How to extract an XIF out of a Lon controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to extract an XIF out of a Lon controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
9603 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to extract an XIF out of a Lon controller

Picard Product_Support
‎2018-09-11 02:59 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:52 AM

Issue

There may be a situation where the External Interface File (XIF) needs to be extracted out of the controller in order to properly set up the controller in a building automation system. 

Product Line

EcoStruxure Building Operation, TAC IA Series, TAC Vista

Environment

  • External Interface File (XIF)
  • NodeUtil
  • Loytec XIF Builder

Cause

These tools will help with the extraction of an XIF file. An XIF file is used to create a Niagara R2 shadow object, a Niagara G3 LMNL file, LonWorks device template, and a SmartStruxure device template. 

Resolution

The device manufacturer should provide an XIF, and in most cases, a DRF kit as well. The XIF provided by the manufacturer of the controller should be used first but if issues arise it may be required to extract the file from the controller. There are a number of tools available that will create an XIF, but the DRF kit cannot be created by any tool and must be supplied by the manufacturer. This MUST be provided along with the device.

The list below covers some of the tools which are available.

  • NodeUtil                          (header: bad,           NVs: ok,                      DMA/File-SCPTs are omitted)
  • Vista's XIF-builder           (header: bad,           NVs: almost ok..,       DMA/File-SCPTs are omitted) 
  • Loytec plugIn                  (does a perfect XIF from a device using Loytec's stack)

 

NodeUtil is available from the Echelon website (free registration is required) - The NodeUtilLauncher package attached makes it easy to use NodeUtil with Loytec interfaces.

  • Loytec XIF Builder is available from the Loytec website (free registration is required)
  • Using Lonmaker and the XIF Builder.
  • Using NL220 and the XIF Builder.
  • If the uploaded XIF still contains some detailed prompted error, refer to Error displayed when importing a device XIF into SmartStruxure.
Labels (3)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
Attachments
NodeUtil Launcher.zip
Tags (3)
  • Find more articles tagged with:
  • 16092
  • importing
  • PeterLarsen22
Was this article helpful? Yes No
0% helpful (0/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore