BACnet MS/TP Bus Communication Troubleshooting Checklist

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • BACnet MS/TP Bus Communication Troubleshooting Checklist
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
9536 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

BACnet MS/TP Bus Communication Troubleshooting Checklist

Picard Product_Support
‎2018-09-09 08:26 AM

Last Updated: Crewman ContentModerator ‎2025-10-15 03:37 AM

Issue

BACnet MS/TP Bus Communication Troubleshooting Checklist

Product Line

TAC IA Series

Environment

I/A Series BACnet controllers (MNB-70, MNB-V1, MNB-V2, MNB-300, MNB-1000) on an MS/TP bus.

Cause

BACnet MS/TP Bus Communication Troubleshooting Checklist

Resolution

This checklist provides several settings/configurations to review when faced with a communication problem at the controller level. The content was compiled from different resources, summarized, and laid out in an easy-to-use manner so as to provide a quick-reference document.

Power

Each controller requires 24 VAC from a Class 2 transformer.

See the Installation Instructions for each controller, and the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7, Chapter 1, “Power Supply Wiring”.

Read-Only Flag

Use the WorkPlace Tech Commissioning Tool (WPTCT) to check “Device Properties” of the controller. If the status is “Operational, Read-Only”, the input voltage to the controller may be too low. See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7, Chapter 1, “Power Supply Wiring”.

Due to the short duration of the low-voltage condition required to set the flag, it is unlikely that you will see it when measuring the input voltage with a digital meter, so check the “Device Properties”, and correct the problem as noted on page 28 of the guide, (reduce transformer loading, reduce wire length between transformer and controller, and /or use wire with higher current rating).

Diagnostic LEDs

The MNB controllers have onboard diagnostic LEDs that are useful in troubleshooting. See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7, Chapter 3, “Communications Hardware Checkout”, Table: “LED Indications”, for a detailed description of the behavior of the LEDs and their diagnostic uses.

Topology

It is very helpful to draw the topology of the bus when you start troubleshooting. If there are no repeaters on the bus, the topology must be a daisy-chain, with no tees or stars. MS/TP network wiring to MN-Sx sensors must be run to the sensor, then to the next controller on the bus, in a daisy-chain; no tees or spurs are allowed. Maximum length of a wire segment is 4000 feet.

See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7, Chapter 1, “MicroNet MS/TP Network Wiring”, for details on Communications wiring.

Repeaters

  • B-LINK-AC-S, Andover Controls MS/TP Repeater
  • B-LINK-AC-F-S, Andover Controls MS/TP Repeater Fiber

See the MicroNet BACnet Smoke Control Systems Manual, F-27419, for details on the use of these wire and fiber repeaters with MNB controllers. See F-27419, Chapter 5, “Approved MS/TP Repeaters”, including the wiring example.

Maximum Number of Devices

The maximum number of MNB controllers depends on the cable used, and the Baud Rate.

See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7,Chapter 1, Table, “Approved Cable Types”.

The MNB controllers are quarter-load devices, so a maximum of 128 or less are allowed on an MS/TP trunk, depending on the cable used.

Addressing

Avoid duplicate addresses.

See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7, Chapter 1, “Required Configuration”,

CAUTION:

“Duplicate addresses on an MS/TP network trunk will result in erratic behavior, lost tokens, and disrupted communication.

There is no software tool that will identify duplicate addresses on an MS/TP network trunk. Typically, if two controllers are set to the same address, one of the controllers will appear to be missing from the list, and the address shared by the two controllers will intermittently come and go from the list.”

Biasing

As a requirement of EIA-485 (formerly RS-485) bus topology, an MS/TP network must have a minimum of one set, and a maximum of two sets, of bias resistors in place. The MNB-300, MNB-1000, UNC-520, and ENC-520 have jumpers to enable or disable the bias resistors.

See bulletin TB06-09, “RS-485 Bias Resistors and the UNC-520-2 / ENC-520-2”, page 3, for a photo of the bias jumpers on a UNC-520-2.

Terminators

A 120-Ohm End-of -Line (EOL) resistor is required across the “MS/TP +” and “MS/TP -” terminals at each controller at the end of a wire segment. The MNB-1000 and MNB-300 are equipped with a jumper-selectable end-of-line (EOL) termination resistor. The default position for the EOL jumper is “EOL termination not present.”

See the MicroNet BACnet Smoke Control Systems Manual, F-27419, Chapter 5, “Approved MS/TP Repeaters”, Figure titled “UL 864 Listed MS/TP Repeater and Isolation”, Note 4, for an important exception, requiring external EOL for the MNB-300 and MNB-1000, when used on a bus with an approved repeater.

If a UNC-520-2, ENC-520, MNB-V1 or MNB-V2 is installed at the end of the trunk, install a discrete 120 Ohm EOL resistor, part number EMSC-546, or equivalent.

Cable

Use of the proper cable is critical to the communications performance of the networked controllers. See the MicroNet BACnet Wiring, Networking, and Best Practices Guide, F-27360-7,Chapter 1, Table, “Approved Cable Types” for a list of recommended cable types. As shown in the table, cable selection affects both the maximum number of controllers allowed on the trunk, and the maximum baud rate.

WorkPlace Tech Interface

The MNB-ROAM-IA is the recommended communications converter for connecting WorkPlaceTech, including the WPT Commissioning and Flow Balance Tools, to an MS/TP trunk. It is supported in versions 5.7.1 and later. A converter that had been recommended earlier, the B & B Electronics model USOPTL4, was found not to operate reliably at speeds above 38.4 K baud. (See Direct MS-TP Connection with B & B Electronics Converters (Revised) - TB08-02-02 for details). The MNB-ROAM-IA supports Bluetooth wireless connection between WorkPlace Tech suite and the MS/TP network, for distances up to about 40 feet. One external Bluetooth adapter has been tested and approved - the Belkin USB adapter. (See Supported models of Bluetooth adapters with WorkPlace Tech for details).

A problem we have seen with some MNB-ROAM-IAs is when trying to add Bluetooth device, the Bluetooth Wizard identifies it as "Serial Port Device, Unknown: Major(0), Minor(0)" instead of "tac-RoamIA:xxxxxxxx" where xxxxxxx is the serial number. There is no way for WPT to use the ROAM-IA if the computer can’t pair with it. Currently, there is no known solution, other than replacing the device.

Divide and Conquer

This is a strategy for dividing a bus into smaller sections in order to isolate a controller or section of bus that might be causing communication problems.

The general idea is to divide the bus in half, and see if communications are possible from one end to the other end. If not, divide each half again, and continue until the problem(s) are found.

Reference Documents

  • F-27360 TAC I/A Series MicroNet BACnet Wiring, Networking, and Best Practices Guide
  • F-27358 TAC I/A Series MicroNet BACnet Workplace Commissioning Tool and Flow Balance Tool User’s Gui...
  • F-27456 TAC I/A Series MicroNet BACnet MNB-70 Zone Controller Installation Instructions
  • F-27345 TAC I/A Series MicroNet BACnet MNB-300 Unitary Controller Installation Instructions
  • F-27346 TAC I/A Series MicroNet BACnet MNB-V1, MNB-V2 VAV Controller Installation Instructions
  • F-27347 TAC I/A Series MicroNet BACnet MNB-1000 Controller Installation Instructions
  • F-27419 TAC I/A Series MicroNet BACnet Smoke Control Systems Manual
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5300
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore