Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,841
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 7
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1839 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 78
    • 79
    • 80
    • …
    • 92
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Unknown Objects errors when trying to download a b3 controller from an AS.

Issue During a Continuum to SmartStruxure 1.2 conversion, getting Unknown Object errors when trying to download to B3 controllers with SmartStruxure. Environment AS b3 Unknown Object Error Cause Non StruxureWare objects exist in the b3 controller. Resolution Set the ACCID of the b3 controller to 0 using a RoamIO. 
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • EcoStruxure Building Operation
1150 Views

Proper shielding where there is no cable shield termination point on a controllers comm terminal.

Issue Third party device does not provide a place to terminate the shield on the comm bus cable. Environment MSTP Infinet Cause Comm cable shielding is required for MSTP and Infinet buses but a controller does not provide a termination point for the shield. Resolution The shield on a comm cable works something like a drain, by redirecting any electrical interference to ground. rather than allowing it to degrade the data signal. If there is more than one grounding point on a shield conductor, often there is the potential that the two ground points have difference of electric potential.   Such a situation could cause the shield to actually introduce electrical interference as the current passes from the point of greatest potential, through the cable and to the point of lowest potential.  For this reason a shield should always be grounded on one end but never be grounded at both ends.  These days many field bus controllers include non grounded shield terminations that simply serve to connect all shield wires as one continuous conductor that are drained by the master controllers shield termination point which is grounded. Where there is no shield termination, simply make sure that the shields from two comm cables are connected together.  
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1216 Views

I/Net Controllers which are supported with StruxureWare Building Operation

Issue I/Net Controllers are Supported in the 1.3.x and higher release of Building Operation Product Line EcoStruxure Building Operation, TAC INET Environment Site running I/Net and StruxureWare Building Operation1.3.x or higher Cause Legacy and support for various I/NET controllers Resolution The following controllers are supported: Routers: NPR 2000 TAC Xenta 527 TAC Xenta 527-NPR Site Controllers: 7798b I/Site Controller 7798c I/Site Controller 7793 Micro Controller Interface 7728 I/Site I/O Controller 7780 Distributed Lighting Control Unit 7716 PCU 7718 PCU 7756 PCU 7760 UCI (Unitary Controller Interface) 7700 DCU (MIP01) 7797 ICI (All Versions) SubLAN Controllers: 72xx Unitary Controllers 7760 Unitary Controller Interface (UCI) DPU 7910a Door Processing Unit DPU 7920 Door Processing Unit (DPU 48K) DIU 7930 Digital Input Unit DIO 7940 Digital Input Output Unit SCU 1200 Security Control Unit SCU 1280 Security Control Unit SCU 1284 Security Control Unit MR Controllers (all HVAC) MR-VAV-AX MR-VAV-X1 MR-VAV-X2 MR88 MR88R MR160 MR55 MR55X MR632 MR-AHU MR-HP
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
2172 Views

Problem with StruxureWare Building Operation Workstation spreadsheet view copy/paste of an Extended Trend Log

Issue Copy/paste does not work for Extended Trend Logs in a Spreadsheet. When attempting to copy/paste an Extended Trend Log, the monitored Trend log is always included in the new Extended Trend Log and it is not possible to change it. Environment Enterprise Server version 1.2 Cause This is a bug which is fixed in version 1.4. Resolution Upgrade to version 1.4 when it is released.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • EcoStruxure Building Operation
1050 Views

How to integrate StruxureWare Building Operation with a hotel booking system.

Issue What is the best way to integrate StruxureWare Building Operation with a hotel booking system?   Environment StruxureWare Building Operation version 1.2 Cause The way to integrate with a third party hotel booking system is in the most cases to use Web services. Web Services are programmable applications accessible from standard Internet protocols. You can use Web Services to consume information, such as temperature from a weather service over the internet. Resolution In most cases the best way to integrate StruxureWare Building Operation with a hotel booking system is to use Web Services. 
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • EcoStruxure Building Operation
1376 Views

Get error message "Could not open or load translation table" when trying to save a Menta file.

Issue Get error message "Could not open or load translation table" when trying to save a Menta file after having edit it in StruxureWare Building Operation. Environment StruxureWare Building Operation version 1.2. Cause Error in the installation of the German Language pack. Resolution Reinstall the language pack.
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Labels:
  • EcoStruxure Building Operation
1911 Views

WorkStation crashes when attempting to create a Web Service

Issue When attempting to create a SOAP Web Service in StruxureWare,  WorkStation crashes after pressing the "Get operations" button for a WSDL file. Environment StruxureWare Workstation version 1.2.0.767 (released 1.2 build) Cause StruxureWare only accepts simple data types in the WSDL file.  Some WSDL files (e.g. Microsoft Exchange Server) uses complex data types (types.xsd) for input parameters and StruxureWare cannot process these data types.   Workstation crashes because of an unhandled exception. Resolution The unhandled exception error crash will be addressed in a future release so that Workstation does not crash upon receiving the error.  At this time, StruxureWare cannot process complex data types in WSDL files, and there are no plans to add this feature.
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Labels:
  • EcoStruxure Building Operation
1123 Views

Adding a named RI (FBD) does not appear as a Input in AS or ES

Issue Adding a named RI (Function Block Diagram) does not appear as a Input in AS or ES Environment StruxureWare Building Operation site with AS or ES using Function Block program Cause Adding a RI (FBD) with the name for example '_PB', it does not appear as a Input in AS or ES Resolution It shouldn't appear as an input on the AS or ES since it is only an input on the Function Block program. You must create the input on the resistive (physical) input on the AS and bind it to the real input on the Function Block. Function Block is a program running on the AS or ES and only will talk to the outputs when bound to the I/O or Input Output object.
View full article
Picard Product_Support
‎2018-09-06 11:06 AM

Labels:
  • EcoStruxure Building Operation
1233 Views

Can ClimateMaster Controllers be integrated with StruxureWare Building Operation?

Issue ClimateMaster controllers are an OEM version(s) of the I/A MNL LON controllers and can only be added as third party devices in SmartStruxure.   Environment ClimateMaster controllers SmartStruxure Cause ClimateMaster is a channel locked product and will not permit  WorkPlaceTech or WorkPlace Tech Editor to have access to the application via upload or download. Resolution ClimateMaster controllers can only be added as third party devices. For help on adding third party devices consult the StruxureWare Building Operation Web Help. There are three web help topics on adding third party devices: Enterprise Server Automation Server Third-Party Licenses
View full article
Picard Product_Support
‎2018-09-06 12:02 PM

Labels:
  • EcoStruxure Building Operation
914 Views

LonWorks on an AS and replacing the template without deleting devices

Issue LonWorks on an AS and replacing the template without deleting devices Environment StruxureWare Building Operation site with LonWorks interface Cause Site would like to replace the XIF template without deleting devices Resolution Unfortunately there is no way to replace the template without removing all devices. Even if the site is fully commissioned and devices are installed, the site must be re-commission and bind everything again. The template cannot be replaced without deleting the devices installed.
View full article
Picard Product_Support
‎2018-09-06 11:04 AM

Labels:
  • EcoStruxure Building Operation
1175 Views

Menu options described in Web Reports Reference Guide are not available in the Web Reports Web Interface

Issue Menu options described in Web Reports Reference Guide are not available in the Web Reports Web Interface Environment Web Reports 1.2 Cause User is not part of the Reports Administrators Group Resolution Log into the ES In the system folder, locate the user logged into Web Reports (System>Domains>domain>Users>username) Select that Users "Group Membership" tab Add the user to the "Reports Administrators" Group
View full article
Picard Product_Support
‎2018-09-06 11:04 AM

Labels:
  • EcoStruxure Building Operation
1079 Views

StruxureWare - What SNVT types are supported in the StruxureWare Building Operation ES and AS?

Issue What SNVT types are supported in the StruxureWare Building Operation ES and AS? Environment SNVT types ES AS Supported Cause Confirmation was required on what SNVT's are supported. Resolution The StruxureWare Building Operation ES and AS support the current published Echelon master SNVT list, to see the full list, please click HERE.
View full article
Picard Product_Support
‎2018-09-10 10:46 PM

Labels:
  • EcoStruxure Building Operation
1032 Views

WorkStation Portal Login

Issue WorkStation Portal Login Environment SBO Site Cause Will StruxureWare Building Operation include a feature in similar to TAC Vista's Portal Login. In other words, a way to make automated log in from another system (3rd party) and use this to create more and more cloud-like service currently used on TAC Vista Webstations Resolution Currently this is not a feature of the current release of StruxureWare Building Operation. 
View full article
Picard Product_Support
‎2018-09-06 10:58 AM

Labels:
  • EcoStruxure Building Operation
1317 Views

Return to Normal Email Notification is only delivered when the Return to Normal notification is acknowledged at the Workstation.

Issue While email notifications for alarm conditions are being delivered promptly, Return to Normal notifications are not delivered until the notification is acknowledged at that the workstation. Environment AS ES Email Notification Cause Email Notification is not configured correctly. Resolution Select the Reset checkbox to have an email delivered when the alarm condition clears. The Normal box should read "Acknowledged Normal" since this delivers a notification that the Off Alarm notification has been acknowledged.
View full article
Picard Product_Support
‎2018-09-06 10:58 AM

Labels:
  • EcoStruxure Building Operation
1346 Views

PIR functionality/ordering options SE7300 series controllers

Issue What is included when the PIR option is ordered? Environment SE7300 series controllers Cause The SE7300 series controllers can be ordered both with and without the PIR option Resolution If the PIR sensor functionality is ordered as included from factory, code 55 (example: SE7600A5545E) should be used. If PIR functionality is not required, code 50 (example: SE7600A5045E) should be used. PIR functionality can be retrofit at any time. For details and part numbers, please see related documentation.
View full article
Picard Product_Support
‎2018-09-06 10:58 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • TAC IA Series
  • TAC Vista
1347 Views

StruxureWare Network 8000 conversion program is changing some "Logic" blocks to a block type called "Invert".

Issue StruxureWare Network 8000 conversion program is changing some "Logic" blocks to a block type called "Invert".   Could this be causing missing pointer issues? Environment SBO 1.2 and later Network 8000 conversion program with any Network 8000 GCM file. Cause This is as designed; see Resolution for explanation.   Resolution A Logic object is 'Migrated" as an Invert object if only used as a single invert gate. The other objects that reference that object as a pointer are changed also to reflect the block name 'Invert'. This is documented in the Technical Reference Guide in section 89.7.
View full article
Picard Product_Support
‎2018-09-06 10:55 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
1326 Views

AS firmware upgrade to version 1.2 or 1.3 fails

Issue Upgrading the Automation Server firmware from version 1.0 to 1.2 or 1.3 fails Upgrading the Automation Server firmware from version 1.1 to 1.3 fails AS is going into failsafe when attempting to upgrade it to version 1.2 Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation 1.2 and 1.3 AS-L AS-B Cause It is not possible to upgrade an AS more than one version at a time. Resolution Upgrading from 1.0 to 1.3 should be done as follows:: Install Device Administrator version 1.1 (if not already done) and upgrade the AS to firmware version 1.1 After the upgrade has finished and the AS is ready, upgrade to version 1.2 from Device Administrator version 1.2 When the AS is ready again, upgrade to version 1.3 from Device Administrator version 1.3  
View full article
Picard Product_Support
‎2018-09-11 09:56 AM

Labels:
  • EcoStruxure Building Operation
1223 Views

Allowable objects that can be Imported / Exported in StruxureWare Building Operation

Issue When importing shortcuts the following warning/error occur WARNING: The property, Target, xxxxxxxx, which has been ignored. Binding Limitations across multi-server configurations Environment SmartStruxure 1.2 / 1.3 Cause Building Operation does not import bindings in a multi-server scenario. If bindings are included in an exported solution, Building Operation displays a warning that the references were not created during an import. Therefore, you must manually recreate referenced bindings: From the Enterprise Server to a value on an Automation Server From an Automation Server to a value on the Enterprise Server From an Automation Server to a value on another Automation Server As a shortcut is basically a binding between two objects, then this holds true in this instance. Resolution Although bindings can be created (hence shortcuts created) across multi-server environments once you export these objects and then attempt to import these at later time or import across a different server, these bindings will be removed. The import process will provide a message "WARNING: The property, Target, , which has been ignored"; these objects are listed in the warning box.  A "Copy to clipboard" option is available so that these can be copied to Notepad (or similar) and then manually re-entered. Refer to the following help topic (you will need to login to the Online help to view this information). http://help.sbo.schneider-electric.com/topics/show.castle?id=5528&locale=en-US&productversion=1.3&a=1  
View full article
Picard Product_Support
‎2018-09-10 11:02 PM

Labels:
  • EcoStruxure Building Operation
945 Views

AS communicate to ES using Telephone line?

Issue AS communicate to ES using Telephone line? Environment SmartStruxure site  Cause Allowing remote access where broadband/ethernet is not available. Plus redundant access when the LAN goes down. Resolution ES and AS communication with the current release requires Ethernet communication. The use of a modem or telephone lines for communication between AS and ES has not been developed. This however is on the roadmap and will be included in a future release. The AS does have USB ports facing down for future connection to external devices such as telephone modems, printers, memory expansion, and expansion modules.  
View full article
Picard Product_Support
‎2018-09-06 10:53 AM

Labels:
  • EcoStruxure Building Operation
1105 Views

StruxureWare Building Operation Demo Database Package

Issue EcoStruxure Building Operation Demo Database Package Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation site Cause EcoStruxure Building Operation Demo Database Package and going between releases. Resolution All current and previous sales packages/demo databases can be found on the Exchange for download. Note: The Demo Database package is a sales and marketing tool for your use "as is." It is not supported through Product Support Services (PSS). If you have product specific technical issues such as installing the software applications (e.g. License Administrator, Enterprise Server) PSS may be able to help. However, PSS does not support the Demo Database contents or features. The Demo Database can be re-installed to return to its original state.
View full article
Picard Product_Support
‎2018-09-11 11:35 AM

Labels:
  • EcoStruxure Building Operation
4274 Views
  • « Previous
    • 1
    • …
    • 78
    • 79
    • 80
    • …
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of