Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,853
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 11
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1850 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 78
    • 79
    • 80
    • …
    • 93
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Why does only one Exception mode work in TAC Xenta 121-FC/HP?

Issue Why does only one Exception mode work in TAC Xenta 121-FC/HP, even if the conditions for more than one Exception mode is fulfilled? Environment TAC Xenta 121-FC, TAC Xenta 121-HP Cause In TAC Xenta 121-FC/HP, with system program version up to 1.25, only one Exception mode could be active at the time. It will always be the exception mode with the lowest number that will be activated. For devices with system program version 1.26 and above, more than one Exception mode could be active. Resolution If the conditions for more than one exception mode are fulfilled, only the exception mode with the lowest number will be activated, for system program version up to 1.25..
View full article
Picard Product_Support
‎2018-09-06 12:26 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1112 Views

Removing a data anomaly from trend data in the Web Report Server.

Issue An initial calculation of KWH produced a artificially high value that was captured by a trend log and is now stored in Report Server. This anomaly is artificially skewing the auto scale feature. Environment Web Report Server Trend Log Extended Trend Log Extended Log Cause The trend data anomaly is artificially skewing the auto scale feature of the trend graph in Report Server. Resolution Open the associated extended trend log. Right click on the entry that is to be corrected and select edit record.  Change the value of the entry to some more acceptable value. Enter  a reason for the change in the comment field. Select save. The new value will appear in place of the original entry with an icon to show that the value was altered. Allow up to 24 hours for the data to be migrated into Web Reports Server.
View full article
Picard Product_Support
‎2018-09-06 12:22 PM

Labels:
  • EcoStruxure Building Operation
894 Views

Calendar entries from 3rd party BACnet devices viewable in WebStation

Issue Calendar entries from 3rd party BACnet devices viewable in WebStation Environment StruxureWare 1.1.0.362 Cause Are calendar entries from 3rd party BACnet devices viewable in WebStation? For calendar entries from third party devices that were not created through StruxureWare Building Operation, they are not shown in WebStation. For example: When integrated a 3rd party BACnet device in StruxureWare Building Operation the integrator of this device created a calendar object on their side. Also created are so sample entries like 24th of December. When uploaded this device and viewing the calendar from the Workstation everything was fine but when viewing WebStation, the calendar entries that were created from the integrator are not shown. Resolution In Webstation 1.1 we only support Single date exceptions. We will support date range and calculated events in 1.2.  
View full article
Picard Product_Support
‎2018-09-06 12:21 PM

Labels:
  • EcoStruxure Building Operation
1090 Views

Compatible versions of I/NET and StruxureWare Building Operation software

Issue Version of I/NET software and StruxureWare Building Operation software Product Line EcoStruxure Building Operation, TAC INET Environment Windows 7 I/Net versions 2.40 and greater Cause With the release of StruxureWare Building Operation's integration with I/NET, customers want to be prepared for it when it comes out and needs to know which version of I/NET software they need to be running to do so. Resolution For the initial rollout, 2.42 was listed as the preparation build to upgrade to for StruxureWare.  Users can upgrade to this build or the current build (2.43 at last edit) and begin upgrading all bin files. This will be required for StruxureWare integration. The bin files did not change between 2.42 and 2.43. Each release of StruxureWare may have a corresponding release of I/NET.  For the time being users will be required to upgrade both I/Net and StruxureWare at the same time. The upgrade from 2.42 to 2.43 is a no-cost upgrade. It should be considered a best practice to upgrade I/NET and StruxureWare at the same time even when not required.  The 1.3.0.938 release of StruxureWare requires I/NET 2.43. If the site upgraded to 2.42 they will not need to upgrade bin files for the controllers.
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
1713 Views

Objects with a "." character at the end of the object name will not bind to other objects.

Issue Cannot bind an input with the name Intern.Temp. Environment StruxureWare Building Operation Binding Point Naming Cause While a "." may be used as a separating character within a point name, it is an illegal object name character when it appears as the last character. StruxureWare Building Operation will generate an Illegal Character error when you attempt to name an object with a trailing "." character. Resolution Rename the object without a "." at the end of the name string and rebind it to the object.
View full article
Picard Product_Support
‎2018-09-06 12:19 PM

Labels:
  • EcoStruxure Building Operation
841 Views

Differences between Continuum Plain English and StruxureWare Building Operation Script

Issue Not all commands in Plain English are available in Building Operation Script. Product Line EcoStruxure Building Operation Environment Script editor in Building Operation Cause Conversion of PE to Building Operation script is unsuccessful. Unsupported Script commands. Resolution Plain English may be imported into Building Operation; however, there are some minor edits that must be performed to make it work. Bindings must be applied. There is some automated manipulation of PE to Script upon import and it should continue to improve in future releases. By creating a "dump" file in Continuum and editing the file to remove the Header and Footer areas, the remaining code can be imported into Building Operation as Script. There are some functions Continuum uses that will not be used in Building Operation, the Script will error upon event to save if unsupported code is used in the imported script. Notification of each line of code is in error will occur upon a save attempt. Navigate to the lines in error and correct the code. The following link has information on PE to Script changes. Log in is required to access full online help: StruxureWare Building Operation Online Help
View full article
Picard Product_Support
‎2018-09-10 07:57 AM

Labels:
  • EcoStruxure Building Operation
2302 Views

The limits on how many AI/AO/BI/BO/RI/RO one can create in one Functional Block Application?

Issue The limits on how many AI/AO/BI/BO/RI/RO, Function Block number, Constant number, public signal number...etc.. one can create in one Functional Block Application? Environment StruxureWare Building Operation site with Functional Block Application Cause What are the limits on how many AI/AO/BI/BO/RI/RO, Function Block number, Constant number, public signal number...etc.. one can create in one Functional Block Application? Resolution There are no limits about how many blocks that could be created, but the Function Block parser has a memory limit. When this limit is exceeded an error text is prompted to the user. There is no way to tell if a site is getting close to that limit.  
View full article
Picard Product_Support
‎2018-09-06 12:16 PM

Labels:
  • EcoStruxure Building Operation
2022 Views

Should I use a UPS for the system and supply the controllers from it?

Issue Can I use a uninterruptible power supply for controllers? UPS Environment site requiring constant power supply or unstable power from grid and need to take into account power supplies Cause Can I use the CX99-PSU-BATT for an ACX5720 controller? If not, then what can I use if the customer wants a UPS for each controller. Should I use a big UPS for the system and supply the controllers from it?   Resolution The CX99-PSU-BATT is 70VA 120/240VAC and really designed for the CX9900 PSU. It is suggested to get one of our APC UPS and run the proper voltage transformer to the ACX5720. The ACX 57xx series is rated with a 24VAC 90VA or 12-28VDC 50W on the power supply which I recommend due to devices which connect to this controller and require power. i.e. door readers UPS or uninterruptible power supplies are available from APC by Schneider Electric.  Background The power drawn by computing equipment is expressed in Watts or Volt-Amps (VA). The power in Watts is the real power drawn by the equipment. Volt-Amps is called the "apparent power" and is the product of the voltage applied to the equipment times the current drawn by the equipment. Both Watt and VA ratings have a use and purpose. The Watt rating determines the actual power purchased from the utility company and the heat loading generated by the equipment. The VA rating is used for sizing wiring and circuit breakers. The VA and Watt ratings for some types of electrical loads, like incandescent light bulbs, are identical. However, for computer equipment the Watt and VA ratings can differ significantly, with the VA rating always being equal to or larger than the Watt rating. The ratio of the Watt to VA rating is called the "Power Factor" and is expressed either as a number (i.e. 0.7) or a percentage (i.e. 70%). The power rating of the UPS UPS have both Watt ratings and VA ratings. Neither the Watt nor the VA rating of a UPS may be exceeded. In most cases, UPS manufacturers only publish the VA rating of the UPS. However, it is a standard in the industry that the Watt rating is approximately 60% of the VA rating, this being the typical power factor of common loads. Therefore, it is safe to assume that the Watt rating of the UPS is 60% of the published VA rating. How to avoid sizing errors Using APC sizing guidelines or and APC Configuration can help avoid these problems, as the load power values are verified. Equipment nameplate ratings are often in VA, which makes it difficult to know the Watt ratings. If using equipment nameplate ratings for sizing, a user might configure a system which appears to be correctly sized based on VA ratings but actually exceeds the UPS Watt rating. By sizing the VA rating of a load to be no greater than 60% of the VA rating of the UPS, it is impossible to exceed the Watt rating of the UPS. Therefore, unless you have high certainty of the Watt ratings of the loads, the safest approach is to keep the sum of the load nameplate ratings below 60% of the UPS VA rating. Note that this conservative sizing approach will typically give rise to an oversized UPS and a larger run time than expected. If optimization of the system and an accurate run time are required, use APC sizing and Worldwide Web configuration tools.  
View full article
Picard Product_Support
‎2018-09-10 11:29 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC INET
  • TAC Vista
1129 Views

Alarm response time

Issue What are the alarm response times for StruxureWare Building Operation Environment StruxureWare Building Operation site Cause Requesting information concerning response times and maximum periods. Need to know when the response is met and provide a written description of the way in which they are met. Time from initiation of an alarm at the source to the annunciation on the engineering StruxureWare Building Operation server: Critical alarms (Plant Shutdown and Safety) <2 seconds Non critical alarms <4 seconds Time from initiation of an alarm to all other BACnet devices to StruxureWare Building Operation server: Critical alarm 20ms Non critical alarms 20ms Time from initiation of a change of state or value to all Lon devices to StruxureWare Building Operation Server: 20ms Resolution We have a requirement that says the following: The time from when a value, monitored by an alarm, passes the trigger value of the alarm, until the alarm is visible in a WorkStation logged onto the parent Enterprise Server shall be: - less than 1000 ms in average over 20 measurements -maximum 2000 ms for each measurement This requirement applies to the Performance Target System. This includes any multi-server environment and also if the value is out on a Lon device, BACnet device or any other device we support. The above requirement is met. We also don’t have different response-priorities for critical and non-critical alarms in StruxureWare Building Operation, they are treated the same.  
View full article
Picard Product_Support
‎2018-09-06 12:10 PM

Labels:
  • EcoStruxure Building Operation
1622 Views

How can I test out the functionality of any web plugins used on my computer?

Issue Many  of our products have Web page functionality, can I test out if my animation plug in's are operating correctly? Environment Web pages, Web Client, Web Server Embedded Pinpoint web pages Silverlight, Flash player, Java and other Web animations. Cause Need to confirm if a web page  Animation plug in operates within the product or just on the Web browser used on the PC.  Resolution See Website: http://bubblemark.com/ for the links to the different animation tests.
View full article
Picard Product_Support
‎2018-09-10 12:40 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • TAC Vista
1136 Views

Software Support for Design 360 and Studio 360

Issue Technical support contact information for Design 360 and Studio 360 Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Other, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Design 360 Studio 360 Cause Design 360 or Studio 360 has issues requiring technical support assistance which is not provided by PSS. Resolution Schneider Electric Employees should contact PSS who will provide you with your Branch Administrator and Technical Expert contact information. Partners may contact Smartware directly for any support of the tool at: Email: techsupport@smartwaretech.com Phone: (716) 213-2222
View full article
Picard Product_Support
‎2018-09-10 10:33 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
3490 Views

The Reliability property on an input returns Under Range even though the Electric Value is within the Reliability level range.

Issue On an input configured with an Engineering Value range of 0 to 5 Degrees Celsius, an electric scale range 470 ohms to 10470 ohms and a reliability range from 470 to 1047 ohms, any input value produces an Under Range in the Reliability Property value. Environment SBO AS Inputs Reliability BACnet Cause The Reliability property references the inputs Engineering Values, not the Electrical Values. Resolution Because the Reliability parameters that are set on SmartStruxure inputs reference the Engineering values, in this example even the maximum value of 5 degrees Celsius would have placed the input value far below the Lower Reliability Level parameter of 470 (ohms).  In this case the solution is to use an Lower Reliability Level of 0 and an Upper Reliability Level of 5.
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • EcoStruxure Building Operation
1293 Views

Unknown Objects errors when trying to download a b3 controller from an AS.

Issue During a Continuum to SmartStruxure 1.2 conversion, getting Unknown Object errors when trying to download to B3 controllers with SmartStruxure. Environment AS b3 Unknown Object Error Cause Non StruxureWare objects exist in the b3 controller. Resolution Set the ACCID of the b3 controller to 0 using a RoamIO. 
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • EcoStruxure Building Operation
1200 Views

Proper shielding where there is no cable shield termination point on a controllers comm terminal.

Issue Third party device does not provide a place to terminate the shield on the comm bus cable. Environment MSTP Infinet Cause Comm cable shielding is required for MSTP and Infinet buses but a controller does not provide a termination point for the shield. Resolution The shield on a comm cable works something like a drain, by redirecting any electrical interference to ground. rather than allowing it to degrade the data signal. If there is more than one grounding point on a shield conductor, often there is the potential that the two ground points have difference of electric potential.   Such a situation could cause the shield to actually introduce electrical interference as the current passes from the point of greatest potential, through the cable and to the point of lowest potential.  For this reason a shield should always be grounded on one end but never be grounded at both ends.  These days many field bus controllers include non grounded shield terminations that simply serve to connect all shield wires as one continuous conductor that are drained by the master controllers shield termination point which is grounded. Where there is no shield termination, simply make sure that the shields from two comm cables are connected together.  
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1242 Views

