Preparing and importing a signed CA certificate

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Preparing and importing a signed CA certificate
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • David_Purser
    David_Purser
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Benji
    Benji
  • Dave_Shore
    Dave_Shore
  • DavidChild
    DavidChild
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
9056 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Preparing and importing a signed CA certificate

Picard Product_Support
‎2018-09-11 07:54 AM

Last Updated: Picard RobertAndriolo Picard ‎2022-12-01 01:23 PM

Issue

There is no information on how to create and prepare signed certificates for import in Building Operation. PEM file format has to be used. If another format is used or the certificate files are not correct, you get a message like this when importing SAXParseException: Reference to invalid character number in line X column Y

Product Line

EcoStruxure Building Operation

Environment

Certificates

Cause

There is no information on how to create signed certificates in Building Operation.

Resolution

Make sure that when preparing the pfx file that the full chain of trust is included in the pfx file. You have various options when preparing a pfx certificate export file, and the private keys and chain of trust are options that must be selected. Otherwise, you won't extract the intermediate certificate or the private key if not included.

  1. Complete a Certificate Request and then request a certificate in PEM format in a .pfx file "container". 
  2. Extract the CA certificate, Intermediate certificate, and private key using the following OpenSSL commands.
    • After executing each command, enter the password if prompted.
    • Make sure you reference the right pfx file. Below filename.pfx is used as an example
    • Make sure you enter the commands manually and do not copy/paste from this article
  3. Download OpenSSL tool here or use OpenSSL installed with EBO 
    • openssl pkcs12 -in filename.pfx -out host.pem -nodes -clcerts -nokeys
    • openssl pkcs12 -in filename.pfx -out inter.pem -nodes -cacerts -nokeys
    • openssl pkcs12 -in filename.pfx -out privkey.prv -nodes -nocerts
  4. The three files produced must then be parsed of any characters that aren't in the part of the certificate/key and in PEM format (or PRV if private key) - basically all the characters before "-----Begin Certificate-----" or after "-----End Certificate-----". Ensure each file ends with a blank line and that a blank line separates each section. This can be done in any text editor; however, this example uses Notepad++ with the "Show All Characters" button selected. Example.png
  5. Import the files into SBO using the certificate manager in the Control panel.

File type conversion

If the host and intermediate certificate are in crt, cer or der format, you can convert them to pem format using the following method/command:

openssl x509 -outform der -in certificate.cer -out certificate.der
openssl x509 -inform der -in certificate.der -out certificate.pem

Replace "certificate.cer" with the name of your file


Determining certificate file type

To determine which filetype a given certificate file has (PEM, DER, or pkcs12/pfx), you can use the following commands (replace "cert.crt" with the name of your file). A valid output will confirm the file type.

PEM
openssl x509 -in cert.crt -text

DER
openssl x509 -in cert.crt -inform DER -text

pkcs12/pfx
openssl pkcs12 -in cert.crt -info

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 18047
  • CraigEllis21
  • DavidPurser22
  • DavidShore22
Was this article helpful? Yes No
86% helpful (6/7)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore