Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

SLP Sensor Modbus RTU issue when used with RPC or Automation Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • SLP Sensor Modbus RTU issue when used with RPC or Automation Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • Dave_Shore
    Dave_Shore
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
4 Likes
3324 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

SLP Sensor Modbus RTU issue when used with RPC or Automation Server

Dave_Shore Schneider Alumni (Retired)
‎2021-02-03 06:29 AM

Issue

  • SLP Sensor Modbus RTU issue when used with RPC or AS
  • Communication errors are seen during normal
  • Values are updated very slowly, can take up to two minutes to populate/update the 15 objects within the SLP.  

Product Line

EcoStruxure Building Operation

Environment

  • Modbus RTU
  • RPC Modbus
  • Automation Server + Premium 
  • SLP SpaceLogic Sensors LSA_APP_REV2.03.19 and REV2.05.21

Cause

Once the Modbus communication is set up between RPC (or AS) and the SLP,  although the values updates fairly regularly, multiple communication errors are also seen

The SLP read speed needs to regulated to prevent overwhelming it

The SLP Modbus transmission voltage is less than the AS

Resolution

Use with RP-C

  • SLP struggles to respond to every request from the RP-C, changing the baud rate to 9600/19200 and increasing the "Silence characters" in the interface to 255 (maximum possible) should stabilize the communications. 
    Modbus_RP-C.png
  • The character spacing cannot be adjusted enough in the RP-C to allow communication at 38400 or 76800

Use with AS/AS-P 

  • Adjust the “Poll point delay” in the Modbus Interface to 80ms
  • The Silence characters and Transmit guard bits may also need to be increased
    ModbusMasterPolldelay.png
  • Baud rate up to 38400 has been tested.

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • DavidShore21
  • DavidShore23
  • RobertAndriolo21
Was this article helpful? Yes No
84% helpful (5/6)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of