Issue
In EcoStruxure Building Operation (EBO) version 6 and later, users may encounter a persistent Modbus Network Offline alarm, even when all Modbus devices under the network are online.
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Enterprise Server
- Building Operation Automation Server Premium(AS-P)
- Building Operation Automation Server Bundled (AS-B)
Cause
The Modbus communication architecture was restructured between EBO versions 5 and 6.
- In EBO version 5, the system could generate alarms for the Modbus network itself being offline.
- In EBO version 6 and later, network-level offline alarms are deprecated. Alarms are now only generated at the device level, not for the network.
If a site is upgraded from version 5 to 6, any existing Modbus network offline alarms will persist, but EBO will no longer monitor or clear them, as it no longer tracks network-level status.
Resolution
To remove the obsolete Modbus network offline alarm in EBO version 6, you have two options:
-
Hide the Alarm
- Since the alarm is no longer relevant in version 6, you can simply suppress or hide it from the alarm list.
-
Delete and Recreate the Modbus Network
- This method ensures complete removal of the alarm. Important: Ensure you have a verified backup before performing these steps:
- Export the Modbus network configuration.
- Delete the network using the “Keep Bindings” option.
- Re-import the network configuration.
- This method ensures complete removal of the alarm. Important: Ensure you have a verified backup before performing these steps: