How to reset the backup to flash circuit breaker on i2/b3 devices
  • How to reset the backup to flash circuit breaker on i2/b3 devices
  • RandyDavis
    RandyDavis
  • AbeMeran
    AbeMeran
  • GavinHe
    GavinHe
  • Dave_Shore
    Dave_Shore
  • JohnBoehmer
    JohnBoehmer
  • Cody_Failinger
    Cody_Failinger
‎2020-09-22 09:25 AM
Last Updated: Sisko GavinHe Sisko ‎2024-04-25 02:42 AM
After 2000 backups an attempt to perform a backup to flash results in the error 'Flash backup for this controller has been disabled.'
EcoStruxure Building Operation, Andover Continuum
  • b3 controller
  • i2 controller
Flash memory has a limited write count; Controllers implement a flash circuit breaker that trips after 2000 backup operations in order to protect the flash device from damage.
(Applies to all b3 and i2 controllers)
In EBO, a command has been added that will re-enable backup to flash after the circuit breaker has been tripped (2000 backups)
  1. From Workstation, in the object tree, right-click the i2/b3 device.
  2. From the context menu select, DEVICE->ENABLE BACKUP TO FLASH
Andover Continuum
From CyberStation command line set the ACCStatusBackup system variable of the device to ACCBackupEnable.
NOTE:
The flash circuit breaker CANNOT be reset from Script/Plain English.  This is by design as it was deemed too risky to allow resetting it programmatically.  A poorly written program could very quickly cause damage to the flash device.