Migrating Infinet controllers from Continuum to EcoStruxure Building Operation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Migrating Infinet controllers from Continuum to EcoStruxure Building Operation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PeterEdvik
    PeterEdvik
  • Dave_Shore
    Dave_Shore
  • Alan_Wood
    Alan_Wood
  • DavidChild
    DavidChild
  • StephenYang
    StephenYang
  • Ramaaly
    Ramaaly
  • JohnBoehmer
    JohnBoehmer
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
12180 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Migrating Infinet controllers from Continuum to EcoStruxure Building Operation

Picard Product_Support
‎2021-02-19 02:37 AM

Last Updated: Admiral StephenYang Admiral ‎2024-07-19 10:29 AM

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Issue

Finding the correct procedure for migrating Infinet controllers from a Continuum controller fieldbus to an AS-P.

Product Line

Andover Continuum,EcoStruxure Building Operation

Environment

  • Continuum Cyberstation
  • Building Operation Automation Server Premium (1.9 onwards)
  • Building Operation Automation Server Bundled (1.9 onwards)

Cause

The wrong procedure has been followed which is not the approved and tested procedure to be used when migrating Infinet controllers from Continuum to EBO. 

Resolution

Procedure for Converting / Transitioning the Infinet Bus

Prior to migrating the Infinet

  1. The RS-485 network cable should be routed in a continuous daisy chain bus configuration. There should not be any stub connections, stars or ring configurations. The bussed cable should pass through each node to be connected with no splits or branches in the cable network.
    Repeaters can be used to achieve the star, distributed star (backbone with clusters), off of the backbone. For additional information, review the article: EBO Webhelp Cabling
  2. Using the conversion tool and other engineering efforts, create the AS-P database for all Infinet devices, Infinet, Interface items, etc. in either a live AS-P or in the PCT.

At the site

  1. From Continuum CyberStation,  the following must be completed to each Infinet controller that you are moving to an AS-P.
    1. Upgrade all Infinet devices that are going to be converted to the latest firmware version.  Firmware upgrading capability will not be available in EBO until a future release.
    2. Clear the memory of all Infinet devices involved before relocated to the AS-P com port by editing the controller object and selecting Runtime > Reset.
  2. If the conversion was done on the PCT, deploy the AS-P.
  3. Verify that the AS-P firmware is 1.9.0.73 or higher.
  4. Disconnect Infinet bus from the Continuum controller com port(s).
  5. Move the Infinet bus (busses) to the corresponding RS485 port(s) on the AS-P.
  6. Confirm that the Infinet devices are all showing online under the AS-P
  7. Download the Infinet devices. *
  8. Backup all Infinet devices to flash memory.  

*  If the Infinet devices share data with other Infinet devices then it may be necessary to repeat this step in order to establish the complete Import/Export table.

PLEASE NOTE

The above steps are important! If not followed, offline and bus problems can occur.

There may be a desire to skip the rest of the controllers, but the steps must be followed The likelihood is high that there will be substantial difficulties in getting the i2 controllers online and in a stable state to accept the download files.

All of the Infinet controllers must be reset in Continuum before moving the bus to the AS-P.  The controllers should then be backup up to flash memory to ensure that they do not revert to their Continuum configuration following a cold start.

If problems occur that make it necessary to abort the migration process and return the controllers to the Continuum system, all of the Infinet controller must have their memory cleared before re-attaching the bus on the comm port of the original Continuum controller.  For those controllers which have not established communications under the AS-P, this will mean performing a hard reset at the Infinet controller hardware.

At no time should the Infinet bus be connected to the both the AS-P and the Continuum controller at the same time as this  confuses the Infinet controllers causes communications issues that will take some time to resolve.

Please also see the "Infinet under the hood" community post

Continuum Conversion Tool NOTES

V3.0.x and v3.1.x Conversion Tools should not be used. The Workaround is to use the 2.0 Conversion Tool then upgrade. (The Conversion tool was fixed by v3.1.2.6000 (CP5))

V3.2.x onwards the Conversion Tool operates correctly

v4.0.3 has an issue converting Infinet controllers, 4.01 or 4.02 should be used instead

Now fixed in v4.0.3.5005 CP3(Known Issues)

v3.x outperform 4.x, 5.x and 6x.(known Issues). The Workaround is to convert the dmp file in CCT 3.x then upgrade the DB to the expected version in PCT or AS-P.

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Tags (17)
  • Find more articles tagged with:
  • 19074
  • AlanWood23
  • as-p
  • Continuum Conversion Tool
  • conversion
  • DavidChild20
  • DavidShore20
  • DavidShore21
  • DavidShore22
  • DavidShore23
  • infinet
  • migration
  • pct
  • RamaAly23
  • StephenYang23
  • StephenYang24
  • transition
Was this article helpful? Yes No
100% helpful (15/15)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of