Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,860
  • TAC IA Series 1,828
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 335
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1858 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 5
    • 6
    • 7
    • …
    • 93
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

EWS / Smart Connector Duplicate Hosted Objects and Binding Issues

Issue When hosting objects from EWS/Smart Connector, such as Security Expert, into EcoStruxure Building Operation (EBO), additional or mismatched object names can result in unresolved bindings and duplicate EWS IDs. Common symptoms include:  - Duplicate EWS IDs with different names - Unresolved or broken bindings - Binding loss after deleting containers   Duplicate EWS IDs with different namesDuplicate EWS IDs with different names Unresolved or broken bindingsUnresolved or broken bindings     Product Line EcoStruxure Building Operation, EcoStruxure Security Expert. Environment EcoStruxure Building Operation Enterprise Server (ES) Security Expert Smart Connector Integration EcoStruxure Web Service (EWS) Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Cause Typical reasons for this to occur: Hosted object names do not match those in Security Expert. Deleting containers without proper renaming can cause binding loss. Resolution   Best Practices for Future Hosting Always rename the hosted object in EBO before rehosting from the hardware folder. This ensures that existing bindings are preserved. Avoid hosting the entire `SecurityExpertServer` container—only host changed or new objects. For Unbound or Irrelevant Objects: - If objects have no bindings, naming is not critical from an EBO perspective - Delete the container and rehost the object from the **Hardware folder**.   To Retain Existing Bindings  Identify the correct object name in the Hosted Containers folder  Copy the name to avoid typos. Delete the duplicate object with the correct name. Rename the existing EWS ID to match the copied name. Save the rename Verify bindings: Right-click the renamed object Select Delete Click Show References Confirm bindings are still valid. Click No to cancel deletion. Repeat this process for each object (inputs, outputs, doors, etc.) that has existing bindings.  
View full article
Guinan RobertAndriolo Guinan
‎2025-06-11 10:23 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:31 AM

Labels:
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
334 Views

Clearing the Smart Connector Hardware Container in Building Operation Server

Issue After making changes to object names in the system, outdated or incorrect names may still appear under the Hardware folder in EcoStruxure Web Services (EWS).     Product Line EcoStruxure Building Operation, EcoStruxure Security Expert. Environment EcoStruxure Building Operation Enterprise Server (ES) EcoStruxure Security Expert Smart Connector Integration EcoStruxure Web Service (EWS). Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Cause When significant changes are made to object names in the system, the Smart Connector may retain outdated data. If a standard Discovery does not update these names, the most effective solution is to clear the Smart Connector database and re-establish the connection.   Resolution To clear the outdated data from the Smart Connector:   Step 1: Access the Smart Connector Portal Open a browser and navigate to http://localhost:8082 (assuming Smart Connector is installed locally). Log in to the Smart Connector Portal. Step 2: Delete the Existing Processor Configuration Go to Configurations → Processor. Locate the Security Expert Discovery Processor. Click the Delete (bin icon) next to it. ⚠️ Do not delete other processors (e.g., Alarm Processor). Step 3: Delete the Existing EWS Server Navigate to the EWS Servers section. Locate the SecurityExpertServer. Click the Delete (bin icon) to remove it.   Step 4: Reconfigure the Processor and EWS Server Follow the instructions in Section 4.4 of the referenced document [1] to: Add a new Security Expert Discovery Processor Configure a new EWS Server Allow 10–15 minutes for the initial discovery process to complete. This will create a fresh snapshot of the current Security Expert database. Once the discovery is complete: Refresh the Hardware folder in EcoStruxure Building Operation. Rehost the new EWS objects as needed. Step 5: Verify Alarm Processor Configuration After re-adding the EWS Server, ensure the Alarm Processor is correctly configured to reference the new server. Refer to Section 4.5 of the same document [1] for detailed steps.   Reference [1] Refer to the official integration guide documentation for more information. Security Expert SmartConnector Version 1.1.0.8 - Installation & User Manual  
View full article
Guinan RobertAndriolo Guinan
‎2025-07-06 06:12 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:31 AM

Labels:
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
205 Views

preventDefault() Javascript function not working on Mouse Up

Issue The preventDefault() JavaScript function does not work as expected when used with the Mouse Up event. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause Users may attempt to override the default behavior of the Building Operation Properties Editor by using preventDefault() on the Mouse Up event. However, the editor is triggered by the Mouse Click event, not Mouse Up. Resolution To successfully prevent the default behavior and override the launch of the Properties Editor: Select the TGML Script where the interaction is defined. Use the onClick event instead of onMouseUp. Add the following line inside the onClick function: evt.preventDefault();​
View full article
Picard Product_Support
‎2018-09-06 09:43 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-29 02:15 AM

Labels:
  • EcoStruxure Building Operation
1851 Views

User names and passwords configured on a Building Operation Domain are not accepted by the AS's.

Issue User names and passwords configured on a Building Operation Domain are not accepted by the Automation Servers (AS). Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause A new Domain was configured on the Enterprise Server (ES), exported, and then imported to each AS. This process creates unrelated Domains across servers, which is not the intended operational setup. It results in duplicate user accounts with potentially different passwords, leading to a complex and unmanageable configuration. Resolution To correctly configure a shared Domain across the ES and ASs, follow these steps: Add ASs to the ES Connect the Workstation to the ES and add the Automation Servers in the usual way. Create a New Domain on the ES Navigate to Control Panel > Domains. Click Add, assign a meaningful name to the Domain. Select the ASs that will share this Domain with the ES. Click Create. Note: The new Domain will be visible when reviewing the ASs, but nothing will appear in the Domain folder on an AS. Set the New Domain as Default (Optional) Right-click the Domain and select Set as Default Domain.                                         Repeat this step on each server. Verify ES IP Address Ensure the ES IP address is correctly configured on all ASs. Create User Groups, Users, and Workspaces Set up the necessary User Groups, Users, and Workspaces for the new Domain. Restart the ES and Log In Log off the Workstation. Restart the ES. Log back in using the new Domain credentials. Log In to ASs Use the new Domain credentials to log in to each AS.
View full article
Picard Product_Support
‎2018-09-11 04:23 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-29 01:55 AM

Labels:
  • EcoStruxure Building Operation
1837 Views

Common Modbus error codes seen in trace logs

Issue Understanding common Modbus error codes that appear in Building Operation trace logs. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Enterprise Server Modbus Cause Modbus protocol errors are seen when looking at Building operation trace logs. Resolution Below are common Modbus error codes observed in trace logs, their meanings, and example log entries. Error Code 4 – Server Device Failure Message: RESP_DATA_MISMATCH Meaning: This error indicates that the Modbus slave device encountered an unrecoverable internal error while attempting to execute the requested command. This is a problem within the slave device itself, not a communication error on the client side. Possible Causes: Attempting to write to a protected memory area Device in an unsuitable state for the command Example Log Entry: Dec 27 08:15:01 AS-P-18E4A6 nsp_servers[1151]: 2024-12-27 08:15:01.767 [1654641088] nsp.pin.modbus.SerTransport Flush buffer. Protocol error code = 4 Error Code 10 – Illegal Data Value Message: Flush buffer. Protocol error code = 10 Meaning: This error suggests the slave device rejected a data value sent by the master. Possible Causes: Value out of acceptable range Attempt to write to a read-only address Example Log Entry: Dec 27 08:15:01 AS-P-18E4A6 nsp_servers[1151]: 2024-12-27 08:15:01.774 [1654641088] nsp.pin.modbus.SerTransport Flush buffer. Protocol error code = 10 Error Code 7 – CRC Header Issue Message: Flush buffer. Protocol error code = 7 Meaning: This error indicates a CRC (Cyclic Redundancy Check) mismatch in the response message. Possible Causes: Incorrect CRC calculation by the device Incomplete or corrupted packet Example Log Entry: 2025-07-22 10:14:39.636 [1666360064] nsp.pin.modbus.SerTransport Flush buffer. Protocol error code = 7
View full article
Spock PeterLarsen Spock
‎2025-08-29 12:50 AM

on ‎2025-08-29 12:50 AM

Labels:
  • EcoStruxure Building Operation
130 Views

TAC Vista to SmartStruxure Interface does not connect in non-English Operation System

Issue The TAC Vista to SmartStruxure Interface fails to connect when the operating system is set to a non-English format. Product Line TAC Vista Environment Vista server Cause This issue occurs due to the Windows Format setting being configured to a non-English language. The interface requires the format to be set to English for proper connectivity. Resolution To resolve the issue: Open Control Panel in Windows. Navigate to Region and Language settings. Under the Formats tab, change the format to English. Click Apply to save the changes. Note: This issue is resolved in Vista version 5.1.9. For instructions on creating the Vista interface in SmartStruxure, refer to How to Create TAC Vista Interface to SmartStruxure.
View full article
Picard Product_Support
‎2018-09-11 06:31 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-28 10:10 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1772 Views

OPC or DDE Integration with EcoStruxure Building Operation

Issue Support for OPC or DDE integration with EcoStruxure Building Operation Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Cause The OPC Server is a software program that converts hardware communication protocol into the OPC protocol. The OPC client software is any program that needs to connect to the hardware. It uses the OPC Server to retrieve data from or send commands to the hardware. Resolution Supported Functionality OPC UA Client functionality is available in EBO version 6.0.1 or higher. Refer to: OPC UA Client Support Currently Not Supported OPC UA Server OPC DA Client/Server DDE Configurations Alternative Integration Options If integration with unsupported protocols is required, consider the following alternatives: Protocol Conversion Use a converter to translate between OPC and a protocol supported by EBO. Examples: OPC Server → BACnet Server EBO BACnet Points → OPC Recommended 3rd Party Tools (not supported by Schneider Electric): Kepware Matrikon SCADA engine Note: Ensure the EBO server's role is clearly defined (e.g., exchanging point values) to determine compatibility. SmartConnector Extension Use a SmartConnector Extension as middleware between EBO and an OPC client/server. Resources: Exchange shop SmartConnector Server EBO SmartDriver and Smart Connector Additional Notes These integration methods involve 3rd party software and may require additional configuration and validation. Schneider Electric does not provide support for 3rd party tools.
View full article
Picard Product_Support
‎2018-09-10 05:35 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-28 10:02 PM

Labels:
  • EcoStruxure Building Operation
5027 Views

Multiple Automation Servers on the same backplane

Issue Is it possible for multiple Automation Servers to be placed on the same backplane and use one power supply? Some known issues in this unsupported configuration: Automation Server only partially discovers the IO Modules Function Block Programs (FBP) remain in an unloaded state (see FBP Unloaded) EBO 2022 (v4.0) and higher, Alarm: IO Driver unexpectedly timed out Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Automation Server (EBO 2022 and above) EcoStruxure Building Operation Power Supply (PS-24V) EcoStruxure Building Central IO Modules Cause The terminal bases provide a path for communication between all connected units on the same backplane; as such, the connection of two or more Automation Servers will cause communication issues between all connected units on that same backplane. See the following article on how to check the CIO node the Automation Server is using: How to identify Automation Server(AS) ID node count   Resolution From EBO 2022 (v4.0.1) due to changes in the Central I/O (CIO), checks are now made in the Automation Server to verify that the server is physically in SLOT 2; if this is not the case, then all Tasks are disabled and will not run.    You cannot connect more than one Automation Server to the backplane. Only one Automation Server is allowed per power supply, the architecture is always "PS-AS-....." and after that I/O modules with additional PS units as needed, but only one Automation Server can exist on the same backplane.   Note that an alarm will also generate if you attempt the following configuration (also not supported)  PS-AS-PS-AS  Alarms will only clear after a restart (warm) of the server 
View full article
Picard Product_Support
‎2018-09-10 11:27 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2025-08-27 04:58 PM

Labels:
  • EcoStruxure Building Operation
2842 Views

License Violation Alarm Triggered Without License Violation Banner displayed

  Issue A License Violation alarm is triggered without displaying a License Violation banner. Alarm reactivates after acknowledgment, approximately every 10 minutes.     Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Potential communication issue, possibly related to return path or port configuration. An incorrect ES port may be in use, contributing to the issue. The Communication Tab [Communication View] and Server List in xbk Analyzer show only the ES, indicating limited server visibility. Resolution Verify Communication Path Ensure the ES is defined as using the same ports across all servers. Confirm that the ports are correctly configured and open on all relevant servers. Review the Communication Tab [Communication View] and Server List Check that all expected servers are listed and actively communicating. If only the ES is visible, investigate potential network or configuration issues. See article for additional information: Updating a Enterprise Server IP Address - Schneider Electric Community Check AS Logs Log in to the Automation Servers to identify any communication errors. These errors may not be visible from the ES alone. Next Steps If the above steps do not resolve the issue or the root cause remains unclear: Refer to the article for possible communication-related troubleshooting options: Enterprise Server and Automation Server Bindings show Unresolved - Schneider Electric Community Refer to the article for additional license troubleshooting options: Troubleshooting EBO license violation issues - Schneider Electric Community Contact your local support organization for further assistance.
View full article
Guinan RobertAndriolo Guinan
‎2025-08-26 02:57 AM

on ‎2025-08-26 02:57 AM

Labels:
  • EcoStruxure Building Operation
186 Views

OPC UA export clarification

Issue After adding an OPC UA server to EBO an export is done from the Device discovery tab to find the objects in the OPC UA server. When the OPC UA server database is big this can take up to a day to finish and sometimes the export is never finished. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause In EBO version 7 there is a workaround for this issue, it is possible to split the export up in smaller pieces and export objects from specified folders from the OPC UA server instead of all objects in the OPC UA server database.   Resolution Introduction The ‘Export configuration’ section in the settings dialog for discovered devices makes it possible to configure the export procedure. By setting the parameters in this section, you can specify the start node and the depth for each export file. This means that you can break down the export into many files instead of one large file containing everything. When importing the series of export files it is recommended to keep the same structure as the OPC UA server has, but it is not a requirement. You can import the export file anywhere under the device, but again, the recommendation is to keep the same structure as on the OPC UA server.   Selecting start node for browse The start node is specified by setting the ‘Start node namespace index’ (specified as an integer value) and the ‘Start node identifier’ (specified as a string value). The supported ‘Start node identifier’ types are string (s=), integer (i=), opaque (o=) and guid (g=). Both ‘Start node namespace index’ and ‘Start node identifier’ are found as properties on each OPC UA object. If these values are empty, faulty, equal to the object node or equal to the root node, the device object is included in the export file. Otherwise, it is omitted. Selecting the depth of browse The depth of an export file is specified as an integer value. It is recommended that this is set to a low number if the export time is expected to take a long time. Values 0, -1 or empty means that no depth limit is used. Getting started   A first step could be to export the root objects. The following configuration will handle that: The export file with this configuration will produce the following result when imported. Since the ‘Start node namespace index’ and the ‘Start node identifier’ are empty, the device object is included, and the import can be done on the ‘OPC UA Client Network’ object Only the root objects were included in the export file since the ‘Export depth’ was set to ‘1’. Next, we would like to populate the ‘BuildingAutomation’ object with 2 levels of child objects. For that we need the namespace index and the identifier of the ‘BuildingAutomation’ object found at the bottom of the property list:   These values are entered into the export configuration: The export file with this configuration will produce the following result when imported on the ‘BuildingAutomation’ object: Now we have a structure with all the root objects. All of them are empty except for BuildingAutomation that has two levels of child objects.   If you realize that the depth chosen was to low, you can simply set the ‘Export depth’ to a higher value and create a new export file from the same start node. The ‘Export configuration’ will now look like below: When importing the new export file we still use the ‘BuildingAutomation’ object as the start object, but since we already have two level of child nodes we need to select the merge option in the import dialog as in the picture below:    
View full article
Janeway Jonas_Brissman Janeway
‎2025-08-26 02:55 AM

on ‎2025-08-26 02:55 AM

Labels:
  • EcoStruxure Building Operation
108 Views

Queue Full Exception in Niagara

Issue Encounter Queue Full Exception in context of "Error writing BACnet point" Product Line EcoStruxure Building Operation, TAC IA Series Environment I/A Series N4 Jace 8000 I/A Series N4 Jace 9000 Niagara Station running as SoftJace or 3rd Party Jace Cause If you notice queue overflow messages in the station dialog, it is essential to know which queue is overflowing. There are many different communications mechanisms in BACnet, and they use different queues. Resolution The canonical reference article is located on Niagara Community: BACnet Tuning Suggestions I have excerpted the following as a Rule of Thumb for the recommended starting configuration: Configure your tuning policies so that write-on-start is not enabled on some of the points - otherwise, the JACE may start with a to-do list that is larger than the queue can handle. The recommended configuration from Tridium is to set BACnet WriteWorker queues to 1.5 times the number of writable points. However, as initial configuration, Product Support has found these values to perform better than the defaults, so change the following values from 1000 to 3000. View the BacnetNetwork Property Sheet Expand Bacnet Comm Expand BACnet Comm -> Server -> Worker and Confirmed Worker Expand BACnet Comm -> Transport Change the various Queue Sizes from 1000 to 3000. Please consult PSS if a change to a value higher than 3000, as that has been found to adversely affect performance. 
View full article
Picard David_Purser Picard
‎2025-08-25 11:21 AM

on ‎2025-08-25 11:21 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
302 Views

Troubleshooting EBO license violation issues

Issue  EBO can have license violation bar without a known reason. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause License enforcement is the process of checking whether a software application has a valid license available to it at runtime. If you do not have enough licenses, a license violation occurs. This is accomplished by a license violation bar in WorkStation and WebStation.   Firstly, the license violation will be yellow, and it can be hidden for 8 hours. You can use Hide to hide the License Violation bar for 7 days. After 7 days, the Hide function is disabled. After 30 days, the bar turns red. Resolution Below information can be collected to help in troubleshooting: Refer to the document Part Number Summary and Hardware Software Matrix for software and features that need licenses and note that some feature licenses can be inherited from parent server to child servers. Get a screenshot of the License information page in the control panel, make sure to have all content in license information page are shown in the screenshots, ex child servers' status. It can tell which feature needs a license or which child server needs a license, refer to License Information Get the License Diagnostics, and entitlement certificates to make sure that required licenses are activated. Install the latest CP/hotfix to make sure that the system is not affected by one of the known license related defects, Make sure that all EBO servers have correct date and time, incorrect date and time can cause license violation, as explained in: Incorrect Automation Server date and time leads to license violation - Schneider Electric Community See this article if you do not see the License banner, but still get a License Violation alarm: License Violation Alarm Triggered Without License Violation Banner displayed - Schneider Electric Community  Check Known issues community. Get screenshots for the following: In ES, "System/LicenseManager/LicenseStatus/ConnectedASLicenseStatus" will show all connected Automation Servers. Show the license violation tab to know which Automation Server has violation as Automation Server may have violation although license information doesn't show that, ex. if the "Change Control" feature is enabled in an Automation server and ES doesn't have a license for it. For parent server and any server that has violation, search in folder "/System/LicenseManager/LicenseStatus". In the object name, write "*" and add columns License Violation, Checked Out License, Available Licenses, Required Licenses, and Installed Licenses. Export the results to XLSX. Check license Metadata for the parent server and any servers have license violation, search in folder "/System/LicenseManager/LicensingMetadata". In object name, write "*" and add columns FeatureVersion, FatureName, ProductVersion, EntitlmentID and Activation ID. Export the results to XLSX.   Get screenshot from FlexNet Publisher web interface, localhost:8888, concurrent tab. Make sure all features are shown in the screenshot, and the entire webpage can be saved instead of taking screenshots. If the server has just started, wait for some minutes till all data is collected.   Collect the logs and configuration files listed below: Log files located in C:\Program Files (x86)\Schneider Electric EcoStruxure\Building Operation x.x\License Server\logs Configuration file located in C:\Program Files (x86)\Schneider Electric EcoStruxure\Building Operation x.x\License Server\conf Using EBO WorkStation, go to module, '/System/Modules/Trace/Loggers/nsp/nsp.csc/nsp.csc.licensemanager", set trace level to debug, reproduce the issue, if possible. Collect the server logs, then set the module trace level back to "information", refer to Collect logs from an Automation Server - Communities and Collect logs from the Enterprise Server and Enterprise Central - Communities.
View full article
Kirk Mahmoud_Sayed Kirk
‎2022-09-19 05:25 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2025-08-25 12:49 AM

Labels:
  • EcoStruxure Building Operation
7066 Views

EBO SAML Single Sign On(SSO) Reverse Proxy support

Issue Unable to configure reverse proxy for SAML-based Single Sign-On (SSO) in EcoStruxure Building Operation (EBO). Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Webstation Cause Although EBO 7.0 has enhanced reverse proxy support, this does not include SAML SSO and EBO does not support reverse proxy configurations for SAML SSO.  This limitation prevents successful integration when a reverse proxy is used in the authentication flow. Resolution At this time, EcoStruxure Building Operation version 7.0 does not support reverse proxy configurations for SAML SSO. This is a known limitation. An enhancement request has been submitted to the Idea Forum to address this functionality in future releases.   To support this request, please visit the Idea Forum and click the thumbs-up icon on the SAML reverse proxy support idea to increase its visibility to the product management team.
View full article
Admiral StephenYang Admiral
‎2025-08-20 10:18 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-24 04:27 PM

Labels:
  • EcoStruxure Building Operation
195 Views

Central I/O Input and Output Specifications

Issue Questions regarding specifications of Central I/O Inputs and Outputs Product Line EcoStruxure Building Operation Environment SmartStruxure I/O Modules: AO-8, AO-8-H AO-V-8, AO-V-8-H DI-16 DO-FA-12, DO-FA-12-H DO-FC-8, DO-FC-8-H RTD-DI-16 UI-8-AO-4, UI-8-AO-4-H, UI-8/AO-4-2, UI-8/AO-4-H-2 UI-8-AO-V-4, UI-8-AO-V-4-H, I/O UI-8/AO-V-4-2, UI-8/AO-V-4-H-2 UI-8-DO-FC-4, UI-8-DO-FC-4-H, UI-8/DO-FC-4-2, UI-8/DO-FC-4-H-2 UI-16 Cause Different I/O modules have varying electrical specifications Resolution Universal Input Specifications Universal inputs can be configured as voltage, current, thermistor, resistance, digital or supervised inputs.   Voltage Input Specifications: Range: 0 to 10 VDC Resolution: 12-bit (UI-8 v2: 16-bit) Accuracy: ±(0.7mV + 0.2% of reading) Current Input Specifications: Range: 0 to 20 mA Resolution: 12-bit (UI-8 v2: 16-bit) Accuracy: ±(0.03 mA + 0.4% of reading) Resistance Input Specifications: 10 Ohm to 10 kOhm 10 kOhm to 60 kOhm Thermistor Input Specifications: Range: -50 to 150° C (-58 to 302° F) Supported Types: 10k Type I (Continuum) 10k Type II (I/NET) 10k Type III (Satchwell) 10k Type IV (FD) 1.8k (Xenta) 10k Linearized (Satchwell DRT) 10k Type V (FD w/ 11k shunt) 1k (Balco) 20k (Honeywell) 2.2k (Johnson Controls) Digital Output Specifications Form C Relay: Terminals: Common (C), Normally Open (NO), Normally Closed (NC) Minimum Pulse Width: 100 ms Isolation: 1500 VAC (coil to contact) Cycle Life: ≥100,000 cycles Contact Rating: 250 VAC, 30 VDC, 3 A Form A Relay: Terminals: Common (C), Normally Open (NO) Minimum Pulse Width: 100 ms Isolation: 1500 VAC Cycle Life: ≥100,000 cycles Contact Rating: 250 VAC, 30 VDC, 2 A LED Indicators: Polarity: Reflects actual output state (ON = active, OFF = inactive) Color: Green Analog Output Specifications Analog outputs can be configured as voltage or current. Voltage Output: Range: 0 to 10 VDC Resolution: 50 mV Accuracy: ±100 mV Terminals: Voltage (V), Return Minimum Load: Source 2 mA, Sink -1 mA Current Output: Range: 0 to 20 mA Resolution: 0.1 mA Accuracy: ±0.2 mA Terminals: Current (I), Return Max Load: ≤650 Ohms Supervised Input Specifications Supervised inputs detect sabotage via resistor monitoring. Detected Conditions: Open circuit, short circuit, contact open/closed Circuit: 5V, 1 or 2 resistors Configurations: Series only, parallel only, series + switch Resistor Range: 1k to 10k Ohms (must be equal values) Note: Resistor value must be defined in the system. RTD Input Specifications RTD-DI-16 specifications are extensive. Refer to the official datasheet: RTD-DI-16 Specification Sheet  
View full article
Picard Product_Support
‎2018-09-11 01:25 PM

Last Updated: Administrator CraigEl Administrator ‎2025-08-22 08:24 PM

Labels:
  • EcoStruxure Building Operation
3714 Views

Summary page or List of All Forced Variables in version 1.4.1 and older

Issue Users need a way to identify all Forced Variables without manually inspecting each point. The goal is to have a summary view—not via Reports Server—but directly accessible on the Automation Server (AS) or Enterprise Server (ES). Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause There is no built-in summary page in versions 1.4.1 and older that lists all Forced Variables. This makes it time-consuming to locate which points are currently forced. Resolution You can locate Forced Variables using the system tree in the Workstation. Navigate to: ES/Servers/AS/System/Modules/RuntimeDBManager/VariableManager/Variables Ensure the isForced column is enabled to view which variables are forced. Additional Notes: This method provides a quick overview without needing to open each individual point. It is especially useful for troubleshooting and auditing system behavior.
View full article
Picard Product_Support
‎2018-09-11 04:00 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-22 07:13 PM

Labels:
  • EcoStruxure Building Operation
1984 Views

LMADMIN.exe - Application Error

Issue After the "Windows is shutting down" message, Windows displays a non-specific memory error: lmadmin.exe - Application Error The instruction at "0x00000000" referenced memory at "0x000000". The memory could not be read. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Cause This issue is caused by Flexera Software, the licensing software used within Building Operation. Flexera does not support Windows XP, which leads to this error during system shutdown. This is a known limitation and will not be addressed in future updates. Resolution There are no known operational impacts associated with this error. It only occurs during shutdown of a Windows XP machine. Upgrading the operating system to a supported version will eliminate this error. Additional Notes This issue is cosmetic and does not affect system performance or licensing functionality. Users are encouraged to migrate away from Windows XP due to broader security and compatibility concerns.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-22 07:01 PM

Labels:
  • EcoStruxure Building Operation
3158 Views

WebReports/Report Server discontinuation in EBO 2022 or higher (Migration to External Log Storage)

Issue Sites using Report Server need to upgrade to EcoStruxure Building Operation (EBO) 2022 or higher, where WebReports/Report Server is no longer supported. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Report Server Building Operation Timescale Database Cause WebReports/Report Server is not supported in EBO 2022 (version 4.0) or higher. Resolution To address this, Schneider Electric provides a Data Migration Assistant (DMA) tool that: Reads data from WebReports 3.x Writes data to External Log Storage Download the DMA Tool External Log Storage Overview Stores historical data from EcoStruxure BMS Storage capacity is limited only by your hardware Historical data is displayed in WorkStation and WebStation (event and trend views) Any server can be configured to write data to TimescaleDB   Any server in the system can be configured to write historical data to the TimescaleDB database. Licensing Requirements External Log Storage requires a license Refer to: Software and Features that Require Licenses Part Number Summary and Hardware Software Matrix Hardware & Software Requirements Ensure compatibility with: TimescaleDB PostgreSQL Recommended specs for large systems (e.g., 100 BMS servers): High-performance SSD Minimum 64 GB RAM Additional CPU capacity Refer to: IT System Planning Guide Merging Log Data External Log Storage reduces extended trend logs on BMS servers You can merge extended trend logs into source logs in External Log Storage See: Merging of Trend Log Data Enhanced Reporting (XLSX Templates) EBO servers (v3.2 or higher) support native reporting with: Text and XLSX formats Advanced XLSX features: formulas, conditional formatting, charts, sparklines Historical data pulled from External Log Storage (PostgreSQL/TimescaleDB) Refer to: Examples for Native EBO Notification Reports
View full article
Kirk Mahmoud_Sayed Kirk
‎2022-06-22 01:54 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-15 06:38 PM

Labels:
  • EcoStruxure Building Operation
5087 Views

How BACnet controllers are established as being Online / Offline

Issue How are BACnet controllers established as being Online / Offline? Product Line EcoStruxure Building Operation Environment BACnet Cause BACnet controllers may appear offline in the system, even though they can still be communicated with. This raises questions about how their online/offline status is determined. Resolution The online/offline status of BACnet devices is managed by the BACnet device manager plugin, which processes BACnet I-Am messages to maintain a device table.   The following rules and mechanisms are used to determine the status of BACnet controllers: Device Discovery and Initial Probing When a new device is discovered, an entry is added to the device table. The system probes the new entry up to four times at 5-second intervals. If the device does not respond within this time, it is declared offline. Offline Detection via MSTP Driver Building Operation uses the MSTP dev driver to monitor token passing. If three consecutive tokens are missed, the device is marked as offline. Probing Offline Devices Once a device is offline, the system sends a Who-Is message every 60 seconds. Offline devices are probed indefinitely at 60-second intervals until they respond. Online devices are never probed. Status Transition A device is considered online once it responds to a request. If it fails to respond, its status is updated to offline, and probing resumes.
View full article
Picard Product_Support
‎2018-09-06 09:47 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-13 05:47 PM

Labels:
  • EcoStruxure Building Operation
2836 Views

Getting data from Rayleigh Instruments RI-78-80-C kWh Meter

Issue How to get data from Rayleigh Instruments RI-78-80-C kWh power meters Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Automation Server (ASP/ASB) Modbus RTU Interface Cause The RI-78-80-C meter provides a single 48-bit Modbus RTU word representing energy in kWh. This word spans three 16-bit registers (registers 0, 1, and 2). The meter: Only responds to a valid 48-bit read Does not return exceptions for invalid or partial register reads Resolution To successfully read the 48-bit value: Step-by-Step Instructions Create a Modbus Group Set an appropriate polling interval. Add Registers Add three 16-bit unsigned registers to the group: ModReg0 (Register 0) ModReg1 (Register 1) ModReg2 (Register 2) Create an Analog Value Example name: kWReading Script Program Use the following calculation: kWReading = ((256 * 256 * ModReg0) + (256 * ModReg1) + ModReg2) / 100 ​ This formula accounts for the fact that each register only uses half of its 16-bit range (values from 0 to 255). The register values represent 1/100 of a kWh, so a scaling factor of /100 is applied. Bind Points Bind the Modbus registers and analog value to the script program. Example Calculation If: ModReg0 = 3 ModReg1 = 167 ModReg2 = 59 Then: kWReading = ((3 × 256 × 256) + (167 × 256) + 59) / 100 = 239419 / 100 = 2394.19 kWh ​   Additional Notes The device may appear online in EcoStruxure even if it’s not responding correctly. This is because the online poll interval mechanism expects a response from a 16-bit register. Since the RI-78-80-C doesn’t respond to invalid reads, it may falsely appear online. To avoid this, set the online poll interval mechanism to “Inhibit”. Compatibility Warning: This device may not function correctly in v2.0 and v3.0 due to changes in offline detection. This issue is resolved in v3.1. Resources Example Modbus Objects and Script RI-78-80-C Exports.zip Numeric Output kWReading   Line Calc1 kWReading = ((256*256*ModReg0) + (256*ModReg1) + ModReg2)/100
View full article
Picard Product_Support
‎2018-09-11 07:08 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-13 05:24 PM

Labels:
  • EcoStruxure Building Operation
3383 Views

Trigger multiple alarms on a single variable

Issue How to trigger different alarms with different alarm texts depending on the value of a single variable Product Line EcoStruxure Building Operation Environment Building Operation Workstation Alarms Cause There is a requirement to trigger different alarms based on the value of a single variable.  As an example, a variable coming from an APC Symmetra UPS will report various alarm states as a number from 1 to 7 in the same variable, and it is required to differentiate the alarm text on each value. Value Status Alarm text 1 unknown Module is in Unknown state from UPS 2 not installed Module not installed in UPS 3 Off OK Module not installed in UPS 4 On OK Module not okay in UPS 5 Off Fail Module off fail in UPS 6 On Fail Module on fail in UPS 7 Lost Communication Module lost comm. in UPS Resolution Here are two examples on how to do it Example 1: 7 different alarms with different alarm texts monitoring the same point Example 2: 1 alarm monitoring a point, and a script dynamically changing the alarm text     From version 1.9 upwards Alarm Decoration is available and could also be used in various ways to achieve the same result.  Similar to example 1 a decoration could be created for each state.  For example for state 3, create a decoration that filters on the active alarm (1) and when the value at change is three (2) override the alarm text message (3) with the relevant text (4). The decorations have the added benefit they can be applied to multiple point alarms.  
View full article
Picard Product_Support
‎2018-09-06 09:12 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:14 AM

Labels:
  • EcoStruxure Building Operation
1472 Views
  • « Previous
    • 1
    • …
    • 5
    • 6
    • 7
    • …
    • 93
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore