"Object already exists" "Cannot add a server that is a clone..." error when creating new AS under an ES
  • "Object already exists" "Cannot add a server that is a clone..." error when creating new AS under an ES
  • RandyDavis
    RandyDavis
  • RobertAndriolo
    RobertAndriolo
  • Sampath_Konda
    Sampath_Konda
  • StephenYang
    StephenYang
  • Jonas_Brissman
    Jonas_Brissman
  • Benji
    Benji
  • AbeMeran
    AbeMeran
‎2018-09-10 04:08 AM
Last Updated: Picard RobertAndriolo Picard ‎2021-09-19 04:19 PM
When attempting to add a new Automation Server under an Enterprise Server that already has one or more AS servers attached it results in an "Object already exists" error
ERROR
Domain: Data access
Info:~/System/Server Communication/Models/xxxxxxxx/Members/xxxxxxxxx in module Run Db manager
xxxxxxxx = Global Unique Identifier (GUID)
The GUID underlined in red in the screenshot above is the duplicated Id.
Additional error message possible depending on EBO release version.
Server Already.jfif
ERROR:
Server already part of a multi server system
Domain: Invalid data
Info: Attempt_To_Add_An_Object_To_The _System_That_Already_Exists
ERROR:
Cannot add a server that is a clone of a server that already exists in your system
Domain: Startup
Technical Info: An added server with name 'XXXXX' has the same unique id as an existing server with the name 'YYYYY' which is not allowed.
  • Building Operation Automation Server
  • Building Operation Automation Server Bundled
The AS that is being added has been restored from a backup created from one of the servers that are already configured under the ES resulting in a duplicate GUID.
  1. Backup the Server
  2. Restore the Server and make sure to select "Restore configuration with new IDs" check box. This will ensure that a new GUID is assigned to the AS.
  3. Add the Server from ES
Please note that the restore function to re-use configuration data from a backup set is supported for all Building Operation supported protocols, except for BACnet and b3 BACnet.