How to use a LTS80 (Lini-Temp) sensor on a 7716 as a two circuit.
  • How to use a LTS80 (Lini-Temp) sensor on a 7716 as a two circuit.
  • RobertAndriolo
    RobertAndriolo
  • sesa139513
    sesa139513
‎2018-09-06 03:18 PM
Last Updated: Picard RobertAndriolo Picard ‎2024-12-12 06:49 PM
How to use an LTS80 (Lini-Temp) sensor on a 7716 as a two-circuit.
TAC INET
I/NET Site
Place a 10K ohm,1/8 watt resistor in the corresponding resistor "A" position.
Jumper J22 to 15V
For Fahrenheit, M = 0.21978, B = -459.6
For Celsius, M = 0.12210, B = -273.0
Using the first input on TB1 as an example, place the white lead of the sensor on terminal 1, place the orange on terminal 3 (+V)
  • TAC INET
Tags (2)
  • 1483
  • RobertAndriolo24