Issue
Set up a two wire LTS80 Lini-Temp sensor on a UC
Product Line
TAC INET
Environment
- UC microcontroller
- LTS80 Lini-Temp sensor
Cause
Conversion coefficients must be set to properly read temperatures.
Resolution
For Fahrenheit: M = 0.4235 B = 32.0 For Centigrade: M= 0.2353 B = 0.0 The sensor's white (WHT) wire ...