Guidelines for combining multiple Continuum databases into one.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Guidelines for combining multiple Continuum databases into one.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1159 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Guidelines for combining multiple Continuum databases into one.

Picard Product_Support
‎2018-09-07 01:49 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:38 AM

Issue

How to combine multiple Continuum DBs into one DB

Product Line

Andover Continuum

Environment

Continuum Cyberstation

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Multiple Continuum site databases need to be combined into a single site database

Resolution

Guideline for combining Multiple sites to one Database

Executing this procedure requires a technician who thoroughly understands Continuum and how it works with SQL Server.

This procedure does not encompass BACnet controllers.

There is a multitude of decisions related to efficiencies and site preferences that are not documented here. The following procedure is intended for use as a guideline for combining multiple databases.

This work must be done offline on a development database and validated on a test bench before

Note:Before proceeding with this procedure you must do the following.

  • Backup the Continuum database in SQL.
  • Backup all the files and folder structure under New Graphic Files. Note that these files may be on the SQL Server or elsewhere on a mapped drive.
  • Back all Cyberstation Profiles.

Steps 1 – 11 must be done before any of the site exports are done.

Preparation

  1. All sites must have the same revision software and CX firmware. NO EXCEPTIONS!
  2. Make sure that all the Alarm Enrollments and Event Notifications have unique names between all sites as these will wind up together in a single database.
  3. Make sure that all the Graphics in the Root directory have unique names between all sites.
  4. Make sure each Schedules in the Root directory has a unique name across all sites.
  5. Make sure each Custom ListViews in the Root directory has a unique name across all sites.
  6. Make sure each Groups in the Root directory has a unique name across all sites.
  7. Make sure each Reports in the Root directory has a unique name across all sites.
  8. Once steps 1-5 are completed, export each class in the root individually.
  9. Import files from step 6 into the new site
  10. The Local Site name on all the sites that will be combined must be named LocalSite.
  11. All workstations must have unique names and ACC IDs between the sites.
  12. All CX, ACX and BCX controllers must have unique names and ACC IDs between the sites.


Note: The safest way to do steps 9 & 10 is to create a new controller in offline mode with the changed ID, then drag and drop copy from the original controller to the new controller.

Panels, reports, and programs then must be edited to bind to the new controller.

Another way to merge the panel, reports, and programs that are in the root is to copy all the panels, programs, and reports to their corresponding controller then export the controller. Doing this will keep all the bindings linked. Then once the controller is imported into the merged database they can be copied back up to the root.

  1. All Commports on all controllers and workstations must be named Comm1, Comm2, etc…
  2. Each site must have the default “ACC” user and password.
  3. All graphic files (.pin) under the New Graphic Files folder must have unique names between the sites.

Merging the databases

  1. Install a standard multi-user Continuum system being sure to size the database big enough to accept all the other databases combined into one database. 
  2. After a clean installation is done, shut down the new workstation and the SQL server.
  3. Copy the empty database files to an area where they won’t get corrupted.
  4. Do a complete site export from each of the sites that will be combined.
  5. Back up all the Graphic files (.Pin) files from the site so that they can be transferred to the new server.
  6. Copy all the backed up Graphic files (.Pin) from each site onto a New Graphics Files folder in the location of choice. Note these files can reside on the SQL server or elsewhere on a mapped drive.
  7. Import each of the site text exports from the old systems into the new system.
  8. After each import check to make sure that each import went cleanly.
  9. Check all the Graphics, Programs, Alarm Enrollments, and Event Notifications to make sure that all the links were made during the import process.
Labels (1)
Labels:
  • Andover Continuum
Tags (4)
  • Find more articles tagged with:
  • 7669
  • AbeMeran23
  • johnboehmer20
  • two
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore