How to Take a Backup Using WinSCP
  • How to Take a Backup Using WinSCP
  • Katha
    Katha
Lt. Commander Katha Lt. Commander
‎2025-10-06 05:30 PM
on ‎2025-10-06 05:30 PM
Access to the correct version of Device Administrator or WorkStation is unavailable, and a backup of the Automation Server is required.
Building Operation Automation Server
In certain scenarios—such as on-site troubleshooting or version incompatibility—the appropriate tools (Device Administrator or WorkStation) may not be accessible. In such cases, an alternative method is needed to perform a backup.
Note: In EBO 2022 (4.0.3) and later, backups can be performed and downloaded using WebStation
Follow these steps to perform a backup using WinSCP, a secure file transfer tool compatible with all system versions.
    • WinSCP is compatible with all versions of EcoStruxure Building Operation.
    • It requires communication over port 22 (SSH).
      Download WinSCP
  1. Launch WinSCP
    • Open the application after installation.
  2. Log In
    • Use the Admin username and password.
    • Select SCP as the protocol.
  3. Navigate to the Backup Folder
    • Browse to the folder containing the server backup files.
    • Refer to the image provided below for the folder location.
    • Download the backup files to your local machine.
Additional Notes
  • Ensure SSH access is enabled on the Automation Server.
  • If login fails, verify credentials and network connectivity.
  • This method is suitable for quick, manual backups when standard tools are unavailable.