How to Mass Create Trend Logs and Extended Trend Logs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to Mass Create Trend Logs and Extended Trend Logs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • PeterLarsen
    PeterLarsen
  • Derrick_Ratliff
    Derrick_Ratliff
  • sesa194431
    sesa194431
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3534 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to Mass Create Trend Logs and Extended Trend Logs

Picard Product_Support
‎2018-09-07 05:13 AM

Last Updated: Spock PeterLarsen Spock ‎2024-03-25 10:38 PM

Issue

How to Mass Create Trend Logs and Extended Trend Logs

Product Line

EcoStruxure Building Operation

Environment

Building Operation Workstation

Cause

If you did not create Trend Logs at the same time as you created the points or values, it is possible to create several trend logs or extended trend logs at the same time.

Resolution

For this example, we assume all of the values are in the same folder. You can hold down SHIFT to select multiple adjacent objects, or CTRL+click to select non-adjacent values

Mass Creation of Interval Trend Logs

  1. Select all of the Values you wish to add the same type of Log to
  2. Right Click and select New connected object>Trend

    1.png

  3. Select the Log type and the settings you wish to use.  Note that the log name will be the values name with either a prefix or suffix defined by the user

    2.png

  4. Be sure to Select a useful folder location, either same folder as each selected object, a different folder, relative to the selected object or a single folder for all created objects.
  5. Click Edit in wizard.
  6. Set the Interval Settings, if iterval log type is selected.

    3.png

  7. Click Next, configure initial meter settings if required, click next tehn click create

Mass Creation of Extended Trend Logs if required

  1. Select the group of Logs you wish to create Extended Trend Logs for
  2. Right Click and select New connected object>Extended Trend Log
  3. Enter the desired settings. Just as above, the Extended log will use the Log' name plus either a prefix or suffix

    4.png

  4. Be sure to Enter an appropriate Location. Use a folder on the ES if you wish these logs to show up on the Reports Server (Report server is not supported in EBO 2022 and higher).
  5. Click Edit in Wizard, Configure the Extended Log as desired, then click create.

Fore more information, refer to: Mass Creating Trend Logs and Mass Creating Extended Trend Logs

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 13750
  • bulk
  • MahmoudSayed23
  • PeterLarsen24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore