Capture BACnet MSTP Traffic with Tshark

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Capture BACnet MSTP Traffic with Tshark
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
6003 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Capture BACnet MSTP Traffic with Tshark

Picard David_Purser Picard
‎2024-04-24 05:43 AM

on ‎2024-04-24 05:43 AM

Issue

When using mstpcap.exe to capture, it automatically stops after 65535 packets. Similarly, when using Wireshark, it will stop capturing if the dissector encounters an issue. This article provides a solution to continuously capture BACnet MS/TP traffic in a ring buffer and store it as files.

Product Line

Andover Continuum, EcoStruxure Building Operation, TAC IA Series

Environment

  • Wireshark
  • Any BACnet MSTP RS-485 network

Cause

Analyze BACnet traffic via capture files.

Resolution

  1. Install Wireshark.
    1. Ensure TShark is checked when installing options. 
      TsharkChecked.png
    2. Ensure Wireshark is installed with Npcap (default) or WinPCap has been installed by IA Series Workplace Tech.
  2. Install mstpcap.exe referencing BACnet MSTP Capture Application. Ensure that mstpcap.exe has been configured for the correct port and baud rate. Here is an example for Command Prompt and PowerShell:
    # Command Prompt
    cd "C:\Program Files\Wireshark\extcap"
    mstpcap.exe com3 38400
    
    # PowerShell
    cd 'C:\Program Files\Wireshark\extcap'
    ./mstpcap.exe com3 38400
  3. Run Tshark to determine the interface being used by mstpcap so that one can reference it by number. For this example, we are going to choose 9. COM3 (BACnet MS/TP on COM3). Please change the number below to the number of your interface. 
  4. Start Tshark capture by entering the following command, updating as needed. The commands below save Test01.pcap to the Username's desktop. Please store to a location that the user has access to write. 
    # Command Prompt
    cd "C:\Program Files\Wireshark"
    tshark.exe -i 9 -b duration:3600 -b files:72 -w "C:\Users\Username\Desktop\Desktop\Test01.pcap​"​
    
    # PowerShell
    cd 'C:\Program Files\Wireshark'
    ./tshark.exe -i 9 -b duration:3600 -b files:72 -w 'C:\Users\Username\Desktop\Desktop\Test01.pcap​'

Note:

  • Change -i 9 to the number of the interface on the capturing machine.
  • Change -b duration to time in seconds (3600 is one hour).
  • Change -b files to the number of files to cycle through (72 is 3 days of 1-hour captures, 3x24).
  • Change -w to write to the location and filename you choose.
  • Change \Username\ to your Windows User, if you want to save to that user's Desktop

Reference: tshark(1) Manual Page (wireshark.org)

Labels (3)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • DavidPurser24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore