How to use the I/A Series R2 (Niagara) WorkPlace Pro to commission LON controllers under an existing LNC-100

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to use the I/A Series R2 (Niagara) WorkPlace Pro to commission LON controllers under an existing LNC-100
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2561 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to use the I/A Series R2 (Niagara) WorkPlace Pro to commission LON controllers under an existing LNC-100

Picard Product_Support
‎2018-09-07 02:36 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:08 AM

Issue

When using the I/A Series R2 (Niagara) WorkPlace Pro to commission LON controllers under an existing LNC-100, configure the Local LON device to match the Domain Length, Domain ID, and Subnet ID programmed in the LNC.

Product Line

TAC IA Series

Environment

  • I/A Series R2 (Niagara) WorkPlace Pro
  • I/A Series Network 8000 LNC-100

Cause

When a third-party network management tool is used to define and commission a LON network, the commissioning tool frequently uses specified domain address instead of the default "zero-length" domain address.  When using the I/A Series (Niagara) R2 WorkPlace Pro to learn a previously commissioned network, Workplace Pro will not be able to discover the LON devices until it has been configured to match the domain address of the network.

Resolution

Click here to see this procedure including screen captures.

  1. If the LNC-100 is already communicating to existing controllers on the LON trunk, document the Domain0, Subnet0, and Node0 addressing in either the SYS:SIM or SYS:SIM2 blocks. You don't need to change the existing address in order to add new LON controllers.
  2. If you will be using Niagara to commission the new LON controllers, set up the LonWorks Service so that the Local LON device is on the same Domain and Subnet as the LNC-100.
    1. Set the Domain length and Domain ID; go to the Properties of the LonWorksService, Netmgmt tab, Engineering tab, domainId, length, domainId.
      For example, if the SYS:SIM block in the LNC-100 has "DOMAIN0=0D, SUBNET0=01,NODE0=120,..."
      then in the UNC, it should be domain length = 1 (byte), and domainId = 0D.
      Apply the changes.
    2. Set the Niagara subnetNodeId properties: subnetId = 01, nodeId = 127.
      The subnet matches SUBNET0 in the SYS:SIM block.
      Leave the Node ID set to 127
      Apply the changes
    3. Recommission the Local Lon Device. (Remember to disconnect the LNC-100 from the trunk before commissioning!)
  3. With the new controllers connected to the LON trunk, go to the Lonworks service, Lon Device Manager, and run the “find” command; the new controllers should be added to the list of nodes. You can use the Lonworks Utilities, command = identify, SubCommand = service pin to be sure you have the correct node. Then commission the new nodes.

Note: Should the LNC-100 be accidentally commissioned, refer to Network 8000 LNC-100 cannot communicate to LON devices under it but can be accessed with WorkPlace T....

Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • 5052
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore