Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Analog Consumer Value displays unit in metric (SI) though configured for imperial (US) units

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Analog Consumer Value displays unit in metric (SI) though configured for imperial (US) units
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • JonGreen
    JonGreen
  • ValerieRod
    ValerieRod

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1729 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Analog Consumer Value displays unit in metric (SI) though configured for imperial (US) units

Ensign ValerieRod Ensign
‎2020-01-14 08:27 AM

on ‎2020-01-14 08:27 AM

Issue

Analog consumer values referencing the temperature of a SmartX Sensor shows in metric units when setup to display imperial units.

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation
  • Building Operation Multi-Purpose Controller
  • Building Operation Multi-purpose VAV
  • Building Operation Room Controller
  • Building Operation IP-IO
  • Building Operation SmartX Sensor

Cause

SmartX Sensor is configured in the device as metric measurements (SI System). Setting Fahrenheit in Display of SmartX Sensor does not convert the values from metric to imperial. Consumer values are configured to use the object being referenced and do not convert measurements. Unit conversion is done within the binding and not the device itself.

Resolution

There are two workarounds:

  1. Option 1: Create an analog value and then bind to consumer value
    1. Step 1: Create an Analog Value. Setup unit settings to (°F) and Save. 1) Settings.JPG
    2. Step 2: Bind Analog Value to temperature from SmartX Sensor and Save2) Binding.JPG
    3. Step 3: In the created Consumer Value, bind the Analog Value to the input binding reference and setup unit settings to (°F) and Save3) Analog Value - F Setting.JPG
 
  1. Option 2: Bind to Consumer Value directly and keep the value in metric
    1. Step 1: In the created Consumer Value, bind the SmartX Sensor temperature to the input binding reference
    2. Step 2: Setup unit settings as configured in the object (°C) and Save.4) Workaround1 - C setting.JPG
Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • ValerieRodriguez20
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of