Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 4
    • 5
    • 6
    • …
    • 501
  • Next »

Can Niagara R2 Send a Soft or Hard Reboot Command to MNB Controllers?

Issue Users want to know if a Niagara R2 UNC-520 can send a soft or hard reboot command to MNB controllers without using additional tools. Product Line TAC IA Series Environment Niagara R2 MNB controllers Cause Niagara R2 does not support sending reboot commands directly to MNB controllers. This limitation exists because reboot functionality is not exposed through the Niagara R2 framework for these devices. Resolution A reboot command cannot be sent from a Niagara R2 station to an MNB controller. To perform a soft or hard reboot, use the WorkPlace Commissioning Tool. There is no alternative method within Niagara R2 for this operation.
View full article
Picard Product_Support
‎2018-09-06 10:17 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 11:05 PM

Labels:
  • TAC IA Series
1165 Views

Unable to Log into JACE-603/645 Using I/A Series R2 Admin Tool

Issue Users cannot log into JACE-603 or JACE-645 hardware using the I/A Series R2 Admin Tool. Product Line TAC IA Series Environment JACE-603 JACE-645 Cause The JACE-603 and JACE-645 controllers are based on the QNX platform and do not support host-level configuration via the R2 Admin Tool. These devices require platform configuration through Niagara G3 tools when licensed accordingly. Resolution Use I/A Series G3 Workbench 3.6.47 or later for all host (platform) configuration of JACE-603 and JACE-645. For integration with I/A Series R2, refer to the Retrofit Board Niagara R2 Install and Startup Guide included with I/A Series G3 (document: docRetrofitBoardR2) version 3.6.47 or later. Supported revisions: R2: 2.301.535 or higher G3: 3.6.47 or higher
View full article
Picard Product_Support
‎2018-09-06 10:13 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 11:02 PM

Labels:
  • TAC IA Series
1005 Views

Does oBIX Service in I/A Series R2 Require Web Services License?

Issue Clarification on whether the oBIX service in I/A Series R2 requires the web services license feature to operate. Product Line TAC IA Series Environment I/A Series R2 oBIX Cause There is confusion regarding licensing requirements for enabling oBIX functionality in I/A Series R2 stations. Resolution The web services license feature (webUi) is not required to run the oBIX service in an I/A Series R2 station. However, the R2 license must include the obix feature for the service to function. Example feature line in the R2 license: features=coreRuntime;bacnet;lonworks;obix If the license does not include the obix feature, the service will not operate.
View full article
Picard Product_Support
‎2018-09-06 10:11 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 10:58 PM

Labels:
  • TAC IA Series
1014 Views

Error Code 80044E34 during Equalization

  Issue Utilizing Equalization and an error code appears, indicating the File Master is unable to add an article (Error Code: 80044E34). Product Line TAC I/NET Environment I/NET Seven Cause The file InetEqzCr.dll needs to be manually registered. Resolution Open the Windows Command Prompt (CMD). Change the directory to: C:\Program Files\Inet Seven\ Run the following command: regsvr32 ineteqzcr.dll Close or exit the Command Prompt. Restart I/NET. Demote all clients and the File Master. Re-promote the File Master and then the clients. Equalization should now work correctly. Warning Ensure you run the command with administrative privileges. Incorrect registration may cause system instability.
View full article
Picard Product_Support
‎2018-09-06 03:08 PM

Last Updated: Picard RobertAndriolo Picard ‎2025-12-04 07:49 PM

Labels:
  • TAC INET
1298 Views

I/A Series R2 BACnet Alarm Fails with E_BACNET_UNRESOLVED_DEVICE_ADDRESS

Issue An I/A Series R2 station fails to send BACnet alarms to a third-party system. The error log shows: tridiumx.bacnet.BACnetException: E_BACNET_UNRESOLVED_DEVICE_ADDRESS . Product Line TAC IA Series Environment I/A Series R2 BACnet Cause The station does not contain a BACnet device object for the target device. Without this object, the system cannot resolve the device address required for alarm routing. Resolution Ensure the station includes the BACnet device object for the target device. This object provides essential details such as IP address and device instance. Verify the target device is online and capable of receiving BACnet alarms. Use BACnetUtility and the learnNetwork command to create BACnet device objects for all target devices. Refer to the I/A Series R2 BACnet Integration Reference Guide (section: Configuring for BACnet Alarm Generation) for detailed steps. Additional Notes: Only Niagara objects exposed as BACnet objects (AIs, AOs, BIs, BOs, MSIs, MSOs) can generate BACnet alarms. Alarms are not regenerated if the BACnet device is offline during transmission. Enterprise Server cannot generate alarms for subordinate stations; each station must be configured individually.
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 06:17 PM

Labels:
  • TAC IA Series
1471 Views

Niagara R2 Enterprise Server IP Address Change Not Retained in Admin Tool

Issue When attempting to modify the IP address of a Niagara R2 Enterprise Server using the Admin Tool, the new IP address values entered in the Network Settings tab are not saved. Product Line TAC IA Series Environment Niagara R2 Cause The Admin Tool’s Network Settings tab for a server station is read-only. Updating the IP address in Windows is sufficient; changes in Admin Tool are not required and will not persist. Resolution Configure the new IP address directly in the Windows network settings. Do not attempt to update the IP address in the Admin Tool Network tab, as it does not store changes for server stations. Treat the Network tab in Admin Tool as informational only for Enterprise Server configurations.
View full article
Picard Product_Support
‎2018-09-06 10:05 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 06:14 PM

Labels:
  • TAC IA Series
1287 Views

Niagara R2 LON-USB Adapter Configuration for LON2 Interface

Issue A LON-USB adapter is configured as LON2 on a Windows laptop. Attempts to change its address to LON1 have failed. The Niagara R2 station running the LonWorks Service defaults to LON1. Can the station use LON2 instead? Product Line TAC IA Series Environment Niagara R2 station Windows laptop with LON-USB adapter Cause The LonWorks Service in Niagara R2 defaults to LON1 for the interface. The inability to modify the adapter address prevents direct use of LON2 without configuration changes. Resolution Open the Admin Tool in Niagara R2. Navigate to the Installation tab and locate the drivers.properties file. Modify the line: lon.deviceName=LON1 to: lon.deviceName=LONx where x is the desired port number (e.g., LON2). Save the changes and restart the station for the new configuration to take effect. 
View full article
Picard Product_Support
‎2018-09-06 10:04 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 06:12 PM

Labels:
  • TAC IA Series
1513 Views

Niagara R2 LON and Serial Tunnel Client Port Configuration

Issue What port is used for the Niagara R2 LON and Serial tunnel clients? Product Line TAC IA Series Environment Niagara R2 Cause Network configuration changes require port forwarding for tunneling. The correct port must be identified to allow communication through routers and firewalls. Resolution The LON and Serial tunnel clients use the same port as the UNC station. Default port: 80 If the station port is modified, the tunnel clients will use the updated port number.
View full article
Picard Product_Support
‎2018-09-06 09:59 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 06:08 PM

Labels:
  • TAC IA Series
1750 Views

FieldServer LON Device Binding Fails in Niagara R2 – Service Type Error

Issue A FieldServer device was successfully commissioned in a Niagara R2 station using LON. However, the Lon Link Manager shows all related bindings with a status of service_type_error , and none of them will bind. Product Line TAC IA Series Environment Niagara R2 station with LON integration using FieldServer device Cause Most FieldServer devices using LON require a different service type than the default standard binding type. Using the incorrect service type prevents successful binding. Resolution Change the binding type from standard to critical in the Lon Link Manager, then attempt to bind the devices again.
View full article
Picard Product_Support
‎2018-09-06 09:58 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 06:06 PM

Labels:
  • TAC IA Series
1267 Views

Reinstalling Niagara G3 on JACE-NXT Previously Running Niagara R2

Issue Can a JACE-NXT controller that was originally installed with Niagara R2 be cleared and re-installed with Niagara G3 for a site upgrade? Product Line TAC IA Series Environment Niagara R2 Niagara G3 JACE-NXT Cause The site is upgrading from Niagara R2 to Niagara G3, requiring confirmation of compatibility and installation steps for JACE-NXT hardware. Resolution Yes, it is possible to reinstall Niagara G3 on a JACE-NXT previously running Niagara R2: Connect via Remote Desktop to access the internal Windows desktop of the JACE-NXT. Install Niagara G3 as you would on any Windows-based system. Check storage type: If the JACE-NXT has a hard drive, there is sufficient space for G3 installation. If it has a flash drive, space is limited. You may need to completely remove Niagara R2 before copying and installing G3 files. Purchase and apply a Niagara G3 license for the unit. Note: Tridium does not provide an upgrade service for this process. It is a manual, do-it-yourself task.
View full article
Picard Product_Support
‎2018-09-06 09:58 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 06:03 PM

Labels:
  • TAC IA Series
1306 Views

Niagara R2 ASD Integration – Serial Tunneling Works with Only One Service

Issue In a Niagara R2 station with two ASD services configured, serial tunneling only works for one service. Attempts to enable tunneling on both services fail. Product Line TAC IA Series Environment Niagara R2 version 522 or higher ASD integration with two ASD services Cause Niagara R2 does not support simultaneous tunneling for multiple ASD services. When tunneling is enabled on both, only the first ASD service establishes a tunnel connection. Resolution Enable tunneling on one ASD service at a time. If tunneling was previously enabled on both services, disable tunneling on the second service. Perform a station restart to apply changes.
View full article
Picard Product_Support
‎2018-09-06 09:55 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 06:00 PM

Labels:
  • TAC IA Series
961 Views

JACE-645 R2 Time Zone Change Not Reflected in Station

Issue Changing the time zone in G3 Platform Administration does not update the time zone in the I/A Series R2 station running on a JACE-645. Product Line TAC IA Series Environment JACE-645 running I/A Series R2 G3 Platform Administration used for configuration Cause The time zone setting in G3 Platform Administration does not automatically update the time.properties file for the R2 station on the JACE. Resolution Manually update the time.properties file on the JACE: In G3 Platform, open File Transfer Client and navigate to /niagara/niagaraR2/sys . Transfer the time.properties file to your PC. Open the file in a text editor (e.g., Notepad), edit the time zone, and save changes. Transfer the updated file back to the JACE using File Transfer Client. Reboot the JACE and confirm the time zone change in the R2 station. 5. Open the station with R2 and confirm the time zone has been altered as desired.
View full article
Picard Product_Support
‎2018-09-06 09:45 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 05:56 PM

Labels:
  • TAC IA Series
1205 Views

ENGINE WATCHDOG TIMEOUT and App Failed on JACE-603/645 with I/A Series R2

Issue When starting an I/A Series R2 station on a JACE-603 or JACE-645 platform, the system displays ENGINE WATCHDOG TIMEOUT STACK DUMP and App Failed. Rebooting the station does not resolve the issue. Product Line TAC IA Series Environment I/A Series R2 I/A Series G3 JACE-603 JACE-645 Cause The failure occurs due to an improper implementation of JRE files required by the R2 mail service when the platform is commissioned with incompatible G3 distribution files. Resolution Perform a clean installation and commission the platform using I/A Series G3 version 3.6.47 distribution files. This ensures proper JRE compatibility and resolves the watchdog timeout issue.
View full article
Picard Product_Support
‎2018-09-06 09:38 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 05:52 PM

Labels:
  • TAC IA Series
1734 Views

R2 UNC Station Fails to Boot – Error: FATAL: Cannot boot station from sns java.lang.NoClassDefFoundError

Issue A Niagara R2 UNC station fails to start and displays the following error in the Standard Output window: FATAL: Cannot boot station from sns java.lang.NoClassDefFoundError: tridium/foundation/prism/Subscription Product Line TAC IA Series Environment R2 UNC Cause This error typically indicates corruption of the operating system or missing Java class definitions required for station boot. Resolution To recover the UNC: Reinstall the operating system (OS) on the UNC. Reinstall the Niagara R2 runtime environment (NRE) and required modules. Restore or redeploy the station after the OS and NRE are successfully installed.
View full article
Picard Product_Support
‎2018-09-06 09:37 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 05:48 PM

Labels:
  • TAC IA Series
1343 Views

Will Saving Changes to a Function Block Program Cause Output Fluctuations?

Issue When modifying a Function Block program in EcoStruxure Building Operation, will outputs cycle or fluctuate after saving changes? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Function Block Programming Cause Function Block programs process signals in cycles, passing values between connected blocks. Each block retains its last value in memory when changes are committed. Stable Output: If logic affecting the output remains unchanged and no Delay blocks are used, outputs typically remain stable. Fluctuating Output: Logic changes that directly impact output signals. Use of Delay blocks in control logic. Delay blocks reset to their default value upon saving, which can cause a one-cycle fluctuation in output. Resolution To prevent physical device damage during program changes: Apply software overrides by forcing output values on I/O modules. Use Hand/Auto/Off (HAO) controllers on output devices. These measures safeguard equipment and allow validation of logic changes after saving.
View full article
Picard Product_Support
‎2018-09-06 10:41 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-04 03:22 PM

Labels:
  • EcoStruxure Building Operation
1684 Views

JACE-645-R2 Fails to Learn BACnet Devices on MSTP Trunk – Error in Application Director

Issue The JACE-645-R2 controller does not learn BACnet devices on its MSTP trunk and displays the following error in the Application Director: devctl rx frame failed: No error java.lang.RuntimeException: mstp rcv failed at tridium.nre.qnx.mstp.QnxMstpDriver.rcvFrameJNI(Native Method) at tridium.nre.qnx.mstp.QnxMstpDriver.access$0(QnxMstpDriver.java) at tridium.nre.qnx.mstp.QnxMstpDriver$MstpTrunkListener.run(QnxMstpDriver.java:287) at java.lang.Thread.run(Unknown Source) Product Line TAC IA Series Environment JACE-645-R2 retrofit board (TRD-RB-645) G3 version 3.8.37 Cause The issue is caused by a problem with the platform drivers in G3 (version 3.8.37) that interface with R2, resulting in MSTP communication failure. Resolution Perform a clean installation using: G3 version: 3.6.47 Commissioning tool: 3.6.406 This resolves the MSTP driver compatibility issue and restores BACnet device learning functionality.
View full article
Picard Product_Support
‎2018-09-06 09:28 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-03 05:39 PM

Labels:
  • TAC IA Series
1848 Views

Identify MNL Controller Profiles and Versions Integrated with Niagara R2 or G3

Issue How to determine which MNL controllers (profile and version number) are integrated with a Niagara R2 or Niagara G3 station. Product Line TAC IA Series Environment Niagara R2 or G3 station with LonWorks integration Cause Users need a quick reference to confirm controller profiles and version numbers for compatibility and troubleshooting during integration. Resolution Use the LonWorks Device Manager in Niagara to list connected MNL controllers and cross-reference them with the table below: Controller Model Profile Version Notes MNLRF103 SIEBE 80:0:16:50:14:4:4:1 – MNLRF2 SIEBE 80:0:16:50:14:4:4:2 Version 2 MNLRF3 SIEBE 80:0:16:50:14:4:4:3 Version 3 MNLRH103 SIEBE 80:0:16:50:33:4:4:1 – MNLRH2 SIEBE 80:0:16:50:33:4:4:2 Version 2 MNLRH3 SIEBE 80:0:16:50:33:4:4:3 Version 3 MNLRR103 SIEBE 80:0:16:50:1e:4:4:1 – MNLRR2 SIEBE 80:0:16:50:1e:4:4:2 Version 2 MNLRR3 SIEBE 80:0:16:50:1e:4:4:3 Version 3 MNLRS1 SIEBE 80:0:16:50:1e:4:4:10 Satellite 1 MNLRS2 SIEBE 80:0:16:50:1e:4:4:11 Satellite 2 MNLRS3 SIEBE 80:0:16:50:1e:4:4:12 Satellite 3 MNLRS4 SIEBE 80:0:16:50:1e:4:4:13 Satellite 4 MNLRV2 SIEBE 80:0:16:50:a:4:4:9 Version 2 MNLRV3 SIEBE 80:0:16:50:a:4:4:a Version 3 MNOTPVA3 SIEBE 80:0:16:50:a:4:4:8 – SiebePEC SIEBE 80:0:16:50:1e:4:4:0 – Tip: Ensure the LonSiebe JAR file is installed in Niagara for proper profile recognition.
View full article
Picard Product_Support
‎2018-09-06 09:26 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-03 05:13 PM

Labels:
  • TAC IA Series
1827 Views

Niagara R2 BACnet Alarms: Sending and Acknowledging from G3 Server Console

Issue Can BACnet alarms generated in Niagara R2 be sent to and acknowledged from a Niagara G3 (AX) Server console? Product Line TAC IA Series Environment Niagara R2 UNC Niagara G3 ENS Cause Users need the ability to view and acknowledge BACnet alarms originating from Niagara R2 within a Niagara G3 console for integrated alarm management. Resolution This integration is possible by configuring the BACnetRecipient object in Niagara R2. Follow these steps: Refer to the “Configuring for BACnet Alarm Generation” section in the R2 BACnet Integration Reference Guide. Add the G3 station as a BACnet device under the R2 BACnetService. Add the R2 UNCs as BACnet devices under the G3 NiagaraNetwork. Tip: The most common oversight is failing to add the G3 station as a BACnet device in R2.
View full article
Picard Product_Support
‎2018-09-06 09:06 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-03 05:00 PM

Labels:
  • TAC IA Series
1533 Views

Active Directory Users Unable to Log In After EcoStruxure Building Operation Upgrade

Issue The EBO system previously operated as expected with Active Directory (AD) integration. Following an upgrade or hotfix, AD users are unable to authenticate and log in to the Enterprise Server (ES). Workstation login error: User account not associated with a group The Workstation Error when trying to login is: User account not associated with a group.     Error(s) message in ES trace log may include: WinES\server\nsp_servers\csc\accountaccess\source\AccountAccess.cpp(486) Workstation Error: User_Not_Associated_With_A_Group (0xc002a) in module Account_Access(28). Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Cause The Windows AD integration performance in EBO was improved since version 2022 by storing and comparing the SID for the AD-groups. During the upgrade from version 3.2.3 to EBO 2022 all EBO groups should have been updated with an AD-connected group SID. This was not done as the AD server was offline when doing the upgrade of the ES. Resolution To enable the legacy method of matching groups during logon, configure the following property: Steps: Open the ES.properties file, typically located at: C:\Program Files (x86)\Schneider Electric EcoStruxure\Building Operation 4.0\Enterprise Server\etc\config Add the following line: NspServer.Windows.Group.MatchByName = true Save the file and restart the Enterprise Server for the changes to take effect.     To take advantage of the Active Directory (AD) performance enhancements introduced in recent versions of EcoStruxure Building Operation, it is necessary to re-establish the link between AD groups and their corresponding EBO groups. Procedure: Open the relevant EBO group configuration. Locate the Windows group name property. Temporarily change its value to an empty string or any placeholder text. Re-enter the correct value, which should match the associated AD group name. Save the changes to complete the re-connection process.   Completing the previously described procedure ensures that the hidden External SID property for the EBO groups is correctly populated. This property was not updated during the upgrade because the process was performed without an active connection to the AD server.  
View full article
Janeway Jonas_Brissman Janeway
‎2023-02-07 08:38 PM

Last Updated: Commander Hernan_Urueña Commander ‎2025-12-03 04:33 PM

Labels:
  • EcoStruxure Building Operation
3116 Views

I/A Series R2/G3 Web Graphics Blocked or Security Warnings After Java Updates

Issue When accessing I/A Series R2 or G3 station graphics via a web browser, graphics fail to load or repeated Java security warnings appear. Common symptoms include: “Application Blocked by Security Settings” “Your security settings have blocked an application from running with an insecure or expired JRE.” Popups warning of security vulnerabilities for each Java applet. In Firefox: “This plugin has security vulnerabilities. Click here to activate the Java(TM) Platform SE Plugin.” Product Line TAC IA Series Environment I/A Series R2 I/A Series G3 Cause Oracle introduced stricter Java security controls starting with Java 7 Update 11 and further tightened them in Update 51 and later. Unsigned or self-signed applets are blocked by default. Known vulnerabilities in older Java versions trigger warnings. Browser plugins (IE, Firefox) enforce additional security prompts. Resolution Several approaches exist depending on site security policy: Option 1: Use Java Exception Site List (Recommended for Java 7u51+) Open Control Panel → Java → Security. Ensure Security Level is High (or Medium if required). Click Edit Site List… → Add. Add URLs for all I/A Series servers and controllers: http://<EnterpriseServer-host-or-IP> http://<UNC-or-JACE-host-or-IP> Confirm changes and restart browser. Option 2: Adjust Java Security Level (Legacy Workaround) For Java 7 Update 17 or earlier: Open Java Control Panel → Security tab. Set Security Level to Medium or Low (not recommended for high-security environments). Restart browser. Option 3: Downgrade Java (Last Resort) Testing shows Java 7u9 does not trigger prompts in IE9. Downgrade only if site policy allows and system is isolated. Option 4: Browser-Specific Workarounds Internet Explorer: Click Run on each security prompt. Firefox: If warning “This connection is untrusted”, click I Understand the Risks. To suppress plugin warnings (not recommended): Enter about:config in address bar. Set extensions.blocklist.enabled to false. Option 5: Clear Java Cache If graphics fail to load after bypassing warnings: Open Java Control Panel → General tab → Temporary Internet Files → Settings. Uncheck Keep temporary files on my computer. Click OK and restart browser.
View full article
Picard Product_Support
‎2018-09-11 04:26 AM

Last Updated: Administrator CraigEl Administrator ‎2025-12-03 04:28 PM

Labels:
  • TAC IA Series
1131 Views
  • « Previous
    • 1
    • …
    • 4
    • 5
    • 6
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore