Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 15
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1845 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 7
    • 8
    • 9
    • …
    • 93
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Galvanic isolation for SHD2/SCD2

Issue Does SHD2/SCD2 have galvanic isolation? Product Line EcoStruxure Building Operation Environment Building Operation SmartX Living Space Sensor Cause Galvanic isolation is a principle of isolating functional sections of electrical systems to prevent current flow; no direct conduction path is permitted. Resolution The SHD2XP2A/SCD2XPXAVX does not have galvanic isolation.
View full article
Kirk MikaelKrantz Kirk
‎2024-04-24 04:18 AM

Last Updated: Janeway PeterEdvik Janeway ‎2024-04-24 04:19 AM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
1642 Views

Long delay in Graphic that displays values read from remote server over EWS

Issue ES is connected to a remote server via EWS; when loading a graphic in a web browser or workstation, the values take a long time to read. (a few minutes.) It makes no difference what the settings for polling are configured for. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Cause Every time the graphic is brought up, the ES needs to subscribe to all values from the external EWS server, this is the cause of the delay. Resolution Workaround Solution: Maintaining Active Subscriptions The recommended workaround solution involves maintaining active subscriptions. This can be achieved through the following methods: Persistent Graphic Display: Always keep the graphic displayed on a client. This is crucial as the subscriptions are terminated when the graphic object is closed. By keeping the graphic open, the subscriptions remain active. Watch View Creation: Create a watch view that includes the values displayed in the graphic. This ensures that the values are constantly monitored and updated. As long as a client subscribes to these values, the update process will be expedited when the graphic is launched. This is because the subscriptions remain active, and the values do not need to be re-initialized. However, if there are no active subscriptions to the values, all values must be set up each time the graphic is opened. This can potentially slow down the process. Therefore, maintaining active subscriptions is highly recommended for efficient operation.
View full article
Captain AbeMeran Captain
‎2024-04-19 11:02 AM

Last Updated: Picard David_Purser Picard ‎2024-04-19 11:05 AM

Labels:
  • EcoStruxure Building Operation
1765 Views

Unable to create new dates and new values in Webstation Calendar

  Issue The WebStation menu used to create new calendar dates and values is not visible. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Webstation Building Operation Enterprise Server Cause The panel used to display the calendar schedule is incorrectly configured Resolution In Workstation, right-click on Panel and go to Properties, go to Show Toolbars, and choose Yes.    Now when you log in to Webstation, you will see the toolbar including the menu on the top of the calendar in the panel.     
View full article
Lt. Commander Ramaaly Lt. Commander
‎2024-04-16 09:48 AM

Last Updated: Administrator CraigEl Administrator ‎2024-04-16 04:45 PM

Labels:
  • EcoStruxure Building Operation
1936 Views

Container Servers create same Instance ID for BACnet interface

Issue When the BACnet Interface is created in Container Servers, the automatically generated Device Object ID aka Instance ID can be the same as another Container Server on the same container host. Product Line EcoStruxure Building Operation Environment Building Operation Edge Server Building Operation Enterprise Server for Linux Cause The algorithm used to pick BACnet Interface Device IDs in individual Automation Servers does not work for Container Servers since they share the same ethernet connection,. Resolution Perform tasks to ensure Instance IDs are unique. One can prevent the issue by ensuring uniqueness when adding the BACnet Interface  When adding Interface -> BACnet Interface, do NOT click Create or Create and Edit, but click Edit in Wizard.  Enter the following data BACnet Name Instance ID (ensuring unique ID to the entire BACnet system) Leave Network Type = IP network Network ID (this should be the same network ID as the IP network is attaching)  One can repair the issue and ensure uniqueness after creating the BACnet Interface. Changing the BACnet Device ID in an Automation Server to configure unique ID Repair Hosting a BACnet controller and IO Module  Fixing References in BACnet/IP Controllers 
View full article
Picard David_Purser Picard
‎2024-04-08 10:08 AM

on ‎2024-04-08 10:08 AM

Labels:
  • EcoStruxure Building Operation
3076 Views

EcoStruxure WebReports Installation Errors (1001 while importing report pack)

Issue Getting an Error 1001 near the end of the EcoStruxure WebReports Installation Reports not functional from WebReports Product Line EcoStruxure Building Operation Environment Web Reports SQL 2008 R2 Windows Server 2008 Windows Server 2012 Cause This error is caused when the WebReports installer is unable to reach SQL Server Reporting Services to configure the WebReports Interface Resolution After a failed install of WebReports you will need to follow the general workflow:   Clean of the Pieces of the failed install. Use the uninstall process listed in the WebReports Reference Guide or Uninstall Process for Web Reports. Correct all possible causes of the failed install Verify that you can connect to the ES using http from the Reports Server PC Verify that you can connect to http://localhost/Reports_SQLInstanceName  Re-install WebReports. NOTE: You may be able to correct the issue without having to remove and re-install WebReports. Possible Issue: The Microsoft Reporting Service SQL databases are not registered Check through SQL Management Studio that the 2 databases "ReportServer$instance" and "ReportServer$instanceTempDB" are registered. If not, the SBO Web Reports installed have nowhere to place the report pack files. If they are not there, you need to add them through "Reporting Services Configuration Manager". Click "Database" and then "Change Database". Here you can chose to create new databases. Possible Issue: Insufficient User Access Log out of Windows and Log back in using a PC admin account. The account logged in for the installation should have full access to Windows and be a DB admin in the SQL Server. Set the User Account Control Settings to Never notify. Possible Issue: PC Configured as a Domain Server In the Server Manager, check that the IIS Role is configured and that there are no Domain Roles assigned to this PC Possible Issue: Another Application is using a Required SQL function Uninstall any application which use SQL on this PC. (The Enterprise Server does not Use SQL) As a Best Practice, the Reports Server should be installed on its own, dedicated PC. Possible Issue: Incorrect Version of SQL Server or Windows Server Check the Reports Server Specification Sheet for your build and verify that you are on the Correct Version of Windows and SQL. Possible Issue: Secure Connection Level set too high This issue typically also results in not being able to log into http://localhost/Reports_SQLExpress. Log into the Reporting Agent Configuration Manager Application Click on the Report Manager URL on the left-hand column Click on the HTTP URL This will give you the correct URL for your installation of SQL If this fails, browse to C:\ProgramFiles\Microsoft SQL Server\MSRS10_50.SQLEXPRESS\Reporting Services\ReportServer (this may vary based on SQL Installation)   Modify the CONFIG file "rsreportserver" Change the Secure ConnectionLevel to "0" Save the file and attempt to log into http://localhost/Reports_SQLExpress again. For more details on this property see: http://technet.microsoft.com/en-us/library/aa179559(v=sql.80).aspx Possible Issue: .NET Framework is not operating correctly. Download the correct version of .NET framework for your version of EBO (The correct required version can be found on WebHelp Reports Server under EcoStruxure Building Operation Software Requirements) Run the installer in "Repair" mode Possible Issue: The Windows account "appuser" is not created because the default password does not meet password policy requirements Temporarily disable password policy on the server and try reinstalling. For clarification of the use of 'appuser', refer to the following article, Report Server "appuser" clarification 
View full article
Picard Product_Support
‎2018-09-11 05:11 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2024-04-07 07:21 PM

Labels:
  • EcoStruxure Building Operation
4532 Views

Energy Expert Compatibility Matrix

Issue There is a need for a single Compatibility Matrix that shows EBO, PME, Energy Expert and relevant software versions all in the same location.   Product Line EcoStruxure Building Operation, Other   Environment EcoStruxure Energy Expert (formerly Power Manager) ETL tool Cause Energy Expert version compatibility information is currently available but is stored in many different places such as release notes and online documentation, rather than one single matrix.   Resolution The full ETL for EBO compatibility matrix is shown in the following table. Energy Expert  PME EBO ETL Integration Utility .NET Framework Power Manager 1.0 7.2.3 1.6.1 3 1.0.14304.2 4.5 Power Manager 1.1 8 1.6.1  1.7.1 4.1 1.0.15306.1 4.5 Power Manager 1.2 8.1 1.6.1  1.7.1  1.8.1 4.3 2.1.16081.1 4.6 Power Manager 1.3 8.2 1.8.1 1.9.x  4.6 2.2.17056.2 4.6 Energy expert 2.0 9 2 5 3.0.18215.3 4.6 Energy expert 3.0 2020 3.0 3.1 6 3.1.19319.1 4.6 Not commercialized  - (n/a) 2021 3.2.3 6 Integrated - (n/a) 4.8 Not commercialised - (n/a) 2022 4.0.2/2022 6 Integrated - (n/a) 4.8 Not commercialised - (n/a) 2023 5.0/2023 6 Integrated - (n/a) 4.8   Great care must be taken when choosing the correct version of ETL to use when integrating Energy Expert and EBO, as there are actually two families of ETL in production.  One ETL designed and tested for PME use only and ETL for EBO designed and tested with an EBO Extract Task specifically for integrating the two systems.  (For example, a version of ETL 4.7 exists, but this is not ETL for EBO and therefore does NOT contain an EBO Extract Task, even though it is a valid version of ETL for the Power Community) New PME 2023 now offers EWS Client 1.2 which can be used to transfer data from EBO to PME instead of ETL.  The merits for and against using this new EWS Client rather than ETL are discussed at length in the PME 2023 System Guide
View full article
Lieutenant JG Robert_Davis Lieutenant JG
‎2020-12-29 10:10 AM

Last Updated: Admiral David_Kendrick Admiral ‎2024-04-04 04:17 AM

Labels:
  • EcoStruxure Building Operation
4691 Views

ES upgrade from 3.2.3.59 to 5.0.3.117 is failing

  Issue Performing an Enterprise Server upgrade preview from 3.2.3.59 to 5.0.3.117, the upgrade fails with the error "INET legacy interface no longer supported." message      Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Cause An existing folder in the Enterprise Server contained graphics underneath the INET interface. This folder was moved within the system, and the INET interface was deleted. However, the moved folder still had links to the INET interface, causing the upgrade to fail since this interface is not supported in Building Operation 2022 (v.4) and above.  Resolution Delete any references in the database linked to the INET Interface. Bindings Diagnostics provides a quick method for locating these unresolved references.   After deleting these objects and/or references, the upgrade will completed successfully.
View full article
Lt. Commander Ramaaly Lt. Commander
‎2024-03-27 01:17 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2024-03-27 04:14 PM

Labels:
  • EcoStruxure Building Operation
2359 Views

How to Mass Create Trend Logs and Extended Trend Logs

Issue How to Mass Create Trend Logs and Extended Trend Logs Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause If you did not create Trend Logs at the same time as you created the points or values, it is possible to create several trend logs or extended trend logs at the same time. Resolution For this example, we assume all of the values are in the same folder. You can hold down SHIFT to select multiple adjacent objects, or CTRL+click to select non-adjacent values Mass Creation of Interval Trend Logs Select all of the Values you wish to add the same type of Log to Right Click and select New connected object>Trend Select the Log type and the settings you wish to use.  Note that the log name will be the values name with either a prefix or suffix defined by the user Be sure to Select a useful folder location, either same folder as each selected object, a different folder, relative to the selected object or a single folder for all created objects. Click Edit in wizard. Set the Interval Settings, if iterval log type is selected. Click Next, configure initial meter settings if required, click next tehn click create Mass Creation of Extended Trend Logs if required Select the group of Logs you wish to create Extended Trend Logs for Right Click and select New connected object>Extended Trend Log Enter the desired settings. Just as above, the Extended log will use the Log' name plus either a prefix or suffix Be sure to Enter an appropriate Location. Use a folder on the ES if you wish these logs to show up on the Reports Server (Report server is not supported in EBO 2022 and higher). Click Edit in Wizard, Configure the Extended Log as desired, then click create. Fore more information, refer to: Mass Creating Trend Logs and Mass Creating Extended Trend Logs
View full article
Picard Product_Support
‎2018-09-07 05:13 AM

Last Updated: Spock PeterLarsen Spock ‎2024-03-25 10:38 PM

Labels:
  • EcoStruxure Building Operation
3257 Views

EBO 5.0 Alarm attachment will display a PDF file instead of TGML graphic when alarm is enabled

  Issue The customer has created an alarm, this alarm has an Attachment that displays a Graphic (Display on Alarm enabled). All the remote Workstations at this site show the graphic popup on alarm, except a single Workstation. That Workstation will display PDF Files 'On alarm', but not TGML graphics. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Building Operation Workstation Cause Either, they at the same time had two monitors and placed the graphic attachment on the other monitor, and then the position was saved. Or by mistake managed to move the attachment out of the current monitor scope Resolution Remove WorkStation cache from both (User + Program data) :  User: C:\Users\*user-name*\AppData\Roaming\Schneider Electric EcoStruxure\Building Operation\WorkStation  Program data: C:\ProgramData\Schneider Electric EcoStruxure\Building Operation\WorkStation The alarm will now display the TGML graphic attachment
View full article
Lt. Commander Ramaaly Lt. Commander
‎2024-03-27 01:14 PM

on ‎2024-03-27 01:14 PM

Labels:
  • EcoStruxure Building Operation
2737 Views

In Webstation Alarm history view is different than in workstation

  Issue EBO 5.0 and all other revisions, In workstation When selecting `View history` of an alarm, we get columns more focused on alarms such as Alarm state, Alarm text,.. etc  But  in WebStation, we have “ View Events “ that shows columns that are more focused on object event history (including Value before, Value After, etc) rather than alarm history.       Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Webstation Building Operation Automation Server Premium Cause Navigating to View Alarm history in webstation is different than in workstation Resolution Alarm is a subset of Event, so it is reasonable to see it is under 'Event viewer'. There is no such a thing called 'Alarm history record' in webstation.This is Function as Designed (FAD) If we click on any of the events, after opening it we can see full alarm details.
View full article
Lt. Commander Ramaaly Lt. Commander
‎2024-03-27 01:12 PM

on ‎2024-03-27 01:12 PM

Labels:
  • EcoStruxure Building Operation
1841 Views

How to check and stop Event data filling up Building Operation Reports Server

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue Log data is not being logged into SQL. The Reports Server indicates that the database is full.   This view will be shown when logging into the WebReports interface. If this chart is not shown, the PC is not running an Express edition of SQL. Product Line EcoStruxure Building Operation Environment Reports Server Cause In most instances, the data that quickly fills the SQL database are Events. Event data fills the SQL Database and prevents log data from passing to the Reports Server database. If the data has filled within a few days, this would indicate an issue, and contacting your local support is the best option here. The Process below allows the user to stop the reporting agent from passing specific information to the Reports Server. If the data files are due to the amount of data stored, then an upgrade to the Standard/Full version of SQL is recommended.   Resolution To verify that the Events table is the likely cause of the SQL filling up, there are Standard Reports in the later versions of SQL.  The below example uses SQL Server version 13.x and shows the "Disk Usage by Top Tables."   If the Standards Reports are not available, then use the following article Building Operation Reports SQL Database Full, for instructions on how to show the details for each table.     The Process below allows the user to stop the reporting agent from passing Event information to the SQL Database: Download the latest SBO Reports Agent Config tool from the community. Load the Tool onto the Reports Server PC. Stop the Reporting Agent Using the Tool Press F7 to get to the Advanced Agent Configuration Page Change the numEventRecordToRead property to 0. This will prevent future event data from being written to the Reports Server database. Press Ok Under the Maintenance tab of the tool - there are two options under Events  Delete future events, alarms, and trends  Delete events and alarms older than... Restart the Reporting Agent This will stop any further Events from being passed through to the SQL Database.  
View full article
Picard Product_Support
‎2018-09-11 11:39 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2024-03-24 06:07 PM

Labels:
  • EcoStruxure Building Operation
408 Views

Building Operation Report Server SQL Database Full

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue SQL Database is full, or the partition the SQL is installed is full Product Line EcoStruxure Building Operation Environment Building Operation Report Server Cause If a site is using SQL Express 2008, the limit is 10 GB. If using the full version(s), it is unlimited. If the database or the partition where the Reports Server resides is full, here are some steps to reduce the SQL table volume and offer a short-term solution. Resolution Before continuing, make sure there is a good backup of the database. Using SQL Server Management Studio, highlight the StruxureWareReportsDB and select New Query Use the following Script in that Query: SELECT t.NAME AS TableName, s.Name AS SchemaName, p.rows AS RowCounts, SUM(a.total_pages) * 8 AS TotalSpaceKB, SUM(a.used_pages) * 8 AS UsedSpaceKB, (SUM(a.total_pages) - SUM(a.used_pages)) * 8 AS UnusedSpaceKB FROM sys.tables t INNER JOIN sys.indexes i ON t.OBJECT_ID = i.object_id INNER JOIN sys.partitions p ON i.object_id = p.OBJECT_ID AND i.index_id = p.index_id INNER JOIN sys.allocation_units a ON p.partition_id = a.container_id LEFT OUTER JOIN sys.schemas s ON t.schema_id = s.schema_id WHERE t.NAME NOT LIKE 'dt%' AND t.is_ms_shipped = 0 AND i.OBJECT_ID > 255 GROUP BY t.Name, s.Name, p.Rows ORDER BY t.Name Select Execute to run that Query as shown in the screen capture below: The Results show each of the tables and the size of those tables as shown in the screen capture below: Purely for example purposes, a script to reduce the number of Events would be delete from tbEvents where DATEDIFF(day, datetimestamp, getdate()) > 180 To gain back the space after deleting rows, right-click on StruxureWareReportsdb > Tasks > Shrink > Database
View full article
Picard Product_Support
‎2018-09-11 02:54 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2024-03-24 06:14 PM

Labels:
  • EcoStruxure Building Operation
6157 Views

Connecting Multiple RPC-12-A Inputs to the Same Dry Contact

Issue In a life safety-related application, such as a fume hood, it is a requirement that the status of the end switch is not shared via peer-to-peer bindings. Instead, the end switch status must be hard-wired to all four controllers. What precautions should be taken to ensure that this will not cause issues. Product Line EcoStruxure Building Operation Environment Building Operation Room Controller (RPC) 24 V Cause Connecting multiple RP-C to the same dry contact.    Resolution Make sure to use individual transformers to each controller (i.e. one transformer to one controller power supply) to minimize the risk of short circuit.
View full article
Kirk MikaelKrantz Kirk
‎2024-03-24 05:32 PM

on ‎2024-03-24 05:32 PM

Labels:
  • EcoStruxure Building Operation
2197 Views

TAC Xenta alarms comes in with a different priority in StruxureWare Building Operation

Issue TAC Xenta alarms are configured with a priority of 1 in Menta, but these same alarms appear with a priority of 100 in EcoStruxure Building Operation. Product Line EcoStruxure Building Operation Environment Building Operation Workstation TAC Xenta 301, TAC Xenta 302, TAC Xenta 401, TAC Xenta 281, TAC Xenta 282 Cause This is per design, Building Operation supports priorities from 0-1000, aligning alarm priorities from TAC Xenta within the range of 100-900 is a deliberate choice. By default, all alarm priorities from TAC Xenta are multiplied by 100 to fit this scheme. Resolution To revert the priority back to the original, open the properties for the alarm and manually adjust the priority.
View full article
Picard Product_Support
‎2018-09-10 01:31 PM

Last Updated: Administrator CraigEl Administrator ‎2024-03-24 05:21 PM

Labels:
  • EcoStruxure Building Operation
1687 Views

Modbus groups with duplicate registers

Issue An increased amount of polling caused by Modbus groups with duplicate registers. Product Line EcoStruxure Building Operation Environment Modbus Building Operation Automation Server Premium (AS-P) Building Operation Automation Server Bundled (AS-B) Building Operation Automation Server (AS) Cause Modbus Register Groups cause multiple resisters to be requested in a single query. This can be a very efficient way of collecting data from a device. See this Article for details. However, if a register is repeated (duplicated) within a group it can cause an increased amount of polling.    The screenshots shows a Modbus Register Group with a Requested group poll interval set to 10,000ms, but the misconfiguration is forcing polls at 500ms. Resolution The resolution is simply to avoid such a configuration. NOTE - If a Modbus Register Group with duplicates registers becomes unstable with some registers showing offline, then disabling the Scattered Read function will usually help.
View full article
Dave_Shore Schneider Alumni (Retired)
‎2022-04-27 07:09 AM

Labels:
  • EcoStruxure Building Operation
1449 Views

MPx Triac Minimum current requirements

Issue There is no minimum current listed on the datasheet for Triac outputs on MPx controller. Product Line EcoStruxure Buildings Operation Environment Building Operation Multi-purpose Controller Cause Triac output not correctly switching due to the very small current load. Resolution The triac used in an MPx controller will run on low voltage and currents. In certain circumstances, the current drawn will not be sufficient to keep the triac in the MPx active. This has been seen to be in the region of 10-15 mA. In this case, a resistor would need to be installed in parallel with the triac to ensure you get a current draw of 20 mA or more for stable operation. It should also be noted that a Triac output is designed to switch AC load (24 VAC, 0.25 A maximum) and not DC load, refer to: Triac Outputs. An improved option to the MPx is an RP-C, RP-V or RP-IO, which can switch DC and AC loads with very low current draw, refer to: Solid-state Relay (SSR) Outputs.
View full article
Spock PeterLarsen Spock
‎2020-03-31 06:54 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-03-13 05:40 AM

Labels:
  • EcoStruxure Building Operation
1343 Views

Sum Alarm in EcoStruxure Building Operation

Issue The Sum Alarm will not trigger when monitoring other Sum Alarms. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server  Building Operation Enterprise Server Cause The Sum Alarm is ignoring other Sum alarms for detection of alarm criteria. Resolution There are two options to resolve this. Configure a 2nd SUM alarm to use criteria that triggers on any of the points that would have triggered the Sum alarm you want to monitor and the other points. You can create a Change of State Alarm to monitor the alarm state of the 1st Sum Alarm. The second Sum alarm can then detect that the Change of State alarm is active. (It might be practical to hide the Change of State alarm by setting the priority to a low value and filter your default alarm view to exclude it in order to avoid double alarm entries in the alarm view of Workstation)
View full article
Picard Product_Support
‎2018-09-06 10:25 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2024-03-12 02:20 AM

Labels:
  • EcoStruxure Building Operation
1855 Views

OGC graphic does not load when opened in Vista Webstation inside StruxureWare Webstation

Issue When opening an OGC graphic using Vista Webstation as a window inside StruxureWare Webstation, the OGC graphic shows "Loading..." with a small cross in the upper left corner, and the graphic never loads. Product Line EcoStruxure Building Operation Environment TAC Vista Webstation Building Operation Webstation   Cause The authentication in the communication between the browser and Vista Webstation is based on sessions and cookies. Due to a security setting on some sites, the initial cookie can not be set in the browser, and the authentication between the OGC graphic page showed in the browser and the web server therefore fails. If the graphic is opened in full screen (see below) or in a new window it will load, and subsequently all OGC graphics will work until the browser is restarted. Button to open the graphic in full screen Resolution On each PC that needs to access the OGC graphics using StruxureWare Webstation do the following: 1. Open Internet Explorer settings by clicking the gear in the upper right corner 2. Click "Privacy" and then "Sites" 3. Write the address of Vista Webstation (e.g. http://ip_address/webstation), click "Allow" and "OK" 4. Restart Internet Explorer   Note: This solution also applies to following issue; After clicking  a Vista Webstation url (direct link to a TGML graphic) in SBO Webstation from a Windows Server 2012 PC using Internet Explorer 11, Vista Webstation is expanding to fill the entire screen (it doesn't stay in the right hand window of SBO Webstation)
View full article
Picard Product_Support
‎2018-09-10 02:27 PM

Last Updated: Janeway Jonas_Brissman Janeway ‎2024-03-08 05:15 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1925 Views

Upgrade Xenta 401, Xenta 300 HW1 to latest system version

Issue Is it possible to upgrade TAC Xenta 401 and TAC Xenta 300 HW1 to latest system version? Product Line EcoStruxure Building Operation  Environment TAC Xenta 401 TAC Xenta 301 TAC Xenta 302 Cause Whenever possible, upgrading to the latest system version will give you all of the latest product fixes and enhancements. Resolution You can upgrade TAC Xenta 300 as well as TAC Xenta 401 to any system version BUT you cannot use HW1 in EcoStruxure Building Operation. All HW versions can be upgraded for use in TAC Vista Classic system.
View full article
Picard Product_Support
‎2018-09-06 10:43 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2024-03-08 04:55 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1957 Views

Domain Usage within SmartStruxure 1.2 and later

Issue The functionality of StruxureWare Domains changed substantially in 1.2. There has been some discussion that the inability to communicate or the failure to transfer data from one SmartStruxure server to another is somehow related to the servers not being in the same StruxureWare Domain. This is not the case. As of 1.2 StruxureWare Domains are not used for communication at all. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server (ES) Building Operation Automation Server Premium (AS-P) Cause StruxureWare Domains are NOT used at all for establishing communication within SmartStruxure 1.2 and later releases If the AS can be added under the ES and no alarms are generated by the added AS, then full data sharing is possible regardless of StruxureWare Domain creation or membership. Resolution If the AS can not be added under the ES then there is a network problem that is preventing communication from the ES to the AS. If the AS can be added, but communication errors or lead verification alarms are generated that show the added AS as the source server, then there are network (or firewall) issues that are preventing the AS from communicating with the ES. If all engineering and configuration is done from the ES with the admin account in the Local Domain All bindings can be created by admin in the local domain All data can be viewed in graphics, trend charts, etc. by admin in the local domain Only data within the local AS can be viewed  by admin logged into the local domain of the AS This is true regardless of WorkStation or WebStation A StruxureWare Domain other than the local domain must be created and the other servers must be added to that StruxureWare Domain in order for users to have access (viewing or otherwise) to objects in the other servers.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2024-03-08 04:13 AM

Labels:
  • EcoStruxure Building Operation
1908 Views
  • « Previous
    • 1
    • …
    • 7
    • 8
    • 9
    • …
    • 93
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of