Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Configuring a Xenta 527/NPR - Combo

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Configuring a Xenta 527/NPR - Combo
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • sesa139513
    sesa139513
  • Roger_Bently
    Roger_Bently
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5192 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring a Xenta 527/NPR - Combo

Picard Product_Support
‎2018-09-06 03:05 PM

Last Updated: Picard RobertAndriolo Picard ‎2024-12-11 05:50 PM

Issue

Configuring a Xenta 527/NPR - Combo

Product Line

TAC INET

Environment

  • I/NET site with a Xenta 527
  • End of Commercialization of TAC INET Building Management System Products

Cause

How to configure a Xenta 527/NPR - Combo

Resolution

When setting up a Xenta 527 NPR or Combo Unit for the first time, there are six basic steps to commissioning the Xenta 527/NPR-Combo. These steps are described below.

  1. Connect the Xenta 527/NPR-Combo to 24 VAC power.
    Refer to the TAC Xenta 527 Installation Instructions (0FL-3956).
  2. Connect a PC to the Xenta 527/NPR-Combo. Attach a serial cable from the computer’s COM port to the RS-232 B port on the front of the Xenta 527/NPR-Combo. Refer to TAC Xenta 511/527/911/913 Handbook (0-004-7870) for complete instructions.
  3. Set the Xenta 527/NPR-Combo's communication parameters. Start a Hyper Terminal Session on your PC. Once the cable is connected, it will display the 527's default information.
    Note: The factory default login/password is root/root, at the dsh> prompt, type inethost then enter.
  4. Now add your I/NET information for reference host, etc.
  5. Restart the unit, when the "dsh>" prompt appears, type setip then enter this command will let you set its IP address and other basic parameters.
    Note: Refer to TAC Xenta Server Manual - TAC Xenta 527/NPR-Combo Supplement (0-004-7682-1) Chapters 3 & 5 for instructions.
  6. Once completed restart the unit again.
  7. Connect the Xenta 527/NPR-Combo to the Ethernet. Attach the Xenta 527/NPR-Combo to the network at the necessary location. Refer to Chapter 4, “Connecting the Xenta 527/NPR-Combo to your Network.
  8. Now ping the unit through the cmd prompt on your PC to verify that communications is taking place on the Network.
  9. If necessary, load the Xenta 527/NPR-Combo’s software.
    Note: The Xenta 527/NPR-Combo is delivered from the factory with preloaded software. If you need to reload this software, you can download it from the EcoXpert website. Before installing downloaded software, review its release information to verify compatibility with your hardware.
  10. Configure the Xenta 527/NPR-Combo to communicate with I/NET. In order for the Xenta 527/NPR-Combo to communicate with I/NET devices from across an Ethernet, you must first define basic communication parameters.
    Tip: You can now access the I/O configuration editor by opening NP Routers. From the Netplus Router Summary, select the router, modify it, and print the configuration for your records or the customers.

Once these steps are followed, your unit should be online, communicating to the Network, and seeing all your controllers at this site.

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (3)
  • Find more articles tagged with:
  • 2044
  • RobertAndriolo24
  • Xenta 527-NPR
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore