Vista webstation & EBO Registration Error message in FIPS - compliant systems

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Vista webstation & EBO Registration Error message in FIPS - compliant systems
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidChild
    DavidChild
  • Dave_Shore
    Dave_Shore
  • sesa150561
    sesa150561
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1911 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Vista webstation & EBO Registration Error message in FIPS - compliant systems

Picard Product_Support
‎2018-09-06 10:15 AM

Last Updated: Sisko DavidChild Sisko ‎2019-11-08 12:34 AM

Issue

  • Vista webstation - Error message in FIPS-compliant systems first time the logging screen is entered and red X instead of values in TGML pictures
  • Error message in FIPS-compliant systems when Windows Communication Foundation is used to serialize generic types: “This implementation is not part of the Windows Platform FIPS validated cryptographic algorithms”
  • Red X instead of values
  • EcoStruxure Building Operation registration WorkStation Error

Product Line

TAC Vista, EcoStruxure Building Operation

Environment

  • Vista
  • Webstation

Cause

System cryptography: Use FIPS compliant algorithms for encryption, hashing and signing

This security setting determines if the Transport Layer Security/Secure Sockets Layer (TL/SS) Security Provider supports only the TLS_RSA_WITH_3DES_EDE_CBC_SHA cipher suite. In effect, this means that the provider only supports the Transport Layer Security (TLS) protocol as a client and as a server (if applicable). It uses only the Triple DES encryption algorithm for the TLS traffic encryption, only the Rivest, Shamir, and Adleman (RSA) public key algorithm for the TLS key exchange and authentication, and only the Secure Hashing Algorithm 1 (SHA-1) for the TLS hashing requirements.

For Encrypting File System Service (EFS), it supports only the Triple Data Encryption Standard (DES) encryption algorithm for encrypting file data supported by the NTFS file system. By default, EFS uses the Advanced Encryption Standard (AES) algorithm with a 256-bit key in the Windows Server 2003 family and DESX algorithm in Windows XP for encrypting file data. For information about EFS, see Encrypting File System.

NOTE - The same errors can occur in EcoStruxure Building Operation when registering.

WS Error.png

Resolution

Go to Local Security Settings
Security Settings > Local Policies > Security Options
System cryptography: Use FIPS compliant algorithms for encryption, hashing and signing = Make sure its disabled

to get to local security you can go to

1. go to start
2. Go to run
3. enter secpol.msc
4. press enter

NOTE - The same errors can occur in EcoStruxure Building Operation when registering. The Resolution is the same

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 13725
  • DavidShore19
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore