Issue
Third Party MSTP controllers are not able to be discovered.
Product Line
EcoStruxure Building Operation
Environment
- StruxureWare Building Operation
- Automation Server (AS)
- 3rd party controllers
Cause
MAC address of the Automation Server's MSTP Network was not configured properly. Under the AS > BACnet Interface > MSTP Network the MAC address is changed from the default value of 0.
Resolution
Change the MSTP Network MAC address from the erroneous value back to 0 and third party controllers will be discovered properly.