Changing the Value of a Sigma Object from a Building Operation Graphic Using a Trackbar Component

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Changing the Value of a Sigma Object from a Building Operation Graphic Using a Trackbar Component
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • sesa125819
    sesa125819
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1531 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Changing the Value of a Sigma Object from a Building Operation Graphic Using a Trackbar Component

Picard Product_Support
‎2018-09-11 03:07 PM

Last Updated: Administrator CraigEl Administrator ‎2025-10-08 06:41 PM

Issue

Users are unable to change the value of a Sigma object using the standard Trackbar component in a Building Operation (SBO) graphic.

Product Line

Satchwell BAS & Sigma

Environment

  • Ecostruxure Building Operation (EBO)
  • Sigma transitioned graphics

Cause

Sigma objects are inherently non-writable. Unlike typical objects in EBO, Sigma objects require a manual override (also known as a “force”) to change their values. The default Trackbar component in EBO does not support this behavior, as it attempts to write directly to the object’s value, which is not permitted for Sigma objects.

Resolution

To enable value changes for Sigma objects via a graphic, the standard Trackbar component 

Trackbar componentTrackbar component

must be modified to include a call to the setForce function. This mimics the behavior of legacy Sigma graphics, where moving a slider would automatically override the object.

Steps to Modify the Trackbar Component:

  1. Open the existing Trackbar component in the graphic editor.
  2. Locate the setCurrentValue function.
  3. Modify the function to include the setForce call before setting the value:
    setForce(fullName, true);
    return setValue(fullName, value);​
 
  1. Ensure the modified Trackbar is bound to the “Value” property of the Sigma object, just as it would be in legacy Sigma.
    • Important: Do not bind the Trackbar to configuration values such as “Fixed value” or “Alarm High Limit,” as these cannot be changed via graphics in transitioned Sigma systems.

Limitations:

  • Only specific values can be overridden in transitioned Sigma systems.
  • Configuration parameters like “Alarm High Limit” or “Fixed value” cannot be modified through graphics.

Additional Resources:

  • Modified Trackbar Component
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
Attachments
Sigma Controls.zip
Tags (2)
  • Find more articles tagged with:
  • 17030
  • CraigEllis25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore