product Line EcoStruxure Buildings Operation Environment Building Operation Multi-purpose Controller Cause Triac output not correctly switching due to the very small current load. Resolution The triac used in an MPx controller will run on low voltage and currents. In certain circumstances, the current drawn will not be sufficient to keep the triac in the MPx active. This has been seen to be in the region of 10-15 mA. In this case, a resistor would need to be installed in parallel with the triac to ensure you get a current draw of 20 mA or more for stable operation. It should also be noted that a Triac output is designed to switch AC load (24 VAC, 0.25 A maximum) and not DC load, refer to: Triac Outputs. An improved option to the MPx is an RP-C, RP-V or RP-IO, which can switch DC and AC loads with very low current draw, refer to: Solid-state Relay (SSR) Outputs.
View full article
Spock PeterLarsen Spock
‎2020-03-31 06:54 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-03-13 05:40 AM

Labels:
  • EcoStruxure Building Operation
1500 Views

Sum Alarm in EcoStruxure Building Operation

Issue The Sum Alarm will not trigger when monitoring other Sum Alarms. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server  Building Operation Enterprise Server Cause The Sum Alarm is ignoring other Sum alarms for detection of alarm criteria. Resolution There are two options to resolve this. Configure a 2nd SUM alarm to use criteria that triggers on any of the points that would have triggered the Sum alarm you want to monitor and the other points. You can create a Change of State Alarm to monitor the alarm state of the 1st Sum Alarm. The second Sum alarm can then detect that the Change of State alarm is active. (It might be practical to hide the Change of State alarm by setting the priority to a low value and filter your default alarm view to exclude it in order to avoid double alarm entries in the alarm view of Workstation)
View full article
Picard Product_Support
‎2018-09-06 10:25 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2024-03-12 02:20 AM

Labels:
  • EcoStruxure Building Operation
2280 Views

OGC graphic does not load when opened in Vista Webstation inside StruxureWare Webstation

Issue When opening an OGC graphic using Vista Webstation as a window inside StruxureWare Webstation, the OGC graphic shows "Loading..." with a small cross in the upper left corner, and the graphic never loads. Product Line EcoStruxure Building Operation Environment TAC Vista Webstation Building Operation Webstation   Cause The authentication in the communication between the browser and Vista Webstation is based on sessions and cookies. Due to a security setting on some sites, the initial cookie can not be set in the browser, and the authentication between the OGC graphic page showed in the browser and the web server therefore fails. If the graphic is opened in full screen (see below) or in a new window it will load, and subsequently all OGC graphics will work until the browser is restarted. Button to open the graphic in full screen Resolution On each PC that needs to access the OGC graphics using StruxureWare Webstation do the following: 1. Open Internet Explorer settings by clicking the gear in the upper right corner 2. Click "Privacy" and then "Sites" 3. Write the address of Vista Webstation (e.g. http://ip_address/webstation), click "Allow" and "OK" 4. Restart Internet Explorer   Note: This solution also applies to following issue; After clicking  a Vista Webstation url (direct link to a TGML graphic) in SBO Webstation from a Windows Server 2012 PC using Internet Explorer 11, Vista Webstation is expanding to fill the entire screen (it doesn't stay in the right hand window of SBO Webstation)
View full article
Picard Product_Support
‎2018-09-10 02:27 PM

Last Updated: Janeway Jonas_Brissman Janeway ‎2024-03-08 05:15 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
2332 Views

Domain Usage within SmartStruxure 1.2 and later

Issue The functionality of StruxureWare Domains changed substantially in 1.2. There has been some discussion that the inability to communicate or the failure to transfer data from one SmartStruxure server to another is somehow related to the servers not being in the same StruxureWare Domain. This is not the case. As of 1.2 StruxureWare Domains are not used for communication at all. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server (ES) Building Operation Automation Server Premium (AS-P) Cause StruxureWare Domains are NOT used at all for establishing communication within SmartStruxure 1.2 and later releases If the AS can be added under the ES and no alarms are generated by the added AS, then full data sharing is possible regardless of StruxureWare Domain creation or membership. Resolution If the AS can not be added under the ES then there is a network problem that is preventing communication from the ES to the AS. If the AS can be added, but communication errors or lead verification alarms are generated that show the added AS as the source server, then there are network (or firewall) issues that are preventing the AS from communicating with the ES. If all engineering and configuration is done from the ES with the admin account in the Local Domain All bindings can be created by admin in the local domain All data can be viewed in graphics, trend charts, etc. by admin in the local domain Only data within the local AS can be viewed  by admin logged into the local domain of the AS This is true regardless of WorkStation or WebStation A StruxureWare Domain other than the local domain must be created and the other servers must be added to that StruxureWare Domain in order for users to have access (viewing or otherwise) to objects in the other servers.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2024-03-08 04:13 AM

Labels:
  • EcoStruxure Building Operation
2068 Views

Changing Block Type in Function Block Editor While Keeping the Same Name

Issue Want to modify the type of a block in the Function Block Editor while retaining the original block's name Product Line EcoStruxure Building Operation. Environment Building Operation Workstation. Function Block Editor. Cause Altering the block type without removing the block first can result in the persistence of old block parameters even if they are incompatible with the new block type. For instance, transitioning from an "Integer Input" block type while the input is in a forced state may cause the new block to retain the forced state, even if it is not applicable, leading to potential issues with un-forcing. Resolution To ensure correct functionality, it is recommended that the old block is removed and the application saved before adding the new block with the original name. This process effectively clears out the old configuration, enabling the new block to contain only the parameters of the new block type.
View full article
Guinan MikaelKrantz Guinan
‎2024-03-12 04:33 PM

on ‎2024-03-12 04:33 PM

Labels:
  • EcoStruxure Building Operation
3851 Views

Will EcoStruxure Building Operation provide any indication of a failure sending a SNMP trap?

Issue Will EcoStruxure Building Operation provide any indication of a failure sending a SNMP trap? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Cause Need to receive an alarm and event if an EBO server couldn't send an SNMP trap. Resolution If there is a failure sending an SNMP trap, EBO will generate a system alarm/event indicating that the trap could not be sent. Note though, that if the trap is sent successfully there is no indication or log entry to indicate so. System Alarm ID Description SNMP send trap failure Failed to send SNMP message.
View full article
Picard Product_Support
‎2018-09-11 08:21 AM

Last Updated: Administrator CraigEl Administrator ‎2024-03-11 11:49 PM

Labels:
  • EcoStruxure Building Operation
1362 Views

Can EBO serve data via Web Services

Issue Need to serve data via Web Services to 3rd party systems.  Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Automation Server Cause Generic Web Services SOAP, Simple XML or Script Web Services cannot act as a server. They can only act as a client to other web servers. Resolution EcoStruxure BMS servers can serve information to another EcoStruxure system using the EcoStruxure Web Services standard. For 3rd party systems, SmartConnector RESTful EWS Gateway can be used to serve EBO data to 3rd party system in a RESTful manner, refer to: Configure SmartConnector RESTful EWS Gateway to serve EBO data - Schneider Electric Community
View full article
Picard Product_Support
‎2018-09-06 09:37 AM

Last Updated: Administrator CraigEl Administrator ‎2024-03-11 11:46 PM

Labels:
  • EcoStruxure Building Operation
1651 Views

Changing the Priority of System Alarms in EcoStruxure Building Operation

Issue How to change the priority of system generated alarms in EcoStruxure Building Operation. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Automation Server Cause Need to change EBO system priority. Resolution Currently, it is not possible to change the priority of system alarms. The default is value 100.  There are currently no plans to add the feature. 
View full article
Picard Product_Support
‎2018-09-06 12:17 PM

Last Updated: Administrator CraigEl Administrator ‎2024-03-11 11:43 PM

Labels:
  • EcoStruxure Building Operation
1924 Views

Convert PEM certificate file to CRT certificate file

Issue Device Administrator requires CRT certificate file to add a certificate to CA Certificates. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Cause If you rename the filetype from .pem to .crt and add via Device Administrator, the Automation Server will still present the following alarm: Alarm Text: System alarm: unable to get local issuer certificate System alarm ID: Invalid certificate for https communications   NOTE: The alarm will be known to have originated from the Automation Server because, in the Source field, the Automation Server will be the root, and the server it is connecting to will be the last. Example: /AS01/System/Communication/Server Certificate/To/ES01 AS01 - Automation Server with the CA Certificate issue ES01 - the EBO server which is was connected as client, which generated the alarm Resolution Reference this article to find OpenSSL installed: OpenSSL installed with EBO Use and modify this command with your filenames:  openssl x509 -in ca.pem -out ca.crt​ Add the .crt certificate file via Device Administator's CA Certificates tab. Reference: CA Certificate Tab (WebHelp)
View full article
Picard David_Purser Picard
‎2024-03-07 08:39 AM

on ‎2024-03-07 08:39 AM

Labels:
  • EcoStruxure Building Operation
4967 Views

Ensure a version of TLS is disabled using OpenSSL

Issue Ensure a version of TLS is disabled using OpenSSL Product Line EcoStruxure Building Operation Environment Enterprise Central Enterprise Server Automation Server Cause Need to verify TLS is disabled on an EBO server in case of incorrect text entry Resolution It is possible to check which TLS protocols are set to be disabled using WorkStation Control Panel's Security Settings or in the Device Administrator SSL Security Settings tab. If the version required is not disabled then consult Disabling TLS and SSH. Once the protocol is set to disabled follow the steps below to verify using OpenSSL Open a command prompt and change directory to the OpenSSL folder. If OpenSSL is not available consult OpenSSL installed with EBO or install OpenSSL as mentioned in Ensuring the SSL Host Certificate and key file are a matching pair To check if TLS is disabled enter the command openssl s_client -connect 'server address':'port'-'TLS version'.  For example if the server IP address is 192.168.5.95 and using port 443:- openssl s_client -connect 192.168.5.95:443 -tls1    openssl s_client -connect 192.168.5.95:443 -tls1_1 openssl s_client -connect 192.168.5.95:443 -tls1_2 openssl s_client -connect 192.168.5.95:443 -tls1_3 If an error is returned (1) and no certificates are available (2) then the TLS version is Disabled. If a certificate chain (3) and certificate details (4) are returned the TLS version is Enabled. The image illustrates only the start of the returned information, more will be available.   For additional information search "OpenSSL s_client" using an online web browser.  The s_client command can be used to test TLS server connectivity, TLS/SSL version support, check cipher suites, and verify server certificates.  
View full article
Sisko GavinHe Sisko
‎2024-03-06 03:19 PM

on ‎2024-03-06 03:19 PM

Labels:
  • EcoStruxure Building Operation
4353 Views

Error when trying to activate embedded license

Issue When trying to activate a license in an AS-P/B the following error message was shown and the activation failed: Online activation: 12:57:24: Executing licensing command 12:57:24: Executing embedded operation: Activate ActivationID: ACT-xxx 12:57:32: Embedded operation: Activate failed: ASEmbeddedAPI internal error: Binary response does not contain feature information Error status information: FNO server response: Z(BACK_OFFICE%DEBACK_OFFICE+']\dBl&%MSM230312018I|B}~%ACT-xxxxx/jlSkkj1%<K!,b7OnpUy7 zqDFG#I$QGGR0:SYWJVGIuW}+iea 0\wR/`;yX'HGX*;;nEl]d0I+nHWh(VD"+a uwpf%XF[N6~!,^?R]y?VPCw\gB{"dSy2K7ph;_=qw.|c]Vp;.nlMbLl-~Z!UY<:=TFZEL~h=\V)>ML)ld0g'PPcjrosy&]p9Y((?II#*B5/U16X;o- 12:57:32: Licensing command completed 12:57:34: Activating licenses failed   Offline activation: 12:56:02: Executing licensing command 12:56:02: Executing embedded operation: ProcessResponseFile ResponseFile: C:\Users\Mitthem\Desktop\Garage\response\xxxxxxx\8ba20b60-b19c-4a5d-8fea-693ef9282c8c.bin 12:56:03: Embedded operation: ProcessResponseFile failed: ASEmbeddedAPI internal error: Binary response does not contain feature information Error status information:  12:56:03: Licensing command completed 12:56:05: Activating licenses failed Product Line  EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Building Operation Automation Server Bundled (AS-B) Building Operation Device Administrator (DA)  Embedded Licenses Cause The reason for the issue was that the number of available licenses for activation was 0, but the error message in DA was not indicating that. The Device Administrator (DA) showed that two licenses were available but were out of sync. Resolution When looking at the Entitlement in DA, it had a yellow dot on it, indicating that it was added offline. In DA version 5.0.2 and later, DA contacts the License server directly when adding an Entitlement in prior versions this was done through the AS-P. In DA version 5.0.2 and later, it is enough that the computer where DA is installed has an internet connection when adding an Entitlement online. After upgrading DA to version 5.0.2 and refreshing the Entitlement, the Device Administrator showed the correct number of available licenses.    If upgrading the site to this version is not possible, the Entitlement ID / Activation ID availability and device list can be verified by using the User Portal FlexNet Login (flexnetoperations.com) It is also possible to run Device Administrator version 5.0.2 with the concurrent site version used as long as the Servers are at 4.0.4 and above to check, verify and activate licenses.     Important Note: Device Administrator 5.0.3 and above will NOT support lower-version Automation Servers as 5.0.2 does.  This is due to new features of embedded licenses for servers as well as the handling of servers without internet connections.  In this case, ALL servers must run the same version as the Device Administrator version when handling licenses.         Further information on Automation Server Licensing Overview is available through the online WebHelp.  
View full article
Janeway Jonas_Brissman Janeway
‎2023-05-01 07:02 AM

Last Updated: Picard RobertAndriolo Picard ‎2024-02-29 10:43 PM

Labels:
  • EcoStruxure Building Operation
7374 Views

PCT 1.x Server shows Added to Parent after being detached from ES

Issue When attempting to detach an AS, PCT continues to shown the server as being attached to the ES.   Product Line EcoStruxure Building Operation Environment Building Operation Project Configuration Tool 1.x (PCT) Cause In PCT, when an AS is detached from its parent ES, the ES name still appears in the Added to parent column of the Servers list. Resolution Once the AS has been detached from an ES it can be added to another ES though Workstation using the following steps even though the "Added to parents" column shows otherwise.   To create a SmartX server In WorkStation, in the System Tree panel, select the Servers folder. On the File menu, point to New and then click Server . In the Create Object wizard, in the Name box, type a name for the SmartX server. In the Description box, type descriptive information about the SmartX server. Click Next . In the Configure IP/DNS Address and Port page, in the Address box, type the IP address or fully qualified domain name of the SmartX server. Notice If the SmartX server has been assigned a dynamic IP address, use the fully qualified domain name of the SmartX server instead of the IP address. In the Protocol box, select a protocol for the SmartX server. For more information, see EcoStruxure BMS Server Communication . In the Port box, enter a port number. Click Create. In the Log on dialog box, in the Password box, type the custom password if required. Click OK.   For more information, see Creating a SmartX Server
View full article
Admiral StephenYang Admiral
‎2019-06-21 06:11 AM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
2357 Views

Embedded License activation fails with error FLXERR_RESPONSE_EXPIRED

Issue Cannot activate embedded license on Automation server, either online or offline, with error: FlexNet Embedded error: The allowed time to process the response has expired.   Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause Automation Server has wrong date and time. Resolution Make sure that Automation Server has correct date, time and time zone. Automation Server can be connected to NTP server to synchronize its clock, refer to Synchronizing the Automation Server Clock.
View full article
Kirk Mahmoud_Sayed Kirk
‎2024-02-28 02:00 AM

Last Updated: Janeway PeterEdvik Janeway ‎2024-02-28 02:02 AM

Labels:
  • EcoStruxure Building Operation
4248 Views

Use Static IP instead of DHCP for critical data exchange with SpaceLogic BACnet/IP controller(s)

Issue In SpaceLogic BACnet/IP controllers, a DHCP configuration takes longer than a Static IP configuration to start BACnet communications after a power cycle or restart. Product Line EcoStruxure Building Operation Environment Building Operation Multi-purpose Controller (MP-C) Building Operation Multi-purpose VAV (MP-V) Building Operation Room Controller (RP-C) Building Operation Room VAV (RP-V) Cause The DHCP IP address assignment flow diagram is depicted in this WebHelp article: IP Address Settings for IP Communications. As a part of the failover process, once the controller receives a DHCP lease, it will send multiple ARP requests to ensure the IP address is not being used by another device, further delaying BACnet communications. If it does not detect another device using that IP, it will use the IP it was given to lease. Also, SpaceLogic BACnet/IP controllers store the IP address and port of the controllers for which they have External Binds (Consumers/Producers). If a device is unavailable at that IP address because the DHCP lease has changed, the controller will have to use WHO-IS to find the new address of that controller. Resolution Configure the SpaceLogic BACnet/IP controller with a Static IP address, so the controller will boot directly using a Static IP address and start communicating via BACnet/IP. If on the AS-P Secondary Network with 10.110.210.0/24 network where AS-P DHCP server leases IP addresses from 2 and goes higher, assign static IP in a higher number range (0-254) for the last octet.
View full article
Picard David_Purser Picard
‎2024-02-26 07:36 AM

on ‎2024-02-26 07:36 AM

Labels:
  • EcoStruxure Building Operation
4994 Views

BACnet alarm doesn't work in Project configuration tool (PCT)

Issue BACnet alarm state doesn't update when the monitored variable triggers the alarm in PCT. Product Line EcoStruxure Building Operation Environment Project Configuration Tool Cause BACnet alarms require a live device to send alarms to EBO. Since PCT doesn't have any live devices, BACnet alarms don't work in PCT. Resolution The BACnet alarm feature is not supported in PCT.
View full article
Admiral StephenYang Admiral
‎2024-01-23 03:00 PM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
4181 Views

Understanding a certificate PEM file

Issue Unsure whether a certificate is in the required PEM file format and what fields it includes to ensure the correct file is installed on the correct server. Sample of certificate -----BEGIN CERTIFICATE----- MIIF+TCCBOGgAwIBAgIRAOUXUXsbB/LpS0VTQsz/HFcwDQYJKoZIhvcNAQELBQAw gY8xCzAJBgNVBAYTAkdCMRswGQYDVQQIExJHcmVhdGVyIE1hbmNoZXN0ZXIxEDAO BgNVBAcTB1NhbGZvcmQxGDAWBgNVBAoTD1NlY3RpZ28gTGltaXRlZDE3MDUGA1UE AxMuU2VjdGlnbyBSU0EgRG9tYWluIFZhbGlkYXRpb24gU2VjdXJlIFNlcnZlciBD QTAeFw0xOTAxMTcwMDAwMDBaFw0xOTA0MTcyMzU5NTlaMFAxITAfBgNVBAsTGERv bWFpbiBDb250cm9sIFZhbGlkYXRlZDERMA8GA1UECxMIRnJlZSBTU0wxGDAWBgNV BAMTD3dlYi1zZWN1cml0eS5jejCCASIwDQYJKoZIhvcNAQEBBQADggEPADCCAQoC ggEBAMNC5twUz78YyvW9Y+avpBZLZjGFLZbNZN3tukWL/1wuwLUrhuCju1IDXWnJ a7vu4IFA/m/fgD68Y+I6BEF/tdw94TGc/X0n+Q326ZB3ff8e5+GF2o2oXQCUEX60 wGv17zIx8jCYZtaP9rWekUzWmkNPagImboWeYSLWkt7GvdJCU7VY8kpKm7Y/JF/P Qs4Z5+d4HMsfknJ+PofI7Ve3wT0aPE4aiQ3+MWryxcnZYzH7xNpeB7UbkfFIeDki 4X1vkVFM2Do07IkY9dO8d0UNI3lDDJDpxCCW4kVOl8yQTRtmyPZmtXk5uoyFcCEh KP5/T2gxNr9KNzIornE0F7LZfpMCAwEAAaOCAowwggKIMB8GA1UdIwQYMBaAFI2M XsRUrYrhd+mb+ZsF4bgBjWHhMB0GA1UdDgQWBBSHdiVoz7sMpYkdFsQWYHoMcJZU IzAOBgNVHQ8BAf8EBAMCBaAwDAYDVR0TAQH/BAIwADAdBgNVHSUEFjAUBggrBgEF BQcDAQYIKwYBBQUHAwIwSQYDVR0gBEIwQDA0BgsrBgEEAbIxAQICBzAlMCMGCCsG AQUFBwIBFhdodHRwczovL3NlY3RpZ28uY29tL0NQUzAIBgZngQwBAgEwgYQGCCsG AQUFBwEBBHgwdjBPBggrBgEFBQcwAoZDaHR0cDovL2NydC5zZWN0aWdvLmNvbS9T ZWN0aWdvUlNBRG9tYWluVmFsaWRhdGlvblNlY3VyZVNlcnZlckNBLmNydDAjBggr BgEFBQcwAYYXaHR0cDovL29jc3Auc2VjdGlnby5jb20wLwYDVR0RBCgwJoIPd2Vi LXNlY3VyaXR5LmN6ghN3d3cud2ViLXNlY3VyaXR5LmN6MIIBBAYKKwYBBAHWeQIE AgSB9QSB8gDwAHYAu9nfvB+KcbWTlCOXqpJ7RzhXlQqrUugakJZkNo4e0YUAAAFo Ww+ePQAABAMARzBFAiEAtZoULgmDyEppYK9nmDWNRjRGcE+BBo/DLaaoaYWg7C8C IH+0UCda6Txcl05inAsMpzlePELyZ3hawgEdmMugK3bXAHYAdH7agzGtMxCRIZzO JU9CcMK//V5CIAjGNzV55hB7zFYAAAFoWw+eiwAABAMARzBFAiEAmdEbql+1pWWf HmpkY34JziCOQzaDlFVtUFen+blgIWwCIBVnwDD3vnwSsrO2T5Clo5Pjqa+xxU7O trLo/ZRGkICBMA0GCSqGSIb3DQEBCwUAA4IBAQAzOM9lS3RSU7rLy8T3BfixHvua ErZ+YOHCHpYhlCeSuFZ66jVHueYWvgfF8A+enRdMM0k0z0PC9enREnumNDq3msCf WYhSLd5lDXiEddg2GCrXkwhOFfOiG0tywS5CD+hLsTq1LQkWDQg7EKlIb6ddhaZO IYEQ9xwE7aehynQEvAjv3UyevMYfvw7glY+MW5bkMfsxPndDD1gDbnYt8kyenjcv odjnkvTw4ngnCy1gF9mVWkgQsE1j34FER1bVtR/FlspI0FB+ogV4Qhso1N23DwtF VDKxH8p+ddYh1LX4b6Oy3dZqzt4HOcunPKsFv36ABpeTs8FPOjgQueTWfHQ4 -----END CERTIFICATE----- Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Central Building Operation Enterprise Server Building Operation Automation Server Building Operation Edge Server Cause A third party provides the certificate files and can have names different from the server installed on and in different formats. Resolution Open the file with a text editor (as seen above in the Issue section). PEM files can include a header or footer that could help identify the certificate. The example above does not. The body has a beginning and ending to describe its contents. —–BEGIN CERTIFICATE REQUEST—– and —–END CERTIFICATE REQUEST—– show a CSR in PEM format. —–BEGIN RSA PRIVATE KEY—– and —–END RSA PRIVATE KEY—– show a private key in PEM format. —–BEGIN CERTIFICATE—– and —–END CERTIFICATE—– show a certificate file in PEM format. The format would look like this if the PEM file included the SSL certificate chain. —–BEGIN CERTIFICATE—– //end-user —–END CERTIFICATE—– —–BEGIN CERTIFICATE—– //intermediate —–END CERTIFICATE—– —–BEGIN CERTIFICATE—– //root —–END CERTIFICATE—– NOTE: There must be a blank line after the END is defined. Ensure there is only one certificate in the file to examine. You may have to copy the file multiple times, open each one, and retain only one per file. Open Command Prompt and find a copy of OpenSSL installed on the machine. OpenSSL installed with EBO Use the following command, where server.pem is the file and file type you are inspecting. openssl.exe x509 -in server.pem -text -noout​ Example output from sample above.  Certificate: Data: Version: 3 (0x2) Serial Number: e5:17:51:7b:1b:07:f2:e9:4b:45:53:42:cc:ff:1c:57 Signature Algorithm: sha256WithRSAEncryption Issuer: C = GB, ST = Greater Manchester, L = Salford, O = Sectigo Limited, CN = Sectigo RSA Domain Validation Secure Server CA Validity Not Before: Jan 17 00:00:00 2019 GMT Not After : Apr 17 23:59:59 2019 GMT Subject: OU = Domain Control Validated, OU = Free SSL, CN = web-security.cz Subject Public Key Info: Public Key Algorithm: rsaEncryption RSA Public-Key: (2048 bit) Modulus: 00:c3:42:e6:dc:14:cf:bf:18:ca:f5:bd:63:e6:af: a4:16:4b:66:31:85:2d:96:cd:64:dd:ed:ba:45:8b: ff:5c:2e:c0:b5:2b:86:e0:a3:bb:52:03:5d:69:c9: 6b:bb:ee:e0:81:40:fe:6f:df:80:3e:bc:63:e2:3a: 04:41:7f:b5:dc:3d:e1:31:9c:fd:7d:27:f9:0d:f6: e9:90:77:7d:ff:1e:e7:e1:85:da:8d:a8:5d:00:94: 11:7e:b4:c0:6b:f5:ef:32:31:f2:30:98:66:d6:8f: f6:b5:9e:91:4c:d6:9a:43:4f:6a:02:26:6e:85:9e: 61:22:d6:92:de:c6:bd:d2:42:53:b5:58:f2:4a:4a: 9b:b6:3f:24:5f:cf:42:ce:19:e7:e7:78:1c:cb:1f: 92:72:7e:3e:87:c8:ed:57:b7:c1:3d:1a:3c:4e:1a: 89:0d:fe:31:6a:f2:c5:c9:d9:63:31:fb:c4:da:5e: 07:b5:1b:91:f1:48:78:39:22:e1:7d:6f:91:51:4c: d8:3a:34:ec:89:18:f5:d3:bc:77:45:0d:23:79:43: 0c:90:e9:c4:20:96:e2:45:4e:97:cc:90:4d:1b:66: c8:f6:66:b5:79:39:ba:8c:85:70:21:21:28:fe:7f: 4f:68:31:36:bf:4a:37:32:28:ae:71:34:17:b2:d9: 7e:93 Exponent: 65537 (0x10001) X509v3 extensions: X509v3 Authority Key Identifier: keyid:8D:8C:5E:C4:54:AD:8A:E1:77:E9:9B:F9:9B:05:E1:B8:01:8D:61:E1 X509v3 Subject Key Identifier: 87:76:25:68:CF:BB:0C:A5:89:1D:16:C4:16:60:7A:0C:70:96:54:23 X509v3 Key Usage: critical Digital Signature, Key Encipherment X509v3 Basic Constraints: critical CA:FALSE X509v3 Extended Key Usage: TLS Web Server Authentication, TLS Web Client Authentication X509v3 Certificate Policies: Policy: 1.3.6.1.4.1.6449.1.2.2.7 CPS: https://sectigo.com/CPS Policy: 2.23.140.1.2.1 Authority Information Access: CA Issuers - URI:http://crt.sectigo.com/SectigoRSADomainValidationSecureServerCA.crt OCSP - URI:http://ocsp.sectigo.com X509v3 Subject Alternative Name: DNS:web-security.cz, DNS:www.web-security.cz CT Precertificate SCTs: Signed Certificate Timestamp: Version : v1 (0x0) Log ID : BB:D9:DF:BC:1F:8A:71:B5:93:94:23:97:AA:92:7B:47: 38:57:95:0A:AB:52:E8:1A:90:96:64:36:8E:1E:D1:85 Timestamp : Jan 17 09:06:16.765 2019 GMT Extensions: none Signature : ecdsa-with-SHA256 30:45:02:21:00:B5:9A:14:2E:09:83:C8:4A:69:60:AF: 67:98:35:8D:46:34:46:70:4F:81:06:8F:C3:2D:A6:A8: 69:85:A0:EC:2F:02:20:7F:B4:50:27:5A:E9:3C:5C:97: 4E:62:9C:0B:0C:A7:39:5E:3C:42:F2:67:78:5A:C2:01: 1D:98:CB:A0:2B:76:D7 Signed Certificate Timestamp: Version : v1 (0x0) Log ID : 74:7E:DA:83:31:AD:33:10:91:21:9C:CE:25:4F:42:70: C2:BF:FD:5E:42:20:08:C6:37:35:79:E6:10:7B:CC:56 Timestamp : Jan 17 09:06:16.843 2019 GMT Extensions: none Signature : ecdsa-with-SHA256 30:45:02:21:00:99:D1:1B:AA:5F:B5:A5:65:9F:1E:6A: 64:63:7E:09:CE:20:8E:43:36:83:94:55:6D:50:57:A7: F9:B9:60:21:6C:02:20:15:67:C0:30:F7:BE:7C:12:B2: B3:B6:4F:90:A5:A3:93:E3:A9:AF:B1:C5:4E:CE:B6:B2: E8:FD:94:46:90:80:81 Signature Algorithm: sha256WithRSAEncryption 33:38:cf:65:4b:74:52:53:ba:cb:cb:c4:f7:05:f8:b1:1e:fb: 9a:12:b6:7e:60:e1:c2:1e:96:21:94:27:92:b8:56:7a:ea:35: 47:b9:e6:16:be:07:c5:f0:0f:9e:9d:17:4c:33:49:34:cf:43: c2:f5:e9:d1:12:7b:a6:34:3a:b7:9a:c0:9f:59:88:52:2d:de: 65:0d:78:84:75:d8:36:18:2a:d7:93:08:4e:15:f3:a2:1b:4b: 72:c1:2e:42:0f:e8:4b:b1:3a:b5:2d:09:16:0d:08:3b:10:a9: 48:6f:a7:5d:85:a6:4e:21:81:10:f7:1c:04:ed:a7:a1:ca:74: 04:bc:08:ef:dd:4c:9e:bc:c6:1f:bf:0e:e0:95:8f:8c:5b:96: e4:31:fb:31:3e:77:43:0f:58:03:6e:76:2d:f2:4c:9e:9e:37: 2f:a1:d8:e7:92:f4:f0:e2:78:27:0b:2d:60:17:d9:95:5a:48: 10:b0:4d:63:df:81:44:47:56:d5:b5:1f:c5:96:ca:48:d0:50: 7e:a2:05:78:42:1b:28:d4:dd:b7:0f:0b:45:54:32:b1:1f:ca: 7e:75:d6:21:d4:b5:f8:6f:a3:b2:dd:d6:6a:ce:de:07:39:cb: a7:3c:ab:05:bf:7e:80:06:97:93:b3:c1:4f:3a:38:10:b9:e4: d6:7c:74:38 ​ Notable fields include, Issuer: CN = : This is the issuer's common name (CN), Sectigo RSA Domain Validation Secure Server CA, which is the name on the certificate that signed it. If it is the same as a Subject: CN =, then it is, in most cases, Self-Signed. CA Certificates are self-signed and added to a client system in a trust store to be trusted. Validity: Not After: This is the expiration date Subject: CN = : This is the server on which it should be installed common name (CN), in this case, web-security.cz Subject Alternative Name: This Subject Alternative Name (SAN) field can specify alternate server names, like local DNS or IP address. If this server is being used to server content from multiple domains and/or subdomains, all will be listed here. In this sample, two DNS names are listed: web-security-cz and www.web-security.cz. Compare the Common Name (CN) or Subject Alternative Name (SAN) to the address or IP address used to access the server; if it is not one of the included names, then certificate validation will fail. Reference this article to check validity: Verify certificates with OpenSSL
View full article
Picard David_Purser Picard
‎2024-02-20 05:43 AM

Labels:
  • EcoStruxure Building Operation
5870 Views

BACnet multi state object number of states and states label

Issue Can the user set the 'Number of States' and the 'State Text' in a multi state object? Product Line EcoStruxure Building Operation Environment BACnet b3 controllers Multi-state values Cause The b3 firmware does not allow the Number of States or State Text to be modified This is Function as designed. Resolution Continuum DOES NOT allow changes to the default number of states and state labels. The 'Number of States' field is read only. An attempt to change any of the label will result in the following error: An error code was returned from a BACnet operation, but the reason could not be determined. The same is seen in EBO if any attempt is made to edit the State Text, see below
View full article
Picard Product_Support
‎2018-09-06 03:54 PM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2024-02-20 01:52 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1941 Views
  • « Previous
    • 1
    • …
    • 29
    • 30
    • 31
    • …
    • 95
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore