Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Using Zigbee VingCard Network and Zigbee Standard Security Network on the Same RP-C

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using Zigbee VingCard Network and Zigbee Standard Security Network on the Same RP-C
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • MikaelKrantz
    MikaelKrantz

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
125 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using Zigbee VingCard Network and Zigbee Standard Security Network on the Same RP-C

Kirk MikaelKrantz Kirk
‎2025-10-23 06:44 AM

Last Updated: Administrator CraigEl Administrator ‎2025-10-23 05:48 PM

Issue

You need to integrate both:

  • VingCard lock
  • MTH-G-5045 / WDC-G-5045 window and presence contacts

…into a Zigbee network on the same RP-C (Room Controller) device.

Product Line

EcoStruxure Building Operation.

Environment

  • Building Operation Room Controller (RPC) 24 V.
  • Zigbee

Cause

When performing device discovery:

  • If using Zigbee VingCard Network, the MTH-G-5045 / WDC-G-5045 devices are not found.
  • If using Zigbee Standard Security Network, the MTH-G-5045 / WDC-G-5045 devices are found.

This occurs because the two Zigbee networks are fundamentally different in protocol and device compatibility.

Resolution

It is not possible to use both Zigbee VingCard Network and Zigbee Standard Security Network simultaneously on the same RP-C device.

You must choose one Zigbee network type per RP-C:

  • If you need VingCard lock integration, use Zigbee VingCard Network.
  • If you need MTH-G-5045 / WDC-G-5045 integration, use Zigbee Standard Security Network.

⚠️ Important: These networks are mutually exclusive on a single RP-C. Consider deploying separate RP-C devices if both network types are required in the same installation.

Labels (2)
Labels:
  • EcoStruxure Building Operation
  • Field Devices
Tags (1)
  • Find more articles tagged with:
  • MikaelKrantz25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore