Issue
TAC Xenta alarms with priority 1 in Menta comes in with a priority of 100 in StruxureWare Building Operation
Environment
StruxureWare Building Operation 1.2
TAC Menta
TAC Xenta 301, TAC Xenta 302, TAC Xenta 401, TAC Xenta 281, TAC Xenta 282
Cause
This is per design. Since Building Operation 1.2 has priorities from 0-1000, it would fit more to have alarm priorities from 100- 900. All alarm priorities from TAC Xenta will be multiplied by 100 by default.
You can change the priority in Building Operations, if you want 0-9 instead.
Resolution
This is per design.
To change it back, open properties for the alarm and change the priority