Issue
Configuring a SetPoint in EcoStruxure Building Operation so that the set value of the SetPoint is retained after a Warm or a Cold Start rather than defaulting to zero.
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Enterprise Server
- Building Operation Automation Server Premium
Cause
The value retention configuration is not held in the initial properties page of the Analogue Value when used as a SetPoint.
Resolution
Navigate to the actual value within the properties page of the Analogue Value. On the right hand side of the GUI there is a Configure button.
Pressing on this button then takes the user to a sub menu where the Retain level option can be enabled.
Once enabled it is then possible to decide whether the SetPoint needs to retain its value under a Warm Start or a Cold Start condition.