Supported BACnet Variable Objects and Properties for Alarm Monitoring

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Supported BACnet Variable Objects and Properties for Alarm Monitoring
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Katha
    Katha

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
333 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Supported BACnet Variable Objects and Properties for Alarm Monitoring

Lt. Commander Katha Lt. Commander
‎2025-10-22 07:24 PM

on ‎2025-10-22 07:24 PM

Issue

When configuring BACnet alarms in EcoStruxure Building Operation (EBO), users may encounter a potentially misleading message in the Monitored Variable description:

Monitored variable: Choose the method for referencing the property that you want to monitor. Select System reference to define a path-based reference to an object or property that is currently located on the EcoStruxure BMS server.

While technically correct, this statement may cause confusion. It suggests that any object or property on the EBO server can be used as a monitored variable for BACnet alarms. However, only specific BACnet objects and properties are supported for each alarm type.

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxture Building Workstation
  • Bacnet
  • Alarms

Cause

The ambiguity arises from the assumption that all BACnet objects and properties are valid for alarm monitoring. In reality, only a subset is supported depending on the alarm type. Misconfiguration can lead to unexpected behavior or non-functional alarms.

Resolution

To ensure proper configuration, refer to the table below for supported combinations of BACnet objects and properties for each alarm type:

Alarm Type Monitored Variable Object Monitored Variable Property
Change of State BACnet Digital Input Value
BACnet Digital Output Value
BACnet Digital Value Value
BACnet Multistate Input Value
BACnet Multistate Output Value
BACnet Multistate Value Value
Change of Value BACnet Analog Input Value
BACnet Analog Output Value
BACnet Analog Value Value
Floating Limit BACnet Analog Input Value
BACnet Analog Output Value
BACnet Analog Value Value
Floating Limit Setpoint Reference BACnet Analog Input Value
BACnet Analog Output Value
BACnet Analog Value Value
BACnet Loop Setpoint
Out of Range BACnet Analog Input Value
BACnet Analog Output Value
BACnet Analog Value Value
BACnet Digital Input Value
BACnet Digital Output Value
BACnet Digital Value Value
BACnet Multistate Input Value
BACnet Multistate Output Value
BACnet Multistate Value Value
Buffer Ready BACnet Trend Log (Any) —

Additional Reference

For more details, see:
🔗 BACnet Alarm Types and Monitored Variables Table


Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • KatharineVasquez25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore