Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

BACnet MSTP Capture Application

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet MSTP Capture Application
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • David_Purser
    David_Purser
  • DavidFisher
    DavidFisher
  • Julio_Cortes
    Julio_Cortes
  • JohnBoehmer
    JohnBoehmer
  • sesa177673
    sesa177673
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
12111 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet MSTP Capture Application

Picard Product_Support
‎2018-09-10 03:46 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-18 05:55 AM

Issue

BACnet MSTP Capture Application

Product Line

Andover Continuum, EcoStruxure Building Operation, TAC IA Series, TAC Vista

Environment

Any Bacnet MSTP Network

Cause

The BACnet MSTP capture application provides the ability to analyze data communications between devices anytime issues are suspected on the network.

Resolution

Download the latest version.

  1. Browse to Steve Karg's  BACnet Protocol Stack - Browse /bacnet-tools at SourceForge.net
  2. Select the version folder
  3. Select bacnet-tools-[n.n.n].zip file to download it
  4. From the zip file, extract mstpcap.exe

Now you can use it via command prompt as described below or install it in C:\Program Files\Wireshark\extcap if want to use with modern Wireshark version.

 

To capture data follow these steps:

  1. Unzip file
  2. Open command prompt with window pointing at location of mstpcap.exe file.  For example:  c:\MSTP Tool>
  3. Daisy chain RS-485 adapter to trunk or connect Roam I/A to jack on MNB device.
  4. Command syntax is as follows:  mstpcap comx baudrate# do not type baudrate just speed.
  5. Control C to stop

Example:

If Using Roam I/A it requires highest baudrate available on the interface.

ROAM I/A Serial port

  • mstpcap comx 115200

If using Roam I/A Bluetooth

  • mstpcap comx 76800

If using an RS-485 adapter it will not support 76,800. This is a PC hardware limitation not a software limitation for further information or instructions on how to use baudrate 76,800 consult text file titled mstpcap.txt or Steve Karg's website: http://steve.kargs.net/bacnet/wireshark-and-bacnet-mstp . 

Example:

  • mstpcap comx baudrate speed

The capture file can be analyzed with WireShark Protocol Analyzer.  WireShark software is available at:

http://www.wireshark.org

Labels (4)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 5637
  • DavidPurser22
  • RobertAndriolo24
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore