Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 9
    • 10
    • 11
    • …
    • 501
  • Next »

Slow Communication Between DMS-3500 and Niagara R2 UNC-520 – Optimization Tips

Issue Communication between a DMS-3500 and a Niagara R2 UNC-520 is slow, causing point updates to occur very slowly. Users need guidance on settings that can be verified and optimized to improve performance. Product Line TAC IA Series Environment Niagara R2 UNC-5x0 DMS-35, DMS-350A, DMS-3500 Cause Several factors can contribute to slow communication: High count of polled objects Lower than optimal baud rate between UNC and DMS Non-optimal settings for the DMS Comm Service Resolution Follow best practices from the DMS Serial Driver Engineering Guide (F-27071). Key recommendations that do not require hardware changes include: Increase Baud Rate Use the maximum allowable baud rate for the DMS serial port (38.4 kbps for DMS-3500). Optimize DmsCommService Settings intermessageDelay = 1500 timeoutHostMsg = 215000 timeoutHostFragment = 110000 maxReadValues = 10 downDeviceRecoveryInterval = 1 maxMultipleMsgs = 3 autoCycleTimeOn = TRUE deltaCycleDifference = 10 deltaCycleChange = 25 globalCycleTime = 15000 Reduce Unnecessary Alarms Disable DMS point alarms that are no longer required from annunciating to the serial port. Optimize Polling Intervals Adjust minimumPollInterval for shadow objects. Example: Space temperature sensors can be set to 30,000–60,000 ms instead of the default 1,000 ms. Limit Poll-Always Points Keep below 600 points if polling at 1,000 ms.
View full article
Picard Product_Support
‎2018-09-06 01:27 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-18 06:33 PM

Labels:
  • TAC IA Series
1359 Views

Resistance Values for EOL Module (RBSC-16) on DMS Microsmart Controller Trunks

Issue The last controller on a Microsmart trunk was removed and discarded without retrieving the End-of-Line (EOL) module. External resistors are needed to temporarily mimic the EOL module for communication stability. Product Line TAC IA Series Environment DMS (all models) Microsmart controller communication trunks Cause During site renovation, the last controller and its EOL module were removed and discarded, leaving the trunk without proper termination. Resolution Using external resistors is not recommended as a permanent solution. However, to stabilize communications until a proper EOL module (RBSC-16) is installed, replicate the following resistance values: Module Type: 8-pin Pin Connections: Pins 1–8: 3.3 kΩ resistor Pins 2–7: No connection Pins 3–6: 150 Ω resistor Pins 4–5: 3.3 kΩ resistor Resistor Specs: ¼ watt, 5% tolerance
View full article
Picard Product_Support
‎2018-09-06 01:11 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-18 06:28 PM

Labels:
  • TAC IA Series
1287 Views

Problem renaming ES or adding SmartX server to ES

Issue When attempting to rename an Enterprise Server (ES) or add a SmartX (Automation) server under an ES, the following error may appear: All subservers must be online at least once before adding (renaming)   Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server – version 2.x and later Cause A mismatch exists between the contents of the MountPoints and Versions folders within the ES database. Although GUID(Globally Unique Identifier)-named pairs may look similar, their contents differ—and cannot just be copied. Resolution Backup: Confirm you have a clean, recent backup of the ES database. Identify unmatched files: Compare the following folders: C:\ProgramData\Schneider Electric EcoStruxure\Building Operation x.x\Enterprise Server\db\System\MountPoints  C:\ProgramData\Schneider Electric EcoStruxure\Building Operation x.x\Enterprise Server\db\System\Versions Delete unmatched versions: In the Versions folder, delete only those GUID-named files that do not have a corresponding file in MountPoints.   Manual comparison required: You must compare GUIDs manually or via script—files can’t be auto-synced.    
View full article
Janeway Jonas_Brissman Janeway
‎2019-06-11 02:10 AM

Last Updated: Commander Hernan_Urueña Commander ‎2025-11-18 05:08 PM

Labels:
  • EcoStruxure Building Operation
2289 Views

Unoccupied Heating Mode Behavior on Type 2 Mode Control in DMS Microsmart

Issue Understanding how unoccupied heating mode operates on a Type 2 Mode Control point in DMS Microsmart. Product Line TAC IA Series Environment DMS Microsmart Cause Perimeter radiation valves remain open or do not adjust correctly during unoccupied periods, causing the space temperature to be too warm when occupancy begins. Resolution The Heat/Cool Differential determines the occupied heating setpoint by subtracting its value from the occupied cooling setpoint. Example: Cooling Setpoint = 74°F Heat/Cool Differential = 4°F → Heating Setpoint = 70°F Night setup values: Cooling Night Setup = 80°F (must be higher than the occupied cooling setpoint) Heating Night Setback = 65°F (must be lower than the occupied heating setpoint) Both night setpoints require a Level 1 STOP command to engage.
View full article
Picard Product_Support
‎2018-09-06 01:03 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-18 04:46 PM

Labels:
  • TAC IA Series
1382 Views

Determine Point Capacity of DMS-3500 on a Live System

Issue How to identify the point capacity of a DMS-3500 controller and verify the actual point count on an active system. Product Line TAC IA Series Environment DMS-3500 Cause When making additions to an existing DMS installation, it is necessary to confirm the remaining point capacity to ensure the system can accommodate additional programming. Resolution   A DMS-3500 supports 250 points maximum. To check the current point count on a live system using OPRIF 11.x: From any screen, press F8 to enter command mode. Type CANCL and press Enter to view the first point in the database. Type PNTID and press Enter to display the first point's name. The three-digit number to the left of the point name should read 001 (first point). Press F5 to display the last point in the system. The three-digit number to the left of the point name indicates the total point count (between 001 and 250).  
View full article
Picard Product_Support
‎2018-09-06 12:55 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-18 04:42 PM

Labels:
  • TAC IA Series
1163 Views

DMS Loop Point Output When Setpoint Equals Process Variable (Proportional-Only Control)

Issue What output does a DMS Loop Point provide when the setpoint and process variable are equal, and only a proportional constant is used? Product Line TAC IA Series Environment DMS control applications using proportional-only loop points Cause When using proportional-only control, the behavior of the loop output at equilibrium (setpoint = process variable) can be unclear, leading to confusion during configuration or troubleshooting. Resolution A proportional-only Loop Point assumes a midrange output when the setpoint and process variable are equal. Midrange means halfway between the loop output high range and low range (typically 100 and 0 respectively). For detailed configuration guidance, refer to DMS Operator Interface User's Guide (F-25467), Chapter 13.
View full article
Picard Product_Support
‎2018-09-06 12:53 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-18 04:39 PM

Labels:
  • TAC IA Series
1432 Views

Ethernet NIM Speed and Duplex Settings for DMS and GCM Modules

Issue What speed and duplex settings do the DMS and GCM Ethernet Network Interface Modules (NIMs) operate at? Product Line TAC IA Series Environment DMS-ETH-001 GCM-ETH-001 Cause Uncertainty about the Ethernet configuration (speed and duplex) can lead to misconfigured switches or network devices, causing communication failures or degraded performance. Resolution Both DMS and GCM Ethernet NIMs comply with the IEEE 802.3 standard as defined in the early 1990s. Port Speed: 10 Mbps Duplex Mode: Half-duplex Ensure that connected network equipment (switches, hubs) is configured to support 10 Mbps half-duplex to maintain reliable communication.
View full article
Picard Product_Support
‎2018-09-06 12:12 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-18 04:27 PM

Labels:
  • TAC IA Series
1234 Views

How to modify a Microsmart point, learned as a Numeric Point, using the Niagara G3 DMS driver.

Issue When Microsmart AP7 (Application Type 7)/Chain Calculation points are learned into Niagara G3 using the DMS driver, they appear as Numeric Points but are not writable. This prevents operators from sending setpoint values to LOOP points in Microsmart controllers. Product Line TAC IA Series Environment Niagara G3 DMS Microsmart Cause AP7 points are learned into the Niagara G3 station as Numeric Points without write capability. These points are not linked to the DMS database, limiting control functionality. Resolution To enable write capability for AP7 points: Locate the AP7 point in Niagara G3. Learn the PVALU element of the AP7 point into the database. Open the Property Sheet of the object and add a Command String. After adding the Command String, an Action option will appear on the Wire Sheet, which can also be transferred to a graphic for operator use.
View full article
Picard Product_Support
‎2018-09-06 12:05 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-18 04:25 PM

Labels:
  • TAC IA Series
1419 Views

Can a DMS-350A Controller Replace a DMS-35 Controller?

Issue Customer needs to replace a failed DMS-35 controller and wants to know if a DMS-350A can be used as a substitute. Product Line TAC IA Series Environment DMS-35 Controller DMS-350A Controller Cause The original DMS-35 controller has failed. Customer has a spare DMS-350A from a previous retrofit project. Resolution Yes, a DMS-350A can replace a DMS-35 controller, provided the following conditions are met: Include at least one DCM MicroSmart controllers connect to the DCM, and the DCM connects to the DMS-350A. Firmware Compatibility Ensure the firmware level in the DMS-350A and DCM matches or exceeds the MicroSmart controllers. Example: If MicroSmart controllers are revision 10.x, then DMS-350A and DCM must be revision 10.x or 11.x. Database Considerations The DMS-35 database cannot be installed directly into a DMS-350A due to DCM requirements. Points in MicroSmart controllers must be re-linked, creating a new database.
View full article
Picard Product_Support
‎2018-09-06 12:06 PM

Last Updated: Administrator CraigEl Administrator ‎2025-11-18 04:24 PM

Labels:
  • TAC IA Series
1193 Views

SAFR Face Scan Works but Fails to Authenticate in EcoStruxure Access Expert

Issue SAFR Face Scan successfully detects faces but does not authenticate users or grant access.        Product Line EcoStruxure Access Expert Environment Access Expert Hosted V3 SAFR Scan Reader using OSDP Cause The default SAFR Scanner Access Feedback Timeout is set to 300 ms, which is too short for proper authentication. In some cases, physical impact during transit may also require light sensor recalibration. Resolution   Access the SAFR Scanner configuration web page and log in. Navigate to System > OSDP settings. Change the Access Feedback Timeout from 300 ms to 1000 ms and click Apply. Test authentication. If issues persist: Perform light sensor calibration (refer to SAFR documentation). SAFR portal: https://safr.com/safr-portal/ (login required)
View full article
Admiral Alan_Wood Admiral
‎2025-11-18 03:26 PM

on ‎2025-11-18 03:26 PM

Labels:
  • EcoStruxure Access Expert
181 Views

Continuum Conversion Tool (CCT) Documentation and Best Practices for Migration to EcoStruxure Building Operation

Issue Guidance is needed for converting Andover Continuum to EcoStruxure Building Operation (EBO) using the Continuum Conversion Tool (CCT), including best practices and troubleshooting tips Product Line EcoStruxure Building Operation Environment Continuum Conversion Tool (CCT) Andover Continuum EcoStruxure Building Operation Cause Although documentation for the Continuum Conversion Tool exists, it is spread across multiple resources and formats (Knowledge Base articles, WebHelp, training materials). This fragmentation can lead to confusion or missed steps during migration. Resolution Refer to the following official resources for detailed guidance: EcoStruxure Building Operation - Technical Reference Guide - Version 6.0 Starts at chapter 214, Page 6312 Andover Continuum to EcoStruxure Building - Frequently Asked Questions - Technology Refresh Training Resource Library: Continuum Transition(Forum) Webhelp: Continuum Conversion Workflow Webhelp: Continuum Conversion Tool Best Practices Perform a Full Backup Back up all Continuum databases and controllers before starting the conversion process. Validate Firmware Compatibility Ensure all Continuum devices are running supported firmware versions prior to migration. Reference:  Continuum Infinet Transition - Make Ready incompatible controllers Conversion of Continuum devices from i2 to b3 Migrating Infinet controllers from Continuum to EBO Change the firmware version in a Continuum controller Continuum Software and Firmware Compatibility Matrix Use a Test Environment First Run the conversion in a non-production environment to identify potential issues before live deployment. Check Naming Conventions Standardize object names in Continuum before conversion to avoid conflicts in EBO. Review Converted Objects After conversion, verify that all points, alarms, and schedules have migrated correctly. Reference: Converting Continuum b3/i2 Tristate outputs to EBO Multistate outputs Document Changes Maintain a detailed record of conversion steps and any manual adjustments for future reference. Plan for Downtime Schedule migration during low-occupancy periods to minimize operational impact. Reference: Andover Continuum Conversion Tool Slow Troubleshooting Common Issues Issue Possible Cause Resolution Conversion Tool Runs Slowly Large database size or insufficient system resources Close other applications, ensure adequate RAM, and run conversion in smaller batches. Missing Objects After Conversion Unsupported object types or naming conflicts Review conversion logs, manually recreate unsupported objects, and standardize names before retrying. Licensing Errors Incorrect EBO license or missing feature Verify EBO license includes Continuum conversion support; update license if needed. Firmware Mismatch Continuum devices not on supported firmware Upgrade firmware to recommended versions before conversion or use Roam I/O to upgrade after conversion. Alarms Not Migrating Correctly Alarm configuration differences between Continuum and EBO Validate alarm mappings post-conversion and adjust manually where necessary.
View full article
Admiral StephenYang Admiral
‎2025-11-18 03:03 PM

on ‎2025-11-18 03:03 PM

Labels:
  • EcoStruxure Building Operation
244 Views

Command Request/Response Window Missing in Niagara G3 DMS Driver

Issue The Command Request / Command Response window is not available when using the Niagara G3 DMS driver. Product Line TAC IA Series Environment Niagara G3 Microsmart driver Cause This feature was present in the Niagara R2 driver but was not carried over to the Niagara G3 driver. Resolution The only available option is to tunnel to the Microsmart controllers using OPRIF for command requests and responses.
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-17 08:01 PM

Labels:
  • TAC IA Series
1258 Views

DMS Panel Serial Port Settings for UltiVist Communication

Issue UltiVist cannot communicate with the DMS panel over a serial connection due to incorrect port settings. Product Line TAC IA Series Environment UltiVist Software DMS Panel Cause The DMS panel’s serial COM port settings were reset to factory defaults, which do not match UltiVist’s required configuration. Resolution Configure the DMS panel’s serial COM port with the following settings to enable communication with UltiVist: Parameter Value Port PORT1 (typically) or PORT2 Baud Rate 9600 Stop Bits 1 Data Bits 7 Parity Even Mode Multi-drop Modem None Note: PORT1 is commonly used for UltiVist connections. Ensure these settings are applied after any factory reset.
View full article
Picard Product_Support
‎2018-09-06 10:55 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-17 07:58 PM

Labels:
  • TAC IA Series
1088 Views

Niagara R2/DMS Integration – Points Not Updating After Database Changes

Issue In a Niagara R2 and DMS integration, some points in the station are not updating after changes to the DMS database. Product Line TAC IA Series Environment Niagara R2 (all versions) DMS (all versions) Cause Controllers and associated DMS points were deleted as part of housekeeping. When points are deleted, added, or re-ordered in the DMS database, the Niagara R2 station does not automatically refresh its point list. Resolution Whenever DMS points are modified or the DMS database is downloaded via OPRIF, perform a re-learn of the DMS panel from the Niagara R2 station: In Niagara Workbench, right-click the DMS container. Select Go > PointListManager. Click GetPointListFromDevice to upload the current DMS database into the station. Important Notes: These steps will not affect existing objects under the specific DMS container. For detailed instructions, refer to the I/A Series Niagara DMS Serial Driver Engineering Guide (F-27071), section “Re-learning The DMS Panel.”
View full article
Picard Product_Support
‎2018-09-06 10:25 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-17 07:54 PM

Labels:
  • TAC IA Series
1294 Views

DMS Ethernet NIM Settings Backup Procedure

Issue Clarification is needed on whether the Ethernet NIM (Network Interface Module) settings are included when performing a DMS database backup. Product Line TAC IA Series Environment DMS-3500 with Ethernet NIM OPRIF 11.4 & 11.6 Cause Backup requirements can be confusing because the DMS database, controller databases, and NIM configuration are stored separately. Users may assume a single backup command covers all components, which is not the case. Resolution A complete DMS backup consists of three steps, all performed using OPRIF: Backup the DMS database Backup each individual MicroSmart controller database Backup Ethernet NIM configuration data separately Important Note: Echelon NIMs do NOT require backup. Ensure all three steps are completed during maintenance to guarantee full system recovery capability.
View full article
Picard Product_Support
‎2018-09-06 10:19 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-17 07:47 PM

Labels:
  • TAC IA Series
1950 Views

MicroSmart Controllers Not Displayed in OPRIF on DMS Jobsite

Issue On a DMS jobsite, the Operator Interface (OPRIF) does not display MicroSmart controllers on the screen. Although multiple controllers are confirmed to be communicating with the DMS, they do not appear in the controller list in OPRIF. Product Line TAC IA Series Environment OPRIF DMS MicroSmart Cause OPRIF displays controllers in groups of 32 per screen and reserves address slots even if they do not exist. If controller addresses start at 33 or higher, the first screen appears blank because it only shows addresses 1–32. Resolution Use the Page Down and Page Up buttons in OPRIF to navigate between controller lists: Page 1: Addresses 1–32 Page 2: Addresses 33–65
View full article
Picard Product_Support
‎2018-09-06 09:50 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-16 08:56 PM

Labels:
  • TAC IA Series
1139 Views

Database Analysis Options for DMS Panels Using OPRIF

Issue A jobsite is visited periodically, and it appears that certain database elements have changed since the previous visit. These elements are not expected to change (unlike setpoints or schedules). The question is whether there is a built-in feature in a DMS panel or the OPRIF programming tool that provides database analysis. Product Line TAC IA Series Environment DMS OPRIF Cause The DMS product does not include built-in database analysis tools. Historically, supervisory computers provided this functionality using tools like UltiVist or SIGNAL, which could analyze databases and save information for future review. Resolution No built-in database analysis feature exists in DMS panels or OPRIF. When only OPRIF is available: Take screenshots of point configuration screens to store values for later comparison. DMS databases are not formatted for offline viewing, so direct comparison between copies is not supported. To compare two database states: Use a second DMS panel as a reference. For advanced analysis, consider using a supervisory computer with compatible tools (e.g., UltiVist, SIGNAL) if available.
View full article
Picard Product_Support
‎2018-09-06 09:45 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-16 08:52 PM

Labels:
  • TAC IA Series
1055 Views

Clear Existing Database from DMS3500 and DMS350A

Issue What is the best way to completely clear an existing database from DMS3500 and DMS350A before reinstalling? Product Line TAC IA Series Environment DMS3500 DMS350A Cause When reinstalling a database, remnants of the previous database may cause conflicts or unexpected behavior. A full hardware-level clear is required to ensure the old database is completely removed. Resolution For DMS3500: Connect via OPRIF and enter Command Mode. Type the command: DBCLR After completion, log back into the DMS3500 and begin the new database installation. For DMS350A: Sign on using the keypad. Enter the command: DBCLR For each connected DCM: Set all 8 toggle switches to ON. Cycle power to the DCM. Wait 10 seconds, then re-address the DCM and cycle power again. Once complete, use OPRIF to start the database installation. Note: The DBCLR command combined with setting toggle switches to ON is considered a hardware-level database clear, ensuring no residual data remains.
View full article
Picard Product_Support
‎2018-09-06 09:43 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-16 08:47 PM

Labels:
  • TAC IA Series
1134 Views

Migration Path for DMS-3500 to Building Operation

Issue Customers need guidance on migrating DMS-3500 systems to the Building Operation platform. Product Line EcoStruxure Building Operation, TAC IA Series Environment DMS-3500 EcoStruxure Building Operation Cause The DMS-3500 system and its databases are not compatible with Building Operation. Schneider Electric does not provide a supported migration path for these legacy systems to Building Operation. Resolution   Direct migration is unsupported. To integrate DMS-3500 data into Building Operation, use a Niagara device as a gateway between the two systems.  
View full article
Picard Product_Support
‎2018-09-06 09:42 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-16 08:40 PM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
1274 Views

How to broadcast a value from one MicroSmart controller to other MicroSmart controllers under the same DMS.

Issue A MicroSmart controller with revision 9 firmware needs to broadcast a point value to other MicroSmart controllers running revision 10 and 11 firmware under the same DMS. The broadcast is not working as expected. Product Line TAC IA Series Environment MicroSmart controllers connected to a DMS Cause Peer-to-peer data sharing was introduced starting with revision 10 MicroSmart firmware. Controllers running revision 9 do not support peer-to-peer communication, so they cannot broadcast or receive values directly. Resolution To enable value sharing: Link the sending point and receiving points to the DMS. Use the sending DMS point in conjunction with the receiving DMS point within the programming logic. The value will then propagate down to the MicroSmart controllers through the DMS.
View full article
Picard Product_Support
‎2018-09-06 09:06 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-16 08:30 PM

Labels:
  • TAC IA Series
1023 Views
  • « Previous
    • 1
    • …
    • 9
    • 10
    • 11
    • …
    • 501
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore