1.8 kOhm thermistor on the RTD-16 I/O module
  • 1.8 kOhm thermistor on the RTD-16 I/O module
  • MikaelKrantz
    MikaelKrantz
Guinan MikaelKrantz Guinan
‎2023-01-18 04:51 PM
Last Updated: Administrator CraigEl Administrator ‎2023-01-18 04:54 PM
Is it possible to use a TAC Xenta 1.8 kOhm thermistor on an RTD-16 Central I/O module?
EcoStruxure Building Operation.
Building Operation I/O Module 16 Ch RTD
Wants to use existing modules instead of adding new modules.
The RTD-16 module is designed to interface with linear resistive inputs such as PT100, PT1000. Thermistors generally have logarithmic scales, therefore it will be hard to program a correct curve function to get an acceptable sensor accuracy. Using a universal input that is made for thermistor readings will give a more accurate reading without additional programming.