BACnet multi state object number of states and states label
  • BACnet multi state object number of states and states label
  • Dave_Shore
    Dave_Shore
  • AbeMeran
    AbeMeran
‎2018-09-06 03:54 PM
Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2024-02-20 01:52 AM
Can the user set the 'Number of States' and the 'State Text' in a multi state object?
  • BACnet b3 controllers
  • Multi-state values
The b3 firmware does not allow the Number of States or State Text to be modified
This is Function as designed.
Continuum DOES NOT allow changes to the default number of states and state labels.
The 'Number of States' field is read only.
An attempt to change any of the label will result in the following error:
An error code was returned from a BACnet operation, but the reason could not be determined.
The same is seen in EBO if any attempt is made to edit the State Text, see below
Labels (2)
Tags (2)
  • 7712
  • DavidShore24