Jace 8000 Serial Port Issue

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Jace 8000 Serial Port Issue
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • JonGreen
    JonGreen

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
9000 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Jace 8000 Serial Port Issue

Guinan RandyDavis Guinan
‎2019-06-20 08:28 AM

Last Updated: Commander JonGreen Commander ‎2020-07-27 10:07 AM

Issue

There are missing serial ports (COM ports) when viewing the 'SerialPortService' under 'PlatformServices' in a station. Some or all COM ports will be missing. Local serial ports and/or serial ports of the attached modules do not function.

Product Line

TAC IA Series

Environment

I/A Series AX Jace 8000

Cause

This could show up for several reasons.

  • This was found during an upgrade to Niagara 4.2.
  • It was also experienced when converting a Jace8000 running N4.2 (or lower N4 version) to AX.
  • This can occur with a new out of the box J8000 to AX conversion if you do not first commission the Jace8000 to Niagara 4.4 or above before converting to AX.

All of these problems are due to older version USBbinary files not being properly updated during commissioning. The LON option module (side-car) might stop communicating on the LON trunk due to the same binary file issue.

Resolution

This can be fixed via serial shell; either by direct connecting with a mini-USB cable or via ssh after it is enabled from the Platform Administration view. It is recommended that PuTTY.exe be downloaded and used as the terminal program to access the shell.

The directions below are CASE-sensitive and must be entered exactly as shown. We recommend that you do not type these commands, but rather use copy-and-paste to avoid typographical errors.

This is especially true of the usbSerialNumber itself -- it is case-SENSITIVE.

By default, PuTTY.exe uses mouse-left-click-drag-and-highlight as an automatic shortcut for copy. Mouse-right-click is the automatic shortcut for paste.
Once logged in type:

    1. Display the USB serial number(s)
      sh [hit enter]
      $ ls /etc/usb [this will display the USB serial number(s), if nothing displays see the note* at the bottom]
      85091090FPGGS41 [this is an example serial number]

    2. Display the available binary files
      $ ls -Rp /sys/images/usb [this will display the available binary files]

      /sys/images/usb/applet-flash-sam4s16.bin*
      /sys/images/usb/vid03eb/pid2404/Tridium232-1_r03.bin*
      /sys/images/usb/vid03eb/pid2425/Tridium485-2_r04.bin*

      Note: You could also see '_r05' instead of '_r04'. If this is your result, make sure to update using the line below.
      /sys/images/usb/vid03eb/pid2425/Tridium485-2_r05.bin*

      The USB ports unavailable is due to the 'Tridium485-2_r04.bin' (or Tridium485-2_r05.bin) file was not written to the USB serial number file. This can be corrected by updating the USB serial number file with the correct binary file using the statement below. Make sure to replace the X in the statement with the highest number binary found in 'STEP 2' above.
      $ echo /sys/images/usb/vid03eb/pid2425/Tridium485-2_r0X.bin > /etc/usb/<usbSerialNumber>

    3. Update the binary file
      Using the example serial number and USB binary file found in STEP 2:
      $ echo /sys/images/usb/vid03eb/pid2425/Tridium485-2_r05.bin > /etc/usb/85091090FPGGS41

Make sure to use the serial number found when 'ls /etc/usb' was called. If there is more than one serial number found, write the command multiple times, once for each serial number found.

Also, make sure to use the highest USB binary file number found. Currently r05 is the highest number. If '_r05' is returned as the available USB binary file, make sure to use '_r05' when updating the USB serial number.

After a reboot, check the SerialPortService to confirm the ports are restored.


*Note: if no usb serial number was found using ls /etc/usb another method would be to call for the slog by typing:

$ sloginfo

An error would have been logged here during the last startup and will display the serial number; example output:
Oct 10 13:42:06 1 6 0 serusb_is_device_supported: Device 2 on bus 0 unrecognized. Using CDC-ACM Class
Oct 10 13:42:07 4 11111 0 error opening /etc/usb/85091090FPGGS41 rc=-1

In addition to the symptoms listed above, the inability to communicate with the LON option module may cause the any of the following messages in the Serial Shell and/or the Platform Administration System Logs:

error opening /etc/usb/<serial number here> rc=-1

U50Read returned unknown rc = 8!!!

io_write failed ldvRC=7, length=<various numbers of bytes>

The Station will most likely show that the LON network is up, but the LON devices are down. The device fault cause may show "unable to write" or something similar.

Labels (1)
Labels:
  • TAC IA Series
Tags (7)
  • Find more articles tagged with:
  • ax
  • lon
  • missing
  • n4
  • RandyDavis19
  • RandyDavis20
  • serial ports
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore