How are the i2/b3920 controllers internal varistors connected to the power input?
  • How are the i2/b3920 controllers internal varistors connected to the power input?
‎2018-09-11 07:48 AM
Last Updated: Crewman ContentModerator ‎2025-08-11 04:08 AM
As part of a site power feed problem investigation where varistors are being blown, how are they connected to the power feed?
i2920, b3920, b4920.
When a site is experiencing power problems and the mains input varistors blow, it is required to know how the damaged varistor is connected.
The 3 varistors are connected between: Live and Earth, Neutral and Earth, Live and Neutral.
The attached sketch shows how  the 3 varistors are connected. The connections are the same for the i2920 and b4920.
  • 16200