Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: EcoStruxure Building Operation
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 15
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "ecostruxure building operation"

View in: "Building Automation Knowledge Base" | Community

1845 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 4
    • 5
    • 6
    • …
    • 93
  • Next »
Label: "EcoStruxure Building Operation" Show all articles

Packets from the EBO onboard packet capture utility are not ordered correctly

  Issue Packets from the EBO onboard packet capture utility are not ordered correctly. In the example below it can be seen that the sequence number of the ACK comes before the REQ despite the timestamp for the ACK being later than the REQ.   Product Line EcoStruxure Building Operation Environment Building Operation Workstation SpaceLogic Server   Cause Out-of-order packets are quite normal on a TCP level. Earlier packets can arrive later due to buffering and other reasons. Applications are able to buffer these messages and rearrange them before they are written to the application.   Since the standard Wireshark pcap utility that EBO uses to capture packets does not sort packets in a batch by time stamp before delivering them to the capture file it is subject to the same irregularities that we would see on any OS.   Resolution This is a common enough issue that Wireshark includes a command line utility named reordercap that can fix packets that can't have been on the network in that order (like an answer being sent before you see the request for it).   In the example below the utility has run through a capture and reordered items and saved the file as a new file.     See the Wireshark reordercap help topic for further information on this utility.
View full article
Administrator CraigEl Administrator
‎2024-10-16 11:54 PM

on ‎2024-10-16 11:54 PM

Labels:
  • EcoStruxure Building Operation
627 Views

How to prevent BACnet client from triggering EBO backup

Issue Any third party BACnet client can initiate an EBO backup. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Cause As of EBO 2023 (5.0.2.109), EBO's BACnet backup operation requires no password which means any BACnet client with the EBO server BACnet interface's device ID can initiate an EBO backup without any restrictions. Any such backup can be identified by looking at the backup description in EBO, the backup will explicitly indicate that it was generated by third party BACnet Workstation.   Resolution EBO 2024 (V6.0.1) or higher: In BACnet Interface basic tab, "Restrict backup and restore service" can be set to Yes to ensure that third-party BACnet clients cannot perform a BACnet backup or restore on the EcoStruxure BMS server. Refer to: BACnet Interface for an Automation Server – Basic Tab and BACnet Interface for an Enterprise Server – Basic Tab   EBO 2022 (4.0.4CP2 or higher) and EBO 2024 (V5.0.3 or higher): A rule can be added to the BACnet service_blacklist to disable BACnet backup service. See https://community.se.com/t5/Building-Automation-Knowledge/BACnet-RULES-implementation-to-disable-features-such-as/ta-p/839 for details on how to create service_black list.   Use the following syntax to create a rule that restricts BACnet back up initiated by 3rd party BACnet client on the EBO server.   <blacklist> <global> <restrict-backup-service/> </global> </blacklist>   Any BACnet client requesting backup from EBO server configured with the above rule will be presented with error similar to screenshot below.
View full article
Captain AbeMeran Captain
‎2023-04-13 04:41 PM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-10-16 07:46 AM

Labels:
  • EcoStruxure Building Operation
1135 Views

WorkStation HTTPS connection and cloud connectivity fail if TLS V1.3 is enabled in a non-supported Windows

Issue WorkStation can't connect via secure communication (HTTPS) to EBO server, although it can connect via non-secure communication (HTTP). Cloud connectivity also fails. WebStation can still connect via HTTPS. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation WorkStation Cause TLS V1.3 is supported in Windows 11 and Windows Server 2022 or later. Enabling it in earlier Windows versions is not support it can lead to problems, as explained in Protocols in TLS/SSL (Schannel SSP) - Win32 apps | Microsoft Learn Resolution Do not enable TLS V1.3, If the installed Windows version doesn't support it (Windows 10 and Windows Server 2019 or earlier), or disable it if it is already enabled by following the below steps:  Open Windows Registry Editor, by writing "regedit" in Start menu.  Goto registry path "HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\Control\SecurityProviders\SCHANNEL\Protocols\TLS 1.3\Client" Make sure that "Enabled" is set 0, and "DisabledByDefault" is set to 1, this will disable TLS V1.3 for clients.  Restart WorkStation.   For more information, refer to: Transport Layer Security (TLS) registry settings | Microsoft Learn Warning! Improper use of regedit may damage PC’s operation.
View full article
Kirk Mahmoud_Sayed Kirk
‎2024-10-16 09:10 AM

on ‎2024-10-16 09:10 AM

Labels:
  • EcoStruxure Building Operation
709 Views

Can Script program read trend logs records from External Log Storage

Issue READ is a Script programming system function that reads trend data from a trend log into a Script program. If there is an External Logs Storage configured, is it possible to access trend log records from the External Log Storage? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause READ Script function doesn't return same number of records as trend log list or chart. Resolution The Script READ (for Trend Logs) system function can only read from the server's internal database and doesn't access records stored in the External Log Storage. For more information, refer to: Trend Log Access Functions.
View full article
Kirk Mahmoud_Sayed Kirk
‎2024-10-15 06:48 AM

on ‎2024-10-15 06:48 AM

Labels:
  • EcoStruxure Building Operation
973 Views

Setup External Log Storage using MSSQL

Issue How to setup and configure External Log Storage in EcoStruxure Building Operation (EBO) when using Microsoft SQL Server as external log storage. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Building Operation Enterprise Server Building Operation Enterprise Central Cause You use External Log Storage feature to store historical data from EcoStruxure BMS. The amount of stored data is limited only by the equipment you use, and not by the capacities of the feature. The External Log Storage feature uses an external database administered by either a combination of TimescaleDB and PostgreSQL software, or Microsoft SQL server. Resolution Please see the below video demonstrating how to: Create a database and user account in Microsoft SQL (MSSQL) Server using Microsoft Server Management Studio. Configure the External Log storage connection between EBO and MSSQL server in EBO. Also please note the following: In the video the "Host address" in EBO is set to the IP address or DNS name\SQLserver instance like this: localhost\SQLEXPRESS. If the SQL server is not located on the same computer as the EBO server only use the IP address or DNS name and no instance on "Host address". The video demonstrates using the version 5 script when configuring the database in the MSSQL server, search External Log Storage - MSSQL Installation Script  to download the appropriate EBO version script. For the example query to manage user permissions download User Rights Script or see attached script.txt. If using MSSQL Express rather than the full MSSQL version it may be necessary to consult External log storage not working with SQL Server Express.    
View full article
Janeway Jonas_Brissman Janeway
‎2023-03-02 05:58 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-10-11 05:47 AM

Labels:
  • EcoStruxure Building Operation
7391 Views

SmartConnector RESTful gateway returns error "Container Id not found"

Issue In Swagger user can login but can't get the id of the root container. Below response is received: "Message": "Container Id not found" Product Line EcoStruxure Building Operation Environment SmartConnector Cause EBO user password need to be changed due to Password Expiry configured in the password policy. When user tries to login to WorkStation or WebStation, below change password dialog will be recieved.   Resolution Make sure to change the user password before reaching the limit the days configured in the Password Policy. Password expiry can also be reconfigured to change number of days or disabled if not needed, refer to Configuring the Password Policy using WorkStation or Configuring the Password Policy using WebStation
View full article
Kirk Mahmoud_Sayed Kirk
‎2024-10-07 06:14 AM

on ‎2024-10-07 06:14 AM

Labels:
  • EcoStruxure Building Operation
589 Views

Jace 9000 Missing BACnet IP Adapters

Issue The en1 network adapter is not an option for assignment when configuring an IP port Product Line TAC IA Series, EcoStruxure Building Operation Environment I/A Series N4 Jace 9000 Building Operation Multi-purpose Controller / VAV (MP-C / MP-V) Building Operation Room Controller / VAV (RP-C / RP-V) Building Operation IP-IO Cause With the switch to Linux for the Jace 9000's operating system, some functions such as sensing adapters work differently when configuring a controller station.     Resolution In N4.13, we have added a new action to find adapters when Jace's are being pre-configured offsite. Start by confirming in the TCP/IP Configuration page that the desired port is configured and enabled. Make sure that some communicating device is connected to the desired port, exhibited by the port's lights on the unit. Examples include a workbench connection, a BACnet IP device/router, or another Niagara Device. Right-click on the "Link" component under the port, and select the "Query For Adapters" option. You should now see the port in the dropdown. Note: With N4.14, using the en1 as a DHCP server is possible.  If using this with BACnet IP MP, RP or IP/IO in Space Logic controllers engineering with Niagara, this is an important consideration for network applications.
View full article
Guinan RandyDavis Guinan
‎2024-10-03 07:51 AM

on ‎2024-10-03 07:51 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
1511 Views

Configure and test RP controller web service

Issue How to configure and test RP controller web service Product Line EcoStruxure Building Operation Environment Building Operation Room Controller (RPC) 24 V Building Operation Room Controller (RPC) 230 V Cause In the RP application, a REST (Representational State Transfer) Web Service API is available to facilitate secure HTTPS communications and allow you to obtain BACnet objects and properties from the controller. Resolution The following video will illustrate how to: Use the SpaceLogic certificate configuration tool to configure keys and certificates in the RP controller. Configure RP controller Web Service settings. Use SoapUI to test RP controller Web Service. Things you need: Software EBO 2022 or later server (Enterprise Server, AS-P or AS-B) and WorkStation. SpaceLogic RP controller, RP-C Advanced, RP-C Pro, RP-C Pro Plus and RP-V Advanced, with firmware V4.00.01 or later. SpaceLogic Certificate Configuration Tool, available from Exchange. Tools SoapUI (to be used for testing) For more information and how to generate certificates, please check RP Controller | Developer Portal. Note: Before configuring the Web Services in RP controller, make sure that there no pending IP changes, by checking "Changes pending" property in IP Network Settings Properties – Basic Tab. If "Changes pending" is true, click Activate changes in the IP commands menu, as explained in Configuring BACnet/IP Controller IP Network Settings For EcoStruxure Building Operation version 4.0.3 or later, a new EBO Workstation command named Export device identifying information is available. It is found in the main context menu of SpaceLogic RP Series controllers and allows the user to save an xml file that can later be imported into the SpaceLogic Certificate Configuration Tool to aid in the efficient configuration of SpaceLogic controllers within the tool. The user may select one or more RP Series controllers when executing the command. Refer to: Exporting Device Information to the SpaceLogic Certificate Configuration Tool  
View full article
Kirk Mahmoud_Sayed Kirk
‎2022-10-05 03:59 AM

Last Updated: Administrator CraigEl Administrator ‎2024-09-18 05:21 PM

Labels:
  • EcoStruxure Building Operation
2633 Views

Red Dot Report shown when viewing WebReports Reports Tree

Issue When viewing WebReports one of the reports has a red dot Product Line EcoStruxure Building Operation Environment Building Operation WebReports Cause Need to understand what the red dot indicates Resolution When viewing the list of WebReports and the reports show one or more with a Red Dot, this designates the report as a dashboard report.  A dashboard report is a report that processes fixed or predefined filtering criteria to generate report output. Unlike prompted reports, dashboard reports process the report output based on the predefined filtering criteria and generate the report output when you select the report.  It is not necessary to enter filtering criteria or click the Run button to generate the report. Please see Dashboard Reports for additional information.
View full article
Picard Product_Support
‎2018-09-11 06:15 AM

Last Updated: Sisko GavinHe Sisko ‎2024-09-17 05:49 AM

Labels:
  • EcoStruxure Building Operation
1419 Views

Reports Tree not shown when logging in to Web Reports

Issue When logging in to Web Reports, the "Reports Tree" to the left is not shown, and an error message is shown stating that login has failed for the user "NT AUTHORITY\IUSR". Product Line EcoStruxure Building Operation Environment Building Operation WebReports Cause This is a result of not following the Web Reports installation guide.  The SQL Server must be installed with an instance name, and the SQL Server must be started by the user "SYSTEM". Resolution There are two solutions to this issue: Reinstall the SQL Server and Web Reports following the installation guide Use the SBO Reports Agent Config tool on the Community to give access to the 'NT AUTHORITY\IUSR' Alternatively for a more in-depth answer consult How to Fix Login Failed For User NT AUTHORITY IUSRS to add the user "NT AUTHORITY\IUSR" to the SQL Server
View full article
Picard Product_Support
‎2018-09-11 01:45 PM

Last Updated: Sisko GavinHe Sisko ‎2024-09-17 05:33 AM

Labels:
  • EcoStruxure Building Operation
2041 Views

Remote Factory Reset of SpaceLogic and EasyLogic devices

Issue Remote Factory Reset of SmartX IP controller MPX RPC IPIO Product Line EcoStruxure Building Operation Environment Building Operation Multi-purpose Controller Building Operation Multi-purpose VAV Building Operation Room Controller (RPC) Building Operation EasyLogic RP-C Building Operation EasyLogic RP-V Building Operation EasyLogic RP IO Expansion Module Building Operation EasyLogic MP-C Cause From v3.1 there is a facility to remotely Factory Reset a SpaceLogic BACnet/IP devices (formerly known as SmartX) and EasyLogic BACnet MS/TP devices. A quick look at the process and what versions of SmartX controller firmware are required Resolution Remote Factory Reset fails if the Controller is at v2.00. Remote Factory Reset operates correctly if the Controller is at v3.00 or higher. A Remote Factory Reset on a Controller with Static IP is best avoided. Although a Factory Reset is now possible, it should not be considered standard work process, but it shows that using DHCP serving of IP addresses does have advantage if a factory reset is required.
View full article
Dave_Shore Schneider Alumni (Retired)
‎2020-04-28 12:10 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-09-13 03:54 AM

Labels:
  • EcoStruxure Building Operation
6938 Views

Extending EBO Zigbee Wireless Mesh Using Repeaters

Issue When a SED-TRH-G-5045 sensor is positioned outside the range of the main EBO Zigbee wireless mesh, what is the recommended method or product to extend the wireless coverage? Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Cause The SED-TRH-G-5045 is a Zigbee pro sleepy end device. Resolution Any Zigbee router within the system can function as a repeater to extend the radio communication. The router should be positioned within the radio range of the sensor and within the range of the RPx or another router. If a Zigbee device is powered by mains, it typically operates as a router. While there are currently no SE products designed solely with "repeater capability," several SE products possess router capabilities in addition to other capabilities, SE8000 SpaceLogic room controller Wiser plug CCTFR6500 Wiser Power Micromodule CCTFR6730 Wiser Room Thermostat with display CCTFR6400 or CCTFR6401. We have not officially tested any 3rd party Zigbee routers, however the IKEA TRÅDFRI repeater is known to work effectively.
View full article
Kirk MikaelKrantz Kirk
‎2024-09-11 06:21 PM

on ‎2024-09-11 06:21 PM

Labels:
  • EcoStruxure Building Operation
  • Field Devices
1187 Views

Screen Brightness Issue on White TRCs

Issue The first batch of White TRCs (produced in 24H1) could appear too bright in some low-light level situations. All future batches (post 24H1) do not have the issue. See the precise list of affected serial numbers in the appendix section below. Product Line EcoStruxure Building Operation Environment SpaceLogic Touchscreen Room Controller Cause The housing color is set in the device’s manufacturing configuration to tell it what color the screen bezel is (black or white). White TRCs produced with an incorrect housing color will read a higher value for light level. This has a direct impact on the backlight dimming levels, and the only effect will be the screen staying brighter in dark rooms. Resolution Customers experiencing brightness issues may simply adjust the backlight brightness parameters to a lower value, which are configurable in the TRC configuration screens and via BACnet/Modbus. This would reduce the overall brightness of the devices immediately, without fixing the housing color. We recommend going with a permanent fix, by setting the housing color via the USB port. The steps to fix this permanently would be: Connect USB-C cable to TRC Log in as an administrator into the TRC’s configuration screens (to enable USB connection) Open a terminal app like hyperterm or putty, with settings: Speed (baud): 115200bps Data bits: 8 Stop bits: 1 Parity: None Paste in the command: #001000061009FE00009C! Device responds: #000E00071009FE0051! To confirm or test, paste in the command: #000C00001009FEE8! Device responds: White housing: #001200011009FE000000F9! Black housing: #001200011009FE000001FA! Examples Below is an example of 4 white TRCs: The two (2) outermost devices are too bright (leftmost and rightmost white TRCs). The two (2) devices in the middle have been corrected to show adequate brightness. Appendix Since the Touch Room Controller’s serial number includes the date code, knowing whether a unit is impacted is very straightforward. Follow these instructions to determine if the unit of interest is impacted: Retrieve the serial number from the unit you suspect has the incorrect housing color. Example: FL24075TRC00002 Examine the serial number date code, wrapped between the “FL” and “TRC” substrings. Example: 24075 Decrypt the date code, using this logic: 24: year 2024 07: week 07 of 2024 5: day 5 of week 7 of 2024 If the date code is between the values 24074 and 24285, the product is impacted. Products outside of this date code range are not impacted, and no fix to housing color will be needed.
View full article
Admiral StephenYang Admiral
‎2024-09-10 11:23 AM

Last Updated: Administrator CraigEl Administrator ‎2024-09-10 07:04 PM

Labels:
  • EcoStruxure Building Operation
688 Views

VPAT or statement of accessibility for EcoStruxure Building Operation

Issue Required a VPAT (Voluntary Product Accessibility Template) or statement of accessibility for EcoStruxure Building Operation. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Cause The Voluntary Product Accessibility Template (VPAT) is a document that evaluates how accessible a particular product is according to the Section 508 Standards. It is a self-disclosing document produced by the vendor which details each aspect of the Section 508 requirements and how the product supports each criterion. VPATs are used by buyers to determine how accessible a product is and where any potential deficiencies are. They are required by some buyers before a purchase is made. More Information can be found from the below public links: Section 508 of the Rehabilitation Act of 1973 Voluntary Product Accessibility Template (VPAT) Overview of Technologies and Formats WHAT IS A VPAT AND HOW IS IT USED? Resolution Schneider Electric does not have a VPAT document for EcoStruxure Building Operation.
View full article
Admiral StephenYang Admiral
‎2024-09-10 11:01 AM

on ‎2024-09-10 11:01 AM

Labels:
  • EcoStruxure Building Operation
601 Views

EcoStruxure Building Operation integration to Network 8000 - Supported Network 8000 devices

Issue Define what Network 8000 devices that can be integrated with EcoStruxure Building Operation. Product Line EcoStruxure Building Operation, TAC I/A Series Environment EcoStruxure Building Operation Automation Server version 1.2 until and including 3.2 Network 8000 Cause Need to know the supported devices for a Network 8000 to EcoStruxure Building Operation upgrade.  Resolution EcoStruxure Building Operation supports the following Network 8000 LCM devices: LCM EcoStruxure Building Operation supports the following Network 8000 ASD devices: Microzone II MicroFlo II LIM PEM  The following Micronet 2000 products are supported: MN-FLO MN-FLO3T MN-HPFC MN-ASDI  The following Network 8000 products are not supported in EcoStruxure Building Operation: CCL GCM LNC SIM GCM PLC Note: EcoStruxure Building Operation version 4.0 (EBO 2022) and higher are not supported
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Last Updated: Guinan RandyDavis Guinan ‎2024-09-09 06:12 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
2132 Views

Remove Unknown Embedded Demo License

Issue How to remove an unknown Embedded Demo License Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium (AS-P) Device Administrator v4.0.5 (EBO 2022) and below Cause The Embedded Demo Licenses are handled from the Device Administrator software. However, if the installed Embedded Demo License in the SpaceLogic servers does not comply with the file in the Device Administrator, the installed Demo License could not be removed. Resolution Instructions shown in the video below are for EBO 2022 (v4.0.5) and below. In the later releases EBO 2023 (v5.x) and above, a feature now allows the Demo licenses to be returned from selected servers.  See WebHelp topic Returning All Demo Licenses from the Selected SpaceLogic Automation Servers  For any License activations/returns to occur, there must be a trusted state (Certificate State) between the server and Device Administrator. Ensure that this is in place before attempting either resolution. For more info, see Certificates Managed using Device Administrator   If this function does not work, you can attempt the manual file name manipulation described below.    To check the name of the installed Embedded Demo License, log in to the SpaceLogic servers from Workstation. Navigate to System, LicenseManager, LicensingMetadata, ClientMetadata, Product 0. In ProductID, you will see the filename of the actual file.   Rename a Demo license file and import it into Device Manager to uncheck the selected Demo License file.   At the end of this session, you will be able to: Remove Unknown Demo License in SpaceLogic servers        
View full article
Kirk MikaelKrantz Kirk
‎2022-11-24 01:49 AM

Last Updated: Administrator CraigEl Administrator ‎2024-09-06 12:39 AM

Labels:
  • EcoStruxure Building Operation
2440 Views

SpaceLogic Sensors missing tabs

Issue Multiple MP-Vs have SpaceLogic Sensors (formerly SmartX Sensors) connected, all with identical configurations.  Some are missing the Properties, Scene Configurations, Button and Scene Configuration tabs. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server Building Operation Room Controller (RPC)  Building Operation RP-V VAV Building Operation Multi-purpose Controller Building Operation Multi-purpose VAV Cause Delete the sensor and add it back, which takes a long time to execute for all sensors Resolution In WorkStation, in the System Tree pane, expand the BACnet Interface and the IP network. Click the BACnet/IP controller device. In the Actions menu, point to Device, Advanced, and then click Restore optional properties. In the Actions menu, point to Device and click Download all objects 
View full article
Lt. Commander Ramaaly Lt. Commander
‎2022-05-12 05:25 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-09-05 07:38 AM

Labels:
  • EcoStruxure Building Operation
1302 Views

SpaceLogic Sensor SXWS HMI references

Issue A large room has multiple SpaceLogic Sensors SXWS (formerly SmartX sensor) and the temperature setpoint is changed in one of them. Is it possible for the temperature setpoint to be changed in the other sensors?  Product Line EcoStruxure Building Operation Environment Building Operation SpaceLogic Sensor Building Operation Room Controller (RPC) Building Operation RP-V VAV Cause In EBO (EcoStruxure Building Operation) version 3.1 a functionality called HMI references is introduced which can be used in this case. This new functionality makes it possible to have bi-directional bindings for the following value types in the RP series controller Blind position: analog value Occupancy override: digital value Fan speed: multistate value HVAC mode: multistate value Light level: analog value Selected scene: analog value Blind slat angle: analog value Temperature setpoint: analog value Resolution This is done by creating a value of the value types supporting the HMI reference functionality in the Application folder of the RP IP controller which the SpaceLogic Sensors are connected to. Then bind that value to the Display properties of each SpaceLogic Sensor       For example an Analog value is created in the Application folder of the RP-C and then bound to the Display Temperature Setpoint property of each connected SpaceLogic sensor. If then changing the Temperature setpoint from the RP-C that will be distributed to all SpaceLogic Sensors. But also if changing the Temperature setpoint in any of the SpaceLogic Sensors that value will be distributed to the other SpaceLogic Sensors and the RP-C.   To see an example on how this can be done please see video:  
View full article
Janeway Jonas_Brissman Janeway
‎2022-02-10 04:21 PM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2024-09-05 07:35 AM

Labels:
  • EcoStruxure Building Operation
1939 Views

Upgrade path from version 1.0 to current version

Issue Upgrade path from version 1.0 to a current version Product Line EcoStruxure Building Operation Environment SmartStruxure Building Operation versions 1.0, 1.1, 1.2, 1.3, 1.4, 1.5, 1.6, 1.7, 1.8, 1.9 EcoStruxure Building Operation versions 2.0, 3.0, 3.1, 3.2, 3.3 (limited), 4.0, 5.0, 6.0 Cause Upgrade path from version 1.0 to current - version Important - The upgrade process is sequential, for example, 1.1 to 1.2 to 1.3 to 1.4 From v1.9, non-sequential upgrades are possible  The primary released versions were, Release Note Dates (approximate) 1.0.0.161   1.1.0.362 Dec 2011 1.2.0.767 July 2012 1.3.0.938 Nov 2012 1.3.0.10100 SP1   1.3.0.20011 SP2   1.4.0.4020 Sept 2013 1.4.1.68-73 Oct 2013 1.5.0.532 July 2014 1.6.0.250 (RC) Dec 2014 1.6.1.5000 Feb 2015 1.6.2.27 Maintenance Release Jun 2016 see TPA-SBO-16-0003 1.7.0.255 (RC) July 2015 1.7.1.89 Oct 2015 1.7.2.29 Maintenance Release Jun 2016 see TPA-SBO-16-0003 1.8.0.244 (RC) Mar 2016 1.8.1.79-87 Jun 2016  1.9.1.95 Apr 2017   1.9.2.45 Maintenance Release Oct 2017  - See release note 1.9.3.24 Maintenance Release April 2018  - See release note 1.9.4.29 Maintenance Release April 2019  - See release note 2.0.1.130 & 135 June 2018 (130(License, WS, Reports Server) 135 - Server (AS, ES, EC)) - See release note 2.0.2.67 Maintenance Release Sep 2018  - See release note 2.0.3.45 Maintenance Release Dec 2018  - See release note 2.0.4.83 Maintenance Release June 2019  - See release note 3.0.1.104 May 2019  - See release note 3.0.2.33 Maintenance Release July 2019  - See release note 3.0.3.11 Maintenance Release Aug 2019  - See release note 3.0.4.43 Maintenance Release Dec 2019  - See release note 3.1.1.312 Dec 2019  - See release note 3.1.2.29 Maintenance Release Mar 2020  - See release note 3.2.1.630 Aug 2020  - See release note 3.2.2.61 Maintenance Release Nov 2020  - See release note 3.2.3.59 Maintenance Release Mar 2021  - See release note 3.3.1.59L Limited distribution release Feb 2021 - intended for specific feature compatibility with some hardware or applications - See release note EBO 2022 (4.0.1.86) Dec 2021 - This version follows v3.x, and reflects a new naming convention focused on release year for clarity - See release note EBO 2022 (4.0.2.559 & 562) Maintenance Release Apr 2022 - WorkStation Hotfix and License Admin 4.0.2.562, others 4.0.2.559, see revised release note EBO 2022 (4.0.3.176) Maintenance Release Jul 2022 - See release note EBO 2023 (5.0.1.86) Dec 2022 - See release note EBO 2024 (6.0.1.93) Mar 2024 - See release note Resolution It is most important to read the Release Notes and System Upgrade Reference Guide for each version you are upgrading to, as there are some special notes that only apply to some installation types. Click Here for Release Notes Click Here for Upgrade documentation The Minimum upgrade path would be as below (See Release Notes for any special instruction) 1.0.0.161 1.1.0.362 See StruxureWare Building Operation v1.0 to v1.1 upgrade issues Appendix A 1.1.0.1225 See Appendix A 1.2.0.767 See Appendix A This version can be avoided by using 1.2.0.1412 if possible 1.2.0.2207 (Hotfix) Available from PSS See also Appendix A 1.3.0.938 See also Appendix A 1.3.0.10100 (SP1) (needed if runtime compatibility is required during upgrade) 1.4.0.4020 or 1.4.1.68 (Only needed if runtime compatibility is required during upgrade) See Upgrading Automation Servers from 1.3 to 1.4 1.5.0.532 1.6.1.5000 See Upgrade to 1.5.0 or 1.6.0 fails 1.7.1.89 1.8.1.87 See Product Announcement 00471 Pre-Upgrade LON Add-On 1.7.1 to 1.8.x 1.9.1.95 Possible to upgrade directly from v1.5, but carefully study the release notes and upgrade instructions Option to 1.9.2.45 Upgrade options more limited with this version, only from v1.7.2, see the release note Option to 1.9.3.24 Upgrade options more limited with this version, only from v1.7.2, see the release note Option to 1.9.4.29 Upgrade options more limited with this version, only from v1.7.2, see the release note 2.0.1.130/135 Possible to upgrade directly from v1.5, but carefully study the release notes and upgrade instructions. NOTE the new License structure for v2.0. 3.0.1.104 Possible to upgrade directly from v1.8, see the table in "System Upgrade Reference Guide" (3.0.1 System Upgrade Overview), but carefully study the release notes and upgrade instructions. NOTE the new Licenses for v3.0. 3.1.1.312 Possible to upgrade directly from v1.8 See Release notes and upgrade documents for full details 3.2.1.630 AS Classic not supported, Win 7 and Win server 2008 not supported 3.3.1.59L Limited distribution release - intended for specific feature compatibility with some hardware or applications, see release note for details. If you do not require the specific features outlined in this Release Notes, it is recommend installing EcoStruxure Building Operation 3.2.x instead EBO 2022 (4.0.1.86 and later) The following protocols, objects, and devices are not supported in EcoStruxure Building Operation 4.0 or higher: I/NET, Sigma, MicroNet, NETWORK 8000 ASD and LCM. A multi-version system supports I/NET, MicroNet, NETWORK 8000 ASD and LCM on automation servers and Sigma on an enterprise server, running an earlier version than 4.0. Report Server/WebReports is not supported in EcoStruxure Building Operation 4.0 or higher. See release notes for details. EBO 2023 (5.0.1.128 and later) New SpaceLogic and Easylogic Controller support, External Storage support for MS SQL, Some support for IPv6, BACnet protocol rev.16, Virtualized Automation Server - Edge Server added,   See release notes for details. EBO 2024 (6.0.1.93 and later) Added New Software Assurnace, Sustainability Pack, EBO Enterprise Server and Enterprise Central for Linux, OPC UA Client Support, Modbus2 Support, Visual Programming for Function Block, XLSX Report, and Touch Room Controller Support. See release notes for details. Appendix A - Upgrading from Specific 1.x Builds Upgrade from V1.0.0.XXXX to V1.3 (via V1.1 and V1.2) Upgrade from 1.0.0.XXXX to 1.1.0.1225 Upgrade from 1.1.0.1225 to 1.2.0.1412 (Do not use 1.2.0.767) Upgrade from 1.2.0.1412 to 1.3 Upgrade from V1.1.0.XXXX to V1.3 (via V1.2) Upgrade from 1.1.0.XXXX to 1.2.0.1412 (Do not use 1.2.0.767) Upgrade from 1.2.0.1412 to 1.3 Upgrade from V1.2.0.767 to V1.3 Apply hotfix 1.2.0.2207 Upgrade from 1.2.0.2207 to 1.3 NOTE: These hotfix builds are not available for download from the Extranet site, you will need to contact Product Support and request them
View full article
Picard Product_Support
‎2021-02-16 12:31 AM

Last Updated: Admiral StephenYang Admiral ‎2024-08-27 10:24 AM

Labels:
  • EcoStruxure Building Operation
16223 Views

Base plate for EBO I/O modules

Issue Do all StruxureWare I/O modules use the same base? Product Line EcoStruxure Building Operation Environment Building Operation I/O Module Cause Want to select the correct I/O module base Resolution Yes all Building Operation I/O modules use the same SXWTBIOW110001 terminal base.
View full article
Picard Product_Support
‎2018-09-06 10:40 AM

Last Updated: Janeway Jonas_Brissman Janeway ‎2024-08-22 06:42 AM

Labels:
  • EcoStruxure Building Operation
1200 Views
  • « Previous
    • 1
    • …
    • 4
    • 5
    • 6
    • …
    • 93
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of