LonWorks Device Not Discovered During Discovery Process

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • LonWorks Device Not Discovered During Discovery Process
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterLarsen
    PeterLarsen

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
230 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

LonWorks Device Not Discovered During Discovery Process

Spock PeterLarsen Spock
‎2025-10-21 04:54 PM

on ‎2025-10-21 04:54 PM

Issue

When upgrading a TAC Vista site to EcoStruxure Building Operation (EBO), LonWorks devices may not be discovered during the device discovery process in the AS-P.

Product Line

EcoStruxure Building Operation

Environment

Building Operation Automation Server Premium (AS-P).

Cause

This issue typically occurs when the original TAC Vista database was configured using a third-party network management tool such as LonMaker or NL220. These tools can assign a custom domain ID to the LonWorks network.

  • Default Domain ID in TAC Vista: 1/11
  • Default Domain ID in EBO: 1/254

If the domain ID used during the initial setup differs from EBO’s default, the AS-P will not detect devices on that domain.

Resolution

  1. Identify the Current Domain ID
    • Use the existing TAC Vista database to determine the domain ID configured on the LonWorks devices.
    • Alternatively, use NodeUtil to identify the domain ID. Refer to the article: Finding LON devices under a different domain length with NodeUtil 
  2. Configure a Spare AS-P
    • Set the domain ID on a spare AS-P to match the existing domain ID used in the site.
    • For guidance, see: How to locate and change the LonWorks domain ID 
  3. Discover Devices
    • Use the spare AS-P (now configured with the matching domain ID) to perform device discovery.
    • The previously undetected devices should now appear and be accessible.
  4. Decommission Devices
    • In the AS-P, navigate to the Actions menu for each discovered device.
    • Select Decommission to revoke the device’s address and stop communication.
  5. Reintegrate Devices
    • After decommissioning, re-add the devices to the LonWorks network.
    • They should now be discoverable by an AS-P configured with the standard EBO domain ID (1/254).
Labels (2)
Labels:
  • EcoStruxure Building Operation
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • PeterLarsen25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore