Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,845
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 44
    • 45
    • 46
    • …
    • 508
  • Next »

RDM Modules on SP-ACX and SP-AC1 controllers

Issue What are the recommendations/limitations around using RDM2 and mRDM2 Reader Expander Modules on SP-ACX and SP-AC1 controllers? Product Line Security Expert Environment SP-ACX SP-AC1 RDM Expander Modules Cause The number of RDM2 and mRDM2 modules which can/should be used on an SP-C/SP-C-Web is well documented, but it is not so clear what limitations exist when using these modules on other SP Controllers. Resolution While SP-ACXs and SP-AC1s have not historically supported SP_RDM2 modules in the past, it is now supported going forward, as detailed in Architectural Guide Lines Security Expert - 4.3.322 available on The Exchange.    This will also receive an official 'new feature' announcement for Security Expert 2023 when it is released later this year.  (Assume controller firmware of 2.08.1320 minimum)   Legacy Continuum AC1 Modules and Security Expert RDM modules have to be used on separate ports and care must be taken when adding new RDM modules as this runs the risk of overtasking the controller, especially when approaching maximum door limits.  SP-ACXs and SP-AC1s are primarily designed as transitional controllers to allow Continuum ACXs and Continuum NetControllers to be transitioned smoothly into a new Security Expert system.   
View full article
Admiral David_Kendrick Admiral
‎2021-07-13 03:12 AM

Labels:
  • EcoStruxure Security Expert
2520 Views

Is LDAP supported in EBO?

Issue As per RFC 4510 The Lightweight Directory Access Protocol (LDAP) is an Internet protocol for accessing distributed directory services that act in accordance with X.500 data and service models. Do EBO servers support LDAP protocol? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause Need to know if EBO supports LDAP protocol. Resolution EBO doesn't support LDAP protocol. EcoStruxure Windows based BMS servers (Enterprise Server/ Enterprise Central) support integerationto Windows Active directory. The Active Directory integration is not using LDAP directly, but the NetLogon service on the Windows OS that ES/EC is running on.  This connection enables inherited user account groups from the Windows Active Directory to EcoStruxure Building Operation software, and allows users to log on to WorkStation with their Windows user accounts. Refer to: Windows Active Directory User Groups and Integrating Windows Active Directory user accounts with EcoStruxure - Communities For EBO 2022 or higher, Authentication using SAML 2.0 is also supported (Edge Server, AS-P, AS-B, ES and EC) . This enables configuring WebStation to use single sign on (SSO) using Federated Authentication, refer to: Federated Authentication. SAML Authentication feature requires license.
View full article
Kirk Mahmoud_Sayed Kirk
‎2023-02-07 06:15 AM

on ‎2023-02-07 06:15 AM

Labels:
  • EcoStruxure Building Operation
2056 Views

SLP Sensor Modbus RTU issue when used with RPC or Automation Server

Issue SLP Sensor Modbus RTU issue when used with RPC or AS Communication errors are seen during normal Values are updated very slowly, can take up to two minutes to populate/update the 15 objects within the SLP.   Product Line EcoStruxure Building Operation Environment Modbus RTU RPC Modbus Automation Server + Premium  SLP SpaceLogic Sensors LSA_APP_REV2.03.19 and REV2.05.21 Cause Once the Modbus communication is set up between RPC (or AS) and the SLP,  although the values updates fairly regularly, multiple communication errors are also seen The SLP read speed needs to regulated to prevent overwhelming it The SLP Modbus transmission voltage is less than the AS Resolution Use with RP-C SLP struggles to respond to every request from the RP-C, changing the baud rate to 9600/19200 and increasing the "Silence characters" in the interface to 255 (maximum possible) should stabilize the communications.  The character spacing cannot be adjusted enough in the RP-C to allow communication at 38400 or 76800 Use with AS/AS-P  Adjust the “Poll point delay” in the Modbus Interface to 80ms The Silence characters and Transmit guard bits may also need to be increased Baud rate up to 38400 has been tested.  
View full article
Dave_Shore Schneider Alumni (Retired)
‎2021-02-03 06:29 AM

Labels:
  • EcoStruxure Building Operation
3436 Views

Redundancy options for the Security Expert Server.

Issue Are there any redundancy options for Security Expert? Product Line EcoStruxure Security Expert Environment Security Expert Stratus everRun Cause Need to provide redundancy for the Security Expert Server. Resolution There are a couple of options for providing server redundancy that can be used with Security Expert. The first option would be to use a downtime prevention product such as Stratus everRun as a hot standby solution. The second option is having a secondary Security Expert server as a cold standby server, if the primary server fails/needs to be taken offline the Security Expert services on the cold standby server can be started to take over. This option is largely manual, there is no automatic switching between two servers with this configuration. There are also a number of considerations to take into account with this option: In this scenario the controllers would be programmed with 2 x event server IP addresses for the primary and cold standby server as a result only 1 server/set of Security Expert services must be running at a time, having both running and therefore the controller having 2 x valid paths back to 2 x different servers concurrently will cause issues with the upload of events, online status and downloads A suitable system/process would need to be put in place to ensure the databases are restored from the primary to the cold standby server There will be 2 different Security Expert servers running which will require 2 separate Security Expert Server license with the same feature set enabled on both Considerations will need to be made with regards to the name of the machine to ensure the Download and Event servers can run, either the machines must have the same name or the name of the server needs to be renamed when required to the name of the cold stand by server An operator would need to verify the state of programmable functions and services. If the primary server failed during the middle of the download when the cold standby server is up and completes a full download some functions/services may require manual starting.
View full article
Picard Product_Support
‎2018-09-06 07:33 AM

Last Updated: Kirk AdamSteele Kirk ‎2023-02-05 04:52 PM

Labels:
  • EcoStruxure Security Expert
2906 Views

Enterprise Central License inheritance by child Enterprise Servers

Issue Can Enterprise Servers inherit licenses from a parent Enterprise Central? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Cause Need to know if Enterprise Central Licenses can be inherited by an Enterprise Server, and then, in turn by Automation Servers. Resolution An Enterprise Server cannot inherit its licenses from a parent Enterprise Central. Licenses can only be inherited from an Enterprise Server by the attached automation servers. Refer to WebHelp article Inherited Licenses and Knowledge Base article SmartX Server License Inheritance in EBO 3.x.
View full article
Kirk Mahmoud_Sayed Kirk
‎2023-02-02 01:14 AM

on ‎2023-02-02 01:14 AM

Labels:
  • EcoStruxure Building Operation
781 Views

How to allow double badge access functionality to Individuals

Warning This article describes a feature that is not standard functionality within the Product Line.  It has been provided to allow customers the option to use this requirement.  Pay particular attention to the Prerequisites of the required programming. Issue Customer requires the functionality for Individuals  to double badge (present their credentials twice) to gain access. Product Line TAC INET Environment Access Control Cause Customer application requirement Resolution Prerequisites: LIMITATIONS: As this is not a standard access control feature within I/NET, it uses custom programming, which therefore reduces/limits the standard features within I/NET The description provided below must be set for ALL individuals with access to the door that requires double badging.  It does NOT cater to custom individual use.  It may be possible to provide additional programming to achieve this, but this is not detailed in this article. Door Automatic Time Schedules (ATS), if applied, can be overridden if the door reader is badged during the scheduled operation.  The functionality of this feature uses event-driven programming, which in its nature is single-shot programming and therefore relies on the following:  Requires reliable communication between SLI/MCI (779x) and the SCU (Door Controller).  The door reads from the SCU must be received by the SLI/MCI to activate the badge/read occurrence. Requires SLI/MCI (779x) CPU loading below 65%. LAN Load of this controller should be below 2%; anything above this can cause the operation to fail/be inconsistent.  Removes the standalone capability of the Door controller (SCU) POINTS The points required for each door that requires this functionality are Door Reader (Internal DO door point as required in I/NET)  Door Strike (External DO Point) must be programmed within the controller Door Intermediate (Internal DO Point). :: Scan Rate 1 second Door Read Count (Internal AO Point). :: Scan Rate 1 second I/NET Controller Summary Note: The address order, as shown in the screenshot above, is important for the overall operation.   That is Read Count must be at a lower address than all other points.  Next the Intermediate point.  The Strike and Reader addresses are fixed by I/NET but must be at a HIGHER address than the Read count and Intermediate points.    DOOR Intercard Interval (sec) should be set as low as possible.  This allows the card to be present within this time setting (minimum is 1 second) Door strike: Configuration of the door/reader must have this set to either. None: When a valid read is received, no action is sent to the strike Exit: Only when an Exit read to Request to exit (REX) is received by the door does it activate the strike.  Strike duration (sec): Should be set 1 second above the scan rate of the Intermediate / Read Count points above.  In this case, it is set to 2 seconds.  Note: this does not have any bearing on how long the strike remains "unlocked" Door editor Programming DOOR No additional programming is required for the door apart from the details provided in the above prerequisites.  ACCESS INITIATED CONTROL (AIC) Add an AIC that will trigger the Intermediate point on a "valid" reader entry for the nominated door. Select the Target point (DR1 Intermediate) Select either Use all individuals in the range which will trigger this action for all individuals.  Note: If selected Individuals are needed to activate this feature, then additional programming is required and not detailed in this article.    Select Reader entry to START the target point  Select which Doors are to trigger this action Access Initiated Control editor POINTS From the screenshots below, it can be seen that: Point DR1 Read Count has two extensions: Calculation (C)  Operation: The result of this calculation is displayed on the DR1 Read Count point.  The calculation adds the value of itself (P0) DR1 Read Count and point (P1) DR1 Intermediate point (where 0=OFF 1=ON), the result of which is then multiplied by the NOT (~) the value of (P2) Door Strike (where sec = 0 Unlk = 1). Result: DR1 Read Count is incremented by one on each valid read.  The counter is reset (zeroed) when the Door Strike is energized.        Event Definition (EV)   Operation: When the point DR1 Read Count crosses the value 1 (the value of 2 represents the double (2) badge), Sequence/Action #1 is triggered.  From the above Event Definition (EV), this runs Sequence/Action Num 1, which is shown below:  Operation: When triggered by the (EV) above, the Door Strike is immediately "Stop"  (Unlocked); after a 5-second delay, the Door Strike is "Start" (secured). Note: The delay of 5 seconds on line #2 determines how long the strike remains in the unlocked state.  Modifying this value will shorten or extend the unlocked state.     Point DR1 Intermediate has only one extension: Calculation (C)  SUMMARY OPERATION A valid card read is presented to the reader; this triggers AIC to turn point DR1 Intermediate to ON. This increments DR1 Read Count by 1 to the value of 1 via its Calculation (C) extension The additional card read repeats Steps 1 and 2 above;  DR1 Read Count value increments to a value of 2. Event Defintin (EV) high-value crossing (>1) triggers Event Sequence #1 Event Sequence #1 unlocks Door Strike 1 and, after a 5-second delay, relocks (secures) Door Strike 1 point. This relock (secure) of Door Strike 1 zeros the DR1 Read Count value via its Calculation (C) extension.  ATTACHMENTS - for reference showing the above details  I/NET Controller SAV file (DCU0201.zip) Backup InetDb (SQL.bak).  (InetDb_DoubleBadge.zip)  
View full article
Guinan RobertAndriolo Guinan
‎2023-02-01 06:15 PM

Labels:
  • TAC INET
870 Views

Report Server "appuser" clarification

Issue When WebReports is installed, two users called "appuser" are created. One is a local Windows user, and one is a SQL user. Product Line EcoStruxure Building Operation Environment WebReports User accounts Cause These users are or have been needed by WebReports Resolution EBO version 2.0 and above: the Windows user account "appuser" is no longer required to operate WebReports.  It is only a requirement during installation. SBO/EBO version 1.8 and above:  In SQL, the "appuser" user account has been removed as it's not essential for the Web Reports to operate correctly. In these versions, if an upgrade from an earlier version is performed and this user account is still present, it can be safely deleted /disabled.     In all other versions: The local Windows user account ([PC_NAME]\appuser) is used for importing report packs (RDL files) and synchronizing between WebReports and Microsoft Reporting Services.   For more information about this account, refer to SmartStruxure WebReports Installation Errors (1001 while importing report pack). To change the password for this Windows user, refer to Changing Report Server "appuser" password.    
View full article
Picard Product_Support
‎2018-09-10 07:09 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2023-02-01 01:11 PM

Labels:
  • EcoStruxure Building Operation
1623 Views

Postgres/TimescaleDB leaves us without a reporting engine. SSRS is licensed part of MSSQL.

Issue Moving from Webreports going to Postgres/TimescaleDB instead, leaves us without a reporting engine. SSRS can supposedly utilise a PostgreSQL database, but SSRS is a licensed part of MSSQL. Product Line EcoStruxure Building Operation Environment Building Operation Timescale Database Cause From EcoStruxure Building Operation version 4.0 (2022) the Building Operation Report Server is no longer supported. Instead, we support PostgreSQL/TimescaleDB, using Dashboards and Excel from within EBO, to make reports, using Notification reports to start Excel and reports. Resolution EBO 3.2 introduced Enhanced Reporting, based on the current feature Notifications in combination with Notification Report Template, which also supports report data such as Alarms, Groups, Multi Log list, Relative events and Users. The Notification result can also be presented in XLSX format and converted to PDF with signing capabilities. If External Log Storage is configured and connected (PostgreSQL/TimescaleDB), then historical report data can be fetched from there.   EBO 2023 introduced External Log Storage support for Microsoft SQL Server in addition to PostgreSQL/TimescaleDB   Information  and examples of Enhanced Reporting and Dashboards can be found in EBO Webhelp, My LearningLink and the Automation Experts Community.   NOTIFICATION REPORTS : EBO Webhelp: Notification Reports  Community: Reporting in EcoStruxure Building Operation 3.2 Community: Reports showcase - share your reports! Community: Get more data out of the system with Notifications! EcoXpert Extranet Video: Community Video : Fusion Fridays - Session 20 Community: Change Control and Enhanced Reporting Lab Guides Community: Example Report Templates  Community: Forced Values Report Example My LearningLink: EcoStruxure Building: Enhanced Reporting and Dashboards 3.2 My Learning Link: EBO 2022: Enhanced Reporting and Dashboards   DASHBOARDS : EBO Webhelp: How Dashboards Work EcoXpert Extranet Video: Dashboards EcoStruxure Building Operation 3.0 - Informational Video Community: What Custom Types have to do with Dashboards Community: Public vs Personal Dashboards Community: Graphics in Dashboards [Advanced] Community: Dashboards: Share your screenshots! EcoXpert Extranet: PA-00701 EcoStruxure™ Building Operation 3.0 Captures the Spotlight
View full article
Kirk MikaelKrantz Kirk
‎2023-01-31 06:29 PM

on ‎2023-01-31 06:29 PM

Labels:
  • EcoStruxure Building Operation
2696 Views

Problem communicating to multiple Socomec Diris A20 Modbus Meters

Issue When using the Modbus RTU X Driver to communicate to multiple Socomec Diris A20 electric meters it has been found only 2 or 3 devices can be networked together, even using a b-Link to boost the signal does not resolve the issue. Product Line Andover Continuum Environment Modbus RTU X Driver on bCX1 or Netcontroller II B-Link repeaters Cause The Socomec Diris A20 meters require a minimum of 4V RS-485 signal to communicate reliably, but the EIA RS-485 standard only calls for a +/- 1.5 volts signal and the Receiver Input sensitivity should be +/- 200mV. When using a bCX1 with the X Driver on Comm1 you will require a b-Link to provide the RS-232 to RS-485 conversion, although the B-Link fully conforms to the EIA RS-485 standard it does not have the drive levels required by the Socomec products. Resolution To resolve the non standard electrical requirement of the Socomec Diris meters use a Socomec RS-422/ RS-485 Repeater this will output the required electrical levels required by the Diris meters, the Socomec  part reference is 48990120.  Please refer to SOCOMEC Communication accessories or RS-422/485 Repeater Operating Instructions   If a B-Link is to be used each RS-485 output that is used will require a separate Socomec repeater.  
View full article
Picard Product_Support
‎2018-09-06 01:18 PM

Last Updated: Sisko GavinHe Sisko ‎2023-01-26 08:16 AM

Labels:
  • Andover Continuum
3083 Views

Script bindings to outputs are not working

Issue When binding Output points in the script editor to the desired outputs, the bindings are not working. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation All Versions Automation Server Central I/O Modules Cause When bindings to the output points the incorrect attribute is being used. Resolution Open binding editor for the desired program. In the right hand pane, choose the desired output to be bound. Expand the point and select Requested Value. Drag the Requested Value to the desired output in the program. Save settings.
View full article
Picard Product_Support
‎2018-09-06 02:13 PM

Last Updated: Sisko GavinHe Sisko ‎2023-01-25 07:21 AM

Labels:
  • EcoStruxure Building Operation
1914 Views

Double feature values for Entitlements

Issue Sometimes the availability count for license features are displayed as double the actual available count for Entitlements. The problem has no functional effect on the system other than that the visual indication of the feature count is wrong. Issue seen in Entitlement View - Features inside a License Product are doubled. Issue seen in Server View. -The issue can be seen temporarily during activation on the server line. -The number of features inside the License Products available for activation under the server are doubled permanently. Server line view after activation. - After the license product has been activated the features on the server are shown correctly. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Secure Boot Building Operation Automation Server Bundled (AS-B) Scalable Cause AS-P Classic and AS-B Classic licenses are NOT affected. None of the Windows licenses are affected.   EBO releases affected: All EBO versions up to and including 4.0.3. The EBO systems that are already running licenses are Not affected. Customers that for any reason reinstall an Entitlement in DA will be affected by the issue. EBO 5.0.1 Resolution This issue is planed to be resolved in the following EBO versions: EBO 4.0.4 EBO 5.0.2
View full article
Janeway Jonas_Brissman Janeway
‎2023-01-25 03:50 AM

Last Updated: Janeway PeterEdvik Janeway ‎2023-01-25 04:17 AM

Labels:
  • EcoStruxure Building Operation
819 Views

1.8 kOhm thermistor on the RTD-16 I/O module

Issue Is it possible to use a TAC Xenta 1.8 kOhm thermistor on an RTD-16 Central I/O module? Product Line EcoStruxure Building Operation. Environment Building Operation I/O Module 16 Ch RTD Cause Wants to use existing modules instead of adding new modules. Resolution The RTD-16 module is designed to interface with linear resistive inputs such as PT100, PT1000. Thermistors generally have logarithmic scales, therefore it will be hard to program a correct curve function to get an acceptable sensor accuracy. Using a universal input that is made for thermistor readings will give a more accurate reading without additional programming.
View full article
Kirk MikaelKrantz Kirk
‎2023-01-18 04:51 PM

Last Updated: Administrator CraigEl Administrator ‎2023-01-18 04:54 PM

Labels:
  • EcoStruxure Building Operation
954 Views

Controlling command priorities with Continuum workstation programs or Infinity controller programs.

Issue What is required to control command priorities in 3rd party controllers using Plain English? Product Line Andover Continuum Environment Continuum Cyberstation BACnet Controller (BCX, B4920, B3) BACnet command priority Plain English Cause Need to understand how to control command priorities and point values with Continuum workstation programs or controller infinity programs. Resolution Command Priority is a BACnet mechanism to decide the control hierarchy of a point, with 1 being the highest priority and 16 being the lowest.  Consider the following:   Default setting for a workstation program priority level is ManualOperator priority 8 Programs located in the workstation default command priorities can be controlled through Bacnet Preferences Controller InfinityPrograms will need to use the WriteProperty function to set a different priority other than priority 10 To relinquish a priority level use Relinquish(pointname, priority level)   The WriteProperty function is written in the format: WriteProperty (object_name, value, priority, index) object_name  Includes a full pathname, followed by a property name. The object identifier and property identifier are combined as one argument value   This actual value to which the property is set. This is optional.  If it is not present, then the next argument, priority, must be present to perform a Relinquish command.  (See the example in Relinquish.)  priority  The priority  number, ranging from 1 (highest) to 16 (lowest).This is optional.  It applies only to a set commandable property.  For controllers:  If it is not present, priority 10, if applicable, is used.  For CyberStation: The value, based on the priority in the BACnet Preferences dialog, is used.  index  This is optional.  It applies only to an array-type BACnet property.  The index is ignored whenever it is not applicable.   Infinity controller samples: This line will write the value of 22 to priority 10 BACnetDevices\BNet_4444\B3_885\B3Num1 = 22 This line will write the value of 33 to priority level 4 WriteProperty(BACnetDevices\BNet_4444\B3_885\B3Num1, 33 , 4 ) This line will relinquish the value for priority level 4 setting the value back to NULL Relinquish(BACnetDevices\BNet_4444\B3_885\B3Num1 , 4 )
View full article
Picard Product_Support
‎2018-09-06 02:10 PM

Last Updated: Sisko GavinHe Sisko ‎2023-01-13 02:23 AM

Labels:
  • Andover Continuum
2143 Views

Modbus/IP and BACnet/IP on AS-P Ethernet Port 2

Issue Is it possible to use both Modbus/IP and BACnet/IP on the same AS-P Ethernet Port 2? Product Line EcoStruxure Building Operation. Environment Building Operation Automation Server Premium Cause There is a need to have both Modbus TCP as well as BACnet/IP devices on the same AS-P secondary Ethernet port. Resolution This is not a common configuration so it has not been tested extensively. With regards to the architectural guidelines, consider the Modbus/IP as BACnet/IP devices. For example, where the maximum number of SpaceLogic BACnet/IP devices per private IP field-bus is 200, adjust this limit to 190 if you have 10 Modbus/IP devices on the secondary Ethernet port.
View full article
Kirk MikaelKrantz Kirk
‎2023-01-16 11:37 PM

Labels:
  • EcoStruxure Building Operation
3982 Views

Max network length when using daisy chain MP-C devices

Issue When connecting MP-C controllers in a daisy chain, do they act as a repeater and boost the signal thus allowing total network distances of greater than 90 meters. Product Line EcoStruxure Building Operation. Environment Building Operation Multi-purpose Controller. Cause Each MP-C acts as a switch and decodes and generates a new fresh packet. Resolution Maximum 100 meters between each device when using daisy chain when connecting MP-C.
View full article
Kirk MikaelKrantz Kirk
‎2023-01-16 04:57 AM

Labels:
  • EcoStruxure Building Operation
1378 Views

Ensuring the SSL Host Certificate and key file are a matching pair

Issue After configuring SSL certificates manually, having an incompatible Host Certificate and Key file can cause the import to EBO to fail. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Central Building Operation Enterprise Server Building Operation Automation Server Cause Host Certificate provides the public key for which the private key is paired. An unmatched Host Certificate and private key will cause the certificate import to fail. Resolution While managing certificates manually, it is recommended to check that the Host Certificate and Key files are a matching pair.   Using the provided Host Certificate (.pem) file and private key (.key or .prv) file Download OpenSSL v1.1.1 Light choosing the EXE file type and correct version (Win64 or Win32), as the latest version letter will be posted to Win32/Win64 OpenSSL Installer for Windows - Shining Light Productions (slproweb.com) or OpenSSL installed with EBO If using Shining Light installer, it is recommended to open command prompt from where certificates are stored on the desktop and substitute openssl with "C:\Program Files\OpenSSL-Win64\bin\openssl.exe". Working with certificate files on the Windows desktop ensures the user will have the correct permission to run the commands, unlike putting certificate files in the Program Files directory where openssl.exe resides. Open PowerShell or Command Prompt Obtain the host certificate md5 hash with this command: openssl x509 -noout -modulus -in filename.pem | openssl md5 Obtain the private key md5 hash using the command below. Use the correct command based on the key file file type openssl rsa -noout -modulus -in filename.prv | openssl md5 openssl rsa -noout -modulus -in filename.key | openssl md5   In this example, the Host Certificate is HostCert.pem and the private key is EcoStruxure.key. The private key was converted to EcoStructure.prv using Step 12 of Installing an SSL Certificate from an External CA - Communities (se.com) These commands make the hash more readable to human eye. We use openssl to inspect the x509 for Certificate and encryption type rsa for the key to produce the modulus (-modulus), which is a long string. You then use (-noout) to prevent the full modulus from printing to the screen. You then create a shorter md5 hash so the human eye can easily compare them. If the md5 hashes match, that indicates that the modulus is a match and proves that the certificate/key is a pair.
View full article
Picard David_Purser Picard
‎2022-12-02 09:46 AM

Labels:
  • EcoStruxure Building Operation
2756 Views

Forcing deletion of personnel objects

Issue By design, the Continuum system cannot delete personnel objects until all the distributed copies can be first removed from the controller(s). In some cases the distributed copies cannot be removed from the controllers, such as when a controller is permanently offline or has been deleted. Product Line Andover Continuum Environment CyberStation Cause Communication failure between CyberStation and controllers. Resolution Starting in CyberStation version 1.94 a new feature has been added that allows the user to force a delete of personnel objects even if the distributed copies cannot be removed. In CyberStation 'Delay Distribution' dialog, a new button has been added; the button is only enabled when CyberStation is in offline edit mode. Make a backup of the Continuum database as a precaution. Close ALL CyberStation workstations. Put CyberStation in Offline edit mode to enable the 'Clean up failed personnel delete distribution' button Click on the button, the system will provide the following warning Click OK to force all personnel deletions that are pending or have failed distribution to complete; any distributed copies in the controllers will be left orphaned. If offline controller returns online orphan distributed personnel records in controller can be removed by one of the following methods: Cool start the controller.  (For controllers that support access control and backup to flash such as the CX9680, ACX5720, ACX5740 . Note that personnel objects ARE NOT saved to flash memory, the controller requests a personnel distribution from CyberStation on cool start). See Restart modes of the second generation Infinity controllers for more information on cool start. Reload the controller from the CyberStation, this will perform a cold start and re-send all objects to the controller followed by a personnel distribution.
View full article
Picard Product_Support
‎2018-09-10 11:20 AM

Last Updated: Admiral Alan_Wood Admiral ‎2023-01-11 10:54 AM

Labels:
  • Andover Continuum
3256 Views

Guidelines for combining multiple Continuum databases into one.

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue How to combine multiple Continuum DBs into one DB Product Line Andover Continuum Environment Continuum Cyberstation Cause Multiple Continuum site databases need to be combined into a single site database Resolution Guideline for combining Multiple sites to one Database Executing this procedure requires a technician who thoroughly understands Continuum and how it works with SQL Server. This procedure does not encompass BACnet controllers. There is a multitude of decisions related to efficiencies and site preferences that are not documented here. The following procedure is intended for use as a guideline for combining multiple databases. This work must be done offline on a development database and validated on a test bench before Note:Before proceeding with this procedure you must do the following. Backup the Continuum database in SQL. Backup all the files and folder structure under New Graphic Files. Note that these files may be on the SQL Server or elsewhere on a mapped drive. Back all Cyberstation Profiles. Steps 1 – 11 must be done before any of the site exports are done. Preparation All sites must have the same revision software and CX firmware. NO EXCEPTIONS! Make sure that all the Alarm Enrollments and Event Notifications have unique names between all sites as these will wind up together in a single database. Make sure that all the Graphics in the Root directory have unique names between all sites. Make sure each Schedules in the Root directory has a unique name across all sites. Make sure each Custom ListViews in the Root directory has a unique name across all sites. Make sure each Groups in the Root directory has a unique name across all sites. Make sure each Reports in the Root directory has a unique name across all sites. Once steps 1-5 are completed, export each class in the root individually. Import files from step 6 into the new site The Local Site name on all the sites that will be combined must be named LocalSite. All workstations must have unique names and ACC IDs between the sites. All CX, ACX and BCX controllers must have unique names and ACC IDs between the sites. Note: The safest way to do steps 9 & 10 is to create a new controller in offline mode with the changed ID, then drag and drop copy from the original controller to the new controller. Panels, reports, and programs then must be edited to bind to the new controller. Another way to merge the panel, reports, and programs that are in the root is to copy all the panels, programs, and reports to their corresponding controller then export the controller. Doing this will keep all the bindings linked. Then once the controller is imported into the merged database they can be copied back up to the root. All Commports on all controllers and workstations must be named Comm1, Comm2, etc… Each site must have the default “ACC” user and password. All graphic files (.pin) under the New Graphic Files folder must have unique names between the sites. Merging the databases Install a standard multi-user Continuum system being sure to size the database big enough to accept all the other databases combined into one database.  After a clean installation is done, shut down the new workstation and the SQL server. Copy the empty database files to an area where they won’t get corrupted. Do a complete site export from each of the sites that will be combined. Back up all the Graphic files (.Pin) files from the site so that they can be transferred to the new server. Copy all the backed up Graphic files (.Pin) from each site onto a New Graphics Files folder in the location of choice. Note these files can reside on the SQL server or elsewhere on a mapped drive. Import each of the site text exports from the old systems into the new system. After each import check to make sure that each import went cleanly. Check all the Graphics, Programs, Alarm Enrollments, and Event Notifications to make sure that all the links were made during the import process.
View full article
Picard Product_Support
‎2018-09-07 01:49 PM

Last Updated: Administrator CraigEl Administrator ‎2023-01-11 07:34 PM

Labels:
  • Andover Continuum
816 Views

Configure the Flexnet License Administrator web portal to use HTTPS

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Cybersecurity vulnerability scans are flagging the Building Operation License Server because it is using HTTP rather than HTTPS Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation License Server Cause The Building Operation License Server contains a web portal for diagnostics and administration. By default, the Building Operation License Server Administration web portal is configured to use HTTP Resolution It is possible from the Administration area of the Building Operation License Server Administration web portal to configure HTTPS communications. Note: this does not change how Ecostruxure Building Operation connects to the license server.   The following process configures the Building Operation License Server Administration web portal to use HTTPS   From a web browser open the Building Operation License Server Administration web portal by typing http://localhost:8888 Once the web portal opens, select Administration at the top right. You will be prompted to log on, use "admin" as the user name. If you have logged in before, use the password you have defined. If not, enter "admin" as the password, and you will then be prompted to create a password. Once signed in Select the Server Configuration tab. Under the Secure Web Server Configuration section, select Enable HTTPS Change HTTPS Port to a unique number e.g. 8443 Select Redirect Non-Secure Web Access to Secure Web Access At the bottom of the page click the Save button and close the web browser tab. Restart the Building Operation X.X License Server from the Windows Services app (services.msc) If the license server is opened using http://localhost:8888 it will now redirect to HTTPS using the port specified in step 4 above
View full article
Administrator CraigEl Administrator
‎2023-01-11 04:50 PM

on ‎2023-01-11 04:50 PM

Labels:
  • EcoStruxure Building Operation
3053 Views

Does EBO 2022 support multi-verson for AS classic (part number - SXWAUTSVR10001)?

Issue How can I find out whether the EBO 2022 multi-version support applies to AS Classic module?  Does it apply to all the AS, AS-P, and AS-B modules? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Cause The EBO 2022 Release Note describes that the EBO 2022 Device Administrator software is not supported on the original AS classic (part number SXWAUTSVR10001) but there is no description of the software backward compatibility of the EBO on AS classic. Resolution An AS classic can continue to exist in a multi-version system; the maximum version an AS classic can operate at is 3.1.2. It is nowhere implied that it is not supported under a multi-version setup. The statement “EBO 2022 does not support AS classic” in the EBO 2022 Release Note is misunderstood. It simply means that one cannot install EBO 2022 on an AS Classic, the same as the previous EBO 3.2 version. Note that the AS Classic will not inherit any features introduced in later EBO releases when operating in a multi-version system.
View full article
Lieutenant | EcoXpert Master SangKim Lieutenant | EcoXpert Master
‎2023-01-09 04:11 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2023-01-10 03:42 PM

Labels:
  • EcoStruxure Building Operation
2181 Views
  • « Previous
    • 1
    • …
    • 44
    • 45
    • 46
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of