Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1895 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 78
    • 79
    • 80
    • …
    • 95
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Analog Consumer Value displays unit in metric (SI) though configured for imperial (US) units

Issue Analog consumer values referencing the temperature of a SmartX Sensor shows in metric units when setup to display imperial units. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Building Operation Multi-Purpose Controller Building Operation Multi-purpose VAV Building Operation Room Controller Building Operation IP-IO Building Operation SmartX Sensor Cause SmartX Sensor is configured in the device as metric measurements (SI System). Setting Fahrenheit in Display of SmartX Sensor does not convert the values from metric to imperial. Consumer values are configured to use the object being referenced and do not convert measurements. Unit conversion is done within the binding and not the device itself. Resolution There are two workarounds: Option 1: Create an analog value and then bind to consumer value Step 1: Create an Analog Value. Setup unit settings to (°F) and Save.  Step 2: Bind Analog Value to temperature from SmartX Sensor and Save Step 3: In the created Consumer Value, bind the Analog Value to the input binding reference and setup unit settings to (°F) and Save   Option 2: Bind to Consumer Value directly and keep the value in metric Step 1: In the created Consumer Value, bind the SmartX Sensor temperature to the input binding reference Step 2: Setup unit settings as configured in the object (°C) and Save.
View full article
Ensign ValerieRod Ensign
‎2020-01-14 08:27 AM

on ‎2020-01-14 08:27 AM

Labels:
  • EcoStruxure Building Operation
2042 Views

Repairing corruption in damaged Workplace Tech and Workplace Tech Editor Visio drawings

Issue Some connectors appear in red on the Workplace Tech Visio drawing.  Connectors cannot be bound to objects. Product Line TAC IA Series, EcoStruxure Building Operation Environment I/A Series WorkPlace Tech Building Operation Workstation (Workplace Tech Editor) Microsoft Visio  Cause Drawing objects become placed off the normal boundaries of the Visio drawing page causing file corruption.  This can occur during improper file saves, Visio crashes or for unknown reasons. Resolution
View full article
JohnBoehmer Schneider Alumni (Retired)
‎2019-12-17 01:47 PM

on ‎2019-12-17 01:47 PM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
1914 Views

File Preparation in Visio to Correct Workplace Tech and Workplace Tech Editor Application Failures

Issue Workplace Tech or Workplace Tech Editor is crashing when accessing a specific Visio file. Product Line TAC IA Series, EcoStruxure Building Operation Environment I/A Series WorkPlace Tech Building Operation Workstation (Workplace Tech Editor) Cause There are a number of possible issues with the Visio 2013 and Visio 2016 files when running in Compatibility Mode.  Compatibility Mode is required for Workplace Tech and Workplace Tech Editor since they are both designed to use the older .vsd file format.  The mentioned Visio versions both use .vsdx as a native file format. Resolution
View full article
JohnBoehmer Schneider Alumni (Retired)
‎2019-11-22 09:17 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
2094 Views

EBO Enterprise Server won't start - Error 216: 0xd8

Issue When attempting to start the Enterprise Server, the user receives the following error message: "Windows could not start the Building Operation Enterprise Server service on Local Computer: Error 216: 0xd8" Product Line EcoStruxure Building Operation Environment Microsoft Windows Building Operation Enterprise Server Building Operation Enterprise Central Cause Windows error 216: 0xd8 means "The version of %1 is not compatible with the version you're running. Check your computer's system information to see whether you need an x86 (32-bit) or x64 (64-bit) version of the program, and then contact the software publisher." It is likely that this error is being received due to the EBO Enterprise Server/Central being installed on a 32-bit Windows Operating System. Resolution Beginning in EBO 2.0 it is no longer supported for the Enterprise Server to run on a 32-bit Operating System. Reference the Enterprise Server Specification Sheet for the appropriate product version you are using to find the list of supported Operating Systems. The Enterprise Server/Central should then be installed on one of the supported 64-bit Operating Systems.
View full article
Lieutenant JG Robert_Davis Lieutenant JG
‎2019-12-17 08:31 AM

on ‎2019-12-17 08:31 AM

Labels:
  • EcoStruxure Building Operation
5622 Views

Performing a Damper Calibration using eCT

Issue Need to perform a damper calibration using eCT Product Line EcoStruxure Building Operation Environment Building Operation eCommissioning Tool (eCT) Cause There is no documentation on how to perform this via eCT. Resolution Ensure your MP-V is not in a hosted state within EBO. Connect to your MP-V device using Windows 10, iOS, or Android via Bluetooth, WiFi, or ethernet connection Expand the menu in the top left corner and select "Browse Objects"  Scroll down until you find the DamperCommand object, select it and tap/click OK  In the Initiate damper calibration Property ID, select False and type in True then click Save
View full article
Commander JonGreen Commander
‎2019-12-16 12:00 PM

on ‎2019-12-16 12:00 PM

Labels:
  • EcoStruxure Building Operation
1326 Views

Error -25: License server system does not support this version of this feature.

Issue While trying to login to either WorkStation or WebStation, or during the startup of the Enterprise Server, an error "Error -25: License server system does not support this version of this feature." appears. Product Line EcoStruxure Building Operation Environment Building Operation Workstation version 2.0.x or later Building Operation Webstation version 2.0.x or later Building Operation Software Administrator version 2.0.x or later Cause The activated license is not at an appropriate version for the corresponding software. The licenses activated in the EBO License Administrator need to be at a version greater than or equal to the version of the Building Operation software being used.  Resolution 1. Workstation - If the Workstation license activated in License Administrator is at Version 1, this license will need to be upgraded to be compatible for any system EBO 2.0 and beyond. To do this, simply notate the Entitlement ID and then return the Workstation License. Once returned, reactivate the license from the previously recorded Entitlement ID. This will upgrade the 1.X License to be used with newer systems. 2. Enterprise Server - If the error is received on an ES, verify that all ES licenses are in place. If the system was upgraded, it is necessary for all previous versions of ES/AS licenses to remain activated in the License Administrator. 
View full article
Lieutenant JG Robert_Davis Lieutenant JG
‎2019-12-10 11:31 AM

Last Updated: Guinan RandyDavis Guinan ‎2019-12-12 12:36 PM

Labels:
  • EcoStruxure Building Operation
3094 Views

Import Lon Variables from Excel

Issue When importing Lon variables from Excel, all variables are created as Inputs, even though the "Direction" column in the Excel file says "Output".   Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause A defect creates all Lon variables as inputs even if the variable is assigned direction as output. Resolution  Create Lon variables with output direction manually.
View full article
Janeway Jonas_Brissman Janeway
‎2019-11-26 02:08 PM

Last Updated: Guinan RandyDavis Guinan ‎2019-11-26 02:18 PM

Labels:
  • EcoStruxure Building Operation
1299 Views

Advanced Display started in kiosk mode

Issue When using Advanced Display and logging in to Webstation, it startups in kiosk mode with limited functionality. Example:   Product Line EcoStruxure Building Operation Environment Building Operation Advanced Display Cause When running Webstation in Advanced Display it is by default started in kiosk mode Resolution Open SmartX HMI Kiosk in Advanced Display In "Webstation setup" delete the part ?kiosk# Example: https://192.168.42.116/?kiosk#  Webstation be started in kiosk mode https://192.168.42.116/  Webstation will start normally
View full article
Janeway Jonas_Brissman Janeway
‎2019-11-08 01:36 PM

Last Updated: Guinan RandyDavis Guinan ‎2019-11-22 09:32 AM

Labels:
  • EcoStruxure Building Operation
4949 Views

Error message trying to save changes in Menta Editor

Issue An error message is displayed when trying to save changes to a Programmable Xenta in Menta Editor. The error message is: Tam32 Save Error Index was out of range. Must be non-negative and less than the size of the collection. Parameter name: index (E) Error message trying to save changes in Menta Editor Product Line EcoStruxure Building Operation Environment Building Operation Workstation 3.0.2 or earlier Xenta 281 Xenta 301 Xenta 401 Cause A defect in Menta Editor causes this error to be displayed when a SNVT name in the Menta application is identical to the programmable Xenta device name.  An example of this is shown below: Resolution This problem has been fixed in Hotfix 3.0.2.2500 and the fix is included in version 3.1. For earlier versions there are two ways to resolve this problem; Either a) rename the Xenta device, or b) rename the SNVT. a) Renaming the Xenta device In Workstation right click the Xenta device and choose Rename Click OK Now you can edit the Xenta in Menta Editor without getting the error message b) Renaming the SNVT Right click the Xenta device and choose Edit In Menta Editor double click the block with the SNVT binding to edit the block Click the Bind... button to edit the binding Change the name, click OK to close the dialogs and Save the changes
View full article
Janeway PeterEdvik Janeway
‎2019-09-22 08:55 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-11-08 01:01 PM

Labels:
  • EcoStruxure Building Operation
1947 Views

How to configure a SetPoint in EcoStruxure Building Operation

Issue Configuring a SetPoint in EcoStruxure Building Operation so that the set value of the SetPoint is retained after a Warm or a Cold Start rather than defaulting to zero. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Cause The value retention configuration is not held in the initial properties page of the Analogue Value when used as a SetPoint. Resolution Navigate to the actual value within the properties page of the Analogue Value. On the right hand side of the GUI there is a Configure button. Pressing on this button then takes the user to a sub menu where the Retain level option can be enabled. Once enabled it is then possible to decide whether the SetPoint needs to retain its value under a Warm Start or a Cold Start condition.
View full article
Admiral David_Kendrick Admiral
‎2019-11-08 02:23 AM

Last Updated: Sisko DavidChild Sisko ‎2019-11-08 02:24 AM

Labels:
  • EcoStruxure Building Operation
2051 Views

Vista webstation & EBO Registration Error message in FIPS - compliant systems

Issue Vista webstation - Error message in FIPS-compliant systems first time the logging screen is entered and red X instead of values in TGML pictures Error message in FIPS-compliant systems when Windows Communication Foundation is used to serialize generic types: “This implementation is not part of the Windows Platform FIPS validated cryptographic algorithms” Red X instead of values EcoStruxure Building Operation registration WorkStation Error Product Line TAC Vista, EcoStruxure Building Operation Environment Vista Webstation Cause System cryptography: Use FIPS compliant algorithms for encryption, hashing and signing This security setting determines if the Transport Layer Security/Secure Sockets Layer (TL/SS) Security Provider supports only the TLS_RSA_WITH_3DES_EDE_CBC_SHA cipher suite. In effect, this means that the provider only supports the Transport Layer Security (TLS) protocol as a client and as a server (if applicable). It uses only the Triple DES encryption algorithm for the TLS traffic encryption, only the Rivest, Shamir, and Adleman (RSA) public key algorithm for the TLS key exchange and authentication, and only the Secure Hashing Algorithm 1 (SHA-1) for the TLS hashing requirements. For Encrypting File System Service (EFS), it supports only the Triple Data Encryption Standard (DES) encryption algorithm for encrypting file data supported by the NTFS file system. By default, EFS uses the Advanced Encryption Standard (AES) algorithm with a 256-bit key in the Windows Server 2003 family and DESX algorithm in Windows XP for encrypting file data. For information about EFS, see Encrypting File System. NOTE - The same errors can occur in EcoStruxure Building Operation when registering. Resolution Go to Local Security Settings Security Settings > Local Policies > Security Options System cryptography: Use FIPS compliant algorithms for encryption, hashing and signing = Make sure its disabled to get to local security you can go to 1. go to start 2. Go to run 3. enter secpol.msc 4. press enter NOTE - The same errors can occur in EcoStruxure Building Operation when registering. The Resolution is the same
View full article
Picard Product_Support
‎2018-09-06 10:15 AM

Last Updated: Sisko DavidChild Sisko ‎2019-11-08 12:34 AM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1919 Views

BACnet devices hosted with duplicate names but getting alarm about the duplicates

Issue Alarms about BACnet devices with duplicate names These are not required on the site Product Line EcoStruxure Building Operation Environment Third Party BACnet Devices Building Operation Enterprise Server Cause In EBO, BACnet device name uniqueness enforcement has been removed but an alarm is sent regardless to alert of the problem. Resolution Disable the alarm if it is not require in the alarm view. This is achieved by right clicking on the alarm in the Alarm Pane and 'Disable Alarm'
View full article
Picard Product_Support
‎2018-09-06 09:10 AM

Last Updated: Sisko DavidChild Sisko ‎2019-11-08 12:31 AM

Labels:
  • EcoStruxure Building Operation
2040 Views

LON Network - Cable Transient Suppression

Issue LON Network - Cable Transient Suppression Product Line EcoStruxure Building OperationTAC IA Series, TAC Vista Environment LON networks that extend beyond the walls of a single building Cause Surge arrestors dissipate transient energy before the cable can provide a low resistance path to the building ground, preventing potential electrical damage. Resolution Click here to download the white paper on this topic: Cable Transient Suppression It is recommended that a Transient Suppression protection device be installed on the LON communications cable at any point where the cable enters or exits the building. The LON is frequently used to connect a collection of controllers in one building with a collection of controllers in one or more other buildings in a campus. The LON may also extend outside the protection of an office building when servicing communications to roof-top equipment and/or outside monitoring equipment. At any location where the LON cable penetrates and extends outside the building compartment, it is recommended that a gas discharge type lightning arrestor be installed across the LON conductor pair and earth ground as shown below. This should be positioned as close as possible to the wall penetration location. The objective is to keep the cable distance as short as possible before the cable suppression is provided. It is important that a heavy gauge earth ground connection be provided to the gas discharge protector with as short a length as possible. Here we want to dissipate the transient energy as soon as possible before the cable extends on into the facility and provide a low resistance path to the building ground. SA2-U8 Surge Arrestor TAC provides a Model SA2-U8 Surge Arrestor which can be used for this purpose. This SA2-U8 device is a gas discharge arrestor packaged in a small DIN rail mountable enclosure. The SA2-U8 is UL864 listed and is the only device that can be used on TAC UL864 listed system. It must be installed on the LON cable at any entry/exit locations. Other Gas Discharge Suppressors On non-UL864 systems, the SA2-U8 may also be used, or the installer may use any one of a number of available 90V gas discharge tube devices. These are typically tubular shaped components and since you need two tubes (one for each of the two LON conductors) a dual element three lead discharge tube is recommended. The device’s leads may be attached to a standard screw terminal block and mounted in most any size electrical box. A collection of some of the suitable gas discharge devices that could be used is as follows: Manufacturer Part Number Bourns 2026-09-C Epcos B88069X8440B202 Citel BTS-90 SRC Devices PMT-090-14   There are other acceptable part numbers available from each of these manufacturers with variations provided in the lead configuration and lengths while maintaining the same 90V protection rating. Devices To Avoid It is not recommended that you use any semiconductor type (Transzorb / TVS / Diode) protection devices. Their higher speed and lower clamping voltage characteristics is not necessary with the inherent protection offered by the FTT-10 and FT-X1 LON transceivers. Such semiconductor based transient suppression devices frequently add some undesirable capacitance to the network which impedes communication performance and most inject signal clamping at voltage levels much lower than necessary or desirable for the Free Topology FTT-10 and FT-X1 based LON networks. The common mode noise immunity of the FTT LON should be much better than that provided by the typical RS485 network. This should provide more tolerance for electrically noisy environments. However, it has been observed that some semiconductor based network protection units have been used that can drastically degrade communications performance. One such device is the Model 91287 from Atlantic Scientific Corp. which was identified by the manufacturer as a LON System protector. This device clamps the signal at one diode drop below ground level which virtually destroys the LON’s common mode noise tolerance. The presence of one of these devices has been found to be the cause of communications problems in a system operating is an electrically noisy environment. This type of communications impairment may be encountered immediately. In other instances, LON retries may cover the problem and the system may operate for extended period of time before environmental or equipment changes raise noise levels above the tolerable threshold. This threshold is now much worse than RS485 networks. This device, and any similar, should be avoided on any LON systems.
View full article
Picard Product_Support
‎2018-09-06 10:46 PM

Last Updated: Janeway PeterEdvik Janeway ‎2019-11-07 05:51 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
2647 Views

Workstation Pro License at v1, site is now v2 or v3, so WorkStation will not run after upgrade

Issue Workstation Pro License fails to allow running of v2.0 or v3.x EcoStruxure WorkStation following an upgrade Product Line EcoStruxure Building Operation Environment WorkStation Licensing Cause Workstation Pro License SXWSWWORK00002 (SW-STATION-PRO-0) is the same for v1.x and v2.x, so that WorkStation Pro should continue to operate after an upgrade. However, there was a License upgrade/change at v1.7 (from v1 to v2) and if the License was registered before this the version remains at v1 and this will not run v2.x WorkStation Resolution The WorkStation Pro License needs to be returned, then re-installed using the online Licensing system.   Before License is returned   After license is returned  The process to return a license can be found in Webhelp.
View full article
Dave_Shore Schneider Alumni (Retired)
‎2018-10-03 02:38 AM

Last Updated: Sisko DavidChild Sisko ‎2019-11-06 06:50 AM

Labels:
  • EcoStruxure Building Operation
2387 Views

Device Administrator crashes immediately when launched

Issue Right after you start the Device Administrator, the program crashes. Product Line EcoStruxure Building Operation Environment SmartStruxure Device Administrator Cause In rare cases, the XML file containing information regarding the default login and device list for the Device Administrator is empty or corrupted. That causes the Device Administrator to crash when launched, as the information in the file doesn't have the correct content format. Resolution Delete the settings.xml file which is automatically generated. Depending on the installed version it may be located in one of the following paths: Version 1.9 and lower "C:\ProgramData\Schneider Electric StruxureWare\Building Operation 1.X\Device Administrator" Version 2.0 onwards "C:\ProgramData\Schneider Electric EcoStruxure\Building Operation X.X\Device Administrator" Start the Device Administrator
View full article
Picard Product_Support
‎2018-09-06 09:31 AM

Last Updated: Picard RobertAndriolo Picard ‎2019-10-30 05:50 PM

Labels:
  • EcoStruxure Building Operation
1986 Views

Workplace Tech Tool/Editor Error "WPObEvt"

Issue When attempting to add an object or connection to a WorkPlaceTech Tool application drawing, a WPObEvt error box is displayed indicating the following error condition: Unhandled Exception during event     Class:   Document     Object:  (drawing file name)     Event:   "ConnectionsAdded", "ConnectionsDeleted", "ShapeAdded" (depends on action)     Error:   (blank) Product Line EcoStruxure Building Operation, TAC IA Series Environment Building Operation Enterprise Server (WorkplaceTech Editor) Building Operation Automation Server (WorkplaceTech Editor) I/A Series WorkPlace Tech Microsoft Visio Cause The comma is the default decimal symbol on international versions of Windows. Visio does not understand the use of the comma as the decimal separator character when used in Workplace Tech or Workplace Tech Editor.  Resolution Depending on the machines operating system, i.e. Windows 7, or Windows 10, and page configuration, the appearance will be slightly different. Open "Control Panel" Select "Region" Click "Additional Settings...." button near bottom right Select the period instead of the comma for the "Decimal symbol"
View full article
Guinan RandyDavis Guinan
‎2019-10-28 10:40 AM

Last Updated: Commander JonGreen Commander ‎2019-10-28 10:41 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
1449 Views

Third Party MSTP controllers are not able to be discovered

Issue Third Party MSTP controllers are not able to be discovered. Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation Automation Server (AS) 3rd party controllers Cause MAC address of the Automation Server's MSTP Network was not configured properly. Under the AS > BACnet Interface > MSTP Network the MAC address is changed from the default value of 0.  Resolution Change the MSTP Network MAC address from the erroneous value back to 0 and third party controllers will be discovered properly.
View full article
Picard Product_Support
‎2018-09-06 10:55 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-10-03 07:16 AM

Labels:
  • EcoStruxure Building Operation
1912 Views

Is it possible to 'hot swap' IO modules?

Issue Is it possible to 'hot swap' IO modules? Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation I/O Modules Cause Some critical applications require 24-hour operation. Resolution The I/O modules allow hot-connection of terminal bases and hot-swapping of the modules to their bases. This design ensures continuous power and communication during service operations.
View full article
Picard Product_Support
‎2018-09-06 09:23 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-10-03 07:02 AM

Labels:
  • EcoStruxure Building Operation
2532 Views

OP panel shows a ! after a value

Issue OP panel shows a ! after a value Product Line TAC Vista, EcoStruxure Building Operation Environment Xenta OP Vista Struxureware Cause If you have a binary value in OP panel, and you connect an analog value to it, the OP will show the "!" Resolution Edit the OP Panel tree, disconnect the analog value and attach a binary value instead. Generate and save the application.
View full article
Picard Product_Support
‎2018-09-06 08:46 AM

Last Updated: Guinan RandyDavis Guinan ‎2019-09-27 12:16 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1306 Views

Offline detection between an Enterprise Server and a SmartX server

Issue How does the offline detection work between an Enterprise Server(ES) and a SmartX server Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause There is no online poll between an ES and a SmartX server, but the SmartX server will be considered as offline if it doesn't respond to any kind of message from the ES. Resolution The ES is constantly asking the SmartX server for new events and alarms so at least every second the ES will communicate with the SmartX server. If one of the messages from the ES is not responded by the SmartX server the ES will send out 3 more with a second in between, if no messages are answered by the SmartX server the ES will consider the SmartX server as offline. There is a 30 seconds delay before the offline alarm pops up in the alarm viewer in Workstation.
View full article
Picard Product_Support
‎2018-09-06 10:59 AM

Last Updated: Guinan RandyDavis Guinan ‎2019-09-19 08:01 AM

Labels:
  • EcoStruxure Building Operation
2686 Views
  • « Previous
    • 1
    • …
    • 78
    • 79
    • 80
    • …
    • 95
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.