Issue
At the completion of the download of a WorkPlace Tech application into an LON controller, the following error window is displayed:
Product Line
TAC IA Series
Environment
- WorkPlace Tech Tool release 5.x.x
- I/A Series MNL Controller application file
Cause
A default nci constant is out of range for its variable type.
Resolution
Verify that all nci values are valid for the SNVT type, re-compile and re-download the application.
The most frequent issue that causes this error is an invalid text string value for a nciLocation SNVT.