I/Net Controllers which are supported with StruxureWare Building Operation

Issue I/Net Controllers are Supported in the 1.3.x and higher release of Building Operation Product Line EcoStruxure Building Operation, TAC INET Environment Site running I/Net and StruxureWare Building Operation1.3.x or higher Cause Legacy and support for various I/NET controllers Resolution The following controllers are supported: Routers: NPR 2000 TAC Xenta 527 TAC Xenta 527-NPR Site Controllers: 7798b I/Site Controller 7798c I/Site Controller 7793 Micro Controller Interface 7728 I/Site I/O Controller 7780 Distributed Lighting Control Unit 7716 PCU 7718 PCU 7756 PCU 7760 UCI (Unitary Controller Interface) 7700 DCU (MIP01) 7797 ICI (All Versions) SubLAN Controllers: 72xx Unitary Controllers 7760 Unitary Controller Interface (UCI) DPU 7910a Door Processing Unit DPU 7920 Door Processing Unit (DPU 48K) DIU 7930 Digital Input Unit DIO 7940 Digital Input Output Unit SCU 1200 Security Control Unit SCU 1280 Security Control Unit SCU 1284 Security Control Unit MR Controllers (all HVAC) MR-VAV-AX MR-VAV-X1 MR-VAV-X2 MR88 MR88R MR160 MR55 MR55X MR632 MR-AHU MR-HP
View full article
Picard Product_Support
‎2018-09-06 11:11 AM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
2211 Views

Problem with StruxureWare Building Operation Workstation spreadsheet view copy/paste of an Extended Trend Log

Issue Copy/paste does not work for Extended Trend Logs in a Spreadsheet. When attempting to copy/paste an Extended Trend Log, the monitored Trend log is always included in the new Extended Trend Log and it is not possible to change it. Environment Enterprise Server version 1.2 Cause This is a bug which is fixed in version 1.4. Resolution Upgrade to version 1.4 when it is released.
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Labels:
  • EcoStruxure Building Operation
1072 Views

How to integrate StruxureWare Building Operation with a hotel booking system.

Issue What is the best way to integrate StruxureWare Building Operation with a hotel booking system?   Environment StruxureWare Building Operation version 1.2 Cause The way to integrate with a third party hotel booking system is in the most cases to use Web services. Web Services are programmable applications accessible from standard Internet protocols. You can use Web Services to consume information, such as temperature from a weather service over the internet. Resolution In most cases the best way to integrate StruxureWare Building Operation with a hotel booking system is to use Web Services. 
View full article
Picard Product_Support
‎2018-09-06 11:08 AM

Labels:
  • EcoStruxure Building Operation
1404 Views

Get error message "Could not open or load translation table" when trying to save a Menta file.

Issue Get error message "Could not open or load translation table" when trying to save a Menta file after having edit it in StruxureWare Building Operation. Environment StruxureWare Building Operation version 1.2. Cause Error in the installation of the German Language pack. Resolution Reinstall the language pack.
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Labels:
  • EcoStruxure Building Operation
1940 Views

WorkStation crashes when attempting to create a Web Service

Issue When attempting to create a SOAP Web Service in StruxureWare,  WorkStation crashes after pressing the "Get operations" button for a WSDL file. Environment StruxureWare Workstation version 1.2.0.767 (released 1.2 build) Cause StruxureWare only accepts simple data types in the WSDL file.  Some WSDL files (e.g. Microsoft Exchange Server) uses complex data types (types.xsd) for input parameters and StruxureWare cannot process these data types.   Workstation crashes because of an unhandled exception. Resolution The unhandled exception error crash will be addressed in a future release so that Workstation does not crash upon receiving the error.  At this time, StruxureWare cannot process complex data types in WSDL files, and there are no plans to add this feature.
View full article
Picard Product_Support
‎2018-09-06 11:07 AM

Labels:
  • EcoStruxure Building Operation
1144 Views

Adding a named RI (FBD) does not appear as a Input in AS or ES

Issue Adding a named RI (Function Block Diagram) does not appear as a Input in AS or ES Environment StruxureWare Building Operation site with AS or ES using Function Block program Cause Adding a RI (FBD) with the name for example '_PB', it does not appear as a Input in AS or ES Resolution It shouldn't appear as an input on the AS or ES since it is only an input on the Function Block program. You must create the input on the resistive (physical) input on the AS and bind it to the real input on the Function Block. Function Block is a program running on the AS or ES and only will talk to the outputs when bound to the I/O or Input Output object.
View full article
Picard Product_Support
‎2018-09-06 11:06 AM

Labels:
  • EcoStruxure Building Operation
1261 Views
  • « Previous
    • 1
    • …
    • 78
    • 79
    • 80
    • …
    • 93
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of