Performing a Damper Calibration using eCT
  • Performing a Damper Calibration using eCT
  • RandyDavis
    RandyDavis
  • JonGreen
    JonGreen
Commander JonGreen Commander
‎2019-12-16 12:00 PM
on ‎2019-12-16 12:00 PM
Need to perform a damper calibration using eCT
Building Operation eCommissioning Tool (eCT)
There is no documentation on how to perform this via eCT.
  1. Ensure your MP-V is not in a hosted state within EBO.
  2. Connect to your MP-V device using Windows 10, iOS, or Android via Bluetooth, WiFi, or ethernet connection
  3. Expand the menu in the top left corner and select "Browse Objects" Screenshot_20191216-142934.jpg
  4. Scroll down until you find the DamperCommand object, select it and tap/click OK Screenshot_20191216-143114.jpg
  5. In the Initiate damper calibration Property ID, select False and type in True then click SaveScreenshot_20191216-143123.jpg