Is it possible to use both Modbus/IP and BACnet/IP on the same AS-P Ethernet Port 2?
EcoStruxure Building Operation.
Building Operation Automation Server Premium
There is a need to have both Modbus TCP as well as BACnet/IP devices on the same AS-P secondary Ethernet port.
This is not a common configuration so it has not been tested extensively. With regards to the architectural guidelines, consider the Modbus/IP as BACnet/IP devices. For example, where the maximum number of SpaceLogic BACnet/IP devices per private IP field-bus is 200, adjust this limit to 190 if you have 10 Modbus/IP devices on the secondary Ethernet port.