Controlling command priorities with Continuum workstation programs or Infinity controller programs.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Controlling command priorities with Continuum workstation programs or Infinity controller programs.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe
  • Carl_Slack
    Carl_Slack
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2409 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Controlling command priorities with Continuum workstation programs or Infinity controller programs.

Picard Product_Support
‎2018-09-06 02:10 PM

Last Updated: Sisko GavinHe Sisko ‎2023-01-13 02:23 AM

Issue

What is required to control command priorities in 3rd party controllers using Plain English?

Product Line

Andover Continuum

Environment

  • Continuum Cyberstation
  • BACnet Controller (BCX, B4920, B3)
  • BACnet command priority
  • Plain English

Cause

Need to understand how to control command priorities and point values with Continuum workstation programs or controller infinity programs.

Resolution

Command Priority is a BACnet mechanism to decide the control hierarchy of a point, with 1 being the highest priority and 16 being the lowest.  Consider the following:

 

  • Default setting for a workstation program priority level is ManualOperator priority 8
  • Programs located in the workstation default command priorities can be controlled through Bacnet Preferences
  • Controller InfinityPrograms will need to use the WriteProperty function to set a different priority other than priority 10
  • To relinquish a priority level use Relinquish(pointname, priority level)

 

The WriteProperty function is written in the format:

WriteProperty (object_name, value, priority, index)

object_name 

  • Includes a full pathname, followed by a property name.
  • The object identifier and property identifier are combined as one argument

value  

  • This actual value to which the property is set.
  • This is optional.  If it is not present, then the next argument, priority, must be present to perform a Relinquish command.  (See the example in Relinquish.)

 priority 

  • The priority  number, ranging from 1 (highest) to 16 (lowest).This is optional.  It applies only to a set commandable property.
  •  For controllers:  If it is not present, priority 10, if applicable, is used.
  •  For CyberStation: The value, based on the priority in the BACnet Preferences dialog, is used.

 index 

  • This is optional.  It applies only to an array-type BACnet property.  The index is ignored whenever it is not applicable.

 

Infinity controller samples:

This line will write the value of 22 to priority 10

BACnetDevices\BNet_4444\B3_885\B3Num1 = 22

This line will write the value of 33 to priority level 4

WriteProperty(BACnetDevices\BNet_4444\B3_885\B3Num1, 33 , 4 )

This line will relinquish the value for priority level 4 setting the value back to NULL

Relinquish(BACnetDevices\BNet_4444\B3_885\B3Num1 , 4 )

Labels (1)
Labels:
  • Andover Continuum
Tags (2)
  • Find more articles tagged with:
  • 4542
  • GavinHeward23
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore