Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Multi-Purpose Manager (MPM) as a BBMD

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Multi-Purpose Manager (MPM) as a BBMD
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
4456 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Multi-Purpose Manager (MPM) as a BBMD

Picard Product_Support
‎2018-09-11 06:54 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:07 AM

Issue

Will the Multi-Purpose Manager (MPM) act as a BACnet IP BBMD?

 

Product Line

EcoStruxure Building Expert

Environment

Site using BACnet and one or more  SmartStruxe Lite Multi-Purpose Manager (SSL MPM) 

Cause

Can the MPM act as a BBMD

Resolution

The MPM cannot act as a BACnet Broadcast Management Device (BBMD), but it can be a foreign device to another BBMD

BACnet protocol includes broadcast traffic which does not pass through on-site routers. For BACnet devices to network across a wide area or across multiple separate sites connected by the Internet, it is necessary to register the BACnet devices with a Schneider BBMD using the Foreign Device Registration function in Building Expert.

For a Multi-Purpose Manager (MPM) running Building Expert to function as a BACnet device, when being managed remotely over a standard TCP/IP network, it must be configured as a Foreign Device. It must also be registered on an Automation Server (AS) on the remote network that acts as a BBMD. Once done, BACnet devices can send messages to the BBMD, which are translated by the BBMD so they can pass over a standard on-site router. Then BBMD forwards the messages to the appropriate destination MPM controlling the Devices for which the BACnet messages were originally intended. Then the MPM translates the messages received over the network from the BBMD into standard BACnet messages and passes them on to the intended Devices as if they were direct BACnet messages.

This Foreign Device Registration feature allows a single user with a StruxureWare Building Operations (StruxureWare Building Operation) terminal to remotely oversee multiple disparate sites simultaneously using BACnet, without having to install expensive direct connections to each site.

You must have Firmware release version 2.9 or higher installed on your Manager to use Foreign Device Registration function.

Here is the BACnet-Specifications-PIC-Statement.pdf
And the  explanation on how to setup the DR-ForeignDeviceRegistration.pdf

Labels (1)
Labels:
  • EcoStruxure Building Expert
Attachments
Tags (3)
  • Find more articles tagged with:
  • 15607
  • MaximeLaudren22
  • pics
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore