Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 7
    • 8
    • 9
    • …
    • 500
  • Next »

How to extract an XIF out of a Lon controller

Issue There may be a situation where the External Interface File (XIF) needs to be extracted out of the controller in order to properly set up the controller in a building automation system.  Product Line EcoStruxure Building Operation, TAC IA Series, TAC Vista Environment External Interface File (XIF) NodeUtil Loytec XIF Builder Cause These tools will help with the extraction of an XIF file. An XIF file is used to create a Niagara R2 shadow object, a Niagara G3 LMNL file, LonWorks device template, and a SmartStruxure device template.  Resolution The device manufacturer should provide an XIF, and in most cases, a DRF kit as well. The XIF provided by the manufacturer of the controller should be used first but if issues arise it may be required to extract the file from the controller. There are a number of tools available that will create an XIF, but the DRF kit cannot be created by any tool and must be supplied by the manufacturer. This MUST be provided along with the device. The list below covers some of the tools which are available. NodeUtil                          (header: bad,           NVs: ok,                      DMA/File-SCPTs are omitted) Vista's XIF-builder           (header: bad,           NVs: almost ok..,       DMA/File-SCPTs are omitted)  Loytec plugIn                  (does a perfect XIF from a device using Loytec's stack)   NodeUtil is available from the Echelon website (free registration is required) - The NodeUtilLauncher package attached makes it easy to use NodeUtil with Loytec interfaces. Loytec XIF Builder is available from the Loytec website (free registration is required) Using Lonmaker and the XIF Builder. Using NL220 and the XIF Builder. If the uploaded XIF still contains some detailed prompted error, refer to Error displayed when importing a device XIF into SmartStruxure.
View full article
Picard Product_Support
‎2018-09-11 02:59 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
9611 Views

MNL-V1RVx, MNL-V2RVx and MNL-V1RVx-2, MNL-V2RVx-2 differences

Issue Are there any functional differences between the following part numbers? MNL-V1RVx vs. MNL-V1RVx-2 MNL-V2RVx vs. MNL-V2RVx-2 Product Line TAC IA Series Environment I/A Series Micronet LON VAV controllers Cause The original part numbers MNL-V1RVx and MNL-V2RVx have been replaced with MNL-V1RVx-2 and MNL-V2RVx-2, respectively. The datasheet F-26365 references the original part numbers (MNL-V1RVx and MNL-V2RVx). Resolution There are no functional differences between the original and updated part numbers. The addition of “-2” in the part number signifies a mechanical enhancement to the VAV actuator assembly. This enhancement was made to reduce the operational noise level of the actuator, improving acoustic performance without altering functionality. Refer to datasheet F-26365-8.pdf for more technical specifications.
View full article
Picard Product_Support
‎2018-09-11 06:00 AM

Last Updated: Administrator CraigEl Administrator ‎2025-09-29 09:22 PM

Labels:
  • TAC IA Series
9639 Views

Where can standard graphics and snippets be found?

Issue Example graphics components required Product Line EcoStruxure Building Operation Environment TGML - Building Operation Graphics Editor Cause No standard graphics or components are supplied within the product. Resolution A Standard graphic component library can be downloaded from the Buildings Download Center. This consists of a number of Component Libraries that can be installed on a Workstation by double clicking on each one. In your TGML Editor, Right click in the Components window and select "Categories" you can then select the categories you require to see in your components section. There are also a lot of standard Snippets that have been developed by users around the world, these are available to download from the EcoStruxure Building Operation Forum - Graphics Exchange.
View full article
Picard Product_Support
‎2018-09-11 02:51 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:28 AM

Labels:
  • EcoStruxure Building Operation
9600 Views

BACnet MS/TP Bus Communication Troubleshooting Checklist

Issue BACnet MS/TP Bus Communication Troubleshooting Checklist Product Line TAC IA Series Environment I/A Series BACnet controllers (MNB-70, MNB-V1, MNB-V2, MNB-300, MNB-1000) on an MS/TP bus. Cause BACnet MS/TP Bus Communication Troubleshooting Checklist Resolution This checklist provides several settings/configurations to review when faced with a communication problem at the controller level. The content was compiled from different resources, summarized, and laid out in an easy-to-use manner so as to provide a quick-reference document. Power Each controller requires 24 VAC from a Class 2 transformer. See the Installation Instructions for each controller, and the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7, Chapter 1, “Power Supply Wiring”. Read-Only Flag Use the WorkPlace Tech Commissioning Tool (WPTCT) to check “Device Properties” of the controller. If the status is “Operational, Read-Only”, the input voltage to the controller may be too low. See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7, Chapter 1, “Power Supply Wiring”. Due to the short duration of the low-voltage condition required to set the flag, it is unlikely that you will see it when measuring the input voltage with a digital meter, so check the “Device Properties”, and correct the problem as noted on page 28 of the guide, (reduce transformer loading, reduce wire length between transformer and controller, and /or use wire with higher current rating). Diagnostic LEDs The MNB controllers have onboard diagnostic LEDs that are useful in troubleshooting. See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7, Chapter 3, “Communications Hardware Checkout”, Table: “LED Indications”, for a detailed description of the behavior of the LEDs and their diagnostic uses. Topology It is very helpful to draw the topology of the bus when you start troubleshooting. If there are no repeaters on the bus, the topology must be a daisy-chain, with no tees or stars. MS/TP network wiring to MN-Sx sensors must be run to the sensor, then to the next controller on the bus, in a daisy-chain; no tees or spurs are allowed. Maximum length of a wire segment is 4000 feet. See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7, Chapter 1, “MicroNet MS/TP Network Wiring”, for details on Communications wiring. Repeaters B-LINK-AC-S, Andover Controls MS/TP Repeater B-LINK-AC-F-S, Andover Controls MS/TP Repeater Fiber See the MicroNet BACnet Smoke Control Systems Manual, F-27419, for details on the use of these wire and fiber repeaters with MNB controllers. See F-27419, Chapter 5, “Approved MS/TP Repeaters”, including the wiring example. Maximum Number of Devices The maximum number of MNB controllers depends on the cable used, and the Baud Rate. See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7,Chapter 1, Table, “Approved Cable Types”. The MNB controllers are quarter-load devices, so a maximum of 128 or less are allowed on an MS/TP trunk, depending on the cable used. Addressing Avoid duplicate addresses. See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7, Chapter 1, “Required Configuration”, CAUTION: “Duplicate addresses on an MS/TP network trunk will result in erratic behavior, lost tokens, and disrupted communication. There is no software tool that will identify duplicate addresses on an MS/TP network trunk. Typically, if two controllers are set to the same address, one of the controllers will appear to be missing from the list, and the address shared by the two controllers will intermittently come and go from the list.” Biasing As a requirement of EIA-485 (formerly RS-485) bus topology, an MS/TP network must have a minimum of one set, and a maximum of two sets, of bias resistors in place. The MNB-300, MNB-1000, UNC-520, and ENC-520 have jumpers to enable or disable the bias resistors. See bulletin TB06-09, “RS-485 Bias Resistors and the UNC-520-2 / ENC-520-2”, page 3, for a photo of the bias jumpers on a UNC-520-2. Terminators A 120-Ohm End-of -Line (EOL) resistor is required across the “MS/TP +” and “MS/TP -” terminals at each controller at the end of a wire segment. The MNB-1000 and MNB-300 are equipped with a jumper-selectable end-of-line (EOL) termination resistor. The default position for the EOL jumper is “EOL termination not present.” See the MicroNet BACnet Smoke Control Systems Manual, F-27419, Chapter 5, “Approved MS/TP Repeaters”, Figure titled “UL 864 Listed MS/TP Repeater and Isolation”, Note 4, for an important exception, requiring external EOL for the MNB-300 and MNB-1000, when used on a bus with an approved repeater. If a UNC-520-2, ENC-520, MNB-V1 or MNB-V2 is installed at the end of the trunk, install a discrete 120 Ohm EOL resistor, part number EMSC-546, or equivalent. Cable Use of the proper cable is critical to the communications performance of the networked controllers. See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7,Chapter 1, Table, “Approved Cable Types” for a list of recommended cable types. As shown in the table, cable selection affects both the maximum number of controllers allowed on the trunk, and the maximum baud rate. WorkPlace Tech Interface The MNB-ROAM-IA is the recommended communications converter for connecting WorkPlaceTech, including the WPT Commissioning and Flow Balance Tools, to an MS/TP trunk. It is supported in versions 5.7.1 and later. A converter that had been recommended earlier, the B & B Electronics model USOPTL4, was found not to operate reliably at speeds above 38.4 K baud. (See Direct MS-TP Connection with B & B Electronics Converters (Revised) - TB08-02-02 for details). The MNB-ROAM-IA supports Bluetooth wireless connection between WorkPlace Tech suite and the MS/TP network, for distances up to about 40 feet. One external Bluetooth adapter has been tested and approved - the Belkin USB adapter. (See Supported models of Bluetooth adapters with WorkPlace Tech for details). A problem we have seen with some MNB-ROAM-IAs is when trying to add Bluetooth device, the Bluetooth Wizard identifies it as "Serial Port Device, Unknown: Major(0), Minor(0)" instead of "tac-RoamIA:xxxxxxxx" where xxxxxxx is the serial number. There is no way for WPT to use the ROAM-IA if the computer can’t pair with it. Currently, there is no known solution, other than replacing the device. Divide and Conquer This is a strategy for dividing a bus into smaller sections in order to isolate a controller or section of bus that might be causing communication problems. The general idea is to divide the bus in half, and see if communications are possible from one end to the other end. If not, divide each half again, and continue until the problem(s) are found. Reference Documents F-27360 TAC I/A Series MicroNet BACnet Wiring, Networking, and Best Practices Guide F-27358 TAC I/A Series MicroNet BACnet Workplace Commissioning Tool and Flow Balance Tool User’s Guide F-27456 TAC I/A Series MicroNet BACnet MNB-70 Zone Controller Installation Instructions F-27345 TAC I/A Series MicroNet BACnet MNB-300 Unitary Controller Installation Instructions F-27346 TAC I/A Series MicroNet BACnet MNB-V1, MNB-V2 VAV Controller Installation Instructions F-27347 TAC I/A Series MicroNet BACnet MNB-1000 Controller Installation Instructions F-27419 TAC I/A Series MicroNet BACnet Smoke Control Systems Manual
View full article
Picard Product_Support
‎2018-09-09 08:26 AM

Last Updated: Crewman ContentModerator ‎2025-10-15 03:37 AM

Labels:
  • TAC IA Series
9548 Views

Reading the Serial Number from a Mifare card

Issue How can Continuum be setup to read the 32 bit serial number from a Mifare smart card for use in access control? Product Line Andover Continuum Environment Using iClass serial number readers: R10, R15, R30, R40, RK40 Custom Wiegand, AccessFormat array Custom Format Cause Mifare smart cards that have been provided and programmed by others may not have the keys available to allow a reader to access the data on the card. Without sending the cards away for re-programming how can the card still be used for access control. Resolution The HID iClass readers (R10, R15, R30, R40, RK40) have the ability to read the 32 bit serial number from a Mifare Smart card. These readers will output a single 32 bit Wiegand string representing the card serial number. To use this on Continuum: Create a numeric point called "AccessFormat" and define it as a manual array with 19 entries. Create a Plain English program in the controller to fill up the array with values as per the Mifare Serial Number spreadsheet. In the door configuration select "Custom Format" and ensure one of the 4 site codes is set to 0. Swipe the card at the reader and open a list view of Events, this will show the card number as the serial number from the card. Create a new Person with card type Custom Wiegand, Site code 0 and set the Card number to the serial number as read in the list view. This may be a 9 or 10 digit number. Notes: If using card numbers in Plain English Programs or displaying in Pinpoint Graphics, you will be restricted to using a maximum of 6 digit numbers (maximum card number being 999,999). See Loss of resolution on metering points when the number is 7 digits or longer for details on this restriction. The old style Personnel editor will not allow the entry of site codes of 0. Use Personnel Manager or set attributes in List Views of Personnel.
View full article
Picard Product_Support
‎2018-09-10 07:40 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:04 PM

Labels:
  • Andover Continuum
9535 Views

Device Administrator SSL Certificate Validation Failed

Issue The SmartX server has a "?" under the server name field and shows the error "SSL certificate validation failed!" as the server state in Device Administrator. In some instances, this may cause a failure to upgrade of the SmartX Server displaying these symptoms.  Product Line EcoStruxure Building Operation Environment Building Operation Device Administrator Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Automation Server Cause The SmartX Server is added into Device Administrator over HTTPS 443 but does not have a valid SSL certificate installed. Resolution Change the connection from HTTPS 443 to HTTP 80 This can be done by clicking into the server settings (click on the "?") Select "Edit Connection"   Change the EBO Server Protocol from HTTPS to HTTP  Create a trusted chain between Device Administrator and the problem SmartX Server using a self-signed certificate by following this workflow
View full article
Lieutenant JG Robert_Davis Lieutenant JG
‎2019-12-19 02:07 PM

Last Updated: Picard RobertAndriolo Picard ‎2021-11-25 03:29 PM

Labels:
  • EcoStruxure Building Operation
9422 Views

Replacement for discontinued I/A Series hardware UNC-410, UNC-520, ENC-410 & ENC-520

Issue Replacement for discontinued I/A Series hardware UNC-410, UNC-520, ENC-410 & ENC-520 Product Line TAC IA Series Environment I/A Series R2 Universal Network Controllers UNC-410 and UNC-520 I/A Series G3 Enterprise Network Controllers ENC-410 and ENC-520 Cause Due to component availability, the following UNC/ENC parts have been discontinued as of 1st December 2013.  Resolution Discontinued UNC/ENC controllers can be replaced with the JACE 603, JACE 645 controllers series. The JACE 603 and JACE 645 are the first network controllers that can run either R2 or G3 Niagara applications when a corresponding license is installed.  New sites and expansions – these Network Controller parts come with the same metal box enclosure as the products they replace: Retrofit applications – these Network Controller parts are a replacement board that fits into an existing UNC/ENC enclosure: Refer to PA-00251 for details.  *Note - The parts for new sites and expansions are not available for all regions. Contact your local Schneider Electric sales representative if you have any questions.  * Updated May 2015 The parts TRD-RB-603-R2 and TRD-RB-645-R2 are not longer available. See below for the equivalent parts. TRD-RB-603-R2 > TRD-RB-603 + TRD-R2-RB-6XX TRD-RB-645-R2 > TRD-RB-645 + TRD-R2-RB-6XX _______________________________________________________________________________________________________ * Updated March 2019 The JACE-603 and JACE-645 has been discontinued as of June 2018.  The recommended replacements are the EcoStruxure Building Operation AS-P or the I/A Series JACE-8000. Refer to PA-00592 I/A Series JACE 600 End of Commercialization. 
View full article
Picard Product_Support
‎2018-09-11 06:35 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:55 AM

Labels:
  • TAC IA Series
9422 Views

How to set the Enterprise Server IP address

Issue How to change the IP address in the EC/ES software when it is grayed out. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Central (EC) and Enterprise Server (ES) Building Operation WorkStation Cause The EC/ES IP address is grayed out in the Network Tab of the Server Properties and cannot be changed.  This setting is only used to view the IP address that the server is currently using - typically the IP of the network interface card of the PC running this.  To change this setting it must be done through the Communications TAB of the server as detailed in the resolution.  Resolution EcoStruxure Building Operation 2.0 and above EBO 2.0 and above now supports multiple NIC configurations, see 2.0.1 Release Notes for details, in particular, the following note.   Note: That from 2.0 the server will still listen for incoming requests on all network adapters so this setting is only used for choosing which communication settings that the server will use to communicate with child servers. This allows other IP protocols on different networks, e.g. BACnet, Modbus, etc. to communicate with the Server.    It is now possible to select which network adapter the Enterprise Central and the Enterprise Server use.  See the following WebHelp Topic Configuring Network Interface Card for an Enterprise Server or for an Enterprise Central StruxureWare Building Operation 1.9 and below  When the IP address of the computer changes the ES will automatically update the "IP/DNS Address" in the Properties, Network tab. If your computer has multiple network connections, ensure that the Network Interface Card (NIC) to be used for the SmartStruxure network is set to be at the top of the list in the Adapters and Bindings. Go to the computer's Control Panel > Network Connections Select "Advanced, Advanced Settings... " from the menu. In the "Connections:" section, select the Network Connection to be used and press the up arrow to move it to the top of the list. For Windows 7 / Server 2008 See the following link on how to change the order of protocol bindings: How to change the network connection priority in Windows 7 For Windows 8 and beyond, please refer to Adapter priority setting unavailable in Windows 10 In addition to the ES Network Properties, there is also the Communication tab in the ES that lists all of the Server IP addresses in the system. If these need to be changed this can be done by selecting the server and clicking on the "Show/ Hide Communication settings" button circled in red below.
View full article
Picard Product_Support
‎2018-09-10 12:50 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:45 AM

Labels:
  • EcoStruxure Building Operation
9382 Views

Which SQL query can be used to identify the database layout being used?

Issue Which SQL query can be used to identify the database layout being used? Environment Vista 5.1.X log database Cause With the release of Vista 5.1.7 came a new logdatabase layout which is designed to improve performance especially in the area of trend and event log management. This means that there are now 2 possible logdatabase configurations. It can be important to know which version is being used before running any queries or accessing the external log data with external tools. Resolution The following query will return the database layout version when run in SQL management studio: select taclogdata.dbo.DSS_SchemaVersion() More information can be found in the Vista 5.1.7 release notes.
View full article
Picard Product_Support
‎2018-09-06 12:22 PM

Labels:
  • TAC Vista
9352 Views

Hotfix file signature validation error during hotfix installation

Issue During installation of hotfix for EBO you get a "Hotfix file signature validation" error saying that Device Administrator cannot verify the issuer of the file signature's certificate.   In older versions of Device Administrator you might get an alternative error message "Invalid hotfix file" saying that the file does not have a valid Schneider signature. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Device Administrator Offline system Version 3.1 and later Cause EBO hotfixes for SmartX Server are signed with a certificate to ensure that only valid files can be used. This certificate must be validated before you can use a new PC to install a hotfix. If the PC has not had any internet connection while previously installing a hotfix or does not have an internet connection, the certificate cannot be validated and hotfix installation therefore fails. Resolution There are two solutions Solution 1 Connect your PC to the Internet and install the hotfix on a SmartX Server. The certificate is validated, and the PC can subsequently be used to install hotfixes on other SmartX Servers, even if you are offline. Solution 2 You can manually import certificates and CRL (Certificate Revocation List) Download and save the following files: http://s1.symcb.com/pca3-g5.crl http://sv.symcb.com/sv.crl If the above URL's are blocked by your browser please download them here or the attached ZIP file.  Start a command prompt (cmd.exe) as administrator. Browse to the folder where the files from step 1 are stored. Run the following commands: CertUtil -AddStore CA pca3-g5.crl CertUtil -AddStore CA sv.crl Export host, intermediate, and root certificates from the hotfix file. Install the 3 certificates with the default selection. Restart Device Administrator and install the hotfix. Video for step 5 and 6:     November 2025: Added Intermediate and Root Certificates for Global Sign. Root: GlobalSign Timestamping Root R45 Intermediate: GlobalSign R45 AATL TimeStamping Root CA 2021
View full article
Guinan MikaelKrantz Guinan
‎2021-02-04 06:22 AM

Last Updated: Picard David_Purser Picard ‎2025-11-07 12:08 PM

Labels:
  • EcoStruxure Building Operation
9305 Views

When logging in to an AS or ES, SBO WorkStation freezes or it takes a very long time to log in

Issue When logging in to an AS or ES, WorkStation freezes or it takes a very long time (>30 minutes) before the login process finishes. Building Operation WorkStation hangs on "Reading data..." when trying to login to an AS or ES Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation WorkStation Cause The problem is related to a delay when validating the license details. It only seems to happen when running a mixed EBO/SBO 1.9.3 system and after having EBO license administrator 2.0.1 previously installed. Resolution Run the SBO License Server Reset tool and perform Reset - Simple Log in to WorkStation, and if the hang or freezing is still present, then follow the next set of instructions. Run Diagnostics in the License Administrator and take note of all the ACT (Activation) and Entitlement IDs Return all the licenses Close all WorkStations and stop all SBO/EBO processes (whichever may be running) Uninstall all License Administrator and License Server Run the SBO License Server Reset tool and perform a Reset - Complete (you will get an output of the commands and result) Install the latest released version of License Administrator and License Server (the latest released version of License Administrator has fixes for virtual servers and some cyber security vulnerabilities, note that License Administrator is backward compatible with earlier SBO versions) Activate the licenses based on the info from step 3 Note: If running the demo license, steps 3 and 4 may be skipped. If problems continue to occur, then send the above details collated (in step 3) and email this/contact support.
View full article
Picard Product_Support
‎2021-01-14 04:23 PM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-28 08:33 AM

Labels:
  • EcoStruxure Building Operation
9235 Views

Additional information needed on the FLEXnet licensing system

Issue For further information, refer to the FLEXnet Licensing End User Guide, available on the Flexera website. Product Line TAC Vista Environment Vista 5 Workstation FLEXnet Licensing Cause If you get this error and attempt to find the End User Guide, you will discover that the company that produces the FLEXnet software has gone through several name changes: Macrovision to Acresso to Flexera. Resolution If you would like a copy of this document, you can find the FLEXnet License Administration Guide (previously called the End User Guide) here.
View full article
Picard Product_Support
‎2018-09-07 11:43 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • TAC Vista
9233 Views

Troubleshooting EBO license violation issues

Issue  EBO can have license violation bar without a known reason. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause License enforcement is the process of checking whether a software application has a valid license available to it at runtime. If you do not have enough licenses, a license violation occurs. This is accomplished by a license violation bar in WorkStation and WebStation.   Firstly, the license violation will be yellow, and it can be hidden for 8 hours. You can use Hide to hide the License Violation bar for 7 days. After 7 days, the Hide function is disabled. After 30 days, the bar turns red. Resolution Below information can be collected to help in troubleshooting: Refer to the document Part Number Summary and Hardware Software Matrix for software and features that need licenses and note that some feature licenses can be inherited from parent server to child servers. Get a screenshot of the License information page in the control panel, make sure to have all content in license information page are shown in the screenshots, ex child servers' status. It can tell which feature needs a license or which child server needs a license, refer to License Information Get the License Diagnostics, and entitlement certificates to make sure that required licenses are activated. Install the latest CP/hotfix to make sure that the system is not affected by one of the known license related defects, Make sure that all EBO servers have correct date and time, incorrect date and time can cause license violation, as explained in: Incorrect Automation Server date and time leads to license violation - Schneider Electric Community See this article if you do not see the License banner, but still get a License Violation alarm: License Violation Alarm Triggered Without License Violation Banner displayed - Schneider Electric Community  Check Known issues community. Get screenshots for the following: In ES, "System/LicenseManager/LicenseStatus/ConnectedASLicenseStatus" will show all connected Automation Servers. Show the license violation tab to know which Automation Server has violation as Automation Server may have violation although license information doesn't show that, ex. if the "Change Control" feature is enabled in an Automation server and ES doesn't have a license for it. For parent server and any server that has violation, search in folder "/System/LicenseManager/LicenseStatus". In the object name, write "*" and add columns License Violation, Checked Out License, Available Licenses, Required Licenses, and Installed Licenses. Export the results to XLSX. Check license Metadata for the parent server and any servers have license violation, search in folder "/System/LicenseManager/LicensingMetadata". In object name, write "*" and add columns FeatureVersion, FatureName, ProductVersion, EntitlmentID and Activation ID. Export the results to XLSX.   Get screenshot from FlexNet Publisher web interface, localhost:8888, concurrent tab. Make sure all features are shown in the screenshot, and the entire webpage can be saved instead of taking screenshots. If the server has just started, wait for some minutes till all data is collected.   Collect the logs and configuration files listed below: Log files located in C:\Program Files (x86)\Schneider Electric EcoStruxure\Building Operation x.x\License Server\logs Configuration file located in C:\Program Files (x86)\Schneider Electric EcoStruxure\Building Operation x.x\License Server\conf Using EBO WorkStation, go to module, '/System/Modules/Trace/Loggers/nsp/nsp.csc/nsp.csc.licensemanager", set trace level to debug, reproduce the issue, if possible. Collect the server logs, then set the module trace level back to "information", refer to Collect logs from an Automation Server - Communities and Collect logs from the Enterprise Server and Enterprise Central - Communities.
View full article
Kirk Mahmoud_Sayed Kirk
‎2022-09-19 05:25 AM

Last Updated: Picard RobertAndriolo Picard ‎2025-08-25 12:49 AM

Labels:
  • EcoStruxure Building Operation
9222 Views

"Object already exists" "Cannot add a server that is a clone..." error when creating new AS under an ES

Issue When attempting to add a new Automation Server under an Enterprise Server that already has one or more AS servers attached it results in an "Object already exists" error ERROR Object already exists Domain: Data access Info:~/System/Server Communication/Models/xxxxxxxx/Members/xxxxxxxxx in module Run Db manager xxxxxxxx = Global Unique Identifier (GUID) The GUID underlined in red in the screenshot above is the duplicated Id. Additional error message possible depending on EBO release version. ERROR: Server already part of a multi server system Domain: Invalid data  Info: Attempt_To_Add_An_Object_To_The _System_That_Already_Exists ERROR: Cannot add a server that is a clone of a server that already exists in your system Domain: Startup  Technical Info: An added server with name 'XXXXX' has the same unique id as an existing server with the name 'YYYYY' which is not allowed. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server  Building Operation Automation Server Bundled Cause The AS that is being added has been restored from a backup created from one of the servers that are already configured under the ES resulting in a duplicate GUID. Resolution Backup the Server Restore the Server and make sure to select "Restore configuration with new IDs" check box. This will ensure that a new GUID is assigned to the AS. Add the Server from ES Please note that the restore function to re-use configuration data from a backup set is supported for all Building Operation supported protocols, except for BACnet and b3 BACnet.  To read more see Web Help To read more see Web help: http://help.sbo.schneider-electric.com/topics/show.castle?id=10228&locale=en-US&productversion=1.7 To read more see Web help: http://help.sbo.schneider-electric.com/topics/show.castle?id=10228&locale=en-US&productversion=1.7
View full article
Picard Product_Support
‎2018-09-10 04:08 AM

Last Updated: Picard RobertAndriolo Picard ‎2021-09-19 04:19 PM

Labels:
  • EcoStruxure Building Operation
9133 Views

Jace 8000 Serial Port Issue

Issue There are missing serial ports (COM ports) when viewing the 'SerialPortService' under 'PlatformServices' in a station. Some or all COM ports will be missing. Local serial ports and/or serial ports of the attached modules do not function. Product Line TAC IA Series Environment I/A Series AX Jace 8000 Cause This could show up for several reasons. This was found during an upgrade to Niagara 4.2. It was also experienced when converting a Jace8000 running N4.2 (or lower N4 version) to AX. This can occur with a new out of the box J8000 to AX conversion if you do not first commission the Jace8000 to Niagara 4.4 or above before converting to AX. All of these problems are due to older version USBbinary files not being properly updated during commissioning. The LON option module (side-car) might stop communicating on the LON trunk due to the same binary file issue. Resolution This can be fixed via serial shell; either by direct connecting with a mini-USB cable or via ssh after it is enabled from the Platform Administration view. It is recommended that PuTTY.exe be downloaded and used as the terminal program to access the shell. The directions below are CASE-sensitive and must be entered exactly as shown. We recommend that you do not type these commands, but rather use copy-and-paste to avoid typographical errors. This is especially true of the usbSerialNumber itself -- it is case-SENSITIVE. By default, PuTTY.exe uses mouse-left-click-drag-and-highlight as an automatic shortcut for copy. Mouse-right-click is the automatic shortcut for paste. Once logged in type: Display the USB serial number(s) sh [hit enter] $ ls /etc/usb [this will display the USB serial number(s), if nothing displays see the note* at the bottom] 85091090FPGGS41 [this is an example serial number] Display the available binary files $ ls -Rp /sys/images/usb [this will display the available binary files] /sys/images/usb/applet-flash-sam4s16.bin* /sys/images/usb/vid03eb/pid2404/Tridium232-1_r03.bin* /sys/images/usb/vid03eb/pid2425/Tridium485-2_r04.bin* Note: You could also see '_r05' instead of '_r04'. If this is your result, make sure to update using the line below. /sys/images/usb/vid03eb/pid2425/Tridium485-2_r05.bin* The USB ports unavailable is due to the 'Tridium485-2_r04.bin' (or Tridium485-2_r05.bin) file was not written to the USB serial number file. This can be corrected by updating the USB serial number file with the correct binary file using the statement below. Make sure to replace the X in the statement with the highest number binary found in 'STEP 2' above. $ echo /sys/images/usb/vid03eb/pid2425/Tridium485-2_r0X.bin > /etc/usb/<usbSerialNumber> Update the binary file Using the example serial number and USB binary file found in STEP 2: $ echo /sys/images/usb/vid03eb/pid2425/Tridium485-2_r05.bin > /etc/usb/85091090FPGGS41 Make sure to use the serial number found when 'ls /etc/usb' was called. If there is more than one serial number found, write the command multiple times, once for each serial number found. Also, make sure to use the highest USB binary file number found. Currently r05 is the highest number. If '_r05' is returned as the available USB binary file, make sure to use '_r05' when updating the USB serial number. After a reboot, check the SerialPortService to confirm the ports are restored. *Note: if no usb serial number was found using ls /etc/usb another method would be to call for the slog by typing: $ sloginfo An error would have been logged here during the last startup and will display the serial number; example output: Oct 10 13:42:06 1 6 0 serusb_is_device_supported: Device 2 on bus 0 unrecognized. Using CDC-ACM Class Oct 10 13:42:07 4 11111 0 error opening /etc/usb/85091090FPGGS41 rc=-1 In addition to the symptoms listed above, the inability to communicate with the LON option module may cause the any of the following messages in the Serial Shell and/or the Platform Administration System Logs: error opening /etc/usb/<serial number here> rc=-1 U50Read returned unknown rc = 8!!! io_write failed ldvRC=7, length=<various numbers of bytes> The Station will most likely show that the LON network is up, but the LON devices are down. The device fault cause may show "unable to write" or something similar.
View full article
Guinan RandyDavis Guinan
‎2019-06-20 08:28 AM

Last Updated: Commander JonGreen Commander ‎2020-07-27 10:07 AM

Labels:
  • TAC IA Series
9152 Views

[Dev File] Xenta 5/7/9xx Modbus RTU Integration to Cummins ModLon 2 Gateway

Issue Integration to the Cummins ModLon 2 gateway with the Xenta 500 / Xenta 700 / Xenta 900 and Modbus RTU Product Line TAC Vista Environment Xenta 511, 527, 701, 711, 721 (5.1.5 up) Xenta 731, 913 (all versions) XBuilder Cummins ModLon 2 Gateway Cause Disclaimer: This device template is intended to provide a starting point for an integrator, and is in no way written to be the mandatory points list for your integration effort. Product Support Services-Dallas has written this device template in an effort to give our customers a starting point and solid example of how to develop a device template for the above product. The integrator will be responsible for any additions or modifications to this device template. Please report any problems to PSS Dallas at product.support@buildings.schneider-electric.com Resolution Please us the following .dev files as a starting point and a guide to the integration. This .dev file contains a set list of registers that PSS assumed would be seen as critical and important to the integration process. If any other data is needed please see this supported document to make the necessary changes. One generator: .dev file Two generators: .dev file   To use these files in Xbuilder please follow these steps: Extract the .dev file from the .zip file in the link above, and place it on your harddrive. In Xbuilder, right click on the Modbus Master device and chose Add Device Browse to the needed .dev file and choose Open. Rename the newly added device to a unique name within the Modbus Master network.
View full article
Picard Product_Support
‎2018-09-07 03:33 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 08:15 PM

Labels:
  • TAC Vista
9142 Views

Preparing and importing a signed CA certificate

Issue There is no information on how to create and prepare signed certificates for import in Building Operation. PEM file format has to be used. If another format is used or the certificate files are not correct, you get a message like this when importing SAXParseException: Reference to invalid character number in line X column Y Product Line EcoStruxure Building Operation Environment Certificates Cause There is no information on how to create signed certificates in Building Operation. Resolution Make sure that when preparing the pfx file that the full chain of trust is included in the pfx file. You have various options when preparing a pfx certificate export file, and the private keys and chain of trust are options that must be selected. Otherwise, you won't extract the intermediate certificate or the private key if not included. Complete a Certificate Request and then request a certificate in PEM format in a .pfx file "container".  Extract the CA certificate, Intermediate certificate, and private key using the following OpenSSL commands. After executing each command, enter the password if prompted. Make sure you reference the right pfx file. Below filename.pfx is used as an example Make sure you enter the commands manually and do not copy/paste from this article Download OpenSSL tool here or use OpenSSL installed with EBO  openssl pkcs12 -in filename.pfx -out host.pem -nodes -clcerts -nokeys openssl pkcs12 -in filename.pfx -out inter.pem -nodes -cacerts -nokeys openssl pkcs12 -in filename.pfx -out privkey.prv -nodes -nocerts The three files produced must then be parsed of any characters that aren't in the part of the certificate/key and in PEM format (or PRV if private key) - basically all the characters before "-----Begin Certificate-----" or after "-----End Certificate-----". Ensure each file ends with a blank line and that a blank line separates each section. This can be done in any text editor; however, this example uses Notepad++ with the "Show All Characters" button selected.  Import the files into SBO using the certificate manager in the Control panel. File type conversion If the host and intermediate certificate are in crt, cer or der format, you can convert them to pem format using the following method/command: openssl x509 -outform der -in certificate.cer -out certificate.der openssl x509 -inform der -in certificate.der -out certificate.pem Replace "certificate.cer" with the name of your file Determining certificate file type To determine which filetype a given certificate file has (PEM, DER, or pkcs12/pfx), you can use the following commands (replace "cert.crt" with the name of your file). A valid output will confirm the file type. PEM openssl x509 -in cert.crt -text DER openssl x509 -in cert.crt -inform DER -text pkcs12/pfx openssl pkcs12 -in cert.crt -info
View full article
Picard Product_Support
‎2018-09-11 07:54 AM

Last Updated: Picard RobertAndriolo Picard ‎2022-12-01 01:23 PM

Labels:
  • EcoStruxure Building Operation
9065 Views

Using IAC 420 as a Replacement for Obsolete IAC 400 Controllers

Issue A failed IAC 400 controller requires replacement, but only an IAC 420 is available. This article provides guidance on using the IAC 420 as a substitute, including key differences and configuration considerations. Product Line Satchwell MicroNet, Satchwell Sigma Environment IAC 400 IAC 420 Cause The IAC 400 controller is no longer manufactured or supported, making direct replacements unavailable. In legacy systems, the IAC 420 may be the only remaining compatible controller on hand, despite also being obsolete. However, differences in hardware and configuration between the two models can lead to confusion or improper operation if not addressed. Resolution Key Differences Between IAC 400 and IAC 420 Feature IAC 400 IAC 420 Input Types 3 x Temperature Inputs 2 x Analogue Inputs 1 x Digital Input 6 x Universal Inputs Communication Cable Screening Terminal 3 used for earthing the communication cable screen Screen must be connected to a good earth, not to Terminal 3 Tables & Offsets Specific to IAC 400 input types Different due to universal inputs—review updated tables and offsets ⚠️ Important: Because the IAC 420 uses universal inputs, existing configurations from the IAC 400 will not directly transfer. You must update the input tables and offsets accordingly. Refer to the document: IAC Controllers – Tables and Offsets for detailed guidance. Wiring Information IAC 400 Wiring Details: Download IAC400A.pdf IAC 420 Wiring Details: Download IAC 420 - DS2801A-1205.pdf Recommendations Compatibility Check: Ensure the IAC 420’s universal inputs can be configured to replicate the IAC 400’s original input types. Documentation Review: Carefully consult wiring diagrams and configuration tables to avoid miswiring or misconfiguration. Testing: After installation, verify all inputs and outputs function as expected. Additional Notes Both the IAC 400 and IAC 420 are obsolete. For long-term reliability, consider migrating to a supported controller platform within the EcoStruxure Building Operation suite.
View full article
Picard Product_Support
‎2018-09-10 11:46 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-29 10:07 PM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
9005 Views

BACnet Interface polling interval settings and usage

Issue How are the 'Advanced Polling Configuration' settings under the BACnet interface to be used? Product Line EcoStruxure Building Operation Environment Enterprise Server (ES) Automation Server (AS) Cause These settings can be used to reduce traffic on the BACnet networks that can overload both the EBO server as well as the devices being polled. Resolution The settings are used to specify an amount of time (in milliseconds) that the server should wait after completing a polling cycle on the applicable BACnet network before starting the next cycle. A polling cycle is the set of point being polled on a particular network interface. For example, lets assume that the Minimum polling interval for MSTPA network has been set to 1000 ms, if you are polling 30 points on MSTP port A then the BACnet plug in will do synchronous ReadProperty requests to poll each of the 30 points one at a time. Once the 30 points are polled, (one polling cycle) the BACnet plug-in will delay 1000ms before polling the 30 points again. (next polling cycle) NOTE: The settings apply to polling ONLY and do not affect communications done via change of value (COV) To find a proper value to use, it is recommended that you start with 1000 ms and then adjust the value up or down based on polling performance. If the polled values update fast enough, increase the minimum polling interval to reduce CPU usage. If the polled values become too sluggish, reduce the minimum polling interval until performance returns to satisfactory levels. It may take some trial and error to find the optimum balance.
View full article
Picard Product_Support
‎2018-09-11 01:11 PM

Last Updated: Captain SharlinaRe Captain ‎2022-09-20 08:45 AM

Labels:
  • EcoStruxure Building Operation
9012 Views

Using WireShark to analyse communications on an Ethernet network

Issue General use of the Wireshark program. Product Line Access Expert, Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Pelco, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Ethernet Networks Cause General Information on using WireShark. Resolution Wireshark is an Ethernet packet analysis programme, Which can be downloaded from: Latest version available from Wireshark Locally stored version 1.0.9 Installing Wireshark If necessary, unzip the WireShark executable file to a suitable location on the PC/Laptop you wish the programme to be installed on. Run the executable file and follow the on-screen instructions. Rules for capturing LAN traffic using Wireshark: Do not use a switch or router to connect the LAN capture PC to the network as these will filter important network activity that you will need to see. You will want to capture everything that is passing over the network at the point of concern. Usually, this means tapping into the ethernet at the Controller or controllers, that is having an issue. midBit-Technologies-LLC-10-100 is an example of a device that can be used to easily tap into the network to take the capture. The monitoring PC must see all traffic from the controller's point of view. The monitoring PC can be connected in either two ways: Connected to the network at the controller The customers IT department can mirror all the network traffic from the controllers port to another port the PC can be connected to. If connected to the network at the controllers, the connection must be made through a true ethernet hub. A hub will not selectively filter important network traffic as a switch or a router will do. More information on what a "true ethernet hub" can be found at http://wiki.wireshark.org/HubReference There are however some switches that feature port mirroring, please see How to Configure a NETGEAR Prosafe Plus Switch for Mirroring. If connected to a mirrored port, the port must mirror 100% of the network traffic to and from the controller. No filtering should be done. Once a complete capture file has been obtained it can be filtered after the fact using WireShark or EtherReal. Using Wireshark Run WireShark Start a trace by choosing the "Capture" menu and then select "Interfaces" Choose the appropriate interface. Generally, this can be identified by its IP Address, but if not, then the packets increasing are an indication. Press the "Start" button. The trace will start and will be similar to the following screenshot. After an appropriate time, the trace can be stopped by selecting "Capture" menu and "Stop" To save the capture file, choose "File" menu and "Save As".
View full article
Picard Product_Support
‎2018-09-07 11:51 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:07 AM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Access Expert
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
8993 Views
  • « Previous
    • 1
    • …
    • 7
    • 8
    • 9
    • …
    • 500
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore