Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Hotfix file signature validation error during hotfix installation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Hotfix file signature validation error during hotfix installation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • David_Purser
    David_Purser

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
6 Likes
11763 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Hotfix file signature validation error during hotfix installation

MikaelKrantz Champion
‎2021-02-04 06:22 AM

Last Updated: David_Purser Champion ‎2025-11-07 12:08 PM

Issue

During installation of hotfix for EBO you get a "Hotfix file signature validation" error saying that Device Administrator cannot verify the issuer of the file signature's certificate.

Hotfix file signature validation.png

 

In older versions of Device Administrator you might get an alternative error message "Invalid hotfix file" saying that the file does not have a valid Schneider signature.

cert-error.png

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled
  • Device Administrator
  • Offline system
  • Version 3.1 and later

Cause

EBO hotfixes for SmartX Server are signed with a certificate to ensure that only valid files can be used. This certificate must be validated before you can use a new PC to install a hotfix.

If the PC has not had any internet connection while previously installing a hotfix or does not have an internet connection, the certificate cannot be validated and hotfix installation therefore fails.

Resolution

There are two solutions

Solution 1

Connect your PC to the Internet and install the hotfix on a SmartX Server. The certificate is validated, and the PC can subsequently be used to install hotfixes on other SmartX Servers, even if you are offline.

Solution 2

You can manually import certificates and CRL (Certificate Revocation List)

  1. Download and save the following files:
    http://s1.symcb.com/pca3-g5.crl
    http://sv.symcb.com/sv.crl
    If the above URL's are blocked by your browser please download them here or the attached ZIP file. 
  2. Start a command prompt (cmd.exe) as administrator.
  3. Browse to the folder where the files from step 1 are stored.
  4. Run the following commands:
    CertUtil -AddStore CA pca3-g5.crl
    CertUtil -AddStore CA sv.crl
  5. Export host, intermediate, and root certificates from the hotfix file.
  6. Install the 3 certificates with the default selection.
  7. Restart Device Administrator and install the hotfix.

Video for step 5 and 6:

 

 

November 2025: Added Intermediate and Root Certificates for Global Sign.
  • Root: GlobalSign Timestamping Root R45
  • Intermediate: GlobalSign R45 AATL TimeStamping Root CA 2021
Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
CRL_Files.zip
GlobalSignCertificates.zip
Tags (5)
  • Find more articles tagged with:
  • DavidPurser25
  • I am having a similar problem. How did you fix it
  • MikaelKrantz21
  • MikaelKrantz24
  • PeterLarsen21
Was this article helpful? Yes No
84% helpful (15/18)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore