How to set the Enterprise Server IP address

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to set the Enterprise Server IP address
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
9371 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to set the Enterprise Server IP address

Picard Product_Support
‎2018-09-10 12:50 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:45 AM

Issue

How to change the IP address in the EC/ES software when it is grayed out.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Central (EC) and Enterprise Server (ES)
  • Building Operation WorkStation

Cause

The EC/ES IP address is grayed out in the Network Tab of the Server Properties and cannot be changed.  This setting is only used to view the IP address that the server is currently using - typically the IP of the network interface card of the PC running this.  To change this setting it must be done through the Communications TAB of the server as detailed in the resolution. 

Resolution

EcoStruxure Building Operation 2.0 and above

EBO 2.0 and above now supports multiple NIC configurations, see 2.0.1 Release Notes for details, in particular, the following note.  

  • Note: That from 2.0 the server will still listen for incoming requests on all network adapters so this setting is only used for choosing which communication settings that the server will use to communicate with child servers.

This allows other IP protocols on different networks, e.g. BACnet, Modbus, etc. to communicate with the Server. 

 

It is now possible to select which network adapter the Enterprise Central and the Enterprise Server use.  See the following WebHelp Topic Configuring Network Interface Card for an Enterprise Server or for an Enterprise Central


StruxureWare Building Operation 1.9 and below 

When the IP address of the computer changes the ES will automatically update the "IP/DNS Address" in the Properties, Network tab.

If your computer has multiple network connections, ensure that the Network Interface Card (NIC) to be used for the SmartStruxure network is set to be at the top of the list in the Adapters and Bindings.

  1. Go to the computer's Control Panel > Network Connections
  2. Select "Advanced, Advanced Settings... " from the menu.
  3. In the "Connections:" section, select the Network Connection to be used and press the up arrow to move it to the top of the list.
  • For Windows 7 / Server 2008 See the following link on how to change the order of protocol bindings: How to change the network connection priority in Windows 7
  • For Windows 8 and beyond, please refer to Adapter priority setting unavailable in Windows 10

In addition to the ES Network Properties, there is also the Communication tab in the ES that lists all of the Server IP addresses in the system.

If these need to be changed this can be done by selecting the server and clicking on the "Show/ Hide Communication settings" button circled in red below.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (5)
  • Find more articles tagged with:
  • 11135
  • PeterLarsen21
  • PeterLarsen22
  • RobertAndriolo20
  • RobertAndriolo21
Was this article helpful? Yes No
80% helpful (4/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore