StruxureWare Building Operation 1.3/1.3 SP1 reports "The upper limit must be greater than or equal to the lower limit and indicates the import is complete".
  • StruxureWare Building Operation 1.3/1.3 SP1 reports "The upper limit must be greater than or equal to the lower limit and ind...
  • CraigEl
    CraigEl
  • sesa139513
    sesa139513
  • Gary
    Gary
‎2018-09-11 04:50 AM
Last Updated: Administrator CraigEl Administrator ‎2025-10-25 07:55 PM
Importing a VisiSat pointslist StruxureWare reports a limit issue and suggests the import is complete.
EcoStruxure Building Operation, Satchwell MicroNet
On one of the VisiSat points being import,  the alarm limits have been incorrectly set.
Although StruxureWare Building Operation 1.3/1.3 SP1 reports that the import completed in X minutes and X second, the import would have failed to complete due to the stated issue.
Unfortunately the reported limit issue can effect 100 points or just the 1 point.
The specific point or points identity is not highlighted in the trace file.
Locate the point and check the alarm limits are entered correctly. The example below show the upper limit and lower limit are reversed.
Change it so the upper limit is above the lower limit.